FX2524MT Trips GFCI Dock Pedestal

Discussion about OutBack Inverters in Marine Applications

Moderators: OutBack Moderator Team, OutBack

Post Reply
CDrive
Forum Junior Member
Posts: 4
Joined: Tue Feb 06, 2024 11:26 am
My RE system: FX2524MT

FX2524MT Trips GFCI Dock Pedestal

Post by CDrive »

More often than not my inverter trips dock power pedestals with GFCI breakers which forces me to bypass.

It is not consistent though. Recently I was plugged into shore power for 4 days before the GFCI tripped and I had to bypass.

After reviewing the manual I am wondering if there is a problem with the neutral-ground switching capability in my unit?

Thanks >> Joe
raysun
Forum Overlord
Posts: 11402
Joined: Tue Jul 26, 2016 5:57 am
My RE system: Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid

Re: FX2524MT Trips GFCI Dock Pedestal

Post by raysun »

CDrive wrote: Fri May 24, 2024 3:05 pm More often than not my inverter trips dock power pedestals with GFCI breakers which forces me to bypass.

It is not consistent though. Recently I was plugged into shore power for 4 days before the GFCI tripped and I had to bypass.

After reviewing the manual I am wondering if there is a problem with the neutral-ground switching capability in my unit?

Thanks >> Joe
The "M" series does have neutral-ground bond switching that opens upon AC Input.
However, the general advice is not to provide AC Input to the inverter via a GFCI protected circuit.
Also, is the pedestal circuit GFCI, or GFCI/AFCI?
CDrive
Forum Junior Member
Posts: 4
Joined: Tue Feb 06, 2024 11:26 am
My RE system: FX2524MT

Re: FX2524MT Trips GFCI Dock Pedestal

Post by CDrive »

Thanks for the reply.

Not sure about GFCI/AFCI. The breaker I am on now is labelled GFR480-1.

Having to deal with these newer pedestals is becoming more common as marinas upgrade.

Do the newer inverters have this same issue?

Thanks >> Joe
raysun
Forum Overlord
Posts: 11402
Joined: Tue Jul 26, 2016 5:57 am
My RE system: Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid

Re: FX2524MT Trips GFCI Dock Pedestal

Post by raysun »

CDrive wrote: Sun May 26, 2024 9:21 am Thanks for the reply.

Not sure about GFCI/AFCI. The breaker I am on now is labelled GFR480-1.

Having to deal with these newer pedestals is becoming more common as marinas upgrade.

Do the newer inverters have this same issue?

Thanks >> Joe
The most active vendor in the mobile/marine arena is Victron. I've noticed on their community site, several mentions of an AC input isolation transformer, and assume that's partly to address such an issue.
I would suspect feeding an inverter grid input via AFCI or GFCI is going to have this result with a broad range of manufacturer's models.
CDrive
Forum Junior Member
Posts: 4
Joined: Tue Feb 06, 2024 11:26 am
My RE system: FX2524MT

Re: FX2524MT Trips GFCI Dock Pedestal

Post by CDrive »

Not planning to consider a different MFR. I have been very happy with the Outback overall.

I have seen iso xfrmrs mentioned in my searches but in a severe case wouldn't they mask a potentially hazardous condition?

Thanks >> Joe
raysun
Forum Overlord
Posts: 11402
Joined: Tue Jul 26, 2016 5:57 am
My RE system: Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid

Re: FX2524MT Trips GFCI Dock Pedestal

Post by raysun »

CDrive wrote: Sun May 26, 2024 10:01 am Not planning to consider a different MFR. I have been very happy with the Outback overall.

I have seen iso xfrmrs mentioned in my searches but in a severe case wouldn't they mask a potentially hazardous condition?

Thanks >> Joe
Mentioned Victron for the frequency of reference to this sort of issue.
Questions about marine AC safety are out of my lane. A good marine electrician should be able to help with this.
CDrive
Forum Junior Member
Posts: 4
Joined: Tue Feb 06, 2024 11:26 am
My RE system: FX2524MT

Re: FX2524MT Trips GFCI Dock Pedestal

Post by CDrive »

Your input is much appreciated.

Now go enjoy the weekend!

Best >> Joe