Loss of power between solar and inverter
I have a grid tied GS4048A with 3.6kW of solar panels. I'm seeing a decent amount of power loss between the solar charge controller and the inverter and I can't figure out why. For example, in the image, 0.36kW is unaccounted for. I guess some could be going to the batteries, but this happens even when the battery is at 100% I have the charging settings according to the battery manufacturer's instructions. I'm posting images of what I think are the relevant settings, but please tell me if there's anything else you need to see. Thanks for your help!
-
- Forum Member
- Posts: 9
- Joined: Sun Jan 31, 2016 4:45 pm
- My RE system: Outback Radian GS4048A Inverter Charger
3600W Solar Array
240Ah 48V Battery Array
FM80-150VDC Solar Charger Controller
FLEXnetDC
Re: Loss of power between solar and inverter
More settings
Another image showing power loss at 100% battery
Another image showing power loss at 100% battery
-
- Forum Emperor
- Posts: 9378
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid
- Mike Curran
- Forum Emperor
- Posts: 2966
- Joined: Sat Aug 28, 2004 6:28 pm
- My RE system: Outback - Garage roof (2007/2017):
- 8 (2x4) Evergreen 180's into one FM80 (2007/2020 - replaced MX60)
- 6 (2×3) ALEO S79-300's into one FM80 (2017)
- 2 grid-tied VFXR3524A-01's series stacked, replaced GVFX's (2020)
- 12 Surrette/Rolls 2V x 1766Ah (2007)
- Hub10.3, Mate3s, FNDC, RTS. Tigo ES maximizers on each PV module.
Westinghouse Solar - Barn roof: (2012)
- 30 (2x15) 235W panels with Enphase M215 microinverters, grid-tied
Outback Skybox - Barn roof: (2019)
- 14 Talesun 275W in series (DC array input to SB inverter/charger)
- 3 SimpliPhi 3.8 batteries, 48V, 225Ah total
- AC coupled input from 14 Talesun 275W, Enphase M215 microinverters
Battery systems operate in grid-tied, net metering w/backup mode
All self-designed and self-installed - Location: Chagrin Falls, Ohio
Re: Loss of power between solar and inverter
I don't have a screenshot to share but I often see the same thing with my Rolls battery system. It's a huge, 15 year old battery and even after charge parameters are met, 100% SOC and selling to grid, there's still 3-400 watts going into the battery to keep it at the sell setpoint (pretty close to float, actually). I'll post an Optics power flow screenshot next time I see it, gotta catch it on a sunny mid-day.
https://ei.tigoenergy.com/p/pZXn7SZQyO45
https://enlighten.enphaseenergy.com/public/systems/Hctc107221
https://enlighten.enphaseenergy.com/public/systems/Hctc107221
-
- Forum Emperor
- Posts: 1090
- Joined: Wed Jan 22, 2020 9:40 am
- My RE system: GS8048A, FM80 w/3,600W PV Fixed, FM80 w/2,700W on Zomeworks tracker, Mate3, 24 Trojan 2V L16 1100AH @ C20, Grid-Tied with Kohler 14RESA LPG Generator and MEP-803 Diesel if needed.
I install and maintain grid-tied and off-grid systems in my area and consult on solar system design/operation. - Location: 80 miles NE of Phoenix at 5500'
Re: Loss of power between solar and inverter
Since you have a FNDC a more accurate measure is to put your cursor over the battery which shows what the shunts are measuring in and out if you have at least two shunts.
-
- Forum Member
- Posts: 9
- Joined: Sun Jan 31, 2016 4:45 pm
- My RE system: Outback Radian GS4048A Inverter Charger
3600W Solar Array
240Ah 48V Battery Array
FM80-150VDC Solar Charger Controller
FLEXnetDC
Re: Loss of power between solar and inverter
My batteries were replaced about two years ago.Mike Curran wrote: ↑Thu Jan 19, 2023 2:24 pm I don't have a screenshot to share but I often see the same thing with my Rolls battery system. It's a huge, 15 year old battery and even after charge parameters are met, 100% SOC and selling to grid, there's still 3-400 watts going into the battery to keep it at the sell setpoint (pretty close to float, actually). I'll post an Optics power flow screenshot next time I see it, gotta catch it on a sunny mid-day.
- EA6LE-ONE
- Forum Czar
- Posts: 875
- Joined: Tue May 05, 2020 7:51 am
- My RE system: System 1:
MATE3s, 3 x Radian GS8048A,
6 x FLEXmax 100, HUB10,
2 x EnergyCell 48V 2700RE,
1 x FLEXnet DC, 6 x FLEXware ICS Plus,
78 x PANASONIC VBHN325SA17 325W
System 2:
MATE3s, Radian GS8048A,
2 x FLEXmax 100, HUB10
1 x EnergyCell 48V 2700RE,
1 x FLEXnet DC, 2 x FLEXware ICS
21 x PANASONIC VBHN325SA17 325W - Location: Providenciales, Turks & Caicos Isl.
Re: Loss of power between solar and inverter
What type of battery is? model?dude8604 wrote: ↑Thu Jan 19, 2023 9:34 pmMy batteries were replaced about two years ago.Mike Curran wrote: ↑Thu Jan 19, 2023 2:24 pm I don't have a screenshot to share but I often see the same thing with my Rolls battery system. It's a huge, 15 year old battery and even after charge parameters are met, 100% SOC and selling to grid, there's still 3-400 watts going into the battery to keep it at the sell setpoint (pretty close to float, actually). I'll post an Optics power flow screenshot next time I see it, gotta catch it on a sunny mid-day.
need to check the maximum charging current for the battery and have global charge enabled if necessary.
acid batteries will continue to draw power once they are considered charged.
edit: from the charging parameter looks like is a flooded Lead acid battery. might need to set the global charge to 48A. check the battery setting from manufacturer.
-
- Forum Member
- Posts: 9
- Joined: Sun Jan 31, 2016 4:45 pm
- My RE system: Outback Radian GS4048A Inverter Charger
3600W Solar Array
240Ah 48V Battery Array
FM80-150VDC Solar Charger Controller
FLEXnetDC
Re: Loss of power between solar and inverter
These are the batteries: https://invertersrus.com/product/lifeline-gpl8dl/EA6LE-ONE wrote: ↑Fri Jan 20, 2023 6:38 amWhat type of battery is? model?dude8604 wrote: ↑Thu Jan 19, 2023 9:34 pmMy batteries were replaced about two years ago.Mike Curran wrote: ↑Thu Jan 19, 2023 2:24 pm I don't have a screenshot to share but I often see the same thing with my Rolls battery system. It's a huge, 15 year old battery and even after charge parameters are met, 100% SOC and selling to grid, there's still 3-400 watts going into the battery to keep it at the sell setpoint (pretty close to float, actually). I'll post an Optics power flow screenshot next time I see it, gotta catch it on a sunny mid-day.
need to check the maximum charging current for the battery and have global charge enabled if necessary.
acid batteries will continue to draw power once they are considered charged.
edit: from the charging parameter looks like is a flooded Lead acid battery. might need to set the global charge to 48A. check the battery setting from manufacturer.
I have 4 of them wired in series.
The technical manual says the maximum charge current is 5C, which would be 1275A, but that seems really high.
Here is the technical manual: https://lifelinebatteries.com/wp-conten ... -06-19.pdf
Also, in the event log it looks like it's only doing bulk charging, it never says Absorb or Float charging. Is that a problem?
-
- Forum Emperor
- Posts: 9378
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid
Re: Loss of power between solar and inverter
A little battery math:These are the batteries: https://invertersrus.com/product/lifeline-gpl8dl/
I have 4 of them wired in series.
48V @ 225AH = 10.8kWH total energy capacity
50% usable (50 Depth of Discharge) = 112.5AH or 5.4kWH.
The battery has sufficient capacity for a "grid backup" role. It would support about a 500W average load for 10 hours before needing recharging.
The modern AGM battery cells have very low internal impedance, and can tolerate high charge currents. I would think charging at 5C would be excessive, however. The charger in the GS4048A at maximum will put out roughly 55A charge current. The FM80 has a maximum output of 80A but will peak at less than that with the specified array.The technical manual says the maximum charge current is 5C, which would be 1275A, but that seems really high.
Both chargers, combine for less than 135A charging current and would appear safe for the battery during Bulk.
It would appear the battery is not being fully charged. The battery should be fully charged at least once a week. Keeping a Lead Acid battery at or near full charge is best for maximum service life.Also, in the event log it looks like it's only doing bulk charging, it never says Absorb or Float charging. Is that a problem?
Try manually initiating a Bulk charge using the Radian. From OpticsRE:
-
- Forum Emperor
- Posts: 1090
- Joined: Wed Jan 22, 2020 9:40 am
- My RE system: GS8048A, FM80 w/3,600W PV Fixed, FM80 w/2,700W on Zomeworks tracker, Mate3, 24 Trojan 2V L16 1100AH @ C20, Grid-Tied with Kohler 14RESA LPG Generator and MEP-803 Diesel if needed.
I install and maintain grid-tied and off-grid systems in my area and consult on solar system design/operation. - Location: 80 miles NE of Phoenix at 5500'
- Mike Curran
- Forum Emperor
- Posts: 2966
- Joined: Sat Aug 28, 2004 6:28 pm
- My RE system: Outback - Garage roof (2007/2017):
- 8 (2x4) Evergreen 180's into one FM80 (2007/2020 - replaced MX60)
- 6 (2×3) ALEO S79-300's into one FM80 (2017)
- 2 grid-tied VFXR3524A-01's series stacked, replaced GVFX's (2020)
- 12 Surrette/Rolls 2V x 1766Ah (2007)
- Hub10.3, Mate3s, FNDC, RTS. Tigo ES maximizers on each PV module.
Westinghouse Solar - Barn roof: (2012)
- 30 (2x15) 235W panels with Enphase M215 microinverters, grid-tied
Outback Skybox - Barn roof: (2019)
- 14 Talesun 275W in series (DC array input to SB inverter/charger)
- 3 SimpliPhi 3.8 batteries, 48V, 225Ah total
- AC coupled input from 14 Talesun 275W, Enphase M215 microinverters
Battery systems operate in grid-tied, net metering w/backup mode
All self-designed and self-installed - Location: Chagrin Falls, Ohio
Re: Loss of power between solar and inverter
This screenshot shows 140 watts going to the battery to maintain voltage at the sell setpoint, 27.2 volts (now showing 27.1 volts), with SOC = 100%. Not unusual.
Edit: View suggested by fcwlp. Note +600 watts to battery
First sunny day in awhile.Edit: View suggested by fcwlp. Note +600 watts to battery