Bypass Battery Temperature Sensor and TempComp on Flexmax 100 afci

Post by mattyxp@yahoo.com »

Hi All,

If you have a Mate3s and Flexmax 100 charge controllers and need to bypass the Battery Temperature Sensor (BTS) and Battery Charging Temperature Compensation for any reason and unplugging the BTS sensor from the Flexmax 100 BTS port/jack does not work to turn off the battery temperature reading on the Mate3s, then here is how to fake out the Mate3s correctly and easily so that the Flexmax 100 battery charging temperature compensation is effectively turned off:

***I had to do this because even with my BTS sensor unplugged from the Flexmax 100 BTS port/jack, my Mate3s still was reading/detecting "ghost" temperature signals between 32 degrees F and 450 degrees F even with the BTS sensor unplugged, which Outback can not explain and/or is not willing to fix with a way to permanently disable battery charging temperature compensation for those of us using lithium batteries who obviously need to disable battery charging temperature compensation.

***You'll need to purchase a RJ11 Screw Terminal...I purchased this one that worked great from Amazon:
https://www.amazon.com/AAOTOKK-Terminal ... 886&sr=8-1

- The Battery Temperature Sensor (BTS) ohms at 10,120ohms when the temperature is at 25 degrees Celsius (77 degrees Fahrenheit).
- Pins 1 & 2 and pins 3 &4 are tied together on the BTS sensor port/jack of the Flexmax 100 charge controller.
- Simply solder a 10kohm resistor and a 120ohm resistor together in series and then put one leg in either pin 1 or 2 and put the other leg in either pin 3 or 4 of the RJ11 Screw Terminal. I used 1w resistors but understand that any watt resistor is fine. Make sure to cover any metal on the exposed resistors with electrical tape to prevent any shorting, etc.
- Plug the RJ11 Screw Terminal with the resistors attached into the BTS port/jack in one of the Flexmax 100 charge controllers.
- That's it and the Mate3s will now read a constant 25 degrees Celsius (77 degrees Fahrenheit).
- With the Mate3s now reading a constant/steady 25 degrees Celsius from the BTS port/jack on one of the Flexmax 100 charge controllers, the Flexmax 100 battery charging temperature compensation will be effectively disabled. This is perfect for lithium battery charging with no battery charging temperature compensation.

For my Simpliphi 48v 3.8kwh lithium batteries, I have set the FLexmax 100 Battery Charging Temperature Compensation settings as follows:
Battery Temp Comp Range: Limited (until Outback Power makes way to turn off Temp Comp completely)
Limited: Lower Battery Voltage: 54 VDC (Charge Controller Float setting)
Limited: Upper Battery Voltage: 56 VDC (Inverter Absorb setting...charge controller setting will be .4v higher)
Temperature Comp Slope: 2 mV/C (set to lowest until Outback Power makes turning
off Temp Comp possible, set to 0 if ever possible)

So, with the BTS sensor port on the Flexmax 100 charge controller always being at a steady 25 degree Celsius, the battery charging temperature compensation will always be automatically offset by 0v...perfect for lithium battery charging...effectively no battery charging temperature compensation.

I hope this helps anyone who needs a way around this stupid issue that could be easily fixed by Outback just having an actual on/off setting for battery charging temperature compensation for all of us using lithium batteries with our systems.

Matt :)
Last edited by mattyxp@yahoo.com on Sun Apr 04, 2021 10:02 am, edited 1 time in total.
fcwlp
Forum Czar
Posts: 995
Joined: Wed Jan 22, 2020 9:40 am
My RE system: GS8048A, FM80 w/3,600W PV Fixed, FM80 w/2,700W on Zomeworks tracker, Mate3, 24 Trojan 2V L16 1100AH @ C20, Grid-Tied with Kohler 14RESA LPG Generator and MEP-803 Diesel if needed.

I install and maintain grid-tied and off-grid systems in my area and consult on solar system design/operation.
Location: 80 miles NE of Phoenix at 5500'

Re: Bypass Battery Temperature Sensor and TempComp on Flexmax 100 afci

Post by fcwlp »

Thanks for documenting the work around.
User avatar
sodamo
Forum Emperor
Posts: 1279
Joined: Mon Apr 03, 2006 1:55 am
My RE system: Totally off grid - Hamakua side, Big Island, Hi

36 Trina 280 & 16 Phono 250 in 48 volt array (fixed) 14080w
Radians GG8048A/GS4048A w GSLCs
4 FM 80 charge controllers
Hub 10.3
FNDC w/3 shunts
Mate 3s
OpticsRE - MMKL - Ninole Hi
12 SimpliPhi 3.8
14Kw Kohler 14RESA Propane

Charging Only
2FX3048T
Hub
FNDC. - shared shunt feeds from Radian FNDC
Mate 3s
10Kw MEP 803a Military gen

Honda EU7000i

Davis VantagePro2 Wx Station
On line at: https://www.wunderground.com/dashboard/pws/KHININOL2
Location: Ninole, Hi

Re: Bypass Battery Temperature Sensor and TempComp on Flexmax 100 afci

Post by sodamo »

So would this work with other components?
David
User avatar
Mike Curran
Forum Emperor
Posts: 2769
Joined: Sat Aug 28, 2004 6:28 pm
My RE system: Outback - Garage roof:
- 8 (2x4) Evergreen 180's into one FM80 (2007/2020 - replaced MX60)
- 6 (2×3) ALEO S79-300's into one FM80 (2017)
- 2 grid-tied VFXR3524A-01's series stacked, replaced GVFX's (2020)
- 12 Surrette/Rolls 2V x 1766Ah (2007)
- Hub10.3, Mate3s, FNDC, RTS. Tigo ES maximizers on each PV module.

Westinghouse Solar - Barn roof: (2012)
- 30 (2x15) 235W panels with Enphase M215 microinverters, grid-tied

Outback Skybox - Barn roof: (2019)
- 14 Talesun 275W in series (DC array input to SB inverter/charger)
- 3 SimpliPhi 3.8 batteries, 48V, 225Ah total
- AC coupled input from 14 Talesun 275W, Enphase M215 microinverters

Battery systems operate in grid-tied, net metering w/backup mode
All self-designed and self-installed
Location: Chagrin Falls, Ohio

Re: Bypass Battery Temperature Sensor and TempComp on Flexmax 100 afci

Post by Mike Curran »

sodamo wrote: Sat Apr 03, 2021 2:40 am So would this work with other components?
Yes - all the RTS is, is a thermistor, a component whose resistance changes with temperature. Any Outback component that accepts an RTS input will see this hack as if it were reading a constant 25°C.

PS When I first read the OP, I was surprised the FM100 cannot accept a temperature compensation slope less than 2 mV/°C, because Skybox does accept 0 mV/°C. In fact, without reading the post thoroughly, I'd initially drafted a response saying just set the slope to 0, but re-reading it discovered that was already tried and not possible. With Skybox it's convenient to be able to do this if you still want to track your lithium battery temperature without temperature-biasing the charging voltage .
https://ei.tigoenergy.com/p/pZXn7SZQyO45
https://enlighten.enphaseenergy.com/public/systems/Hctc107221
raysun
Forum Emperor
Posts: 7748
Joined: Tue Jul 26, 2016 5:57 am
My RE system: Flexpower Two: (2) FXR3048A-01, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
Honda EU7000is gas fuel generator

Re: Bypass Battery Temperature Sensor and TempComp on Flexmax 100 afci

Post by raysun »

I'd suggest using precision wire wound resistors instead of carbon or foil units. They will have more stability long term. Also, might want to take a peek at the resistors temperature coefficient to make sure you're not inadvertently creating a thermistor all over again.
santafedave
Forum Virtuoso
Posts: 89
Joined: Sat Dec 05, 2020 8:05 pm
My RE system: GS8048-A-300AFCI 8 KW 48V Mate3s with 2 FM100 charge controllers pre wired.
21 Canadian Solar 320 Watt PERC MC4 CS3K-320MS panels.
3 Canadian Solar 325W Module Mono Perc 1000VDC panels.
8 FullRiver AGM DC400-6 Sealed Batteries 415AH 6V L16 size.
Fireraptor quick disconnect.

Re: Bypass Battery Temperature Sensor and TempComp on Flexmax 100 afci

Post by santafedave »

Afternoon Mattyxp. I am having problems with my RTS on my radian system. I put together the hack you posted here and I was wondering if you are able to read the temp on the dashboard of the OpticsRE screen. I have attached a screen shot of my screen and I don't have a temp readout anymore.
RTS hack opticre screen showing no temps.png
santafedave
Forum Virtuoso
Posts: 89
Joined: Sat Dec 05, 2020 8:05 pm
My RE system: GS8048-A-300AFCI 8 KW 48V Mate3s with 2 FM100 charge controllers pre wired.
21 Canadian Solar 320 Watt PERC MC4 CS3K-320MS panels.
3 Canadian Solar 325W Module Mono Perc 1000VDC panels.
8 FullRiver AGM DC400-6 Sealed Batteries 415AH 6V L16 size.
Fireraptor quick disconnect.

Re: Bypass Battery Temperature Sensor and TempComp on Flexmax 100 afci

Post by santafedave »

Here is a screen shot when I unplugged the RTS from the radian. Showing a unbelievable temp.
Temps when RTS is unplugged from Radian.png
mattyxp@yahoo.com
Forum Member
Posts: 24
Joined: Sun Jan 17, 2021 12:11 pm
My RE system: Mate3s
VFX3648 x2 units master/slave setup w/ PSX-240 Transformer
Flexmax100 afci x 2 units
Flexnet DC
HUB10 port hub
32 REC360aa alpha solar panels with total wattage of 11,520w
20kw Perkins diesel backup generator

Re: Bypass Battery Temperature Sensor and TempComp on Flexmax 100 afci

Post by mattyxp@yahoo.com »

Hi Santafedave,
My OpticsRE shows the 77degree temp under the battery voltage in the upper right Power Flow chart and I can also see the 77degree flat line steady temp on the hourly chart if I select the "F" option from the far right drop down tab in the hourly chart.
Your inverter is a different model than mine so maybe that causes OpticsRE to display the temps differently...I don't know.
I also see your temp fluctuating in your screenshot. My hack does not allow for any temperature fluctuation so either you didn't implement the temp hack or maybe you disabled it completely for the entire day shown in your screenshot...ya got me kinda confused here.
I am using a Mate3S that is has its firmware up to date.
I am not grid tied and I see that you are grid tied...not sure if this would cause any differences in our OpticsRE displays.
You can also look at the temp directly on the Mate3S unit.
I also see that you are using FullRiver AGM batteries...when they die early which mine did, get a warranty refund (like pulling teeth but possible) and get lithium batteries...so much better.
Have you already replaced the RTS with a new unit to eliminate that potentially being the cause of your ghost extreme temps?
The "ghost" extreme temp fluctuations you are getting are similar to what I was seeing with my system. Outback could never figure out what was causing them and just blamed it on "random signals" of some sort that was not their problem.
My hack will stop the issue by forcing 77 degree temp at all times, but then your temp comp won't work with your AGM batteries...but this is better than the huge temp comp that the false extreme temps will cause.
Or Outback could get off its ass and just put in a temp comp slope setting option of 0 in our inverter settings and this would fix the problem the right way...but that won't happen, Outback has flat out refused to fix their ghost extreme temp problem.
Hope this helps...
Matt :)
santafedave
Forum Virtuoso
Posts: 89
Joined: Sat Dec 05, 2020 8:05 pm
My RE system: GS8048-A-300AFCI 8 KW 48V Mate3s with 2 FM100 charge controllers pre wired.
21 Canadian Solar 320 Watt PERC MC4 CS3K-320MS panels.
3 Canadian Solar 325W Module Mono Perc 1000VDC panels.
8 FullRiver AGM DC400-6 Sealed Batteries 415AH 6V L16 size.
Fireraptor quick disconnect.

Re: Bypass Battery Temperature Sensor and TempComp on Flexmax 100 afci

Post by santafedave »

Thanks for the update Mattyxp. I did replace the RTS with a new unit and that didn't work. I also worked with Unbound Solar my supplier of the solar system. I had the tech on the phone and he was logged into my OpticsRE and I showed him what happens when the temps get above 86.9 degrees. We went thru a few steps like unplugging the RTS and checking the temps thru Optics. I then put the RTS gauge into a bag with cold packs in it and after the temps went below 86.9 bam the system started producing and selling to the grid again. After that I ordered the new RTS and that still didn't work. I am resigned to using the mini fridge that I bought during the summer months. I don't have problems with the system during the winter time because the temps don't go above 86.9. I have my system inside my well shed so they are out of the elements. I am going to try your hack again this next spring and try and see if that works. You plug yours directly into the CC port and I am plugging mine into the Inverter Radian port so maybe that is the difference. I am saving my aluminum cans and plastic bottles so I can get me some Lithium! Hopefully the price comes down a little! Thanks again for posting your info here it really helps out! D.
FlyingDiscHawaii
Forum Whiz
Posts: 44
Joined: Wed Sep 02, 2015 3:27 pm
My RE system: PV panels:
Kyocera 120- 120 watt max - (x12)
2 strings of 6 - (36 cell units ? or watt?)
combiner in the E-panel / what breakers? - 15 AMP DC

Charge Controller:
OutBack FlexMax - 80 amp max

Batteries:
Hawker 2 volt used submarine batteries

Inverter:
OutBack FX2524 - sealed unit

OutBack Mate 2 Controller - no hub

Generator:
Honda EU3000is - not working under load
we now use that little Ryobi

Remainder of system:
Midnite Solar e-Panel thingy ..
looking for a desulfator - is this neccessary?
Location: Puna, Big Island of Hawai'i
Contact:

Re: Bypass Battery Temperature Sensor and TempComp on Flexmax 100 afci

Post by FlyingDiscHawaii »

Has this been fixed for 2022?

Just wondering if I should consider the FlexMax 1000.
santafedave
Forum Virtuoso
Posts: 89
Joined: Sat Dec 05, 2020 8:05 pm
My RE system: GS8048-A-300AFCI 8 KW 48V Mate3s with 2 FM100 charge controllers pre wired.
21 Canadian Solar 320 Watt PERC MC4 CS3K-320MS panels.
3 Canadian Solar 325W Module Mono Perc 1000VDC panels.
8 FullRiver AGM DC400-6 Sealed Batteries 415AH 6V L16 size.
Fireraptor quick disconnect.

Re: Bypass Battery Temperature Sensor and TempComp on Flexmax 100 afci

Post by santafedave »

We are gonna get our first 90 degree day tomorrow and I am waiting to see if the inverter compensates for the temp increase above 86 degrees. Everything is working at this moment in time, but, if the inverter stops selling to the grid back into the fridge the temp sensor goes!
santafedave
Forum Virtuoso
Posts: 89
Joined: Sat Dec 05, 2020 8:05 pm
My RE system: GS8048-A-300AFCI 8 KW 48V Mate3s with 2 FM100 charge controllers pre wired.
21 Canadian Solar 320 Watt PERC MC4 CS3K-320MS panels.
3 Canadian Solar 325W Module Mono Perc 1000VDC panels.
8 FullRiver AGM DC400-6 Sealed Batteries 415AH 6V L16 size.
Fireraptor quick disconnect.

Re: Bypass Battery Temperature Sensor and TempComp on Flexmax 100 afci

Post by santafedave »

Inverter RTS reads 87.3 degrees today and no problems with the Grid/Sell. Will wait and see when the temps his 100 in June, but, maybe the firmware update to 1.4.7 helped. On an off topic I just read and article about renewables and what they said was interesting:

According to a 2020 report by the Financial Times, “wind and solar are intrinsically deflationary, whereas fossil fuels are intrinsically inflationary.” The economics of renewables and fossil fuels are profoundly different. While fossil fuels require continued inversions of cash to keep exploring for new resources and drilling new wells, renewable resources operate on simple economies of scale. “You simply have to build the infrastructure in the right place to capture the energy that is already there and that is freely available once that has been built,” writes FT. And as technology improves and economies of scale kick in, “capital-investment costs fall dramatically over time while the short-run marginal cost of production is zero.”

This makes sense and the long term costs of solar are already baked into the upfront costs to get up and running!
User avatar
Mike Curran
Forum Emperor
Posts: 2769
Joined: Sat Aug 28, 2004 6:28 pm
My RE system: Outback - Garage roof:
- 8 (2x4) Evergreen 180's into one FM80 (2007/2020 - replaced MX60)
- 6 (2×3) ALEO S79-300's into one FM80 (2017)
- 2 grid-tied VFXR3524A-01's series stacked, replaced GVFX's (2020)
- 12 Surrette/Rolls 2V x 1766Ah (2007)
- Hub10.3, Mate3s, FNDC, RTS. Tigo ES maximizers on each PV module.

Westinghouse Solar - Barn roof: (2012)
- 30 (2x15) 235W panels with Enphase M215 microinverters, grid-tied

Outback Skybox - Barn roof: (2019)
- 14 Talesun 275W in series (DC array input to SB inverter/charger)
- 3 SimpliPhi 3.8 batteries, 48V, 225Ah total
- AC coupled input from 14 Talesun 275W, Enphase M215 microinverters

Battery systems operate in grid-tied, net metering w/backup mode
All self-designed and self-installed
Location: Chagrin Falls, Ohio

Re: Bypass Battery Temperature Sensor and TempComp on Flexmax 100 afci

Post by Mike Curran »

santafedave wrote: Sun Nov 07, 2021 8:02 amYou plug yours directly into the CC port and I am plugging mine into the Inverter Radian port so maybe that is the difference.
Per the Flexmax_100_afci manual:
Screenshot_20220323-132448_Adobe Acrobat.jpg
https://outbackpower.com/downloads/docu ... manual.pdf
https://ei.tigoenergy.com/p/pZXn7SZQyO45
https://enlighten.enphaseenergy.com/public/systems/Hctc107221
santafedave
Forum Virtuoso
Posts: 89
Joined: Sat Dec 05, 2020 8:05 pm
My RE system: GS8048-A-300AFCI 8 KW 48V Mate3s with 2 FM100 charge controllers pre wired.
21 Canadian Solar 320 Watt PERC MC4 CS3K-320MS panels.
3 Canadian Solar 325W Module Mono Perc 1000VDC panels.
8 FullRiver AGM DC400-6 Sealed Batteries 415AH 6V L16 size.
Fireraptor quick disconnect.

Re: Bypass Battery Temperature Sensor and TempComp on Flexmax 100 afci

Post by santafedave »

Thanks for the reply Mike. So I should plug the RTS into my master CC 9 instead if the inverter? I would use the extra port on the CC for this plug? Thanks, David.
User avatar
Mike Curran
Forum Emperor
Posts: 2769
Joined: Sat Aug 28, 2004 6:28 pm
My RE system: Outback - Garage roof:
- 8 (2x4) Evergreen 180's into one FM80 (2007/2020 - replaced MX60)
- 6 (2×3) ALEO S79-300's into one FM80 (2017)
- 2 grid-tied VFXR3524A-01's series stacked, replaced GVFX's (2020)
- 12 Surrette/Rolls 2V x 1766Ah (2007)
- Hub10.3, Mate3s, FNDC, RTS. Tigo ES maximizers on each PV module.

Westinghouse Solar - Barn roof: (2012)
- 30 (2x15) 235W panels with Enphase M215 microinverters, grid-tied

Outback Skybox - Barn roof: (2019)
- 14 Talesun 275W in series (DC array input to SB inverter/charger)
- 3 SimpliPhi 3.8 batteries, 48V, 225Ah total
- AC coupled input from 14 Talesun 275W, Enphase M215 microinverters

Battery systems operate in grid-tied, net metering w/backup mode
All self-designed and self-installed
Location: Chagrin Falls, Ohio

Re: Bypass Battery Temperature Sensor and TempComp on Flexmax 100 afci

Post by Mike Curran »

santafedave wrote: Thu Mar 24, 2022 7:57 am Thanks for the reply Mike. So I should plug the RTS into my master CC 9 instead if the inverter? I would use the extra port on the CC for this plug? Thanks, David.
I'd check the details in the manual David. I'm not really familiar with the FM100 (extra port?). All I know is it says your RTS should be plugged into your FM100. If you have 2 I'd assume that'd be the master, if there is such a thing for FM100s.
https://ei.tigoenergy.com/p/pZXn7SZQyO45
https://enlighten.enphaseenergy.com/public/systems/Hctc107221
santafedave
Forum Virtuoso
Posts: 89
Joined: Sat Dec 05, 2020 8:05 pm
My RE system: GS8048-A-300AFCI 8 KW 48V Mate3s with 2 FM100 charge controllers pre wired.
21 Canadian Solar 320 Watt PERC MC4 CS3K-320MS panels.
3 Canadian Solar 325W Module Mono Perc 1000VDC panels.
8 FullRiver AGM DC400-6 Sealed Batteries 415AH 6V L16 size.
Fireraptor quick disconnect.

Re: Bypass Battery Temperature Sensor and TempComp on Flexmax 100 afci

Post by santafedave »

Morning. Here is and update for my RTS. I tightened all battery posts to specs and tightened the 175 amp breaker battery contacts. I also noticed after installing update 1.4.7 that my inverter is showing different values per battery temp's on my system. Attached is a pic of my inverter status as of this am. Also wondering what the GT number value means? It changes values and I tried looking this reading up on the manual and OpticsRE page and found no reference?
Inverter Status RTS 040322.png
raysun
Forum Emperor
Posts: 7748
Joined: Tue Jul 26, 2016 5:57 am
My RE system: Flexpower Two: (2) FXR3048A-01, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
Honda EU7000is gas fuel generator

Re: Bypass Battery Temperature Sensor and TempComp on Flexmax 100 afci

Post by raysun »

santafedave
Forum Virtuoso
Posts: 89
Joined: Sat Dec 05, 2020 8:05 pm
My RE system: GS8048-A-300AFCI 8 KW 48V Mate3s with 2 FM100 charge controllers pre wired.
21 Canadian Solar 320 Watt PERC MC4 CS3K-320MS panels.
3 Canadian Solar 325W Module Mono Perc 1000VDC panels.
8 FullRiver AGM DC400-6 Sealed Batteries 415AH 6V L16 size.
Fireraptor quick disconnect.

Re: Bypass Battery Temperature Sensor and TempComp on Flexmax 100 afci

Post by santafedave »

Thanks Raysun! Sometimes I think I need to go back to university and get a degree in electrical engineering to understand some of the settings on the Radian!
raysun
Forum Emperor
Posts: 7748
Joined: Tue Jul 26, 2016 5:57 am
My RE system: Flexpower Two: (2) FXR3048A-01, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
Honda EU7000is gas fuel generator

Re: Bypass Battery Temperature Sensor and TempComp on Flexmax 100 afci

Post by raysun »

There's a lot of stuff going on in these systems. I'm thankful I don't need to understand it all to use it all.
santafedave
Forum Virtuoso
Posts: 89
Joined: Sat Dec 05, 2020 8:05 pm
My RE system: GS8048-A-300AFCI 8 KW 48V Mate3s with 2 FM100 charge controllers pre wired.
21 Canadian Solar 320 Watt PERC MC4 CS3K-320MS panels.
3 Canadian Solar 325W Module Mono Perc 1000VDC panels.
8 FullRiver AGM DC400-6 Sealed Batteries 415AH 6V L16 size.
Fireraptor quick disconnect.

Re: Bypass Battery Temperature Sensor and TempComp on Flexmax 100 afci

Post by santafedave »

Well the radian did it again. Temps hit 87.8 degrees and this happened:
RTS shut off at 87.8 degrees 040722.png
santafedave
Forum Virtuoso
Posts: 89
Joined: Sat Dec 05, 2020 8:05 pm
My RE system: GS8048-A-300AFCI 8 KW 48V Mate3s with 2 FM100 charge controllers pre wired.
21 Canadian Solar 320 Watt PERC MC4 CS3K-320MS panels.
3 Canadian Solar 325W Module Mono Perc 1000VDC panels.
8 FullRiver AGM DC400-6 Sealed Batteries 415AH 6V L16 size.
Fireraptor quick disconnect.

Re: Bypass Battery Temperature Sensor and TempComp on Flexmax 100 afci

Post by santafedave »

Here is a screen shot of the status page on the radian:
GS8048A Status Screen showing TCTV's and Battery V with GT number at 255.png
santafedave
Forum Virtuoso
Posts: 89
Joined: Sat Dec 05, 2020 8:05 pm
My RE system: GS8048-A-300AFCI 8 KW 48V Mate3s with 2 FM100 charge controllers pre wired.
21 Canadian Solar 320 Watt PERC MC4 CS3K-320MS panels.
3 Canadian Solar 325W Module Mono Perc 1000VDC panels.
8 FullRiver AGM DC400-6 Sealed Batteries 415AH 6V L16 size.
Fireraptor quick disconnect.

Re: Bypass Battery Temperature Sensor and TempComp on Flexmax 100 afci

Post by santafedave »

CC settings for the FM-100's 040822.png
So the 8048 did it again today when temps hit 87.8 degrees F. What is wrong with my inverter? Attached is the status with the GT number at 4 and I watched it decline from 74 on down? Anybody have any ideas about this issue? I can't unplug the RTS because I get false 400 degree readings on the inverter? I tried using the hack and that didn't work either. I know that my system is supposed to work on hot summer days and when I put the RTS in a mini fridge and cool it off my system starts selling back to the grid again!
Offsetting not selling GT number 4 040822.png
santafedave
Forum Virtuoso
Posts: 89
Joined: Sat Dec 05, 2020 8:05 pm
My RE system: GS8048-A-300AFCI 8 KW 48V Mate3s with 2 FM100 charge controllers pre wired.
21 Canadian Solar 320 Watt PERC MC4 CS3K-320MS panels.
3 Canadian Solar 325W Module Mono Perc 1000VDC panels.
8 FullRiver AGM DC400-6 Sealed Batteries 415AH 6V L16 size.
Fireraptor quick disconnect.

Re: Bypass Battery Temperature Sensor and TempComp on Flexmax 100 afci

Post by santafedave »

Here is a screen shot of the 8048 working as it is supposed to. What settings are wrong on my inverter? Last year I spent and hour with the rep from Unbound Solar and we could not figure out the problem. Do you all think that the circuit board might be bad? Is there a phone number I can call to reach someone at Outback and discuss this with? Thanks.
Back to selling after reducing temps .png
User avatar
Mike Curran
Forum Emperor
Posts: 2769
Joined: Sat Aug 28, 2004 6:28 pm
My RE system: Outback - Garage roof:
- 8 (2x4) Evergreen 180's into one FM80 (2007/2020 - replaced MX60)
- 6 (2×3) ALEO S79-300's into one FM80 (2017)
- 2 grid-tied VFXR3524A-01's series stacked, replaced GVFX's (2020)
- 12 Surrette/Rolls 2V x 1766Ah (2007)
- Hub10.3, Mate3s, FNDC, RTS. Tigo ES maximizers on each PV module.

Westinghouse Solar - Barn roof: (2012)
- 30 (2x15) 235W panels with Enphase M215 microinverters, grid-tied

Outback Skybox - Barn roof: (2019)
- 14 Talesun 275W in series (DC array input to SB inverter/charger)
- 3 SimpliPhi 3.8 batteries, 48V, 225Ah total
- AC coupled input from 14 Talesun 275W, Enphase M215 microinverters

Battery systems operate in grid-tied, net metering w/backup mode
All self-designed and self-installed
Location: Chagrin Falls, Ohio

Re: Bypass Battery Temperature Sensor and TempComp on Flexmax 100 afci

Post by Mike Curran »

https://ei.tigoenergy.com/p/pZXn7SZQyO45
https://enlighten.enphaseenergy.com/public/systems/Hctc107221
santafedave
Forum Virtuoso
Posts: 89
Joined: Sat Dec 05, 2020 8:05 pm
My RE system: GS8048-A-300AFCI 8 KW 48V Mate3s with 2 FM100 charge controllers pre wired.
21 Canadian Solar 320 Watt PERC MC4 CS3K-320MS panels.
3 Canadian Solar 325W Module Mono Perc 1000VDC panels.
8 FullRiver AGM DC400-6 Sealed Batteries 415AH 6V L16 size.
Fireraptor quick disconnect.

Re: Bypass Battery Temperature Sensor and TempComp on Flexmax 100 afci

Post by santafedave »

Ok. Here is an update on my RTS. I unplugged it last month as the temps started to go up in my area. The system has been working without problems since that time. I am now wondering if I should plug the RTS into my CC9 and see if it will use the slope and charge my batteries appropriately. If I do that will I be able to change values using the OPTICsRE program?