Grid-Tie settings during extended grid-down situation?
Moderators: OutBack Moderator Team, OutBack
-
boyd.badten
- Forum Member
- Posts: 6
- Joined: Sat May 18, 2024 6:02 am
- My RE system: Outback FP1 VFXR3648A
FM80, Mate3s
2X Fortress eFlex 5.4kWh (LFP)
8X Hyundai HiS-S410YH 410W Panels
Grid-Tie settings during extended grid-down situation?
I have used Outback inverters and CC's since about 2012. My current system is less than 3 years old, seems well adjusted and is effective.
My priorities for having the system are
1. To have electricity during any length of grid outage.
2. To offset the cost of grid-supplied power. It offsets approximately half of our household needs, with no economizing measures.
It is configured for grid-tie operation. We have experienced grid-down situations here and there. The system continued to work in the absence of grid power--solar charged batteries, house drew current from inverter/battery. The longest outage I can remember is about 8-9 hours. We simply turned off or chose not to use energy-hog appliances, watched the battery level vs. the amount of sun available and all was well. I did not reconfigure the system. It just re-connected with the grid again when it became available.
My question is--if a grid-down situation happens which is much longer, such as weeks or longer, is it OK to just leave the [Mate3s] inverter and CC system configs set for grid-tie operation? I understand that if my home was an off-grid cabin in the woods that it would better to be fully configured for off-grid. But is there any serious downside to simply leaving a residential system in grid-tie mode for an extended period of grid outage?
Outback FP1 VFXR3648A
FM80, Mate3s
2X Fortress eFlex 5.4kWh (LFP)
8X Hyundai HiS-S410YH 410W Panels
My priorities for having the system are
1. To have electricity during any length of grid outage.
2. To offset the cost of grid-supplied power. It offsets approximately half of our household needs, with no economizing measures.
It is configured for grid-tie operation. We have experienced grid-down situations here and there. The system continued to work in the absence of grid power--solar charged batteries, house drew current from inverter/battery. The longest outage I can remember is about 8-9 hours. We simply turned off or chose not to use energy-hog appliances, watched the battery level vs. the amount of sun available and all was well. I did not reconfigure the system. It just re-connected with the grid again when it became available.
My question is--if a grid-down situation happens which is much longer, such as weeks or longer, is it OK to just leave the [Mate3s] inverter and CC system configs set for grid-tie operation? I understand that if my home was an off-grid cabin in the woods that it would better to be fully configured for off-grid. But is there any serious downside to simply leaving a residential system in grid-tie mode for an extended period of grid outage?
Outback FP1 VFXR3648A
FM80, Mate3s
2X Fortress eFlex 5.4kWh (LFP)
8X Hyundai HiS-S410YH 410W Panels
-
chrisski
- Forum Czar
- Posts: 536
- Joined: Fri May 17, 2024 7:23 pm
- My RE system: Dual 8048 Radian w/ Load Center
Mate 3
Flex max 100 afci X 4
Fortress eFlex 5.1 kWh Battery X 8
TP1000 for Internet Connectivity - Location: Central AZ, lowland desert
Re: Grid-Tie settings during extended grid-down situation?
I have two 8048s and am gridtied.
My impression is Outback is better for off grid than on grid, so equipment would last longer.
My big concerns with extended off grid are:
1) automatic shutoff with low batteries. Not sure this exists.
2) getting used to extended cutbacks on electricity to prevent low battery shutoff. My daily loads peak around 160kWh.
3) I have no way to charge the batteries other than the MPPT. I would require a 17 kW to to 22 kW generator to run loads and charge. I have none.
I’m sure you thought of these issues and for me it’s more of changing from a grid tied to off grid mindset.
My big thing is the grid tied mode does not charge the battery well. That’s a hole other issue I don’t want to distract from your thread.
My impression is Outback is better for off grid than on grid, so equipment would last longer.
My big concerns with extended off grid are:
1) automatic shutoff with low batteries. Not sure this exists.
2) getting used to extended cutbacks on electricity to prevent low battery shutoff. My daily loads peak around 160kWh.
3) I have no way to charge the batteries other than the MPPT. I would require a 17 kW to to 22 kW generator to run loads and charge. I have none.
I’m sure you thought of these issues and for me it’s more of changing from a grid tied to off grid mindset.
My big thing is the grid tied mode does not charge the battery well. That’s a hole other issue I don’t want to distract from your thread.
-
dgsantafedave
- Forum Whiz
- Posts: 36
- Joined: Tue Mar 25, 2025 2:36 pm
- My RE system: GS8048A,FM80-150VDCFM100-300VDC-AFCI,FM100-300VDC
Re: Grid-Tie settings during extended grid-down situation?
Get yourself one of these if you have a tractor!
-
tiludicrous
- Forum Junior Member
- Posts: 1
- Joined: Mon Oct 30, 2023 12:51 am
Re: Grid-Tie settings during extended grid-down situation?
I think your approach makes sense, especially since your system has already demonstrated that it can transition through grid outages without manual reconfiguration. However, I'd distinguish between operating in grid-tie mode during a normal outage and relying on the system as a long-term off-grid installation.
For an outage lasting several weeks, I'd pay particular attention to battery reserve settings, low-voltage cutoffs, charging priorities, and how the system behaves when solar production is insufficient. With roughly 8.2 kW of PV and 10.8 kWh of battery storage, you have a useful setup, but consecutive days of poor weather could change the picture considerably.
One resource worth reviewing is the OutBack FXR Operator's Manual . It explains the differences between Grid Tied, Backup, and other input modes, which may help clarify what to expect during a prolonged outage.
For an outage lasting several weeks, I'd pay particular attention to battery reserve settings, low-voltage cutoffs, charging priorities, and how the system behaves when solar production is insufficient. With roughly 8.2 kW of PV and 10.8 kWh of battery storage, you have a useful setup, but consecutive days of poor weather could change the picture considerably.
One resource worth reviewing is the OutBack FXR Operator's Manual . It explains the differences between Grid Tied, Backup, and other input modes, which may help clarify what to expect during a prolonged outage.
-
ralphday224
- Forum Guru
- Posts: 196
- Joined: Sat Mar 07, 2015 3:25 pm
Re: Grid-Tie settings during extended grid-down situation?
My only problem with a pto generator is having to warm up the diesel tractor before starting it. That's a problem if the battery state is low after a storm, or during a storm and outage. Went with a 3cylinder 10kw Nissan diesel. it only gets exercised now...utility is my multi billion dollar generator. It's nice to know it's there
-
JRHill
- Forum Emperor
- Posts: 3124
- Joined: Thu Feb 17, 2011 11:12 am
- My RE system: 48v OB inverter and charge controller, hub and mate3s.
- Location: PNW
- Contact:
Re: Grid-Tie settings during extended grid-down situation?
Grid tied... for a moment let's forget about all the selling stuff and pretend that the grid is available to charge the batteries and the rest flow through to feed loads within the max allowed which is 30aac for the VFXR. So to me it matters not whether one is off-grid and the source is a generator or one is grid tied and that is your AC source. Why should any changes be needed as long as the source is sufficient? I had always stayed with the 'Gen Input Mode: Gen' but have not been happy because I could never get the configured battery charge max to be or close to a real 20aac - it seemed more like 16aac (equivalent in watts) that actually arrived at the batteries. I tried 'Support' but that didn't get more to the batteries. So just last month I set the Gen Mode to UPS and as soon as the inverter connected it zoomed up immediately to the equivalent of 19.85aac. Hurray. When I investigated further I settled on 'Backup' for the mode and all is wonderful. And I'm working the generator a bit harder which is good.
Again, why should anything need to be changed unless the AC source is inadequate in which case you can probably merely select the AC Input Select Priority between the separate settings stored for GEN or GRID assuming you don't have to change the Charger AC Limit because you need more available for pass through? And this might be an excellent case for using Support which is a really cool feature if your use case justifies it.
Hopefully this makes sense and I haven't screwed up trying to describe it.
Again, why should anything need to be changed unless the AC source is inadequate in which case you can probably merely select the AC Input Select Priority between the separate settings stored for GEN or GRID assuming you don't have to change the Charger AC Limit because you need more available for pass through? And this might be an excellent case for using Support which is a really cool feature if your use case justifies it.
Hopefully this makes sense and I haven't screwed up trying to describe it.
-
raysun
- Forum Overlord
- Posts: 13665
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid
Re: Grid-Tie settings during extended grid-down situation?
Gen is universally recommended because it accepts "dirtier" AC which accomodates a wider array of cheap generators. It comes at a cost of efficiency. The typical inverter charger conversion efficiency of 80% is pared down to 60% or less.
Support is problematic as Outbacks implementation is half baked at best. While it eschews the Gen "Brute Mode" in favor of accepting only cleaner AC thus promising higher efficiency, its actual Support function only works in narrow use cases. I do not know if that impacts charge efficiency.
UPS was suggested to me by tech support back in the day, and when I studied the details of its function immediately rejected it as wholly unsuitable to my off-grid charging. I have since replaced the specific knowledge of the exact shortcoming with a Talking Heads song in my aging brain and don't care to restudy the manuals as to why it was a bad call.
Backup may well be the best option, but it too reads a bit like the small print in one of those miracle drug ads so consult your care provider about whether it is right for you.
My solution was to put in an EG4 Chargeverter AC charger. I named it Honeybadger because it don't GAF about inverter modes.
Support is problematic as Outbacks implementation is half baked at best. While it eschews the Gen "Brute Mode" in favor of accepting only cleaner AC thus promising higher efficiency, its actual Support function only works in narrow use cases. I do not know if that impacts charge efficiency.
UPS was suggested to me by tech support back in the day, and when I studied the details of its function immediately rejected it as wholly unsuitable to my off-grid charging. I have since replaced the specific knowledge of the exact shortcoming with a Talking Heads song in my aging brain and don't care to restudy the manuals as to why it was a bad call.
Backup may well be the best option, but it too reads a bit like the small print in one of those miracle drug ads so consult your care provider about whether it is right for you.
My solution was to put in an EG4 Chargeverter AC charger. I named it Honeybadger because it don't GAF about inverter modes.