Power Fluxuation with generator

Post by wpmaura »

I run a generator for an hour at night to assist batteries or rain etc. But when I cut it.off there seems to be a dip in power. Should that be seemless?
raysun
Forum Emperor
Posts: 4806
Joined: Tue Jul 26, 2016 5:57 am
My RE system: Flexpower Two: (2) FXR3048A-01, (2) FM80, MATE3s, FlexNetDC
SimpliPhi 48-3.8 (6 @ 48v)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
Honda EU7000is gas fuel generator

Re: Power Fluxuation with generator

Post by raysun »

It depends on the manner of cutoff, perhaps.

Is the generator simply being powered down, or is the AC IN being DROPPED first?
wpmaura
Forum Whiz
Posts: 46
Joined: Wed Feb 19, 2020 1:25 pm
My RE system: flex power one 3kw. 16 x 6v 415ah Rolls, 15x 270watt 30V 9amp panels

Re: Power Fluxuation with generator

Post by wpmaura »

I just cut the generator off its a 6kw pull cord
wpmaura
Forum Whiz
Posts: 46
Joined: Wed Feb 19, 2020 1:25 pm
My RE system: flex power one 3kw. 16 x 6v 415ah Rolls, 15x 270watt 30V 9amp panels

Re: Power Fluxuation with generator

Post by wpmaura »

is there a way of dropping it from mate
raysun
Forum Emperor
Posts: 4806
Joined: Tue Jul 26, 2016 5:57 am
My RE system: Flexpower Two: (2) FXR3048A-01, (2) FM80, MATE3s, FlexNetDC
SimpliPhi 48-3.8 (6 @ 48v)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
Honda EU7000is gas fuel generator

Re: Power Fluxuation with generator

Post by raysun »

The Mate3/3s has a hard button labeled AC INPUT.

It has a menu that will allow input DROP and USE.
provo
Forum Czar
Posts: 737
Joined: Thu Jul 27, 2006 4:34 pm
My RE system: Sixteen Evergreen EC-120
(4 strings, total 1920W)
Eight Rolls S-550 (2 strings, total ~800Ah @ 24V)
One FM80
One VFXR3524A
Hub 10
Mate3s
FNDC and Trimetric
Honda EU3000is generator
Location: Sierra foothills

Re: Power Fluxuation with generator

Post by provo »

raysun wrote: Fri Oct 16, 2020 8:02 am
It has a menu that will allow input DROP and USE.
DROP doesn't turn off generator, though. AGS does.
raysun
Forum Emperor
Posts: 4806
Joined: Tue Jul 26, 2016 5:57 am
My RE system: Flexpower Two: (2) FXR3048A-01, (2) FM80, MATE3s, FlexNetDC
SimpliPhi 48-3.8 (6 @ 48v)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
Honda EU7000is gas fuel generator

Re: Power Fluxuation with generator

Post by raysun »

But its a manual start generator.

The smoothest manual transition is to DROP the AC INPUT, then power down the generator.

AGS will do it all programmatically, but requires an AGS compatible generator.
wpmaura
Forum Whiz
Posts: 46
Joined: Wed Feb 19, 2020 1:25 pm
My RE system: flex power one 3kw. 16 x 6v 415ah Rolls, 15x 270watt 30V 9amp panels

Re: Power Fluxuation with generator

Post by wpmaura »

That did the trick. Thanks