OpticsRE weidness

Discussion about the OutBack OpticsRE system monitor

Moderators: OutBack Moderator Team, OutBack

User avatar
sodamo
Forum Emperor
Posts: 1344
Joined: Mon Apr 03, 2006 1:55 am
My RE system: Totally off grid - Hamakua side, Big Island, Hi

36 Trina 280 & 16 Phono 250 in 48 volt array (fixed) 14080w
Adding 12 Hyundai 365 (4380) 18460w total
Radians GG8048A/GS4048A w GSLCs
4 FM 80 charge controllers
Hub 10.3
FNDC w/3 shunts
Mate 3s
OpticsRE - MMKL - Ninole Hi
15 SimpliPhi 3.8 (57kw) (1125 AH)
14Kw Kohler 14RESA Propane

Charging Only
2FX3048T
Hub
FNDC. - shared shunt feeds from Radian FNDC
Mate 3s
10Kw MEP 803a Military gen

Honda EU7000i

Davis VantagePro2 Wx Station
On line at: https://www.wunderground.com/dashboard/pws/KHININOL2
Location: Ninole, Hi

OpticsRE weidness

Post by sodamo »

Something going on?
Last night my optics going nuts.
soc graph crashed to zero.
pV showed as producing hundreds of Kwh power even though dark, spiking to over 42,000 a couple times.
This morning, my primary system has been renamed.

???
David
User avatar
Bryce Millet
Software Engineering
Posts: 308
Joined: Tue Nov 08, 2016 12:46 pm

Re: OpticsRE weidness

Post by Bryce Millet »

From the software side of things: Looks like your charge controller on port 9 started pushing a bunch of erroneous data around the same time the SOC went haywire and crashed to zero. The other charge controller data seems fine.

Our logs are showing a "SD Card Bad or Unformatted" error and a "Inverter on port 1 has detected a Battery Voltage Sensor Failure ." So if you have not done so, you may want to remove the SD card and do a full FAT32 file format after saving any files on it that you would like to keep. Corrupted SD cards can cause all kinds of strange behavior to happen with data reporting to OpticsRE.

Beyond that, I don't have much I can recommend you do besides maybe a power cycle of the Mate3s and monitoring the system to see if additional errors are appearing. The FN-DC might need to be recalibrated if it's consistently reporting the wrong state of charge even after a reboot, so keep an eye on it to make sure the percentage looks correct for your voltage levels after a charging cycle.
Bryce Millet
Software Engineering


Alpha Technologies Inc. | OutBack Power Technologies
3767 Alpha Way Bellingham WA 98226 USA
http://www.alpha.com | http://outbackpower.com/
wolfridge
Forum Member
Posts: 20
Joined: Mon Nov 05, 2018 10:27 am
My RE system: Manson Creek B.C.
36 Hanwha 300watt panels
2-FM100
Radian GS8048A
OUTBACK Load Center GSLC 175-PV-120/240
Outback FN-DC Flexnet
Mate3s
Sacred Sun 48 Volt 500 Ahr Carbon Battery Bank
Perkins 10kw and two Kubota 8kw
Way Off Grid
Location: Manson Creek B.C.

Re: OpticsRE weidness

Post by wolfridge »

Same has been happening to me the last couple days. Went through all the trouble shooting steps with support and they concluded my Mate3s was faulty and needed replacement. I have ordered a new one.
My site has named itself Outback Power Technologies. When I correct the name it only sticks for a few minutes and then reverts back. My system shows generator running and charging at random times. Solar charging is all over. Battery charge changes randomly.
Replaced SD card no change. Erased logs and renewed them. Events show constant trying to upgrade all parts of system including Mate3s.

Reading from the Mate3s screen remain correct and accurate. System works normally/
User avatar
sodamo
Forum Emperor
Posts: 1344
Joined: Mon Apr 03, 2006 1:55 am
My RE system: Totally off grid - Hamakua side, Big Island, Hi

36 Trina 280 & 16 Phono 250 in 48 volt array (fixed) 14080w
Adding 12 Hyundai 365 (4380) 18460w total
Radians GG8048A/GS4048A w GSLCs
4 FM 80 charge controllers
Hub 10.3
FNDC w/3 shunts
Mate 3s
OpticsRE - MMKL - Ninole Hi
15 SimpliPhi 3.8 (57kw) (1125 AH)
14Kw Kohler 14RESA Propane

Charging Only
2FX3048T
Hub
FNDC. - shared shunt feeds from Radian FNDC
Mate 3s
10Kw MEP 803a Military gen

Honda EU7000i

Davis VantagePro2 Wx Station
On line at: https://www.wunderground.com/dashboard/pws/KHININOL2
Location: Ninole, Hi

Re: OpticsRE weidness

Post by sodamo »

Thanks, guys
Kinda strange. Especially the Optics antics.
Will monitor over weekend. Called OB tech, but too late and left msg. Hopefully resolve Monday.

This has been a very reliable system up until last month
David
User avatar
sodamo
Forum Emperor
Posts: 1344
Joined: Mon Apr 03, 2006 1:55 am
My RE system: Totally off grid - Hamakua side, Big Island, Hi

36 Trina 280 & 16 Phono 250 in 48 volt array (fixed) 14080w
Adding 12 Hyundai 365 (4380) 18460w total
Radians GG8048A/GS4048A w GSLCs
4 FM 80 charge controllers
Hub 10.3
FNDC w/3 shunts
Mate 3s
OpticsRE - MMKL - Ninole Hi
15 SimpliPhi 3.8 (57kw) (1125 AH)
14Kw Kohler 14RESA Propane

Charging Only
2FX3048T
Hub
FNDC. - shared shunt feeds from Radian FNDC
Mate 3s
10Kw MEP 803a Military gen

Honda EU7000i

Davis VantagePro2 Wx Station
On line at: https://www.wunderground.com/dashboard/pws/KHININOL2
Location: Ninole, Hi

Re: OpticsRE weidness

Post by sodamo »

At the suggestion of my installer, we removed the Mate3?
Made it thru the night without a hiccup.
Just lucky or found the problem? Don’t know.
Will keep this Mate3 out of system until I can talk with OB tech Monday.
David
wolfridge
Forum Member
Posts: 20
Joined: Mon Nov 05, 2018 10:27 am
My RE system: Manson Creek B.C.
36 Hanwha 300watt panels
2-FM100
Radian GS8048A
OUTBACK Load Center GSLC 175-PV-120/240
Outback FN-DC Flexnet
Mate3s
Sacred Sun 48 Volt 500 Ahr Carbon Battery Bank
Perkins 10kw and two Kubota 8kw
Way Off Grid
Location: Manson Creek B.C.

Re: OpticsRE weidness

Post by wolfridge »

Support recommended the same for me, but I left it in. It works normally just reports wrong to the Opticre. I left it in as this time of year we use the Generator autostart and it is working normally. Good Luck, my new one is on its way.
User avatar
sodamo
Forum Emperor
Posts: 1344
Joined: Mon Apr 03, 2006 1:55 am
My RE system: Totally off grid - Hamakua side, Big Island, Hi

36 Trina 280 & 16 Phono 250 in 48 volt array (fixed) 14080w
Adding 12 Hyundai 365 (4380) 18460w total
Radians GG8048A/GS4048A w GSLCs
4 FM 80 charge controllers
Hub 10.3
FNDC w/3 shunts
Mate 3s
OpticsRE - MMKL - Ninole Hi
15 SimpliPhi 3.8 (57kw) (1125 AH)
14Kw Kohler 14RESA Propane

Charging Only
2FX3048T
Hub
FNDC. - shared shunt feeds from Radian FNDC
Mate 3s
10Kw MEP 803a Military gen

Honda EU7000i

Davis VantagePro2 Wx Station
On line at: https://www.wunderground.com/dashboard/pws/KHININOL2
Location: Ninole, Hi

Re: OpticsRE weidness

Post by sodamo »

We use autostart as well, but pretty much weather dependent. If decent weather I’ll just not run pool and hot tub to keep load down, otherwise I could just do manual gen.
David
wolfridge
Forum Member
Posts: 20
Joined: Mon Nov 05, 2018 10:27 am
My RE system: Manson Creek B.C.
36 Hanwha 300watt panels
2-FM100
Radian GS8048A
OUTBACK Load Center GSLC 175-PV-120/240
Outback FN-DC Flexnet
Mate3s
Sacred Sun 48 Volt 500 Ahr Carbon Battery Bank
Perkins 10kw and two Kubota 8kw
Way Off Grid
Location: Manson Creek B.C.

Re: OpticsRE weidness

Post by wolfridge »

We are in our snow season. Lucky if we see the sun but all the summer folks are gone now. Nice and quiet. No forest fires.
User avatar
sodamo
Forum Emperor
Posts: 1344
Joined: Mon Apr 03, 2006 1:55 am
My RE system: Totally off grid - Hamakua side, Big Island, Hi

36 Trina 280 & 16 Phono 250 in 48 volt array (fixed) 14080w
Adding 12 Hyundai 365 (4380) 18460w total
Radians GG8048A/GS4048A w GSLCs
4 FM 80 charge controllers
Hub 10.3
FNDC w/3 shunts
Mate 3s
OpticsRE - MMKL - Ninole Hi
15 SimpliPhi 3.8 (57kw) (1125 AH)
14Kw Kohler 14RESA Propane

Charging Only
2FX3048T
Hub
FNDC. - shared shunt feeds from Radian FNDC
Mate 3s
10Kw MEP 803a Military gen

Honda EU7000i

Davis VantagePro2 Wx Station
On line at: https://www.wunderground.com/dashboard/pws/KHININOL2
Location: Ninole, Hi

Re: OpticsRE weidness

Post by sodamo »

Start of our rainy season, but we are in bad drought. Only 6 inches rain this month and that was mostly this week. My average for Nov is 18, but lowest I’ve recorded is 9.01. We are at 1100 ft elevation, so cloud cover can affect us.
David
JRHill
Forum Emperor
Posts: 2590
Joined: Thu Feb 17, 2011 11:12 am
My RE system: 48v OB inverter and charge controller, hub and mate3s.
Location: PNW
Contact:

Re: OpticsRE weidness

Post by JRHill »

Wow.... A drought with "Only 6 inches rain this month." That's just under 1/2 of a year's total for us. :lol:
User avatar
sodamo
Forum Emperor
Posts: 1344
Joined: Mon Apr 03, 2006 1:55 am
My RE system: Totally off grid - Hamakua side, Big Island, Hi

36 Trina 280 & 16 Phono 250 in 48 volt array (fixed) 14080w
Adding 12 Hyundai 365 (4380) 18460w total
Radians GG8048A/GS4048A w GSLCs
4 FM 80 charge controllers
Hub 10.3
FNDC w/3 shunts
Mate 3s
OpticsRE - MMKL - Ninole Hi
15 SimpliPhi 3.8 (57kw) (1125 AH)
14Kw Kohler 14RESA Propane

Charging Only
2FX3048T
Hub
FNDC. - shared shunt feeds from Radian FNDC
Mate 3s
10Kw MEP 803a Military gen

Honda EU7000i

Davis VantagePro2 Wx Station
On line at: https://www.wunderground.com/dashboard/pws/KHININOL2
Location: Ninole, Hi

Re: OpticsRE weidness

Post by sodamo »

Well Jim, normal for us is 120-140 inches a year.
We don’t have public water or well, just catchment.
David
raysun
Forum Overlord
Posts: 10391
Joined: Tue Jul 26, 2016 5:57 am
My RE system: Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid

Re: OpticsRE weidness

Post by raysun »

At the other end of the island, we live in a mesic dry forest and would consider it exceptional to get 36" of rain in a year.
User avatar
sodamo
Forum Emperor
Posts: 1344
Joined: Mon Apr 03, 2006 1:55 am
My RE system: Totally off grid - Hamakua side, Big Island, Hi

36 Trina 280 & 16 Phono 250 in 48 volt array (fixed) 14080w
Adding 12 Hyundai 365 (4380) 18460w total
Radians GG8048A/GS4048A w GSLCs
4 FM 80 charge controllers
Hub 10.3
FNDC w/3 shunts
Mate 3s
OpticsRE - MMKL - Ninole Hi
15 SimpliPhi 3.8 (57kw) (1125 AH)
14Kw Kohler 14RESA Propane

Charging Only
2FX3048T
Hub
FNDC. - shared shunt feeds from Radian FNDC
Mate 3s
10Kw MEP 803a Military gen

Honda EU7000i

Davis VantagePro2 Wx Station
On line at: https://www.wunderground.com/dashboard/pws/KHININOL2
Location: Ninole, Hi

Re: OpticsRE weidness

Post by sodamo »

Survived another night without issue.

Will put the Mate3 back into system to make sure OpticsRE is active and call tech support. Will they agree Mate3 is my problem? I don’t know for sure it is, but will ask. I’m hopefull issue has been identified.
David
User avatar
sodamo
Forum Emperor
Posts: 1344
Joined: Mon Apr 03, 2006 1:55 am
My RE system: Totally off grid - Hamakua side, Big Island, Hi

36 Trina 280 & 16 Phono 250 in 48 volt array (fixed) 14080w
Adding 12 Hyundai 365 (4380) 18460w total
Radians GG8048A/GS4048A w GSLCs
4 FM 80 charge controllers
Hub 10.3
FNDC w/3 shunts
Mate 3s
OpticsRE - MMKL - Ninole Hi
15 SimpliPhi 3.8 (57kw) (1125 AH)
14Kw Kohler 14RESA Propane

Charging Only
2FX3048T
Hub
FNDC. - shared shunt feeds from Radian FNDC
Mate 3s
10Kw MEP 803a Military gen

Honda EU7000i

Davis VantagePro2 Wx Station
On line at: https://www.wunderground.com/dashboard/pws/KHININOL2
Location: Ninole, Hi

Re: OpticsRE weidness

Post by sodamo »

Ok, this is frustrating. 9 calls to tech support this morning, 8 dropped, finally get my turn and tech puts me in another cue. Not trusting I wouldn’t drop again, left call back number and back to waiting.
David
JRHill
Forum Emperor
Posts: 2590
Joined: Thu Feb 17, 2011 11:12 am
My RE system: 48v OB inverter and charge controller, hub and mate3s.
Location: PNW
Contact:

Re: OpticsRE weidness

Post by JRHill »

Yeah, I went through that once with OB TS. When I did get call backs it was the worst possible time for a connection and I don't know where the problem was so not placing any blame. Not just OB but for all of these things it would be cool to get a text saying "We're calling you in 5 minutes." That also solves the thing of sitting around awaiting the call back and it doesn't happen. It would save the time of all parties involved.
User avatar
sodamo
Forum Emperor
Posts: 1344
Joined: Mon Apr 03, 2006 1:55 am
My RE system: Totally off grid - Hamakua side, Big Island, Hi

36 Trina 280 & 16 Phono 250 in 48 volt array (fixed) 14080w
Adding 12 Hyundai 365 (4380) 18460w total
Radians GG8048A/GS4048A w GSLCs
4 FM 80 charge controllers
Hub 10.3
FNDC w/3 shunts
Mate 3s
OpticsRE - MMKL - Ninole Hi
15 SimpliPhi 3.8 (57kw) (1125 AH)
14Kw Kohler 14RESA Propane

Charging Only
2FX3048T
Hub
FNDC. - shared shunt feeds from Radian FNDC
Mate 3s
10Kw MEP 803a Military gen

Honda EU7000i

Davis VantagePro2 Wx Station
On line at: https://www.wunderground.com/dashboard/pws/KHININOL2
Location: Ninole, Hi

Re: OpticsRE weidness

Post by sodamo »

Over an hour on phone with Kevin at Tech support 🤙

I had 8 dropped calls before talking with anyone and Kevin have to call me back 5 times. Ahhh, wifi calling and poor att signal.

Kevin was great.
Took awhile, but determined at problem with the AUX Relay stack which affected AGS gen start. New board coming.

Forgot to ask how to get my OpticsRE system name changed back.
Will update once I get new board.

I agree JR, don’t like unknown waits.
David
wolfridge
Forum Member
Posts: 20
Joined: Mon Nov 05, 2018 10:27 am
My RE system: Manson Creek B.C.
36 Hanwha 300watt panels
2-FM100
Radian GS8048A
OUTBACK Load Center GSLC 175-PV-120/240
Outback FN-DC Flexnet
Mate3s
Sacred Sun 48 Volt 500 Ahr Carbon Battery Bank
Perkins 10kw and two Kubota 8kw
Way Off Grid
Location: Manson Creek B.C.

Re: OpticsRE weidness

Post by wolfridge »

You can right click on your site when you log in, the click on settings devices and mate3. There you can name the site
User avatar
Bryce Millet
Software Engineering
Posts: 308
Joined: Tue Nov 08, 2016 12:46 pm

Re: OpticsRE weidness

Post by Bryce Millet »

sodamo wrote: Mon Nov 20, 2023 2:09 pm Over an hour on phone with Kevin at Tech support 🤙

I had 8 dropped calls before talking with anyone and Kevin have to call me back 5 times. Ahhh, wifi calling and poor att signal.

Kevin was great.
Took awhile, but determined at problem with the AUX Relay stack which affected AGS gen start. New board coming.

Forgot to ask how to get my OpticsRE system name changed back.
Will update once I get new board.

I agree JR, don’t like unknown waits.
See Wolfridge's reply above for getting the system name changed.

You should be able to find it in the System Tools menu (Gear in the top right corner) -> Devices. The field at the top should be "System Name". If you change that it should update.
Bryce Millet
Software Engineering


Alpha Technologies Inc. | OutBack Power Technologies
3767 Alpha Way Bellingham WA 98226 USA
http://www.alpha.com | http://outbackpower.com/
JRHill
Forum Emperor
Posts: 2590
Joined: Thu Feb 17, 2011 11:12 am
My RE system: 48v OB inverter and charge controller, hub and mate3s.
Location: PNW
Contact:

Re: OpticsRE weidness

Post by JRHill »

Sigh. (five more characters) Sigh.
User avatar
sodamo
Forum Emperor
Posts: 1344
Joined: Mon Apr 03, 2006 1:55 am
My RE system: Totally off grid - Hamakua side, Big Island, Hi

36 Trina 280 & 16 Phono 250 in 48 volt array (fixed) 14080w
Adding 12 Hyundai 365 (4380) 18460w total
Radians GG8048A/GS4048A w GSLCs
4 FM 80 charge controllers
Hub 10.3
FNDC w/3 shunts
Mate 3s
OpticsRE - MMKL - Ninole Hi
15 SimpliPhi 3.8 (57kw) (1125 AH)
14Kw Kohler 14RESA Propane

Charging Only
2FX3048T
Hub
FNDC. - shared shunt feeds from Radian FNDC
Mate 3s
10Kw MEP 803a Military gen

Honda EU7000i

Davis VantagePro2 Wx Station
On line at: https://www.wunderground.com/dashboard/pws/KHININOL2
Location: Ninole, Hi

Re: OpticsRE weidness

Post by sodamo »

Not a right click for me, but readily found how to rename. Thanks guys.
David
User avatar
EA6LE-ONE
Forum Czar
Posts: 937
Joined: Tue May 05, 2020 7:51 am
My RE system: System 1:
MATE3s, 3 x Radian GS8048A,
6 x FLEXmax 100, HUB10,
24 x SimpliPhi 48V,
1 x FLEXnet DC, 6 x FLEXware ICS Plus,
78 x PANASONIC VBHN325SA17 325W

System 2:
MATE3s, Radian GS8048A,
2 x FLEXmax 100, HUB10
15 x SimpliPhi 48V,
1 x FLEXnet DC, 2 x FLEXware ICS
21 x PANASONIC VBHN325SA17 325W
Location: Providenciales, Turks & Caicos Isl.

Re: OpticsRE weidness

Post by EA6LE-ONE »

sodamo wrote: Fri Nov 17, 2023 1:39 pm Something going on?
Last night my optics going nuts.
soc graph crashed to zero.
pV showed as producing hundreds of Kwh power even though dark, spiking to over 42,000 a couple times.
This morning, my primary system has been renamed.

???
I got this weird events happening over time. there is nothing wrong with you system if is very rare. 2 of my system names were changed. this seem to be a glitch with opticsRE for the name change. for the power spikes could be some errors in the data collection or when uploaded to opticsRE.
if is a every day occurrence, then probably something wrong with the mate.
User avatar
EA6LE-ONE
Forum Czar
Posts: 937
Joined: Tue May 05, 2020 7:51 am
My RE system: System 1:
MATE3s, 3 x Radian GS8048A,
6 x FLEXmax 100, HUB10,
24 x SimpliPhi 48V,
1 x FLEXnet DC, 6 x FLEXware ICS Plus,
78 x PANASONIC VBHN325SA17 325W

System 2:
MATE3s, Radian GS8048A,
2 x FLEXmax 100, HUB10
15 x SimpliPhi 48V,
1 x FLEXnet DC, 2 x FLEXware ICS
21 x PANASONIC VBHN325SA17 325W
Location: Providenciales, Turks & Caicos Isl.

Re: OpticsRE weidness

Post by EA6LE-ONE »

I had couple weird reading over 3 years on one system
error1.jpg
error2.jpg
User avatar
EA6LE-ONE
Forum Czar
Posts: 937
Joined: Tue May 05, 2020 7:51 am
My RE system: System 1:
MATE3s, 3 x Radian GS8048A,
6 x FLEXmax 100, HUB10,
24 x SimpliPhi 48V,
1 x FLEXnet DC, 6 x FLEXware ICS Plus,
78 x PANASONIC VBHN325SA17 325W

System 2:
MATE3s, Radian GS8048A,
2 x FLEXmax 100, HUB10
15 x SimpliPhi 48V,
1 x FLEXnet DC, 2 x FLEXware ICS
21 x PANASONIC VBHN325SA17 325W
Location: Providenciales, Turks & Caicos Isl.

Re: OpticsRE weidness

Post by EA6LE-ONE »

this is on the other system:
error3.jpg
error4.jpg
User avatar
sodamo
Forum Emperor
Posts: 1344
Joined: Mon Apr 03, 2006 1:55 am
My RE system: Totally off grid - Hamakua side, Big Island, Hi

36 Trina 280 & 16 Phono 250 in 48 volt array (fixed) 14080w
Adding 12 Hyundai 365 (4380) 18460w total
Radians GG8048A/GS4048A w GSLCs
4 FM 80 charge controllers
Hub 10.3
FNDC w/3 shunts
Mate 3s
OpticsRE - MMKL - Ninole Hi
15 SimpliPhi 3.8 (57kw) (1125 AH)
14Kw Kohler 14RESA Propane

Charging Only
2FX3048T
Hub
FNDC. - shared shunt feeds from Radian FNDC
Mate 3s
10Kw MEP 803a Military gen

Honda EU7000i

Davis VantagePro2 Wx Station
On line at: https://www.wunderground.com/dashboard/pws/KHININOL2
Location: Ninole, Hi

Re: OpticsRE weidness

Post by sodamo »

Hmmmm

So yesterday, as means to ferret out whether I had a Mate3 program, Tech Support linked my secondary Mate3 to OpticsRE and my Radian system via MAC address. Currently the Radian system appears to be reporting OpticsRE via its original Mate3 just fine.
However, I want to return the secondary Mate3 to my FX system. Completely verified and changed settings for the FX side. If I go to Online OpticsRE, that system shows but Gateway is not online. Doubled checked connects and rebooted. Nada
So I went to add a new system and it says MAC address already in use, call Support.

Am I missing something? Anyway to get reconnected without playing phone tag?
David
raysun
Forum Overlord
Posts: 10391
Joined: Tue Jul 26, 2016 5:57 am
My RE system: Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid

Re: OpticsRE weidness

Post by raysun »

Anyway to get reconnected without playing phone tag?
TMK - the MAC address transfer has to be done on the "back end" by Support.
The only User method is to register it as a new system, losing all data previously associated with the Mate's MAC address.