FX2012MT AC POwer error led
Moderators: OutBack Moderator Team, OutBack
-
jfguay2
- Forum Member
- Posts: 12
- Joined: Sun Dec 10, 2017 6:57 am
- My RE system: 5 siemens SP-75 , Outback Flexmax 80, Outback FX2012MT inverter, 2 Crown CR240 6v batteries
FX2012MT AC POwer error led
Hello,
Recently, I have started experimenting an issue where my inverter will come on once hooked to the battery bank, as usual, but when I plug in shore power, the ac in led comes on, but once the relay tries to connect, the error led comes on for a second and then both ac in led and the error led go off. This goes on and on forever. This started happening after I took my battery bank off the motorhome, and put in back in , reconnecting everything. I am certain the polarity is fine, so I am wondering whether I burned something in the inverter that is preventing in to properly activate the internal relay to pass on the 120 v shore power to the motor home.
Any idea before I dissassemble the beast?
Recently, I have started experimenting an issue where my inverter will come on once hooked to the battery bank, as usual, but when I plug in shore power, the ac in led comes on, but once the relay tries to connect, the error led comes on for a second and then both ac in led and the error led go off. This goes on and on forever. This started happening after I took my battery bank off the motorhome, and put in back in , reconnecting everything. I am certain the polarity is fine, so I am wondering whether I burned something in the inverter that is preventing in to properly activate the internal relay to pass on the 120 v shore power to the motor home.
Any idea before I dissassemble the beast?
-
pss
- Forum Emperor
- Posts: 1325
- Joined: Mon Jul 24, 2017 8:40 am
- My RE system: 8330 watts in three strings, Flexmax 60 x 3, Radian 8048A, GSLC load center, Mate 3S, Hub 10.3, FN-DC and 900 Amp, 48V Trojan T105-RE battery bank.
Re: FX2012MT AC POwer error led
Just my two cents, but relays are magnetic switches in many cases and can easily stop working properly without notice. They are subject to wearing out. Hopefully you eliminated this aspect already.
-
raysun
- Forum Overlord
- Posts: 13677
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid
Re: FX2012MT AC POwer error led
Have you looked in the system logs to see what error(s) displays?
-
jfguay2
- Forum Member
- Posts: 12
- Joined: Sun Dec 10, 2017 6:57 am
- My RE system: 5 siemens SP-75 , Outback Flexmax 80, Outback FX2012MT inverter, 2 Crown CR240 6v batteries
Re: FX2012MT AC POwer error led
No I haven't yet, as I still need to unmount the beast from within the storage bay, so that I can open it up. Where could I find a wiring diagram of the thing?pss wrote:Just my two cents, but relays are magnetic switches in many cases and can easily stop working properly without notice. They are subject to wearing out. Hopefully you eliminated this aspect already.
-
jfguay2
- Forum Member
- Posts: 12
- Joined: Sun Dec 10, 2017 6:57 am
- My RE system: 5 siemens SP-75 , Outback Flexmax 80, Outback FX2012MT inverter, 2 Crown CR240 6v batteries
Re: FX2012MT AC POwer error led
I suppose I have to use the Mate to get that right? I am pretty certain I look at all I can access through the Mate2 that I have connected to the inverter, but could not see anything. Under which menu should I look? For some reason, I feel as though I don't have access to the complete array of settings of the FM2012MT through the mate2. For instance, I can't change the charging settings, and don't have access to a bunch of other settings, don't know why.raysun wrote:Have you looked in the system logs to see what error(s) displays?
Any help or insight would be greatly appreciated.
Regards,
JF
-
Kurt Lundquist
Re: FX2012MT AC POwer error led
Before removing the inverter I suggest you verify the AC voltage at the inverter input. Check the Mate2 to see what it says for AC input voltage or use an external meter. Watch what happens as the inverter tries to connect to the AC source.
It sounds like you might have a Mate2M instead of a normal Mate2. Check out this manual for guidance http://www.outbackpower.com/downloads/d ... manual.pdf
-Kurt
It sounds like you might have a Mate2M instead of a normal Mate2. Check out this manual for guidance http://www.outbackpower.com/downloads/d ... manual.pdf
-Kurt
-
jfguay2
- Forum Member
- Posts: 12
- Joined: Sun Dec 10, 2017 6:57 am
- My RE system: 5 siemens SP-75 , Outback Flexmax 80, Outback FX2012MT inverter, 2 Crown CR240 6v batteries
Re: FX2012MT AC POwer error led
Kurt Lundquist wrote:Before removing the inverter I suggest you verify the AC voltage at the inverter input. Check the Mate2 to see what it says for AC input voltage or use an external meter. Watch what happens as the inverter tries to connect to the AC source.
It sounds like you might have a Mate2M instead of a normal Mate2. Check out this manual for guidance http://www.outbackpower.com/downloads/d ... manual.pdf
-Kurt
I will do that tonight. Thanks for the information on the fact its a MATE2M. By reading the manual, I came across how to access the advanced menu, which is hidden!! Never knew that and never could figure it out.
thanks a bunch, will report back tomorrow with my findings.
-
jfguay2
- Forum Member
- Posts: 12
- Joined: Sun Dec 10, 2017 6:57 am
- My RE system: 5 siemens SP-75 , Outback Flexmax 80, Outback FX2012MT inverter, 2 Crown CR240 6v batteries
Re: FX2012MT AC POwer error led
Ok well things are getting worse, as as soon as I plug the inverter on batteries, the fan comes on but I get no led on anymore, nothing at all, and nothing either through the mate2m.Kurt Lundquist wrote:Before removing the inverter I suggest you verify the AC voltage at the inverter input. Check the Mate2 to see what it says for AC input voltage or use an external meter. Watch what happens as the inverter tries to connect to the AC source.
It sounds like you might have a Mate2M instead of a normal Mate2. Check out this manual for guidance http://www.outbackpower.com/downloads/d ... manual.pdf
-Kurt
What could it be at this point...?
-
jfguay2
- Forum Member
- Posts: 12
- Joined: Sun Dec 10, 2017 6:57 am
- My RE system: 5 siemens SP-75 , Outback Flexmax 80, Outback FX2012MT inverter, 2 Crown CR240 6v batteries
Re: FX2012MT AC POwer error led
I left the inverter connected all night and this morning, I had a power on green led light on!! I can now access the Mate2M. Will try and see if any errors are coming up. Still can't get the power in to trigger the passthrough relay. From a quick look this morning, before I went to work, my low voltage (ac) cut off is showing at 0, and same with the high voltage (0), and can't seem to change the values either. Obviously, something is wrong ...
-
jfguay2
- Forum Member
- Posts: 12
- Joined: Sun Dec 10, 2017 6:57 am
- My RE system: 5 siemens SP-75 , Outback Flexmax 80, Outback FX2012MT inverter, 2 Crown CR240 6v batteries
Re: FX2012MT AC POwer error led
Ok, further assessment shows not error from the Mate at all. I have removed the inverted from the RV so to troubleshoot properly, and upon connecting the inverter to my 12v batteries, it came on as expected. I then connected the shore power and the charger kicked on properly as well, and I then started an EQ of the battery. That lasted for 30 minutes, at which point, the error led on the Inverter is flashing again, and the AC in continually tries to turn the relay on (based on what I understand) I have verified on ac input settings on the mate not to avail, every thing looks fine. I wonder whether something heats up inside the inverter and after a little while (some charging for instance) the heat makes the relay too sensitive and it won<t go on.
Here is what happens: https://youtu.be/RH2kFYWxvm8
I don<t have any other explanation and I am desperate. Any one can chime in on what I should do next?
Thanks in advance,
JF :-k
Here is what happens: https://youtu.be/RH2kFYWxvm8
I don<t have any other explanation and I am desperate. Any one can chime in on what I should do next?
Thanks in advance,
JF :-k
-
Kurt Lundquist
Re: FX2012MT AC POwer error led
Measure AC voltage at the inverter input terminals with a true RMS meter while going through the same process. What happens to the AC voltage when you see the inverter disconnect? What is the size/length of the shore power cord?
-Kurt
-Kurt
-
jfguay2
- Forum Member
- Posts: 12
- Joined: Sun Dec 10, 2017 6:57 am
- My RE system: 5 siemens SP-75 , Outback Flexmax 80, Outback FX2012MT inverter, 2 Crown CR240 6v batteries
Re: FX2012MT AC POwer error led
Ok, well I thought I would update this old thread with an update. I only had a chance to bring the broken inverter out of storage recently, and decided to open it up, vaguely remembering where this thread had left things. I quickly noticed a ribbon cable (14 pins) connecting two components, which at least 6wires had shorted following what I suspect was a melt of the ribbon given it looked squished and folded at that portion. Thinking that this could possibly be the culprit, I patentiently proceeded to bypassed the sorted portion of the ribbon with wires I soldered, put he ribbon back in and voila! Working inverter. I am so happy!! Wished I had taken photos of the ribbon to share here. Anyways, wanted to post that update here!
-
raysun
- Forum Overlord
- Posts: 13677
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid
Re: FX2012MT AC POwer error led
Good news!
Back from the dead, it should be named Lazurus.
The robbon cables can get pinched between chassis and cover of not carefully routed out of the way.
Back from the dead, it should be named Lazurus.
The robbon cables can get pinched between chassis and cover of not carefully routed out of the way.