Post by wtfg »

I had a Skybox for a year before Outback replaced it with a radian 8048
When I would force a charge it would go to the Absorb charge setting and stop charging, unless I had the absorb time set
If absorb time was 10 minutes it would reach Absorb and charge for 10 minutes

My radian if a force a charge it only charges to what I have the absorb time set too
if I set it for a hour it will go past the Absorb setting until the hour total charge time is reached
If I have Absorb time set for 15 minutes, it quits charging after 15 minutes and never reach Absorb charge setting

Doesn't seem normal to me
Thanks
raysun
Forum Emperor
Posts: 9546
Joined: Tue Jul 26, 2016 5:57 am
My RE system: Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid

Re: radian battery settings

Post by raysun »

The description seems odd indeed.
Perhaps post a screen shot of the Radian Battery Charger parameters?

Also, updating your profile with the current configuration and exact battery details would be helpful.

Seeing as there appears to be AC coupled inverters in the mix as well, describing how they are configured in the system may help get to the bottom of things.
wtfg
Forum Whiz
Posts: 32
Joined: Sat Dec 04, 2021 11:06 am
My RE system: Radian with 14.3kw LiFepo4 batteries for backup
JBD 200amp 48volt 16s BMS (EVE 280AH)
22 canadian Solar 325 watt panels
With Enphase Micro Inverters AC coupled to Radian
Location: Mn

Re: radian battery settings

Post by wtfg »

Here are my Radian settings
Screen Shot 2023-03-15 at 7.46.24 AM.png
Screen Shot 2023-03-15 at 7.45.48 AM.png
User avatar
Mike Curran
Forum Emperor
Posts: 2985
Joined: Sat Aug 28, 2004 6:28 pm
My RE system: Outback - Garage roof (2007/2017):
- 8 (2x4) Evergreen 180's into one FM80 (2007/2020 - replaced MX60)
- 6 (2×3) ALEO S79-300's into one FM80 (2017)
- 2 grid-tied VFXR3524A-01's series stacked, replaced GVFX's (2020)
- 12 Surrette/Rolls 2V x 1766Ah (2007)
- Hub10.3, Mate3s, FNDC, RTS. Tigo ES maximizers on each PV module.

Westinghouse Solar - Barn roof: (2012)
- 30 (2x15) 235W panels with Enphase M215 microinverters, grid-tied

Outback Skybox - Barn roof: (2019)
- 14 Talesun 275W in series (DC array input to SB inverter/charger)
- 3 SimpliPhi 3.8 batteries, 48V, 225Ah total
- AC coupled input from 14 Talesun 275W, Enphase M215 microinverters

Battery systems operate in grid-tied, net metering w/backup mode
All self-designed and self-installed
Location: Chagrin Falls, Ohio

Re: radian battery settings

Post by Mike Curran »

This application note https://outbackpower.com/downloads/docu ... radian.pdf describes some special programming that's needed when AC-coupling to a Radian. Maybe your answer is in there - I'm no Radian expert.
https://ei.tigoenergy.com/p/pZXn7SZQyO45
https://enlighten.enphaseenergy.com/public/systems/Hctc107221
wtfg
Forum Whiz
Posts: 32
Joined: Sat Dec 04, 2021 11:06 am
My RE system: Radian with 14.3kw LiFepo4 batteries for backup
JBD 200amp 48volt 16s BMS (EVE 280AH)
22 canadian Solar 325 watt panels
With Enphase Micro Inverters AC coupled to Radian
Location: Mn

Re: radian battery settings

Post by wtfg »

I did the software update for AC coupling on the Mate3 and Radian
raysun
Forum Emperor
Posts: 9546
Joined: Tue Jul 26, 2016 5:57 am
My RE system: Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid

Re: radian battery settings

Post by raysun »

if I set it for a hour it will go past the Absorb setting until the hour total charge time is reached
If I have Absorb time set for 15 minutes, it quits charging after 15 minutes and never reach Absorb charge setting
A small point. The Absorb Time setting is in 0.1H increments, so 6 minutes, 12 minutes, 18 minutes, etc.

54V is pretty low charging target for a 16S LFP. Is this an attempt at a maximum state of charge around 75-80%?

The normal charge behavior is a Bulk (Constant Current) stage until the Absorb Voltage is reached at which point an Absorb (Constant Voltage) phase is executed for Absorb Time. The setting of Absorb Time has no impact on the Constant Current (Bulk) phase, however, the time to reach the Absorb Voltage can vary with battery State of Charge at the time the charge cycle begins.

Is there another charging source (e.g.: the AC coupled inverters) that is driving the battery voltage above the Absorb Voltage value?
Is the Radian calibrated to the battery voltage? (IIRC, the internal voltmeter resolution is +/-0.4V).
wtfg
Forum Whiz
Posts: 32
Joined: Sat Dec 04, 2021 11:06 am
My RE system: Radian with 14.3kw LiFepo4 batteries for backup
JBD 200amp 48volt 16s BMS (EVE 280AH)
22 canadian Solar 325 watt panels
With Enphase Micro Inverters AC coupled to Radian
Location: Mn

Re: radian battery settings

Post by wtfg »

It seems like mine stays in bulk for one minute than switches to absorb
From my event notification
raysun
Forum Emperor
Posts: 9546
Joined: Tue Jul 26, 2016 5:57 am
My RE system: Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid

Re: radian battery settings

Post by raysun »

wtfg wrote: Wed Mar 15, 2023 10:28 am It seems like mine stays in bulk for one minute than switches to absorb
From my event notification
OK. That would seem to indicate the battery is reaching 54V after a minute. Can you confirm when that voltage is reached?
wtfg
Forum Whiz
Posts: 32
Joined: Sat Dec 04, 2021 11:06 am
My RE system: Radian with 14.3kw LiFepo4 batteries for backup
JBD 200amp 48volt 16s BMS (EVE 280AH)
22 canadian Solar 325 watt panels
With Enphase Micro Inverters AC coupled to Radian
Location: Mn

Re: radian battery settings

Post by wtfg »

It seems so
Ill raise the absorb to 56 and try charging again, and watch the process

The reason I messed with the absorb setting was because my BMS was bad it was dropping 2.5 volts across the solenoid randomly causing Radian to charge
And I didn't want to overcharge the batteries
I replaced the BMS Sunday
raysun
Forum Emperor
Posts: 9546
Joined: Tue Jul 26, 2016 5:57 am
My RE system: Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid

Re: radian battery settings

Post by raysun »

While charging, my LFP is at 75% @ 54V, and 99% @ 56V.
Try -
Absorb Voltage: 56V
Absorb Time: 0.1H
User avatar
Mike Curran
Forum Emperor
Posts: 2985
Joined: Sat Aug 28, 2004 6:28 pm
My RE system: Outback - Garage roof (2007/2017):
- 8 (2x4) Evergreen 180's into one FM80 (2007/2020 - replaced MX60)
- 6 (2×3) ALEO S79-300's into one FM80 (2017)
- 2 grid-tied VFXR3524A-01's series stacked, replaced GVFX's (2020)
- 12 Surrette/Rolls 2V x 1766Ah (2007)
- Hub10.3, Mate3s, FNDC, RTS. Tigo ES maximizers on each PV module.

Westinghouse Solar - Barn roof: (2012)
- 30 (2x15) 235W panels with Enphase M215 microinverters, grid-tied

Outback Skybox - Barn roof: (2019)
- 14 Talesun 275W in series (DC array input to SB inverter/charger)
- 3 SimpliPhi 3.8 batteries, 48V, 225Ah total
- AC coupled input from 14 Talesun 275W, Enphase M215 microinverters

Battery systems operate in grid-tied, net metering w/backup mode
All self-designed and self-installed
Location: Chagrin Falls, Ohio

Re: radian battery settings

Post by Mike Curran »

This is off topic and it certainly looks like Raysun has you covered, but I just had to ask, are you using a relay to disconnect your microinverter array in order to control battery charging? Because a Radian set up for AC-coupling will do that for you without the need for a relay. Just sayin'...
The reason I messed with the absorb setting was because my BMS was bad it was dropping 2.5 volts across the solenoid randomly causing Radian to charge
And I didn't want to overcharge the batteries
https://ei.tigoenergy.com/p/pZXn7SZQyO45
https://enlighten.enphaseenergy.com/public/systems/Hctc107221