VFXR3524A AC out

Discussion about the Power System AC Disconnect (PSAC)

Moderators: OutBack Moderator Team, OutBack

Post Reply
provo
Forum Emperor
Posts: 1324
Joined: Thu Jul 27, 2006 4:34 pm
My RE system: 16 Evergreen EC-120 (4 strings, total 1920W)
2 SimpliPhi 3.8-m-24V (150Ah each)
One FM80
One VFXR3524A
Hub 10
Mate3s
FNDC
Honda EU3000is generator
Grid connection, no selling back
Location: Sierra foothills

VFXR3524A AC out

Post by provo »

A newbie question I should’ve resolved 16 years ago.

Outback put my system together with a VFX3524, which has since been upgraded to a VFXR3524A, but the situation is the same. OB used a bypass rocker (shown in their schematic below) with the bypass bkr and the normal bkr both 50A.

As it is now, the 50A bypass breaker would be fine running all the loads (or loads plus charging) up to 50AAC, but the normal breaker being 50A could draw much more than the 29AAC (25AAC?) that the inverter is able to supply. The obvious solution would be to drop the normal breaker to 25A.

I’ve never come close to exceeding the inverter’s output rating, but this is starting to bother me. It seems the inverter doesn’t protect itself from excessive loads. Do I have that right?

VFXR AC Out.png
raysun
Forum Overlord
Posts: 10189
Joined: Tue Jul 26, 2016 5:57 am
My RE system: Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid

Re: VFXR3524A AC out

Post by raysun »

The circuit breakers are intended to protect the wiring, not the equipment. In the case of this equipment, the inverter has the wherewithal to protect itself. Should loads demand more than the inverter is rated for, it will shut down and raise an "AC Shorted" error.
If the AC Input and Output wiring is capable of safely carrying 50A, the circuit breakers should be OK.
provo
Forum Emperor
Posts: 1324
Joined: Thu Jul 27, 2006 4:34 pm
My RE system: 16 Evergreen EC-120 (4 strings, total 1920W)
2 SimpliPhi 3.8-m-24V (150Ah each)
One FM80
One VFXR3524A
Hub 10
Mate3s
FNDC
Honda EU3000is generator
Grid connection, no selling back
Location: Sierra foothills

Re: VFXR3524A AC out

Post by provo »

raysun wrote: Mon Jun 26, 2023 9:44 pm The circuit breakers are intended to protect the wiring, not the equipment. In the case of this equipment, the inverter has the wherewithal to protect itself. Should loads demand more than the inverter is rated for, it will shut down and raise an "AC Shorted" error.
If the AC Input and Output wiring is capable of safely carrying 50A, the circuit breakers should be OK.
That's good news, thanks!

There's another note that bothered me about the AC Input breaker, from the VFXR Owner's Manual: "The loads powered by the inverter must not exceed the size of the inverter’s transfer relay. CAUTION: Current draw in excess of the transfer relay rating can damage the transfer relay. This damage is not covered by warranty. Use protective devices of appropriate size."

I also don't want to fry the transfer relay -- is the 50A AC Input breaker a problem when the inverter is in pass-through mode? Does that need to be reduced to 30A? (Or even 25A, since 3500W/128VAC = 27A.)
JRHill
Forum Emperor
Posts: 2578
Joined: Thu Feb 17, 2011 11:12 am
My RE system: 48v OB inverter and charge controller, hub and mate3s.
Location: PNW
Contact:

Re: VFXR3524A AC out

Post by JRHill »

"The loads powered by the inverter must not exceed the size of the inverter’s transfer relay. CAUTION: Current draw in excess of the transfer relay rating can damage the transfer relay. This damage is not covered by warranty. Use protective devices of appropriate size."

Here's the way I take that: Its OB's CYA.

"I’ve never come close to exceeding the inverter’s output rating..." If your inverter is shutting down regularly or predictably you definitely need to resolve the source of the overload. I can't imagine the inverter's transfer relay frying under a 'once in a blue moon' occurrence. If it fries in one occurance its not a breaker - its a fancy fuse :shock:

"Outback put my system together..." You are saying they spec'ed the design?

Lastly, breakers, switches, etc of quality are going to have a margin of safety. As an example, if your load passes the breaker's rating there might be a slight delay before if opens the circuit. But the inverter should have already errored out and shut down unless it is in pass through or support mode. Frankly I would rather have the inverter shut itself down rather than having a breaker open under an overload.
raysun
Forum Overlord
Posts: 10189
Joined: Tue Jul 26, 2016 5:57 am
My RE system: Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid

Re: VFXR3524A AC out

Post by raysun »

If the wiring is 6ga, think you're OK.
Screenshot_20230627_062210_Drive.jpg
provo
Forum Emperor
Posts: 1324
Joined: Thu Jul 27, 2006 4:34 pm
My RE system: 16 Evergreen EC-120 (4 strings, total 1920W)
2 SimpliPhi 3.8-m-24V (150Ah each)
One FM80
One VFXR3524A
Hub 10
Mate3s
FNDC
Honda EU3000is generator
Grid connection, no selling back
Location: Sierra foothills

Re: VFXR3524A AC out

Post by provo »

JRHill wrote: Tue Jun 27, 2023 9:21 am
"Outback put my system together..." You are saying they spec'ed the design?
I told them what batteries I was planning to use, what CC (MX60), and what inverter (VFX3524). They put it together (PSAC and PSDC boxes) plus the other components (I had to mount my Trimetric 2020). This was when they shipped a fully assembled and wired massive dark green metal panel -- I just mounted it on the wall and hooked up the batteries and the house subpanel.

Then the Support team and the User Forum fielded my questions for many months... :grin:
provo
Forum Emperor
Posts: 1324
Joined: Thu Jul 27, 2006 4:34 pm
My RE system: 16 Evergreen EC-120 (4 strings, total 1920W)
2 SimpliPhi 3.8-m-24V (150Ah each)
One FM80
One VFXR3524A
Hub 10
Mate3s
FNDC
Honda EU3000is generator
Grid connection, no selling back
Location: Sierra foothills

Re: VFXR3524A AC out

Post by provo »

raysun wrote: Tue Jun 27, 2023 9:22 am If the wiring is 6ga, think you're OK.
I believe it is, but I'll check today. Thanks for the responses.
provo
Forum Emperor
Posts: 1324
Joined: Thu Jul 27, 2006 4:34 pm
My RE system: 16 Evergreen EC-120 (4 strings, total 1920W)
2 SimpliPhi 3.8-m-24V (150Ah each)
One FM80
One VFXR3524A
Hub 10
Mate3s
FNDC
Honda EU3000is generator
Grid connection, no selling back
Location: Sierra foothills

Re: VFXR3524A AC out

Post by provo »

JRHill wrote: Tue Jun 27, 2023 9:21 am
Here's the way I take that: Its OB's CYA.

Frankly I would rather have the inverter shut itself down rather than having a breaker open under an overload.
Thanks for the assurances -- just checking that it WILL shut itself down before getting damaged :shock:
raysun
Forum Overlord
Posts: 10189
Joined: Tue Jul 26, 2016 5:57 am
My RE system: Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid

Re: VFXR3524A AC out

Post by raysun »

provo wrote: Tue Jun 27, 2023 9:50 am
JRHill wrote: Tue Jun 27, 2023 9:21 am
Here's the way I take that: Its OB's CYA.

Frankly I would rather have the inverter shut itself down rather than having a breaker open under an overload.
Thanks for the assurances -- just checking that it WILL shut itself down before getting damaged :shock:
I had two instances of "AC Shorted" shutdowns with my older single FX3048T setup, both caused by Microwave/Toaster Oven/Blow Drier simultaneous operation. The disconnects (AC IN and AC OUT) were 30A, IIRC, and the AC OUT didn't trip.

In both cases, the inverter protected itself from overload by shutting down. While I have no desire to test it regularly, I have confidence in the shutdown function.
raysun
Forum Overlord
Posts: 10189
Joined: Tue Jul 26, 2016 5:57 am
My RE system: Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid

Re: VFXR3524A AC out

Post by raysun »

It's weird. This post does not show up in "Active Topics" for me.
Anyone else seeing that?
JRHill
Forum Emperor
Posts: 2578
Joined: Thu Feb 17, 2011 11:12 am
My RE system: 48v OB inverter and charge controller, hub and mate3s.
Location: PNW
Contact:

Re: VFXR3524A AC out

Post by JRHill »

"...which has since been upgraded to a VFXR3524A"

I'm curious: why didn't you go to 48v at that time, other than additional battery expense. Maybe you don't need it?
JRHill
Forum Emperor
Posts: 2578
Joined: Thu Feb 17, 2011 11:12 am
My RE system: 48v OB inverter and charge controller, hub and mate3s.
Location: PNW
Contact:

Re: VFXR3524A AC out

Post by JRHill »

raysun wrote: Tue Jun 27, 2023 2:53 pm It's weird. This post does not show up in "Active Topics" for me.
Anyone else seeing that?
It's because I chimed in.
provo
Forum Emperor
Posts: 1324
Joined: Thu Jul 27, 2006 4:34 pm
My RE system: 16 Evergreen EC-120 (4 strings, total 1920W)
2 SimpliPhi 3.8-m-24V (150Ah each)
One FM80
One VFXR3524A
Hub 10
Mate3s
FNDC
Honda EU3000is generator
Grid connection, no selling back
Location: Sierra foothills

Re: VFXR3524A AC out

Post by provo »

JRHill wrote: Tue Jun 27, 2023 5:40 pm
I'm curious: why didn't you go to 48v at that time, other than additional battery expense. Maybe you don't need it?
I actually don't need it, plus it was just a simple swapping out of the MX60 for an FM80, and one inverter with another of the same parameters. Going to 48V would have been more work for not much reward, and even more so once I got hooked into the utility.

I practice the KISS thing like a religion :grin: .