GVFX3648 maximums?

Discussion about OutBack Inverters in Grid Tie Applications

Moderators: OutBack Moderator Team, OutBack

Post Reply
User avatar
shastatodd
Forum Expert
Posts: 65
Joined: Thu Oct 17, 2002 11:01 pm
My RE system: SYSTEM ONE:
A single, turbocharged GVFX-3648 inverter (includes DT kludge for generator charging); 4.5 kW STC of actively tracked PV; turbocharged FM80 charge controller; eight, Surrette FC-420 lead calcium wet cell batteries; E-Meter (Link-10).

SYSTEM TWO:
A single, sealed GTFX-2524 inverter; 2.0 kW STC of actively tracked PV; turbocharged FM60 charge controller; four, Surrette FC-420 lead calcium wet cell batteries; E-Meter (Link-10).

The combined inverter systems typically sell an average of 20 kWh/day.
Peak summer selling is around 40 kWh/day.
Location: Mt. Shasta, CA.
Contact:

GVFX3648 maximums?

Post by shastatodd »

typical cold sell.png
Has anyone here worked with Outback FX inverters selling to the grid?
I'm asking this because I'm curious what the safe maximum load point is?

I recently had to change out a rack of failed modules and the new ones put out a larger amount of power than the old ones, which is taking my selling wattage from 2.8 kW to about 3.2 KW. The inverter ran pretty hot selling 2.8 so I'm wondering if it's going to survive selling 3.2 even though it's supposedly rated at 3.6 kW.

The FETS and capacitors are fine, but the transformer seems to be the big heat source.

I have seen the transformer typically run at 100 "counts" or 174f. Working hard this goes to 80 "counts" (lower is hotter) or 193f. The software throttles the unit back at 38 "counts" or 250f.
The FETS run around 165 "counts" or 121f. Throttle back on them is 79 "counts" or 194f.

Also that 30 amp cube relay on the AC board seems to fail after a few years of work. Yes 30 amps at 120 volts = 3600 watts, but even running it at 2800 watts (23 amps) seems to be hard on it.

This is of course dependent on ambient air temperatures and fortunately PV output sags with temp so those two things work together.
Last edited by shastatodd on Mon Nov 13, 2023 2:54 pm, edited 1 time in total.
User avatar
Mike Curran
Forum Emperor
Posts: 3195
Joined: Sat Aug 28, 2004 6:28 pm
My RE system: Outback - Garage roof (2007/2017):
- 8 (2x4) Evergreen 180's into one FM80 (2007/2020 - replaced MX60)
- 6 (2×3) ALEO S79-300's into one FM80 (2017)
- 2 grid-tied VFXR3524A-01's series stacked, replaced GVFX's (2020)
- 12 Surrette/Rolls 2V x 1766Ah (2007)
- Hub10.3, Mate3s, FNDC, RTS. Tigo ES maximizers on each PV module.

Westinghouse Solar - Barn roof: (2012)
- 30 (2x15) 235W panels with Enphase M215 microinverters, grid-tied

Outback Skybox - Barn roof: (2019)
- 14 Talesun 275W in series (DC array input to SB inverter/charger)
- 3 SimpliPhi 3.8 batteries, 48V, 225Ah total
- AC coupled input from 14 Talesun 275W (manually switched during outages), Enphase M215 microinverters

Battery systems operate in grid-tied, net metering w/backup mode
All self-designed and self-installed
Location: Chagrin Falls, Ohio

Re: GVFX3648 maximums?

Post by Mike Curran »

I used to have a couple of GVFX3624s that sold to grid but my PV array (3.24kw) isn't large enough to really tax them. I will say that selling to grid shouldn't place any more stress on your inverter than an equivalent in loads does. Make sure the cooling intake filter(s) are clean - I found mine pretty gummed up once.
20180522_130726.jpg
https://ei.tigoenergy.com/p/pZXn7SZQyO45
https://enlighten.enphaseenergy.com/public/systems/Hctc107221
As of 8/25/23 Westinghouse array down to 21 panels, Skybox DC array out of commission.
User avatar
shastatodd
Forum Expert
Posts: 65
Joined: Thu Oct 17, 2002 11:01 pm
My RE system: SYSTEM ONE:
A single, turbocharged GVFX-3648 inverter (includes DT kludge for generator charging); 4.5 kW STC of actively tracked PV; turbocharged FM80 charge controller; eight, Surrette FC-420 lead calcium wet cell batteries; E-Meter (Link-10).

SYSTEM TWO:
A single, sealed GTFX-2524 inverter; 2.0 kW STC of actively tracked PV; turbocharged FM60 charge controller; four, Surrette FC-420 lead calcium wet cell batteries; E-Meter (Link-10).

The combined inverter systems typically sell an average of 20 kWh/day.
Peak summer selling is around 40 kWh/day.
Location: Mt. Shasta, CA.
Contact:

Re: GVFX3648 maximums?

Post by shastatodd »

My power building has filtered air so years ago I pulled out that inverter intake air filter as well as the case's "bug screens" to improve the air flow.