FM60 Auxillary Output

Post by DaveM »

I'm planning to use an FM60's aux output, via a Mate3s to run auto gen start.
I'll be purchasing a GSCM through Atkinson Electronics, and asked them about the appropriate wiring.

I was told:
If the FM60 uses a dry contact (relay), then you do not need a relay in between the GSCM and the inverter.
However, I'm not sure if the FM60 uses a dry contact as their Aux output or not. I'm sure it must be in the manual, but I have missed it. Can someone confirm? Thanks!
raysun
Forum Overlord
Posts: 11402
Joined: Tue Jul 26, 2016 5:57 am
My RE system: Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid

Re: FM60 Auxillary Output

Post by raysun »

FlexMax AUX ports provide 12VDC when ON.
A small external 12V relay with (1A) inline fuse would provide dry contacts.
DaveM
Forum Junior Member
Posts: 4
Joined: Sat Sep 19, 2020 6:07 am
My RE system: Radian GS8048A
FM100 charge controller
18 of 320W modules
8 of Rolls 6CS-25PS @ 850Ah
FNDC
Mate3s
Hub10

Re: FM60 Auxillary Output

Post by DaveM »

Thank you very much!