Recommendations for replacing batteries

Discussion about OutBack Inverters in Grid Tie Applications

Moderators: OutBack Moderator Team, OutBack

Post Reply
zoranm61
Forum Member
Posts: 10
Joined: Sun Nov 30, 2025 9:49 am
My RE system: 24 Solar panels, 12 panels in each array configured as 4 strings with 3 panels
PV Combiner with 2 outputs
Outback Power GS8048 Battery Inverter
2x Outback FM60 Charge Controllers
Battery Bank (4x Deka MK 12V 245Ah, size 8D)

Recommendations for replacing batteries

Post by zoranm61 » Sat Oct 10, 2026 12:09 am

My system has 4 8A8DLTP-DEKA 12V 250Ah AGM batteries that are ~14 years old. It looks like it is time to replace them. I would appreciate any recommendations on replacement, should I get the same ones (assuming they are still available), or different ones. Thanks.

raysun
Forum Overlord
Posts: 13668
Joined: Tue Jul 26, 2016 5:57 am
My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid

Re: Recommendations for replacing batteries

Post by raysun » Sat Oct 10, 2026 8:51 am

AGM batteries that lasted 14 years? That's amazing longevity.
The system is being used as backup to the grid?
Out of curiosity, what was the solution to the Radian not turning on a while back?

zoranm61
Forum Member
Posts: 10
Joined: Sun Nov 30, 2025 9:49 am
My RE system: 24 Solar panels, 12 panels in each array configured as 4 strings with 3 panels
PV Combiner with 2 outputs
Outback Power GS8048 Battery Inverter
2x Outback FM60 Charge Controllers
Battery Bank (4x Deka MK 12V 245Ah, size 8D)

Re: Recommendations for replacing batteries

Post by zoranm61 » Sat Oct 10, 2026 10:00 am

Yes, batteries are for grid backup.
The solution was to replace the mother board. Once I did that, everything was fine! Thanks again for your help!

raysun
Forum Overlord
Posts: 13668
Joined: Tue Jul 26, 2016 5:57 am
My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid

Re: Recommendations for replacing batteries

Post by raysun » Sat Oct 10, 2026 12:57 pm

Right. Float service is an AGM "superpower" and though the same can done with lithium ferro phosphate batteries, there's no particular advantage in going to that chemistry.

The battery model you have is still available, actually manufactured in the USA, and is in the top tier of AGM deep cycle batteries. It has fast charging (for lead acid). Also low internal resistance so will easily "cold start" the Radian.

The Outback equipment was architected around lead acid, and that's a strong argument for staying with the chemistry for your application. A 14 year service life in your use case is a strong argument for replacing like with like.

On an unrelated note, the Outback gear is robust and long lived. It is not, however, eternal. The engineers allowed that the equipment was designed with a 10 year service life. However, many systems in moderate duty last longer. 14 more years? If so call the Guinness Book of World Records. Certainly some more years. However, in the past decade dramatic strides have been made in renewable energy technology. If you should confront a system/component failure that costs more than $2k to fix, it would be time to take a serious look at alternatives.

zoranm61
Forum Member
Posts: 10
Joined: Sun Nov 30, 2025 9:49 am
My RE system: 24 Solar panels, 12 panels in each array configured as 4 strings with 3 panels
PV Combiner with 2 outputs
Outback Power GS8048 Battery Inverter
2x Outback FM60 Charge Controllers
Battery Bank (4x Deka MK 12V 245Ah, size 8D)

Re: Recommendations for replacing batteries

Post by zoranm61 » Tue Oct 13, 2026 8:50 am

Thanks Raysun! I am aware that the system is getting old, and might need some major changes/upgrades in the near future. I am just wondering what you would suggest in the case I need to do that. Also, my panels are Suniva, any thoughts on how efficient they are after ~14 years.
Thanks!!!

raysun
Forum Overlord
Posts: 13668
Joined: Tue Jul 26, 2016 5:57 am
My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid

Re: Recommendations for replacing batteries

Post by raysun » Tue Oct 13, 2026 11:29 am

Do you plan on any changes in the way the system will be used?
If not, for your purpose, I'd replace like with like, battery wise. 14 years speaks for itself.
The alternate choice would be Lithium Ferro Phosphate (LFP) which would also work fine in float/standby. However, it would likely take at least three 48V @ 100Ah monoblocs with 200A BMS in each to "cold boot" a Radian, something an AGM does without blinking. There's a pre-boot gimmick to using a smaller LPF battery, but who wants to fool with gimmicks when the inverter needs restarting?
There's been steady improvements in solar panels. Whether to replace or not comes down to two questions:
• Are the current panels meeting current needs?
If so, replacing for the sake of replacing is something only I'd do, AFIK. Panels have a long life and if there's no damage or degradation affecting their keeping the battery charged, there's little need.
It may be worth having the arrays and wiring inspected for any wear or damage that may cause performance or safety issues.
• Is there a plan to change usage patterns?
Modern panels are so much less expensive than in the past. Even with Trump tariffs eating into our buying power, panels are a relative bargain. I just bought 440W panels in Hawaii for $180 ea. I'm repaneling my array in the same footprint as rhe old one but it adds ⅓ more total power. (My old ones went on the roofs of folks who lost panels in our hurricanes this year.)
Your FM60s can each handle 3000W @ 48V. Six 440-450W panels would be a good fit.

As far as upgrading the system, there's been significant strides in the past 15 years. That's another discussion. Feel free to message me .

zoranm61
Forum Member
Posts: 10
Joined: Sun Nov 30, 2025 9:49 am
My RE system: 24 Solar panels, 12 panels in each array configured as 4 strings with 3 panels
PV Combiner with 2 outputs
Outback Power GS8048 Battery Inverter
2x Outback FM60 Charge Controllers
Battery Bank (4x Deka MK 12V 245Ah, size 8D)

Re: Recommendations for replacing batteries

Post by zoranm61 » Wed Oct 14, 2026 10:41 pm

Thanks Raysun!
- There are 6kW of panels (spec) and the system is basically 4.8kW. I am inclined to keep the panels as they are for now. I did inspect everything last year and it was in good shape.
- On the system itself (Outback Power) it works for now, but something could happen any day and getting support is hard to impossible. So before I invest in new batteries (most likely I will do just that), I wanted to look into the complete picture. What would be inverter options you would recommend? Anything I would need to with charge controllers?
- My current system is net metering (giving up time of use benefits) with battery grid backup. It seems to me (I reviewed the power bills etc) it is probably ok to keep that configuration.
Thanks!