2xFXR3048A in Master/Slave not giving 240V
Moderators: OutBack Moderator Team, OutBack
2xFXR3048A in Master/Slave not giving 240V
As title suggests....more details:
Setup with HUB10 & Mate3
Inverter ranking: port 1 Master, port 2 Slave
GridZero configuration
600AH lithium battery
5500W solar support via 2x Flexmax80
Inverters FWs match
Master outputs 120V and positively synchronized with associated grid leg
Slave outputs 120V but negatively synchronized with its associated grid leg
So grid terminals (across the 2 inverters) is 240V
But inverter output (across the 2 inverters) is 0V
Mate does not indicate any errors.....any suggestions?
Setup with HUB10 & Mate3
Inverter ranking: port 1 Master, port 2 Slave
GridZero configuration
600AH lithium battery
5500W solar support via 2x Flexmax80
Inverters FWs match
Master outputs 120V and positively synchronized with associated grid leg
Slave outputs 120V but negatively synchronized with its associated grid leg
So grid terminals (across the 2 inverters) is 240V
But inverter output (across the 2 inverters) is 0V
Mate does not indicate any errors.....any suggestions?
-
- Forum Overlord
- Posts: 10407
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid
Re: 2xFXR3048A in Master/Slave not giving 240V
A few suggestions:
• Confirm the AC Input wiring for the two inverters is: Master Hot = L1, Neutral = N; L2 Sub-Phase Master = Hot = L2, Neutral = N.
• Confirm the Stacking configuration is Series (Classic) stacking and not Parallel.
• On the Hub: Inverter 1 (Master) on Port 1; Inverter 2 (L2 Sub-Phase Master) on Port 2
• In the Hub: Confirm jumpers are set for Series stacking. Hub label showing jumpers set for Series stacking.
• Confirm the AC Input wiring for the two inverters is: Master Hot = L1, Neutral = N; L2 Sub-Phase Master = Hot = L2, Neutral = N.
• Confirm the Stacking configuration is Series (Classic) stacking and not Parallel.
• On the Hub: Inverter 1 (Master) on Port 1; Inverter 2 (L2 Sub-Phase Master) on Port 2
• In the Hub: Confirm jumpers are set for Series stacking. Hub label showing jumpers set for Series stacking.
Re: 2xFXR3048A in Master/Slave not giving 240V
Raysun, thanks for the suggestion.....but where can I toggle series vs parallel stacking? I am not aware of any jumpers on the HUB....you mean physical jumpers?
-
- Forum Overlord
- Posts: 10407
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid
Re: 2xFXR3048A in Master/Slave not giving 240V
Series/Parallel stacking is set via the Mate (can't be done in Optics).
Yes, 10 physical jumpers in the Hub.
Re: 2xFXR3048A in Master/Slave not giving 240V
Ok, I'll check into this when I get back to the customer location tomorrow. I did not know about the jumpers, and I didn't find any option for series/parallel, only for Master/Slave, but I'll look again.
Re: 2xFXR3048A in Master/Slave not giving 240V
This is the HUB...it doesn't match the info in the manual, so I'm not exactly sure how to adjust.
Re: 2xFXR3048A in Master/Slave not giving 240V
I think instead of Master/Slave, I should set Master / L2 Phase Master.....this seems to be working.
-
- Forum Overlord
- Posts: 10407
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid
Re: 2xFXR3048A in Master/Slave not giving 240V
Master / Slave is Parallel stacking verbiage. (120V single phase out.)
Master / L2 Sub Phase Master is Series stacking. (240V split phase out.)
Last edited by raysun on Fri Sep 29, 2023 9:37 am, edited 1 time in total.
-
- Forum Overlord
- Posts: 10407
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid
Re: 2xFXR3048A in Master/Slave not giving 240V
Note on the right side of the circuit board. There is a cluster of 10 jumper pins pairs with 5 jumper plugs. One bank is marked "Single Phase" (and has the jumpers on it), the other is marked 3 Phase/Split. Move the 5 jumpers to the 3Phase/Split pins.
-
- Forum Overlord
- Posts: 10407
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid
Re: 2xFXR3048A in Master/Slave not giving 240V
Also, by convention, the L2 Sub Phase Master is plugged into Hub port 7. (AFIK, this is to support some old software release.)
Re: 2xFXR3048A in Master/Slave not giving 240V
Ok, yes, everything working now, thanks a bunch for the assist. BTW, FX2 is plugged into port 2....working fine.
-
- Forum Overlord
- Posts: 10407
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid
Re: 2xFXR3048A in Master/Slave not giving 240V
Yes, it will work with the L2 Sub Phase Master plugged into Port 2, but its not the convention. If the customer contacts OB Tech Support in the future it will be one (minor) obfuscation. Also, (in the unlikely event) the should the system be expanded to 4 inverters, L1 Slave will need to be in Port 2.