FM 80 controller status screen

Website & Forum Discussions
Check here for our Welcome Message

Moderators: administrator, OutBack Moderator Team, OutBack

Post Reply
bright.frank@gmail
Forum Junior Member
Posts: 1
Joined: Mon Jul 01, 2024 12:35 pm
My RE system: FLEXmax 80

FM 80 controller status screen

Post by bright.frank@gmail »

Basic question regarding my small off-grid system: I need an explanation for each of the readings on the status screen. That is, what “drives” each of the readings. I do have a Honda generator for backup, and it also charges the batteries (through the inverter) when it is running the house. Thank you.
raysun
Forum Overlord
Posts: 11415
Joined: Tue Jul 26, 2016 5:57 am
My RE system: Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid

Re: FM 80 controller status screen

Post by raysun »

The Flexmax 60/80 Owners Manual can be downloaded here: https://www.outbackpower.com/downloads/ ... manual.pdf
It details all the settings and readings.
The FM80 and inverter can charge the battery simultaneously, though autonomously. For them to work in concert, their charging parameters need to be set properly. Also, care should be taken to assure the combined charge rate does not exceed the battery's maximum rating.