The breaker box from Hell

Post by pioneerMan » Mon Sep 07, 2026 1:04 pm

Don't blame me, I didn't do this mess. The guy on this property before me wired this thing up. He's dead now. The 6 heavy duty black wires coming into the box supply power to 2 mobile homes, 3 wires each. I think maybe the wires are aluminum, but not sure. The run to my house is at least 400 feet. It's crazy to me that the Outback inverter's AC output is the small yellow Romax wire coming in to the breaker box. Not sure why he thought we needed such heavy gauge wires going to the mobile homes, considering the most this inverter can put out is 2800 watts. Maybe thinking ahead for a future upgrade?

Is there anything I can buy that I can shove the ends of those 3 wires into, which would then offer a smaller tip to go into the breakers better? Just trying to clean this up and make it safer.

Thanks.

elect1.jpeg

elect2.jpeg

elect3.jpeg

raysun
Forum Overlord
Posts: 13646
Joined: Tue Jul 26, 2016 5:57 am
My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid

Re: The breaker box from Hell

Post by raysun » Mon Sep 07, 2026 3:01 pm

When it comes to AC wiring I mainly leave it to the guys who do it for a living. All that definitely looks sketchy.
The inverter is an FX2812 yes? They are rated around 25AAC @ 120V so 10AWG wire with 30A disconnect would be good for AC output to the load panel.

SumPowerRays
Forum Guru
Posts: 198
Joined: Tue Oct 11, 2022 7:48 pm
My RE system: Off Grid
(1) Flexpower Radian 8048A
MATE3s, HUB 10.3, FN-DC, RTS,
(2) FLEXmax 100 AFCI charge controllers
(12) Northstar Blue 190FT batteries 606 AH
(24) REC 365NP2 Panels.
(4) Arrays of 2190 watts each.
Location: Central Washington State

Re: The breaker box from Hell

Post by SumPowerRays » Tue Sep 08, 2026 8:18 pm

Polaris lugs!
This link is for wire sizes 1/0 through #14 awg.
https://www.homedepot.com/p/Polaris-1-0 ... /303578418
They also come in size #4 awg to 14 awg.

If your local home depot doesn't have stock and you don't want to wait.

Then there is a Platt Electric Supply in Logan, Utah and Platt in Ogden. Platt will usually have these Polaris lugs in stock. If not it is 1 day delivery to the store to get stock. Great supply house.

You should probably place a Romex connector on the yellow romex wire entering the box to prevent it from moving around and chafing the insulation.

pioneerMan
Forum Czar
Posts: 584
Joined: Wed Jan 09, 2019 3:40 pm
My RE system: 12 volt system
6 Lion Energy model 700 batteries, 12V each
12 solar panels (Mitsubishi 125 Watt)
Outback VFX2812 inverter and two FLEXmax 60 inverters
Mate 3s
Dual fuel 4500 watt generator
Location: Northern Utah

Re: The breaker box from Hell

Post by pioneerMan » Tue Sep 08, 2026 8:36 pm

SumPowerRays wrote: ↑
Tue Sep 08, 2026 8:18 pm
Polaris lugs!
Perfect, this is just the solution I was hoping for. Thank you.

JRKsolar
Forum Guru
Posts: 160
Joined: Thu Aug 20, 2020 11:35 am
My RE system: Outback GS8048A
4) Kilovault HAB 7.5
2) Outback Flexmax 100 AFCI
12) Mission Solar 375W
8) Canadian Solar 395W
Tigo TS4-A2F

Re: The breaker box from Hell

Post by JRKsolar » Thu Sep 10, 2026 12:12 pm

Sunpower,
Thanks for the link, I've always wanted a good solution.

fcwlp
Forum Emperor
Posts: 1415
Joined: Wed Jan 22, 2020 9:40 am
My RE system: GS8048A, FM80 w/3,600W PV Fixed, FM80 w/2,700W on Zomeworks tracker, Mate3, 24 Trojan 2V L16 1100AH @ C20, Grid-Tied with Kohler 14RESA LPG Generator and MEP-803 Diesel if needed.

I install and maintain grid-tied and off-grid systems in my area and consult on solar system design/operation.
Location: 80 miles NE of Phoenix at 5500'

Re: The breaker box from Hell

Post by fcwlp » Sat Sep 12, 2026 8:42 am

The reason for the large gauge wire is to minimize the voltage drop after the long run. The reason to use Al is cost. I just did an install where the house was 500' away. With a 60A draw, to keep in the ~3.5% voltage drop range required 3/0 Al or 1/0 Cu. Al URD (direct burial) Quadruplex cost $2,350, Cu wires 2x 1/0 L1&L2, 1 AWG N and 4 AWG G cost is ~$12,000. Plus installation time in the trench for the URD was about 15 minutes versus many hours of assembling conduit and pulling 500' of wire.
.
On Al wires always be sure to use an antioxidant when making connections. The Polaris type connectors generally have an antioxidant in them.
.
To clean up your breaker box, put a junction box below the breaker box and make the Polaris splice within that box. All splices must be made in an accessible junction box. Makes the load center much cleaner.
.
It also time to replace your load center. It is definitely an obsolete panel with breakers no longer available. If it is a Federal Pacific or Challenger panel, I would definitely replace as the breakers have a history of overheating and causing fires.

pioneerMan
Forum Czar
Posts: 584
Joined: Wed Jan 09, 2019 3:40 pm
My RE system: 12 volt system
6 Lion Energy model 700 batteries, 12V each
12 solar panels (Mitsubishi 125 Watt)
Outback VFX2812 inverter and two FLEXmax 60 inverters
Mate 3s
Dual fuel 4500 watt generator
Location: Northern Utah

Re: The breaker box from Hell

Post by pioneerMan » Sat Sep 12, 2026 11:45 am

fcwlp wrote: ↑
Sat Sep 12, 2026 8:42 am
To clean up your breaker box, put a junction box below the breaker box and make the Polaris splice within that box. All splices must be made in an accessible junction box. Makes the load center much cleaner. It also time to replace your load center. It is definitely an obsolete panel with breakers no longer available. If it is a Federal Pacific or Challenger panel, I would definitely replace as the breakers have a history of overheating and causing fires.
Thank you for the advice. I think I'm going to hire an electrician.