temp sensor fault

Post by Aore Adventures »

gday guys started to get the attached fault on #4 inverter over the weekend while charging from our genset, we have had very little sun the last 3 weeks.

it seems to clear and still function normally , but you can see that optics loses the temp read out on the transformer then reappears.

i have issues with this inverter before having to change two sets of cards the quas stack was commissioned approx September 2020

ideas appreciated cheers
Attachments
Screenshot 2024-04-01 181817.png
Screenshot 2024-04-01 185850.png
Screenshot 2024-04-01 181950.png
raysun
Forum Overlord
Posts: 10865
Joined: Tue Jul 26, 2016 5:57 am
My RE system: Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid

Re: temp sensor fault

Post by raysun »

The internal temperature sensor is mounted to the bottom of the transformer frame (with hi temp silicon glue, I think.)
It's this part: https://www.zonnaenergy.com/parts/outba ... mp-sensor/

The alerts and disappearing temperature reading sounds like the sensor may be intermittent, or the connection on the control board (?) is loose or corroded.
User avatar
Aore Adventures
Forum Virtuoso
Posts: 94
Joined: Sun May 29, 2016 2:42 am
My RE system: Quad stack VFXR3048E
5 x FM80'S
1 x FlexNet DC
1 x Mate 3s
2 x Hub 10
45 x REC 370 watt Alpha Panels
24 x 2900ah 2v Hoppecke flooded cells in solar air-conditioned Battery room

1 x VFXR 3048E
2 x FM80
1 x FlexNet DC
1 x Hub 10
18 x REC 370 watt Alpha Panels
24 x 2170ah 2v Hoppecke flooded cells

Kubota 18kva backup gen set
Dunlite 12kva inverter back up gen set
Generator start battery solar charger 80watt panel morning star shs-10 controller
Location: Aore Island Vanuatu
Contact:

Re: temp sensor fault

Post by Aore Adventures »

mate you are a champion, with all info regarding outback

i have contacted my supplier to see what they will do to fix the issue as it should be still under the 5yr warranty period.

cheers
raysun
Forum Overlord
Posts: 10865
Joined: Tue Jul 26, 2016 5:57 am
My RE system: Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid

Re: temp sensor fault

Post by raysun »

Aore Adventures wrote: Mon Apr 01, 2024 5:49 pm mate you are a champion, with all info regarding outback

i have contacted my supplier to see what they will do to fix the issue as it should be still under the 5yr warranty period.

cheers
Yep. Good luck!