Just a quick question that I'm sure I already know the answer to but would love a little confirmation.
One of my recent installations is a DC Coupled (FM100 AFCI) Dual Radian Grid Connected (Net Metering), system with 750Ah of SimpliPhi batteries. The System is working great and the client is happy. So happy in fact she wants to add more solar. Instead of using another FM100, I'd like to AC Couple the new solar array (using Enphase IQ7+) to the Radian's critical load panel. I have installed multiple AC Coupled systems, but just not one on my existing DC Coupled Systems. I see no reason why both cannot work harmoniously, assuming I stay below the 75% of the 16kW output of the dual radians (no more than 12.8kW of Grid Tied input) and the batteries can comfortably handle the added charge current (which they easily can). Does anyone else see any issues with this combining the two different strategies?
One of my recent installations is a DC Coupled (FM100 AFCI) Dual Radian Grid Connected (Net Metering), system with 750Ah of SimpliPhi batteries. The System is working great and the client is happy. So happy in fact she wants to add more solar. Instead of using another FM100, I'd like to AC Couple the new solar array (using Enphase IQ7+) to the Radian's critical load panel. I have installed multiple AC Coupled systems, but just not one on my existing DC Coupled Systems. I see no reason why both cannot work harmoniously, assuming I stay below the 75% of the 16kW output of the dual radians (no more than 12.8kW of Grid Tied input) and the batteries can comfortably handle the added charge current (which they easily can). Does anyone else see any issues with this combining the two different strategies?
- Mike Curran
- Forum Emperor
- Posts: 3602
- Joined: Sat Aug 28, 2004 6:28 pm
- My RE system: Outback - Garage roof (2017):
- 6 (2×3) ALEO S79-300's into one FM80 (2017-25, restored 9-7-2026)
- 2 grid-tied VFXR3524A-01's series stacked, replaced GVFX's (2020)
- 6 Simpliphi 3.8kwh, 24V, 900Ah (replaced 2007-25 vintage Rolls)
- Hub10.3, Mate3s, FNDC. Tigo ES maximizers on each PV module.
Westinghouse Solar - Barn roof: (2012)
- 24 (2x12) 235W Lightways panels with Enphase M215 microinverters plus 6 - 275W Talesun panels, also with M215s, grid-tied
Outback Skybox - Barn roof: (2019)
- 14 Trina Solar 270W in series (DC array input to SB inverter/charger), installed 3/5/24 (replaced original 2019 Talesun DC array)
- 3 SimpliPhi 3.8 batteries, 48V, 225Ah total
- AC coupled input from 14 Talesun 275W, Enphase M215 microinverters
Battery systems operate in grid-tied, net metering w/backup mode
All self-designed and self-installed - Location: Chagrin Falls, Ohio
Re: AC & DC Coupling Simultaniously
The Radian has AC-coupling capability. There's no reason this won't work. My system does this with Skybox but the Radian is similarly capable. I'm sure there are others on the forum who are already doing this with their Radian(s).
https://ei.tigoenergy.com/p/pZXn7SZQyO45
https://enlighten.enphaseenergy.com/public/systems/Hctc107221
https://enlighten.enphaseenergy.com/public/systems/Hctc107221
-
Positive Power
- Forum Member
- Posts: 15
- Joined: Thu Jun 10, 2021 6:04 pm
Re: AC & DC Coupling Simultaniously
That’s my thought too. Indeed I have seen others do it as well. Thanks for your feedback.
Re: AC & DC Coupling Simultaniously
What are the best practices for monitoring and controlling an AC-coupled system?Positive Power wrote: ↑Thu Apr 06, 2023 6:55 pmThat’s my thought too. Indeed I have seen others do it as well. Thanks for your snake gamefeedback.
- Mike Curran
- Forum Emperor
- Posts: 3602
- Joined: Sat Aug 28, 2004 6:28 pm
- My RE system: Outback - Garage roof (2017):
- 6 (2×3) ALEO S79-300's into one FM80 (2017-25, restored 9-7-2026)
- 2 grid-tied VFXR3524A-01's series stacked, replaced GVFX's (2020)
- 6 Simpliphi 3.8kwh, 24V, 900Ah (replaced 2007-25 vintage Rolls)
- Hub10.3, Mate3s, FNDC. Tigo ES maximizers on each PV module.
Westinghouse Solar - Barn roof: (2012)
- 24 (2x12) 235W Lightways panels with Enphase M215 microinverters plus 6 - 275W Talesun panels, also with M215s, grid-tied
Outback Skybox - Barn roof: (2019)
- 14 Trina Solar 270W in series (DC array input to SB inverter/charger), installed 3/5/24 (replaced original 2019 Talesun DC array)
- 3 SimpliPhi 3.8 batteries, 48V, 225Ah total
- AC coupled input from 14 Talesun 275W, Enphase M215 microinverters
Battery systems operate in grid-tied, net metering w/backup mode
All self-designed and self-installed - Location: Chagrin Falls, Ohio
Re: AC & DC Coupling Simultaniously
Make sure your battery based inverter responds properly when there's a grid outage and total PV input to your system exceeds your load requirements. In this situation your battery- based inverter should dither its AC output frequency to force the grid-tied inverter to disconnect. If this doesn't happen your battery could become overcharged.
https://ei.tigoenergy.com/p/pZXn7SZQyO45
https://enlighten.enphaseenergy.com/public/systems/Hctc107221
https://enlighten.enphaseenergy.com/public/systems/Hctc107221
-
clarkef
- Forum Guru
- Posts: 149
- Joined: Wed Oct 31, 2018 9:43 am
- My RE system: Radian 8048A w/PV GSLC
FM100 CC x3
10KW of 72 cell panels (5S3P x2)
2200AH (usable) of Li-Ion modules @48v with SIMP-BMS
Midnite Combiners, SPDs
MilSurp MEP-802A ‘5K’ Generator
Off-grid - Location: South Central KY
Re: AC & DC Coupling Simultaniously
As others said the main thing is to have the Radiian system larger than the grid tied it’s going to manage when grid forming. That way the Radian can freq shift the output as needed to modulate the grid-tie inverters. If the gridtie system is larger than the Radians, the radians lose the ability to form a grid and control the output of the grid tie by shifting the power frequency.
If you have a backup generator, when the generator is energized, the grid tie inverters must be disconnected from the backup panel. You cannot safely interconnect a generator and grid-tie inverters. Outback used to sell a relay for this but it was just a DPDT 240v AC relay powered by the generator AC in. Wiring is covered in the outback tech note for AC coupling.
Re: AC & DC Coupling Simultaniously
How will frequency shifting be coordinated when batteries approach full SOC will the Radian curtail the Enphase system reliably without interfering with DC PV production?
Retro Bowl College
Retro Bowl College
-
clarkef
- Forum Guru
- Posts: 149
- Joined: Wed Oct 31, 2018 9:43 am
- My RE system: Radian 8048A w/PV GSLC
FM100 CC x3
10KW of 72 cell panels (5S3P x2)
2200AH (usable) of Li-Ion modules @48v with SIMP-BMS
Midnite Combiners, SPDs
MilSurp MEP-802A ‘5K’ Generator
Off-grid - Location: South Central KY
Re: AC & DC Coupling Simultaniously
That’s exactly what it does. As batteries approach the float value configured in the radian charging section, the radian shifts the output frequency away from 60hz to slow the production of the grid tied inverters. The closer to full charge the higher the frequency shift until the frequency shift enough to shutdown the grid tied inverter(s).
- Mike Curran
- Forum Emperor
- Posts: 3602
- Joined: Sat Aug 28, 2004 6:28 pm
- My RE system: Outback - Garage roof (2017):
- 6 (2×3) ALEO S79-300's into one FM80 (2017-25, restored 9-7-2026)
- 2 grid-tied VFXR3524A-01's series stacked, replaced GVFX's (2020)
- 6 Simpliphi 3.8kwh, 24V, 900Ah (replaced 2007-25 vintage Rolls)
- Hub10.3, Mate3s, FNDC. Tigo ES maximizers on each PV module.
Westinghouse Solar - Barn roof: (2012)
- 24 (2x12) 235W Lightways panels with Enphase M215 microinverters plus 6 - 275W Talesun panels, also with M215s, grid-tied
Outback Skybox - Barn roof: (2019)
- 14 Trina Solar 270W in series (DC array input to SB inverter/charger), installed 3/5/24 (replaced original 2019 Talesun DC array)
- 3 SimpliPhi 3.8 batteries, 48V, 225Ah total
- AC coupled input from 14 Talesun 275W, Enphase M215 microinverters
Battery systems operate in grid-tied, net metering w/backup mode
All self-designed and self-installed - Location: Chagrin Falls, Ohio
Re: AC & DC Coupling Simultaniously
FWIW, the max GDI system output when ac-coupled to a Radian is 7.6kw, per this document:
https://outbackpower.com/downloads/docu ... radian.pdf
https://outbackpower.com/downloads/docu ... radian.pdf
https://ei.tigoenergy.com/p/pZXn7SZQyO45
https://enlighten.enphaseenergy.com/public/systems/Hctc107221
https://enlighten.enphaseenergy.com/public/systems/Hctc107221
-
clarkef
- Forum Guru
- Posts: 149
- Joined: Wed Oct 31, 2018 9:43 am
- My RE system: Radian 8048A w/PV GSLC
FM100 CC x3
10KW of 72 cell panels (5S3P x2)
2200AH (usable) of Li-Ion modules @48v with SIMP-BMS
Midnite Combiners, SPDs
MilSurp MEP-802A ‘5K’ Generator
Off-grid - Location: South Central KY
Re: AC & DC Coupling Simultaniously
That is right. The Radian needs be able to muscle around the grid tie inverters to control their output. If the GTI are larger than the radian then they end up controlling the output frequency and the radian can’t shutoff or reduce the GTI output when loads are less than what’s being generated or used for battery charging.Mike Curran wrote: ↑Sun Jan 04, 2026 12:13 pmFWIW, the max GDI system output when ac-coupled to a Radian is 7.6kw, per this document:
-
PaulMillner
- Forum Whiz
- Posts: 30
- Joined: Tue Dec 10, 2019 6:10 pm
- My RE system: GS8040A, six Samsung SDI ESS Energy Storage Battery 16S 60 Volt - Mega 3.3 kWh, Firman 5.5 kW natural gas electric start generator
- Location: Berkeley CA
- Contact:
Re: AC & DC Coupling Simultaniously
>> If the GTI are larger than the Radian, then they end up controlling the output frequency…
It’s a different problem than that, I think. The GTI perturbs the wave form every second to see if the “grid” is still there… the grid is expected to be robust, and not allow the perturbation to affect system waveform. As the GTI size approaches Radian size, the Radian can’t adequately suppress the strong perturbation . The GTI concludes grid is absent, and disconnects.
OTOH, if the Radian starts increasing the frequency, the GTI will notice the discrepancy.
The AC-coupled gotcha that isn’t adequately publicized, IMHO, is that Radian only supports AC coupling in grid-tied mode. But, my POCO forbids export, so I operate in mini-grid instead. In mini-grid, the Radian can’t export excess solar, so runaway battery charging can occur. I’ve got the aux relay set up in generator mode… controlling a contractor that disconnects the GTI from the critical loads panel. On a sunny day, it cycles that relay ~every half hour to control battery voltage.
I’m not clear that paralleling a second Radian helps… *if* the master keeps the extra inverters in standby. I don’t see how a standby inverter can help resist waveform perturbation.
I’m adding a DC contactor (golf cart master relay) controlled by a JK BMS. If battery voltage goes too high, the inverter will be disconnected from the battery. Redundancy is good! Otherwise, if the Radian processor were to freeze, the aux relay could stay engaged, the H bridge would still rectify the AC-coupled input, and bad things could happen.
Paul
It’s a different problem than that, I think. The GTI perturbs the wave form every second to see if the “grid” is still there… the grid is expected to be robust, and not allow the perturbation to affect system waveform. As the GTI size approaches Radian size, the Radian can’t adequately suppress the strong perturbation . The GTI concludes grid is absent, and disconnects.
OTOH, if the Radian starts increasing the frequency, the GTI will notice the discrepancy.
The AC-coupled gotcha that isn’t adequately publicized, IMHO, is that Radian only supports AC coupling in grid-tied mode. But, my POCO forbids export, so I operate in mini-grid instead. In mini-grid, the Radian can’t export excess solar, so runaway battery charging can occur. I’ve got the aux relay set up in generator mode… controlling a contractor that disconnects the GTI from the critical loads panel. On a sunny day, it cycles that relay ~every half hour to control battery voltage.
I’m not clear that paralleling a second Radian helps… *if* the master keeps the extra inverters in standby. I don’t see how a standby inverter can help resist waveform perturbation.
I’m adding a DC contactor (golf cart master relay) controlled by a JK BMS. If battery voltage goes too high, the inverter will be disconnected from the battery. Redundancy is good! Otherwise, if the Radian processor were to freeze, the aux relay could stay engaged, the H bridge would still rectify the AC-coupled input, and bad things could happen.
Paul