I have a Radian GS4048A , 4000 watts of solar, grid tied, and 9600 watts of battery back up, and a 22 KW backup generator. During last power outage I have to use the Mate 3 to manually use the generator. Old settings were to use batteries through a sub panel. When batteries get low the generator starts but once the batteries are charged the generator stops. I wanted the generator all the time. Now I have the setting back to Auto, but the inverter will not turn on. It flashes on and then goes back to off. So I am not getting any power to the grid or getting the batteries charged. I have discounted the batteries and solar with breakers, and reintroduced the power.
Any suggestions?
Thanks
Any suggestions?
Thanks
Re: Radian GS4048A will not turn on
Hello,
What is the measured battery voltage across the inverter battery terminals? When you open the upper inverter cover, on the left side circuity, do you see lights on the small top board and by the ribbon cable? IS this system normally set for Grid Tied with sell back? For more immediate support, please call 360-618-4363 M-F 6:30am-4pm PDT while on site or email us at support@outbackpower.com
All the best,
Kim
What is the measured battery voltage across the inverter battery terminals? When you open the upper inverter cover, on the left side circuity, do you see lights on the small top board and by the ribbon cable? IS this system normally set for Grid Tied with sell back? For more immediate support, please call 360-618-4363 M-F 6:30am-4pm PDT while on site or email us at support@outbackpower.com
All the best,
Kim
Technical Support


-
raysun
- Forum Overlord
- Posts: 13666
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid
Re: Radian GS4048A will not turn on
^^^^^^^^^^^^This^^^^^^^^^^^^
-
rmosborn411
- Forum Member
- Posts: 5
- Joined: Fri Jul 17, 2026 10:38 am
- My RE system: Outback 4048, 4000 watts of solar, 9600 watts of battery backup, Mate 3, and a 22 KW back up generator.
Re: Radian GS4048A will not turn on
Voltage is 52 volts. I have not removed the cover, but my system is supposed to be set to grid tie and sell back. I unplugged the batteries, filled with water and reconnected batteries. I just looked at SWEPCO and we are now sell power again to SWEPCO. Started about 5 days ago. But the Mate 3 still says inverter off. My back up generator will no longer start automatically.
I can send pictures of all the Mate 3 screens if that will help.
Thanks
I can send pictures of all the Mate 3 screens if that will help.
Thanks
-
rmosborn411
- Forum Member
- Posts: 5
- Joined: Fri Jul 17, 2026 10:38 am
- My RE system: Outback 4048, 4000 watts of solar, 9600 watts of battery backup, Mate 3, and a 22 KW back up generator.
Re: Radian GS4048A will not turn on
I had a bad battery wire. Cleaned everything up and reset inverter and I am now feeding power back to the grid.
Thanks
Thanks
Re: Radian GS4048A will not turn on
Glad to hear! Thank you for the update.rmosborn411 wrote: ↑Mon Sep 14, 2026 11:00 amI had a bad battery wire. Cleaned everything up and reset inverter and I am now feeding power back to the grid.
Thanks
Cheers!
--Kim
Technical Support


-
rmosborn411
- Forum Member
- Posts: 5
- Joined: Fri Jul 17, 2026 10:38 am
- My RE system: Outback 4048, 4000 watts of solar, 9600 watts of battery backup, Mate 3, and a 22 KW back up generator.
Re: Radian GS4048A will not turn on
I posted a question about changing the setting on my Radian to load start vs voltage start. Can you search for it and see if you can help.Kim.R wrote: ↑Mon Sep 14, 2026 11:56 amGlad to hear! Thank you for the update.rmosborn411 wrote: ↑Mon Sep 14, 2026 11:00 amI had a bad battery wire. Cleaned everything up and reset inverter and I am now feeding power back to the grid.
Thanks
Cheers!
--Kim
Thanks
Re: Radian GS4048A will not turn on
rmosborn411 wrote: ↑Mon Sep 14, 2026 1:34 pmI posted a question about changing the setting on my Radian to load start vs voltage start. Can you search for it and see if you can help.Kim.R wrote: ↑Mon Sep 14, 2026 11:56 amGlad to hear! Thank you for the update.rmosborn411 wrote: ↑Mon Sep 14, 2026 11:00 amI had a bad battery wire. Cleaned everything up and reset inverter and I am now feeding power back to the grid.
Thanks
Cheers!
--Kim
Thanks
Did you post it in the forums and if so did you do it under a differnt lon in than the one you are using in this thread, as I only see 4 posts to your username?
If you find the post, you can snag the web address from the browser and link it to me.
All the best,
-Kim
Technical Support


Re: Radian GS4048A will not turn on
I am also currently available on Live Chat. Go to www.outbackpower.com and click on the chat bubble.
Cheers,
-Kim
Cheers,
-Kim
Technical Support


-
rmosborn411
- Forum Member
- Posts: 5
- Joined: Fri Jul 17, 2026 10:38 am
- My RE system: Outback 4048, 4000 watts of solar, 9600 watts of battery backup, Mate 3, and a 22 KW back up generator.
Re: Radian GS4048A will not turn on
I believe I sent an email. I did get a call from a gentleman from technical support, Thank you. We made some changes and he said I needed to update the Firmware which I did. I would just like to know if the changes we made do what I want without further changes. My Genrac would not start until my batteries went below the threshold setting. We have a subpanel that ran lights and refrigerators for a short period. I want the Genrac to start as soon as we lose power due to household changes no longer run off the batteries first. He called me at 903-276-0411
It may be that the changes just would not take effect until I updated the firmware. Does that sound right?
Thanks for your help.
It may be that the changes just would not take effect until I updated the firmware. Does that sound right?
Thanks for your help.
-
raysun
- Forum Overlord
- Posts: 13666
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid
Re: Radian GS4048A will not turn on
This user forum isn't a primary channel for the tech support people to deliver end user assistance. @Kim drops by time permitting to help out, but the email system and the chat line are better choices if you have something more than a "one and done" issue.
If you'd like other users to help as well, please include the details of the system configuration in question.
If you'd like other users to help as well, please include the details of the system configuration in question.