I have a question I am working on a solution for. We have a home that is 100% off grid as there is no grid where we are at. I have a question about lengthening gen run time when we have a loss of power. This is what is happening occasionally when we use too much power
Batteries get low to set shut off point → Out Back system shuts down → Automatic transfer switch sees loss of normal power → ATS (Kohler RDT-CFNC-0200B-QS7, 200A/240V) starts Kohler 14KW gen → generator powers house/charges batteries → battery voltage recovers enough for Out Back to restart → ATS sees "normal" power again → ATS transfers back and shuts generator down → batteries quickly fall again because they have only charged for 15 min or so → repeat. This leads to the generator having to start and shut down 10+ times if this happens at night which is when it typically occurs since the batteries run down if the AC's are on and we use too much power.
So my options I am investigating are 1. If my ATS has a timer feature so I can tell it to run for say an hour before shutting down or 2. Wire/program my outback system to the gen so the ATS is not needed and the Outback controller runs the start and stop of the gen. I believe the outback will allow me to program specific parameters for how long to keep the gen running and set values for starting and stopping. This I believe will require some rewiring/reprogramming which is always a bit of an adventure for me. Or are there other option I'm not thinking of?
Thank you.
ATS programing question or ???
Moderators: OutBack Moderator Team, OutBack
-
Rancho Partera
- Forum Member
- Posts: 11
- Joined: Wed Jun 22, 2022 11:08 am
- My RE system: GS8040A inverter, Flexmax 100 and Flexmax 80, FlexNet DC, Mate 3, communications hub, 20 405 W solar panels, 24 L16 400 A, FullRiver AGM, 48 volt system
-
raysun
- Forum Overlord
- Posts: 13668
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid
Re: ATS programing question or ???
I don't use Automatic Generator Start (AGS) but Outback has a robust AGS system operated by the Mate. It can be programmed for a more elegant start than system shutdown.
The radian has its own internal transfer switch(es) to accept AC power to pass through to loads and to drive the battery charger function.
The external transfer switch can be eliminated/repurposed.
The radian has its own internal transfer switch(es) to accept AC power to pass through to loads and to drive the battery charger function.
The external transfer switch can be eliminated/repurposed.
- bluespur
- Forum Guru
- Posts: 158
- Joined: Wed Feb 23, 2011 2:32 pm
- My RE system: VFX3024x2
Flexmax60x2
3000W total solar, 135w panel array and 220w panel array
Mate3
12xHawker Perfect Plus 8PZS120 FLA batteries
Own built generator Kubota D600 engine, 7.5Kw gen head - Location: Arahura Valley, New Zealand
Re: ATS programing question or ???
I concur with Ray, option 2, enabling AGS in your Outback kit and retiring the ATS is your simplest solution for power continuity, take a look at the AGS tab in the Mate3 settings, its not too difficult.