My system stopped charging from the AC connect

Discussion about adding energy storage to grid-dependent inverters using OutBack Power technology
Post Reply
Neil
Forum Expert
Posts: 65
Joined: Fri Feb 28, 2014 3:50 pm
My RE system: six 200 watt Silicon Energy Cascade panels
Outback Power Flexpower One system vfx3648
Four 100 amphour batteries sealed
updated to Mate3s

My system stopped charging from the AC connect

Post by Neil »

my system does charge my four 100 AH batteries from my panels.
But recently it stopped charging my batteries from the AC connect . Normally when I would connect the system to AC it will go through it's connect routine . Very soon the inverter's cooling fan will turn on and then the AC will connect and start charging the batteries.

But now it doesn't get past that stage. The fan doesn't come on . I recently had replaced a the inverter's control board and the system WAS charging with
AC. My guess ? Maybe I have to replace the cooling fan ? The inverter DOES make 110 power so the inverter is working

Any thoughts ?
User avatar
Mike Curran
Forum Emperor
Posts: 2767
Joined: Sat Aug 28, 2004 6:28 pm
My RE system: Outback - Garage roof:
- 8 (2x4) Evergreen 180's into one FM80 (2007/2020 - replaced MX60)
- 6 (2×3) ALEO S79-300's into one FM80 (2017)
- 2 grid-tied VFXR3524A-01's series stacked, replaced GVFX's (2020)
- 12 Surrette/Rolls 2V x 1766Ah (2007)
- Hub10.3, Mate3s, FNDC, RTS. Tigo ES maximizers on each PV module.

Westinghouse Solar - Barn roof: (2012)
- 30 (2x15) 235W panels with Enphase M215 microinverters, grid-tied

Outback Skybox - Barn roof: (2019)
- 14 Talesun 275W in series (DC array input to SB inverter/charger)
- 3 SimpliPhi 3.8 batteries, 48V, 225Ah total
- AC coupled input from 14 Talesun 275W, Enphase M215 microinverters

Battery systems operate in grid-tied, net metering w/backup mode
All self-designed and self-installed
Location: Chagrin Falls, Ohio

Re: My system stopped charging from the AC connect

Post by Mike Curran »

When you say "AC" I assume you mean grid. If so, my garage system may be similar to yours. For mine, my inverter will not use the grid to charge unless the battery reaches the refloat or rebulk voltage setpoint(s). It's normal for mine to use my PV to charge the battery every day (I'm grid tied so barring a power outage, my loads are supported by the grid, not the battery), so I'm wondering how you have your system set up so that you're expecting the inverter to do the charging?

Maybe you could explain a bit more about how your system is set up, that would help us help you.
https://ei.tigoenergy.com/p/pZXn7SZQyO45
https://enlighten.enphaseenergy.com/public/systems/Hctc107221
Neil
Forum Expert
Posts: 65
Joined: Fri Feb 28, 2014 3:50 pm
My RE system: six 200 watt Silicon Energy Cascade panels
Outback Power Flexpower One system vfx3648
Four 100 amphour batteries sealed
updated to Mate3s

Re: My system stopped charging from the AC connect

Post by Neil »

Mike Curran wrote: Wed Apr 20, 2022 8:52 am When you say "AC" I assume you mean grid. If so, my garage system may be similar to yours. For mine, my inverter will not use the grid to charge unless the battery reaches the refloat or rebulk voltage setpoint(s). It's normal for mine to use my PV to charge the battery every day (I'm grid tied so barring a power outage, my loads are supported by the grid, not the battery), so I'm wondering how you have your system set up so that you're expecting the inverter to do the charging?

Maybe you could explain a bit more about how your system is set up, that would help us help you.
This system is installed in my box truck. The truck has panels on its' roof. When I say AC I mean connected to grid via a simple long extension cord to my house or any other AC source. I do need to get familiar with any related settings for AC connection as I haven't had time to dive into that yet.. Anyway, AC grid connection is a sometimes thing since my truck sometimes needs grid power to charge the batteries for lack of sun.

As I mentioned before, the batteries do charge from the panels. And the inverter is capable of producing AC output. But when the AC connect switch is open the fan does not come on . The system aborts the connection and then repeatedly tries again to connect but fails at the moment the fan should come on
User avatar
Mike Curran
Forum Emperor
Posts: 2767
Joined: Sat Aug 28, 2004 6:28 pm
My RE system: Outback - Garage roof:
- 8 (2x4) Evergreen 180's into one FM80 (2007/2020 - replaced MX60)
- 6 (2×3) ALEO S79-300's into one FM80 (2017)
- 2 grid-tied VFXR3524A-01's series stacked, replaced GVFX's (2020)
- 12 Surrette/Rolls 2V x 1766Ah (2007)
- Hub10.3, Mate3s, FNDC, RTS. Tigo ES maximizers on each PV module.

Westinghouse Solar - Barn roof: (2012)
- 30 (2x15) 235W panels with Enphase M215 microinverters, grid-tied

Outback Skybox - Barn roof: (2019)
- 14 Talesun 275W in series (DC array input to SB inverter/charger)
- 3 SimpliPhi 3.8 batteries, 48V, 225Ah total
- AC coupled input from 14 Talesun 275W, Enphase M215 microinverters

Battery systems operate in grid-tied, net metering w/backup mode
All self-designed and self-installed
Location: Chagrin Falls, Ohio

Re: My system stopped charging from the AC connect

Post by Mike Curran »

As I mentioned before, the batteries do charge from the panels. And the inverter is capable of producing AC output. But when the AC connect switch is open the fan does not come on . The system aborts the connection and then repeatedly tries again to connect but fails at the moment the fan should come on
Okay, makes a bit more sense now.

However, "when the AC connect switch is open" sounds (to me, anyway) like that's when you're on battery power. An open switch means no connection. Is that what you mean?

Also, "the system aborts the connection" - what exactly is happening? What indication do you have?

Finally, "repeatedly tries again to connect but fails at the moment the fan should come on" - again, what exactly are you seeing?
https://ei.tigoenergy.com/p/pZXn7SZQyO45
https://enlighten.enphaseenergy.com/public/systems/Hctc107221
Neil
Forum Expert
Posts: 65
Joined: Fri Feb 28, 2014 3:50 pm
My RE system: six 200 watt Silicon Energy Cascade panels
Outback Power Flexpower One system vfx3648
Four 100 amphour batteries sealed
updated to Mate3s

Re: My system stopped charging from the AC connect

Post by Neil »

Mike Curran wrote: Wed Apr 20, 2022 9:33 am
As I mentioned before, the batteries do charge from the panels. And the inverter is capable of producing AC output. But when the AC connect switch is open the fan does not come on . The system aborts the connection and then repeatedly tries again to connect but fails at the moment the fan should come on
Okay, makes a bit more sense now.

However, "when the AC connect switch is open" sounds (to me, anyway) like that's when you're on battery power. An open switch means no connection. Is that what you mean?

Also, "the system aborts the connection" - what exactly is happening? What indication do you have?

Finally, "repeatedly tries again to connect but fails at the moment the fan should come on" - again, what exactly are you seeing?
Thanks for trying even though I haven't described things very well ..

Sorry I meant the AC connect switch is turned ON or it is connecting AC to my Outback

By abort I mean the system looks like it is trying to connect AC but then starts the process over .. A red light briefly goes on then off at the bottom of the vertical row of LED indicators that visually let us know what the status iof things is straight above the inverter .
raysun
Forum Emperor
Posts: 7742
Joined: Tue Jul 26, 2016 5:57 am
My RE system: Flexpower Two: (2) FXR3048A-01, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
Honda EU7000is gas fuel generator

Re: My system stopped charging from the AC connect

Post by raysun »

Are there any event messages on the Mate?
User avatar
EA6LE-ONE
Forum Czar
Posts: 788
Joined: Tue May 05, 2020 7:51 am
My RE system: System 1:
MATE3s, 3 x Radian GS8048A,
6 x FLEXmax 100, HUB10,
2 x EnergyCell 48V 2700RE,
1 x FLEXnet DC, 6 x FLEXware ICS Plus,
78 x PANASONIC VBHN325SA17 325W

System 2:
MATE3s, Radian GS8048A,
2 x FLEXmax 100, HUB10
1 x EnergyCell 48V 2700RE,
1 x FLEXnet DC, 2 x FLEXware ICS
21 x PANASONIC VBHN325SA17 325W
Location: Providenciales, Turks & Caicos Isl.

Re: My system stopped charging from the AC connect

Post by EA6LE-ONE »

Neil wrote: Wed Apr 20, 2022 9:10 am When I say AC I mean connected to grid via a simple long extension cord to my house or any other AC source.
Maybe the cord is damaged, not the correct gauge for the length and you have a big dip in voltage or reversed polarity.
Neil
Forum Expert
Posts: 65
Joined: Fri Feb 28, 2014 3:50 pm
My RE system: six 200 watt Silicon Energy Cascade panels
Outback Power Flexpower One system vfx3648
Four 100 amphour batteries sealed
updated to Mate3s

Re: My system stopped charging from the AC connect

Post by Neil »

EA6LE-ONE wrote: Thu Apr 21, 2022 7:13 pm
Neil wrote: Wed Apr 20, 2022 9:10 am When I say AC I mean connected to grid via a simple long extension cord to my house or any other AC source.
Maybe the cord is damaged, not the correct gauge for the length and you have a big dip in voltage or reversed polarity.
My chord is plenty heavy duty and I've had it in use for years
Neil
Forum Expert
Posts: 65
Joined: Fri Feb 28, 2014 3:50 pm
My RE system: six 200 watt Silicon Energy Cascade panels
Outback Power Flexpower One system vfx3648
Four 100 amphour batteries sealed
updated to Mate3s

Re: My system stopped charging from the AC connect

Post by Neil »

raysun wrote: Thu Apr 21, 2022 3:08 pm Are there any event messages on the Mate?
I don't think there are but I'll try connecting again and see if any are generated
Neil
Forum Expert
Posts: 65
Joined: Fri Feb 28, 2014 3:50 pm
My RE system: six 200 watt Silicon Energy Cascade panels
Outback Power Flexpower One system vfx3648
Four 100 amphour batteries sealed
updated to Mate3s

Re: My system stopped charging from the AC connect

Post by Neil »

It stopped connecting to my AC because my physical connection to AC was faulty . I solved that and the vfx3648 is connecting to AC again . yay