Suggestions for New Array with (2) FM100s

Discussion about the FM100 AFCI Charge Controller
Post Reply
shoot24p
Forum Whiz
Posts: 28
Joined: Tue Sep 12, 2023 3:41 pm
My RE system: Off-Grid
(2) Radian GS8048A Inverters
(3) ReLion RB48V200 Batteries
(20) 300w Hyundai Panels (6kw)
(8) 370w LG Panels (3kw)
(2) FM100 AFCI Charge Controllers
Honda eu7000is Generator

Suggestions for New Array with (2) FM100s

Post by shoot24p » Fri Sep 11, 2026 3:01 pm

I'm looking into replacing my aging and miss-matched solar array. I'd like to max out what our system can safely handle without making any other upgrades other than the modules and rewiring strings as needed. I have an off-grid 48v system with (2) FM100s, (2) GS8048 Radians and 600ah of Relion LiFePO4 batteries.

We have a south-facing garage roof where we can easily replace our 28 panels, but no room for any more. We could also add more panels elsewhere on the house roof, but would like to avoid for now.

My installer is suggesting 440w Qcells. Does this seem like a good option? That would give us about 12.3kW. Looks like the (2) FM100s are rated for 14kW @48v. But I'm doubting the extra cost of building and wiring a second array would be worth the additional 2kW.

Also, our garage gets HOT in the summer, so I'm sure I'd be bumping into the output temperature limits anyway.

Any suggestions for how the strings should be configured? Matched and split equally between the two? I think this should be possible as long as it's OK to run the strings close to the 300v limit.

Any other specific modules I should be looking at? My installer is pretty solid with standard residential installations, (and they did ours originally) but they definitely don't specialize in Outback systems, so I want to do as much research as I can.

raysun
Forum Overlord
Posts: 13646
Joined: Tue Jul 26, 2016 5:57 am
My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid

Re: Suggestions for New Array with (2) FM100s

Post by raysun » Fri Sep 11, 2026 5:19 pm

440W is a good form factor and cost point. Qcells have a good track record.
Yes, I'd split what can fit on one roof between the two FM100.
You will need to do some careful temperature calculations for cold weather V(oc).
A 7S at 40V(oc) = 280V - uncomfortably close to thd 300V limit which cannot be exceeded without damage to the FM100.
6S3P is 18 per array.
Last edited by raysun on Fri Sep 11, 2026 8:12 pm, edited 2 times in total.

chrisski
Forum Czar
Posts: 532
Joined: Fri May 17, 2024 7:23 pm
My RE system: Dual 8048 Radian w/ Load Center
Mate 3
Flex max 100 afci X 4
Fortress eFlex 5.1 kWh Battery X 8
TP1000 for Internet Connectivity
Location: Central AZ, lowland desert

Re: Suggestions for New Array with (2) FM100s

Post by chrisski » Fri Sep 11, 2026 6:07 pm

Record cold in your area will drive how many in series. 5 x 400 watt panels use my area in super hot phoenix.

Six would exceed or be more nvomfirtanly close to the record cold limits with VOC.

My first array with 10 kW with 2 x FM 100s 4s3p to each controller.

raysun
Forum Overlord
Posts: 13646
Joined: Tue Jul 26, 2016 5:57 am
My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid

Re: Suggestions for New Array with (2) FM100s

Post by raysun » Fri Sep 11, 2026 8:19 pm

6S @ 40V(oc) is 240V. Is there a possibility of a 60V excursion? Most of my North European friends are pretty comfortable with 20% headroom.

shoot24p
Forum Whiz
Posts: 28
Joined: Tue Sep 12, 2023 3:41 pm
My RE system: Off-Grid
(2) Radian GS8048A Inverters
(3) ReLion RB48V200 Batteries
(20) 300w Hyundai Panels (6kw)
(8) 370w LG Panels (3kw)
(2) FM100 AFCI Charge Controllers
Honda eu7000is Generator

Re: Suggestions for New Array with (2) FM100s

Post by shoot24p » Fri Sep 11, 2026 8:31 pm

Thanks for the info. I live in North County San Diego, so we get a few frosty mornings, but rarely below 35F, record cold is somewhere around 10F.

I see…Splitting 28 panels evenly between the two controllers doesn’t leave many options for how to run them. Could I split it 12/16? Series of 4 on each? That would be just a hair over 7000w on one controller. I could just get 430w panels to be safe?

Definitely not room for any more, and I think if I get any less it wouldn’t be worth the effort.

raysun
Forum Overlord
Posts: 13646
Joined: Tue Jul 26, 2016 5:57 am
My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid

Re: Suggestions for New Array with (2) FM100s

Post by raysun » Fri Sep 11, 2026 10:31 pm

From a pragmatic standpoint two arrays: 4S4P and 4S3P would make the best use of the 28 panel real estate.

User avatar
Specialist
Forum Expert
Posts: 65
Joined: Sat Aug 22, 2020 11:25 pm
My RE system: 1x GS8048A
2z FM100
1x FM80
1x Mate3s
20x Qcell 400w
9x Global Power 420w
600ah Pytes v5.
Location: Puerto Rico

Re: Suggestions for New Array with (2) FM100s

Post by Specialist » Fri Sep 11, 2026 10:52 pm

Use the outback excell for pv sizing.

I have 5s3p of qcell 410w on 2x fm100.

You can match 6S3P in first fm100 and 5s3P on 2nd fm100

shoot24p
Forum Whiz
Posts: 28
Joined: Tue Sep 12, 2023 3:41 pm
My RE system: Off-Grid
(2) Radian GS8048A Inverters
(3) ReLion RB48V200 Batteries
(20) 300w Hyundai Panels (6kw)
(8) 370w LG Panels (3kw)
(2) FM100 AFCI Charge Controllers
Honda eu7000is Generator

Re: Suggestions for New Array with (2) FM100s

Post by shoot24p » Sat Sep 12, 2026 11:02 am

According to the sizing tool, looks like 5s3p is the sweet spot for 440w panels to safely max out the FM100. I'm going to see if there is a way to squeeze another two modules up there (30 total) so we can just run that to each charge controller.

If not, we'll go with 430w and use 4s4p and 4s3p. Thanks.

Post Reply