I’m having an issue with Mini Grid mode on my OpticsRE system and would appreciate any ideas before I dig further with support.
System
Radian GS8048A inverter + Mate3s
Ark Lithium LiFePO4 batteries 4x48V
Mini Grid is the active AC Input Mode
Connect to Grid = 52.4 V
Connect Delay = 2 minutes
LBCO = 48 V (matches Ark’s recommended inverter setting; BMS low cutout is ~41 V)
Symptoms
The automatic Mini Grid connection is not working. When battery voltage drops to and stays at or below 52.4 V for well longer than 2 minutes, the system does not connect to the grid. I’ve had to manually toggle the AC Input Connect/Drop setting in OpticsRE to force a connection.
If I set AC Input to USE/Connect, it connects to the grid immediately and runs the loads from AC even when battery voltage is significantly above 52.4 V (it ignores the batteries).
What I’ve already checked:
- HBX, Grid Use Time, and Load Grid Transfer are all disabled.
- Mini Grid is confirmed as the active mode.
- I previously had FLEXtime scheduling active. On 10/13 the event log showed errors that pending instructions for “OutBack Sched 2 AC Mode Hour” and “Minute” were removed from the queue (so the schedule changes did not fully apply). I later went back, disabled the schedules, set them to 0 hours / 0 minutes, and the event log then showed the changes applied successfully with no errors.
- Rebulk is set to 50 V (below the Connect to Grid setpoint).
- Voltage has been observed sitting around 52.0–52.2 V for extended periods with no automatic connection.
I’ve opened a support ticket but so far have only been asked for the site name. And now it's the weekend. Happy to provide more details or screenshots if helpful.
Thanks!