An update on the FXR issue of CPM: my problem has been getting to Absorb voltage with the generator and if I do for long enough to set the CPM flag. Its just not happening. Last night (after sundown so no FM) I had increased the Absorb setting to 56.0 / .1 hour and had the FNDC disconnected. I got to ~55.6 and the generator charge dropped as always (recently). I Rebulked and it went to 56.0 and dropped the generator with <1 minute Absorb. Third try and I got somewhere around 3 minutes of Absorb, certainly not 6 minutes. Of course no CPM as the FNDC was disconnected but theoretically it should've been achieved. One thing is for sure, the FNDC is NOT a contributing factor in reaching and holding the Absorb set point.
I had thought about just leaving the FNDC disconnected - I'm ordering a Victron. I had thought that the only thing I miss is the shunts anyway. But this AM I reviewed the Mate3s manual. Without the FNDC the Battery Status LEDs revert back to lead battery technology. So the Green 'all is good' LED will stay lit from 50vdc or higher. Honk/snort/growl from me with SimpliPhi's. That will not work. Yeah, LVCO,
if that works, should protect the PHIs. Additionally I could turn on the 2 Minute AGS start above LVCO. But having that Green status light is a quick-at-a-glance notification that attention will be needed, even if its not that accurate on SOC, would be missed.
Tonight's last ditch test is to set FXR to 56.4 / .1 hour. It's not exactly like doing the same thing and expecting different results as I've tried a bunch of singular changes each time and watching closely. Frankly, I hope something is different but not holding my breath.
My thanks to Raysun is in order!
One last note from the Mate3s Overview doc:
Take a look at the Notes. "Gaps in the table (higher-voltage units) are due to the resolution of the inverter’s DC meter." The word "resolution" is neither precision nor accuracy. So even if you calibrate the inverter's voltage is that number consistent? If it's NOT consistent, by calibrating the inverter you just slide the scale up or down a bit. And if you have multiple inverters and whether or not you have a FNDC this adds some curiosity.