Radian GS4048A will not turn on

Dual Input, 120/240, stainless steel form factor design for unsurpassed surge capability
Post Reply
rmosborn411
Forum Member
Posts: 5
Joined: Fri Jul 17, 2026 10:38 am
My RE system: Outback 4048, 4000 watts of solar, 9600 watts of battery backup, Mate 3, and a 22 KW back up generator.

Radian GS4048A will not turn on

Post by rmosborn411 » Tue Jul 21, 2026 1:04 pm

I have a Radian GS4048A , 4000 watts of solar, grid tied, and 9600 watts of battery back up, and a 22 KW backup generator. During last power outage I have to use the Mate 3 to manually use the generator. Old settings were to use batteries through a sub panel. When batteries get low the generator starts but once the batteries are charged the generator stops. I wanted the generator all the time. Now I have the setting back to Auto, but the inverter will not turn on. It flashes on and then goes back to off. So I am not getting any power to the grid or getting the batteries charged. I have discounted the batteries and solar with breakers, and reintroduced the power.
Any suggestions?

Thanks

User avatar
Kim.R
Forum Virtuoso
Posts: 98
Joined: Thu Dec 05, 2024 2:22 pm

Re: Radian GS4048A will not turn on

Post by Kim.R » Thu Jul 23, 2026 2:13 pm

Hello,
What is the measured battery voltage across the inverter battery terminals? When you open the upper inverter cover, on the left side circuity, do you see lights on the small top board and by the ribbon cable? IS this system normally set for Grid Tied with sell back? For more immediate support, please call 360-618-4363 M-F 6:30am-4pm PDT while on site or email us at support@outbackpower.com

All the best,
Kim
Technical Support

Image

raysun
Forum Overlord
Posts: 13666
Joined: Tue Jul 26, 2016 5:57 am
My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid

Re: Radian GS4048A will not turn on

Post by raysun » Thu Jul 23, 2026 9:35 pm

^^^^^^^^^^^^This^^^^^^^^^^^^

rmosborn411
Forum Member
Posts: 5
Joined: Fri Jul 17, 2026 10:38 am
My RE system: Outback 4048, 4000 watts of solar, 9600 watts of battery backup, Mate 3, and a 22 KW back up generator.

Re: Radian GS4048A will not turn on

Post by rmosborn411 » Mon Jul 27, 2026 5:44 pm

Voltage is 52 volts. I have not removed the cover, but my system is supposed to be set to grid tie and sell back. I unplugged the batteries, filled with water and reconnected batteries. I just looked at SWEPCO and we are now sell power again to SWEPCO. Started about 5 days ago. But the Mate 3 still says inverter off. My back up generator will no longer start automatically.
I can send pictures of all the Mate 3 screens if that will help.
Thanks

rmosborn411
Forum Member
Posts: 5
Joined: Fri Jul 17, 2026 10:38 am
My RE system: Outback 4048, 4000 watts of solar, 9600 watts of battery backup, Mate 3, and a 22 KW back up generator.

Re: Radian GS4048A will not turn on

Post by rmosborn411 » Mon Sep 14, 2026 11:00 am

I had a bad battery wire. Cleaned everything up and reset inverter and I am now feeding power back to the grid.

Thanks

User avatar
Kim.R
Forum Virtuoso
Posts: 98
Joined: Thu Dec 05, 2024 2:22 pm

Re: Radian GS4048A will not turn on

Post by Kim.R » Mon Sep 14, 2026 11:56 am

rmosborn411 wrote: ↑
Mon Sep 14, 2026 11:00 am
I had a bad battery wire. Cleaned everything up and reset inverter and I am now feeding power back to the grid.

Thanks
Glad to hear! Thank you for the update.


Cheers!
--Kim
Technical Support

Image

rmosborn411
Forum Member
Posts: 5
Joined: Fri Jul 17, 2026 10:38 am
My RE system: Outback 4048, 4000 watts of solar, 9600 watts of battery backup, Mate 3, and a 22 KW back up generator.

Re: Radian GS4048A will not turn on

Post by rmosborn411 » Mon Sep 14, 2026 1:34 pm

Kim.R wrote: ↑
Mon Sep 14, 2026 11:56 am
rmosborn411 wrote: ↑
Mon Sep 14, 2026 11:00 am
I had a bad battery wire. Cleaned everything up and reset inverter and I am now feeding power back to the grid.

Thanks
Glad to hear! Thank you for the update.


Cheers!
--Kim
I posted a question about changing the setting on my Radian to load start vs voltage start. Can you search for it and see if you can help.
Thanks

User avatar
Kim.R
Forum Virtuoso
Posts: 98
Joined: Thu Dec 05, 2024 2:22 pm

Re: Radian GS4048A will not turn on

Post by Kim.R » Mon Sep 14, 2026 2:32 pm

rmosborn411 wrote: ↑
Mon Sep 14, 2026 1:34 pm
Kim.R wrote: ↑
Mon Sep 14, 2026 11:56 am
rmosborn411 wrote: ↑
Mon Sep 14, 2026 11:00 am
I had a bad battery wire. Cleaned everything up and reset inverter and I am now feeding power back to the grid.

Thanks
Glad to hear! Thank you for the update.


Cheers!
--Kim
I posted a question about changing the setting on my Radian to load start vs voltage start. Can you search for it and see if you can help.
Thanks

Did you post it in the forums and if so did you do it under a differnt lon in than the one you are using in this thread, as I only see 4 posts to your username?
If you find the post, you can snag the web address from the browser and link it to me.

All the best,
-Kim
Technical Support

Image

User avatar
Kim.R
Forum Virtuoso
Posts: 98
Joined: Thu Dec 05, 2024 2:22 pm

Re: Radian GS4048A will not turn on

Post by Kim.R » Mon Sep 14, 2026 2:34 pm

I am also currently available on Live Chat. Go to www.outbackpower.com and click on the chat bubble.


Cheers,
-Kim
Technical Support

Image

rmosborn411
Forum Member
Posts: 5
Joined: Fri Jul 17, 2026 10:38 am
My RE system: Outback 4048, 4000 watts of solar, 9600 watts of battery backup, Mate 3, and a 22 KW back up generator.

Re: Radian GS4048A will not turn on

Post by rmosborn411 » Thu Sep 17, 2026 4:29 pm

I believe I sent an email. I did get a call from a gentleman from technical support, Thank you. We made some changes and he said I needed to update the Firmware which I did. I would just like to know if the changes we made do what I want without further changes. My Genrac would not start until my batteries went below the threshold setting. We have a subpanel that ran lights and refrigerators for a short period. I want the Genrac to start as soon as we lose power due to household changes no longer run off the batteries first. He called me at 903-276-0411
It may be that the changes just would not take effect until I updated the firmware. Does that sound right?

Thanks for your help.

raysun
Forum Overlord
Posts: 13666
Joined: Tue Jul 26, 2016 5:57 am
My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid

Re: Radian GS4048A will not turn on

Post by raysun » Thu Sep 17, 2026 5:05 pm

This user forum isn't a primary channel for the tech support people to deliver end user assistance. @Kim drops by time permitting to help out, but the email system and the chat line are better choices if you have something more than a "one and done" issue.

If you'd like other users to help as well, please include the details of the system configuration in question.

Post Reply