Mini Grid not connecting automatically (solved?)

Dual Input, 120/240, stainless steel form factor design for unsurpassed surge capability
Post Reply
IdahoSunshine
Forum Whiz
Posts: 34
Joined: Mon Dec 16, 2024 12:46 pm
My RE system: • Outback 8000W GS8048A-01 inverter
• Mate3s communications controller
• Hub10-Outback, Communications Hub, 10 ports, 10.3
• Outback Radiant Prewired GS Load Center with 175A Inverter disconnects, GFDI an PV disconnects for two charge controllers, FLEXnet DC with 3 shunts, GSLC175-PV-120/240
• Outback Charge Controller, MPPT, 80A, FM80 (2)
• ARK, 100A, 48V Lithium Ion (LiFeP04) battery (4)
• Midnite Solar Combiner Box, 120A for 6 PV breakers (2)
• Canadian Solar 355w Poly Split Cell Silver Frame 35mm White Backsheet T4 1500v, CS3U-355P-F16 (24)
• Champion 9375-Watt Dual Fuel Portable Generator, Electric Start
Location: Idaho
Contact:

Mini Grid not connecting automatically (solved?)

Post by IdahoSunshine » Fri Oct 16, 2026 6:17 pm

i all,

I’m having an issue with Mini Grid mode on my OpticsRE system and would appreciate any ideas before I dig further with support.

System

Radian GS8048A inverter + Mate3s
Ark Lithium LiFePO4 batteries 4x48V
Mini Grid is the active AC Input Mode
Connect to Grid = 52.4 V
Connect Delay = 2 minutes
LBCO = 48 V (matches Ark’s recommended inverter setting; BMS low cutout is ~41 V)

Symptoms
The automatic Mini Grid connection is not working. When battery voltage drops to and stays at or below 52.4 V for well longer than 2 minutes, the system does not connect to the grid. I’ve had to manually toggle the AC Input Connect/Drop setting in OpticsRE to force a connection.

If I set AC Input to USE/Connect, it connects to the grid immediately and runs the loads from AC even when battery voltage is significantly above 52.4 V (it ignores the batteries).

What I’ve already checked:
  • HBX, Grid Use Time, and Load Grid Transfer are all disabled.
  • Mini Grid is confirmed as the active mode.
  • I previously had FLEXtime scheduling active. On 10/13 the event log showed errors that pending instructions for “OutBack Sched 2 AC Mode Hour” and “Minute” were removed from the queue (so the schedule changes did not fully apply). I later went back, disabled the schedules, set them to 0 hours / 0 minutes, and the event log then showed the changes applied successfully with no errors.
  • Rebulk is set to 50 V (below the Connect to Grid setpoint).
  • Voltage has been observed sitting around 52.0–52.2 V for extended periods with no automatic connection.
Has anyone seen Mini Grid fail to honor the Connect to Grid voltage + delay even when the conflicting functions are off and FLEXtime is cleared? Any other settings (Absorb Time, etc.) that commonly block this behavior?

I’ve opened a support ticket but so far have only been asked for the site name. And now it's the weekend. Happy to provide more details or screenshots if helpful.

Thanks!
Last edited by IdahoSunshine on Tue Oct 20, 2026 11:58 am, edited 1 time in total.

raysun
Forum Overlord
Posts: 13665
Joined: Tue Jul 26, 2016 5:57 am
My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid

Re: Mini Grid not connecting automatically

Post by raysun » Fri Oct 16, 2026 7:17 pm

The joy of living 100% otf grid is in its simplicity. IDK about Minigrid but do recall several threads that mentioned the subject.
Maybe a forum search will turn up some useful info.

IdahoSunshine
Forum Whiz
Posts: 34
Joined: Mon Dec 16, 2024 12:46 pm
My RE system: • Outback 8000W GS8048A-01 inverter
• Mate3s communications controller
• Hub10-Outback, Communications Hub, 10 ports, 10.3
• Outback Radiant Prewired GS Load Center with 175A Inverter disconnects, GFDI an PV disconnects for two charge controllers, FLEXnet DC with 3 shunts, GSLC175-PV-120/240
• Outback Charge Controller, MPPT, 80A, FM80 (2)
• ARK, 100A, 48V Lithium Ion (LiFeP04) battery (4)
• Midnite Solar Combiner Box, 120A for 6 PV breakers (2)
• Canadian Solar 355w Poly Split Cell Silver Frame 35mm White Backsheet T4 1500v, CS3U-355P-F16 (24)
• Champion 9375-Watt Dual Fuel Portable Generator, Electric Start
Location: Idaho
Contact:

Re: Mini Grid not connecting automatically

Post by IdahoSunshine » Fri Oct 16, 2026 7:57 pm

Thanks raysun, I've rummaged thru the forum and saw similar problems with Mini Grid but with different specifics.

ralphday224
Forum Guru
Posts: 196
Joined: Sat Mar 07, 2015 3:25 pm

Re: Mini Grid not connecting automatically

Post by ralphday224 » Sat Oct 17, 2026 3:57 am

I've never had the grid not connect when using HBX mode. HBX with no charger enabled lets the grid carry the loads while the battery status is lower than yuour setpoint. After a stretch of cloudy weather I'll have to initiate a charge which means disabling HBX...then shut down the charge and re-set to HBX. A little more hands on, but it's also eyes on, never used auto charging here.

IdahoSunshine
Forum Whiz
Posts: 34
Joined: Mon Dec 16, 2024 12:46 pm
My RE system: • Outback 8000W GS8048A-01 inverter
• Mate3s communications controller
• Hub10-Outback, Communications Hub, 10 ports, 10.3
• Outback Radiant Prewired GS Load Center with 175A Inverter disconnects, GFDI an PV disconnects for two charge controllers, FLEXnet DC with 3 shunts, GSLC175-PV-120/240
• Outback Charge Controller, MPPT, 80A, FM80 (2)
• ARK, 100A, 48V Lithium Ion (LiFeP04) battery (4)
• Midnite Solar Combiner Box, 120A for 6 PV breakers (2)
• Canadian Solar 355w Poly Split Cell Silver Frame 35mm White Backsheet T4 1500v, CS3U-355P-F16 (24)
• Champion 9375-Watt Dual Fuel Portable Generator, Electric Start
Location: Idaho
Contact:

Re: Mini Grid not connecting automatically

Post by IdahoSunshine » Sat Oct 17, 2026 4:25 am

Thanks ralphday I've seen that as an option, and may well end up using HBX if I can't get this figured out.

IdahoSunshine
Forum Whiz
Posts: 34
Joined: Mon Dec 16, 2024 12:46 pm
My RE system: • Outback 8000W GS8048A-01 inverter
• Mate3s communications controller
• Hub10-Outback, Communications Hub, 10 ports, 10.3
• Outback Radiant Prewired GS Load Center with 175A Inverter disconnects, GFDI an PV disconnects for two charge controllers, FLEXnet DC with 3 shunts, GSLC175-PV-120/240
• Outback Charge Controller, MPPT, 80A, FM80 (2)
• ARK, 100A, 48V Lithium Ion (LiFeP04) battery (4)
• Midnite Solar Combiner Box, 120A for 6 PV breakers (2)
• Canadian Solar 355w Poly Split Cell Silver Frame 35mm White Backsheet T4 1500v, CS3U-355P-F16 (24)
• Champion 9375-Watt Dual Fuel Portable Generator, Electric Start
Location: Idaho
Contact:

Re: Mini Grid not connecting automatically

Post by IdahoSunshine » Sat Oct 17, 2026 4:10 pm

I'm going to play around with Grid Zero and see if that mode will kick on when the voltage is low.

chrisski
Forum Czar
Posts: 536
Joined: Fri May 17, 2024 7:23 pm
My RE system: Dual 8048 Radian w/ Load Center
Mate 3
Flex max 100 afci X 4
Fortress eFlex 5.1 kWh Battery X 8
TP1000 for Internet Connectivity
Location: Central AZ, lowland desert

Re: Mini Grid not connecting automatically

Post by chrisski » Sun Oct 18, 2026 2:53 am

FWIW, I have also not gotten mini grid to exit automatically. First was a single radian, and then I am now a dual radian.

IdahoSunshine
Forum Whiz
Posts: 34
Joined: Mon Dec 16, 2024 12:46 pm
My RE system: • Outback 8000W GS8048A-01 inverter
• Mate3s communications controller
• Hub10-Outback, Communications Hub, 10 ports, 10.3
• Outback Radiant Prewired GS Load Center with 175A Inverter disconnects, GFDI an PV disconnects for two charge controllers, FLEXnet DC with 3 shunts, GSLC175-PV-120/240
• Outback Charge Controller, MPPT, 80A, FM80 (2)
• ARK, 100A, 48V Lithium Ion (LiFeP04) battery (4)
• Midnite Solar Combiner Box, 120A for 6 PV breakers (2)
• Canadian Solar 355w Poly Split Cell Silver Frame 35mm White Backsheet T4 1500v, CS3U-355P-F16 (24)
• Champion 9375-Watt Dual Fuel Portable Generator, Electric Start
Location: Idaho
Contact:

Re: Mini Grid not connecting automatically

Post by IdahoSunshine » Sun Oct 18, 2026 5:19 am

Thanks Chris, hopefully Grid Zero or HBX will work as programmed. What is your workaround?

IdahoSunshine
Forum Whiz
Posts: 34
Joined: Mon Dec 16, 2024 12:46 pm
My RE system: • Outback 8000W GS8048A-01 inverter
• Mate3s communications controller
• Hub10-Outback, Communications Hub, 10 ports, 10.3
• Outback Radiant Prewired GS Load Center with 175A Inverter disconnects, GFDI an PV disconnects for two charge controllers, FLEXnet DC with 3 shunts, GSLC175-PV-120/240
• Outback Charge Controller, MPPT, 80A, FM80 (2)
• ARK, 100A, 48V Lithium Ion (LiFeP04) battery (4)
• Midnite Solar Combiner Box, 120A for 6 PV breakers (2)
• Canadian Solar 355w Poly Split Cell Silver Frame 35mm White Backsheet T4 1500v, CS3U-355P-F16 (24)
• Champion 9375-Watt Dual Fuel Portable Generator, Electric Start
Location: Idaho
Contact:

Re: Mini Grid not connecting automatically

Post by IdahoSunshine » Sun Oct 18, 2026 6:10 am

I’ve now tested Grid Zero as well, and it is not honoring DoD Volts.

Confirmed:

Mode = Grid Zero
DoD Volts = 52.4 V
HBX, Grid Use Time, Load Grid Transfer, and FLEXtime all disabled
No conflicting event-log entries
Behavior:

If AC Input is Dropped (“off”), it never connects to the grid even when voltage goes below DoD Volts.
If AC Input is USE (“on”), it shifts the loads to the grid even when voltage is well above DoD Volts (observed at 53.1 V).

This is the same pattern I saw with Mini Grid: the voltage-based logic is ignored, and connection is controlled only by the manual AC Input USE/Drop state.

JRKsolar
Forum Guru
Posts: 162
Joined: Thu Aug 20, 2020 11:35 am
My RE system: Outback GS8048A
4) Kilovault HAB 7.5
2) Outback Flexmax 100 AFCI
12) Mission Solar 375W
8) Canadian Solar 395W
Tigo TS4-A2F

Re: Mini Grid not connecting automatically

Post by JRKsolar » Mon Oct 19, 2026 6:56 pm

I use mini grid and it works for me as long as the grid supply is within tolerance. I've had times when the grid voltage is too far off and the radian won't accept it. Sometimes it'll kick on and off as the grid voltage fluctuates. Annoying, but not the inverter's fault.

IdahoSunshine
Forum Whiz
Posts: 34
Joined: Mon Dec 16, 2024 12:46 pm
My RE system: • Outback 8000W GS8048A-01 inverter
• Mate3s communications controller
• Hub10-Outback, Communications Hub, 10 ports, 10.3
• Outback Radiant Prewired GS Load Center with 175A Inverter disconnects, GFDI an PV disconnects for two charge controllers, FLEXnet DC with 3 shunts, GSLC175-PV-120/240
• Outback Charge Controller, MPPT, 80A, FM80 (2)
• ARK, 100A, 48V Lithium Ion (LiFeP04) battery (4)
• Midnite Solar Combiner Box, 120A for 6 PV breakers (2)
• Canadian Solar 355w Poly Split Cell Silver Frame 35mm White Backsheet T4 1500v, CS3U-355P-F16 (24)
• Champion 9375-Watt Dual Fuel Portable Generator, Electric Start
Location: Idaho
Contact:

Re: Mini Grid not connecting automatically

Post by IdahoSunshine » Tue Oct 20, 2026 5:55 am

Thanks JKK, I think my grid voltage is OK, I'm now testing whether Parms Not Met is the culprit.

IdahoSunshine
Forum Whiz
Posts: 34
Joined: Mon Dec 16, 2024 12:46 pm
My RE system: • Outback 8000W GS8048A-01 inverter
• Mate3s communications controller
• Hub10-Outback, Communications Hub, 10 ports, 10.3
• Outback Radiant Prewired GS Load Center with 175A Inverter disconnects, GFDI an PV disconnects for two charge controllers, FLEXnet DC with 3 shunts, GSLC175-PV-120/240
• Outback Charge Controller, MPPT, 80A, FM80 (2)
• ARK, 100A, 48V Lithium Ion (LiFeP04) battery (4)
• Midnite Solar Combiner Box, 120A for 6 PV breakers (2)
• Canadian Solar 355w Poly Split Cell Silver Frame 35mm White Backsheet T4 1500v, CS3U-355P-F16 (24)
• Champion 9375-Watt Dual Fuel Portable Generator, Electric Start
Location: Idaho
Contact:

Re: Mini Grid not connecting automatically

Post by IdahoSunshine » Tue Oct 20, 2026 12:01 pm

ralphday224 wrote: ↑
Sat Oct 17, 2026 3:57 am
I've never had the grid not connect when using HBX mode.
This seemed to be the answer for me, thanks.

Quick update for anyone stuck in the same loop:

I’ll admit I barely understand all the deep programming under the hood here, but I'll try to explain:

My research indicates that the FlexNet DC (FNDC) is the system's battery monitor box, and its job is to give the inverter a "handshake" to confirm the batteries are 100% full. Unfortunately, this monitor is old technology meant for lead-acid batteries, and it failed in my case to recognize when my Lithium (LiFePO4) batteries were full. Because the inverter never gets that mandatory full-battery handshake, the automated "Mini Grid" mode doesn't get the go-ahead to drop the AC connection.

Switching to HBX (High Battery Transfer) mode seems to have worked so far.

One quick tip: If your phone or computer keeps throwing timeout errors when you try to save these settings online, enter them directly in the Mate3s.

raysun
Forum Overlord
Posts: 13665
Joined: Tue Jul 26, 2016 5:57 am
My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid

Re: Mini Grid not connecting automatically (solved?)

Post by raysun » Tue Oct 20, 2026 2:25 pm

It could be that. It also could be the charge cycle logic built into the inverter itself. Due to the interruptible nature of inverter charging, there's a complex algorithm that can extend a single charge cycle through several charge sessions. All the events that use inverter charging as a trigger need to see the Absorb phase has completed. This is true whether or not an FNDC is being used.
That's why mini grid or the other inverter modes fire off when manual AC USE is selected, as that resets the internal charge logic on the inverter. So does the REBULK parameter if its value is properly set.
So will the Mate when Global Charge Termination Control is enabled, and properly triggered by the FNDC. I used an FNDC for years with my lithium battery and got accurate results from it. That may take some parameter fiddling dependent on the system average discharge rate but it can be done.
HBX works because its strictly a Mate function and charger states are ignored for initiation.

JRKsolar
Forum Guru
Posts: 162
Joined: Thu Aug 20, 2020 11:35 am
My RE system: Outback GS8048A
4) Kilovault HAB 7.5
2) Outback Flexmax 100 AFCI
12) Mission Solar 375W
8) Canadian Solar 395W
Tigo TS4-A2F

Re: Mini Grid not connecting automatically (solved?)

Post by JRKsolar » Wed Oct 21, 2026 5:59 am

Fwiw, I don't have fndc, just voltage based, so it does seem like it might be an fndc issue. Raysun has a ton of experience with it, so maybe he can help tweak the settings. Personally, I've found voltage settings to work well, maybe because my usage is pretty predictable.

raysun
Forum Overlord
Posts: 13665
Joined: Tue Jul 26, 2016 5:57 am
My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid

Re: Mini Grid not connecting automatically (solved?)

Post by raysun » Wed Oct 21, 2026 8:12 am

For any trigger event voltage will be preferable to SoC.

Post Reply