Problem:
The GFDI does not trip when only the PV Array is connected. But it trips as soon as I connect the battery.
Questions:
How do I fix this problem?
System description:
This is a new installation of Flex Power One, with the following key components:
1. MATE3 Serial Number MA1614F0100289
2. Inverter Model VFXR3048E and Serial number VFXR1545F1623283
3. FlexMax 80
4. FlexNet DC
5. Lithium Ion Battery
5.1 Nominal voltage: 48v
5.2 Rated capacity: 100Ah
5.3 Rated reserved energy: 4800Wh
5.4 Standard charging current: 20A
5.5 Standard discharging current: 50A
5.6 Maximum continuous discharging current: 100A
Battery causing the GFDI to trip
-
- Forum Emperor
- Posts: 8024
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: Flexpower Two: (2) FXR3048A-01, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
Honda EU7000is gas fuel generator
Re: Battery causing the GFDI to trip
Just as a general precaution, the charge controller should never be attached to PV without first being attached to the battery, or damage to the unit can result.
Does GFDI trip when the the battery is connected but the PV disconnected?
If no, does it trip when the PV is subsequently connected?
The GFDI is wired to disconnect the charge controller from the battery in the event of a ground fault in the PV array. If it continues to trip when the controller is properly connected: battery first, then PV, look for the ground fault in the array wiring.
Does GFDI trip when the the battery is connected but the PV disconnected?
If no, does it trip when the PV is subsequently connected?
The GFDI is wired to disconnect the charge controller from the battery in the event of a ground fault in the PV array. If it continues to trip when the controller is properly connected: battery first, then PV, look for the ground fault in the array wiring.