flexmax -80 lowering generator load

Discussion about OutBack Inverters in Off Grid Applications

Moderators: OutBack, OutBack Moderator Team

Post Reply
purifiedlife
Forum Junior Member
Posts: 1
Joined: Tue Mar 14, 2023 1:12 pm
My RE system: outback fm80
schneider sw-4048
16 trojan lead acid
12 Q peak duo 37 330

flexmax -80 lowering generator load

Post by purifiedlife »

We are offgrid and use a champion 3650 generator and it's inputting roughly 3000w. The generator is tired so I need to lower the load on the generator when charging the system. I want to lower the input to 2500-2800 because the generator keeps tripping only I can't figure out where in the inverter to do this. Thank you
raysun
Forum Emperor
Posts: 9546
Joined: Tue Jul 26, 2016 5:57 am
My RE system: Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid

Re: flexmax -80 lowering generator load

Post by raysun »

Of course, the FlexMax80 charges the battery independently of the inverter charger, and has no bearing on the generator's operation.

The Schneider SW 4048 listed in your profile isn't Outback equipment, so you might find a more detailed answer to generator load management from a Schneider user forum (if such exists.)

A quick scan of the SW 4048 manual turned up two potential controls: AC IN Breaker and Load Shave. I have no experience with either, but AC IN Breaker looks like it may be set to a maximum AC Input value, and the inverter will lower charge current accordingly. Load Shave appears to be some form of overall AC load management that switches between charging and inverting when demand dictates.

The inverter charger also has a Max Chg Rate parameter which appears to set its charge current limit.
fcwlp
Forum Emperor
Posts: 1113
Joined: Wed Jan 22, 2020 9:40 am
My RE system: GS8048A, FM80 w/3,600W PV Fixed, FM80 w/2,700W on Zomeworks tracker, Mate3, 24 Trojan 2V L16 1100AH @ C20, Grid-Tied with Kohler 14RESA LPG Generator and MEP-803 Diesel if needed.

I install and maintain grid-tied and off-grid systems in my area and consult on solar system design/operation.
Location: 80 miles NE of Phoenix at 5500'

Re: flexmax -80 lowering generator load

Post by fcwlp »

Given that the Schneider SW 4048 was a Xantrex SW 4048 and prior to that a Trace unit it does have some Outback heritage (Outback came out of Xantrex) and setting are relatively similar thru the lineage.
.
You have to get into the Basic Setup menu and change menu item 12E.
- Press Inv and Gen buttons simultaneously (this can be tricky depending on how sticky they are and coordinated you are)
- Scroll to Menu 12
- Scroll down to item 12E Max Charge Amps AC
- make the changes, probably 22A
- Scroll to Menu 14
- Push INV to save