Post by Andrew Simpson »

MATE is not dropping the grid when HBX-Drop set point is reached.
Does it manually but not automatic.
Setting 25 V for 0.1 hr
HBX-Use at 23.5 for 0.2
Batteries at 26.5
Mike Curran
Forum Emperor
Posts: 1893
Joined: Sat Aug 28, 2004 6:28 pm
My RE system: Outback - Garage roof:
- 8 (2x4) Evergreen 180's into one FM80 (2007/2020 - replaced MX60)
- 6 (2×3) ALEO S79-300's into one FM80 (2017)
[***2 grid-tied GVFX3524's classic stacked for 120/240VAC (2007-2020)]
- 2 grid-tied VFXR3524A-01's series stacked, ***replaced GVFX's (2020)
- 12 Surrette/Rolls 2V x 1766Ah (2007)
- Hub10.3, Mate3s, FNDC, RTS, OpticsRE. Tigo Energy ES maximizers on each PV module.

Westinghouse Solar - Barn roof: (2012)
- 30 (2x15) 235W panels with Enphase M215 microinverters, grid-tied

Outback Skybox - Barn roof: (2019)
- 14 Talesun 275W in series (DC array input to SB inverter/charger)
- 3 SimpliPhi 3.8 batteries, 48V, 225Ah total
- AC coupled input (manual switch during grid outage only) from 14 Talesun 275W,
Enphase M215 microinverters, normally direct grid tied

All self-designed and self-installed
Location: Chagrin Falls, Ohio

Re: HBX-DROP

Post by Mike Curran »

I'm not familiar with the 3024J inverter but my own GVFX inverters have a fixed rebulk voltage setting of 25.0 volts. If yours have this fixed rebulk setpoint as well then it's possible your system goes to a bulk/absorb cycle when it reaches 25 volts instead of dropping the grid.

BTW, that's a pretty low voltage setpoint to drop grid - seems like it should be higher, at 25 volts your system probably can't afford to drop the grid. Try raising the drop setpoint, that might also prevent a bulk cycle from starting.

Also, while searching for info about your inverter I ran across this thread http://outbackpower.com/forum/viewtopic.php?t=7505 Maybe it'll help.
http://www.tigoenergy.com/site.php?95b2dca2-ca6c
https://enlighten.enphaseenergy.com/public/systems/Hctc107221
Andrew Simpson
Forum Junior Member
Posts: 2
Joined: Tue Oct 06, 2020 10:35 pm
My RE system: Two 3024J in split phase
FM 80
12 Solar World PV
FlexNet
Eight Trojan 415

Re: HBX-DROP

Post by Andrew Simpson »

My HBX-DROP voltage was higher but I thought the batteries may have lost a cell so reduced it. Have serviced the batteries / terminals and painted the rack. Waiting to reinstall and hoping this will solve the issue. We use an FM 80 to charge and have a FLEXnet DC installed. The screen on the FM 80 is blank and I wonder whether that is also affecting the coms.
Thanks for your response.