SimpliPhi Full Charge and CPM

raysun
Forum Emperor
Posts: 7802
Joined: Tue Jul 26, 2016 5:57 am
My RE system: Flexpower Two: (2) FXR3048A-01, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
Honda EU7000is gas fuel generator

Re: SimpliPhi Full Charge and CPM

Post by raysun »

inverter was 54.4, CC 54.3 and system at 54.1
The active charger is going to read a bit higher. In bulk its always raising the target voltage above the battery voltage to keep charge flowing.

Was the FM80 calibrated with the firmware VBAT setting, or the trim pot on the circuit board in the FM80s wiring compartment?

I'm not sure about the FNDC. Mine drifts .1 or .2 in some circumstances. Usually it's in tight agreement though.
provo
Forum Emperor
Posts: 1105
Joined: Thu Jul 27, 2006 4:34 pm
My RE system: 16 Evergreen EC-120 (4 strings, total 1920W)
2 SimpliPhi 3.8-m-24V (150Ah each)
One FM80
One VFXR3524A
Hub 10
Mate3s
FNDC
Honda EU3000is generator
Location: Sierra foothills

Re: SimpliPhi Full Charge and CPM

Post by provo »

raysun wrote: Sat Jan 22, 2022 5:52 pm
Set up charging on a single inverter, with no PV.
Absorb=56.0V
CRA=9.0A
Charging was about 25ADC (4A per block) and proceeded slowly to 100% SoC, then to 56.0V Absorb, and termination.

The FNDC did not report CPM, though the Victron, using the same criteria, did.
I've never charged that slowly, but I do keep the bulk current to ~13A per block. Then I can get to CPM in 6-8m. At 15A per block it can take 9m or more. Seems very sensitive! This is with inverter at 28.0V and CC at 28.2V.

Fortunately I rarely pull more than 110Ah out of the batteries overnight so I can usually finish absorb with CPM by noon.
JRHill
Forum Emperor
Posts: 2391
Joined: Thu Feb 17, 2011 11:12 am
My RE system: 48v OB inverter and charge controller, hub and mate3s.
Location: PNW
Contact:

Re: SimpliPhi Full Charge and CPM

Post by JRHill »

raysun wrote: Sat Jan 22, 2022 8:58 pm
inverter was 54.4, CC 54.3 and system at 54.1
The active charger is going to read a bit higher. In bulk its always raising the target voltage above the battery voltage to keep charge flowing.

Was the FM80 calibrated with the firmware VBAT setting, or the trim pot on the circuit board in the FM80s wiring compartment?

I'm not sure about the FNDC. Mine drifts .1 or .2 in some circumstances. Usually it's in tight agreement though.
I calibrated the inverter and the CC via software (from the Mate3).
raysun
Forum Emperor
Posts: 7802
Joined: Tue Jul 26, 2016 5:57 am
My RE system: Flexpower Two: (2) FXR3048A-01, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
Honda EU7000is gas fuel generator

Re: SimpliPhi Full Charge and CPM

Post by raysun »

I never found the CC VBAT calibration to be very precise. The trim pot method seems to be more so.
raysun
Forum Emperor
Posts: 7802
Joined: Tue Jul 26, 2016 5:57 am
My RE system: Flexpower Two: (2) FXR3048A-01, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
Honda EU7000is gas fuel generator

Re: SimpliPhi Full Charge and CPM

Post by raysun »

I've never charged that slowly, but I do keep the bulk current to ~13A per block. Then I can get to CPM in 6-8m. At 15A per block it can take 9m or more. Seems very sensitive! This is with inverter at 28.0V and CC at 28.2V.
The only thing I can think of is the BMS doing some late-stage "top balancing" of the cells. When I watch the Absorb cycle, I notice a fair amount of charge current "bounce", especially noticeable when focusing on the CRA target. The current may fall below CRA, only to "bounce" above it briefly. This happens repeatedly during the Absorb time until the net current falls well below CRA. I get the sense this is influenced by the charge current leading up to Absorb, and how the anode is "packed", but that is merely supposition on my part.

Watch for the "balancing bounce" and see if it may be affecting the time it takes to reach CPM.
JRHill
Forum Emperor
Posts: 2391
Joined: Thu Feb 17, 2011 11:12 am
My RE system: 48v OB inverter and charge controller, hub and mate3s.
Location: PNW
Contact:

Re: SimpliPhi Full Charge and CPM

Post by JRHill »

raysun wrote: Sun Jan 23, 2022 10:35 am
I've never charged that slowly, but I do keep the bulk current to ~13A per block. Then I can get to CPM in 6-8m. At 15A per block it can take 9m or more. Seems very sensitive! This is with inverter at 28.0V and CC at 28.2V.
The only thing I can think of is the BMS doing some late-stage "top balancing" of the cells. When I watch the Absorb cycle, I notice a fair amount of charge current "bounce", especially noticeable when focusing on the CRA target. The current may fall below CRA, only to "bounce" above it briefly. This happens repeatedly during the Absorb time until the net current falls well below CRA. I get the sense this is influenced by the charge current leading up to Absorb, and how the anode is "packed", but that is merely supposition on my part.

Watch for the "balancing bounce" and see if it may be affecting the time it takes to reach CPM.
Now this is interesting to me. With the max voltage of 56.4vdc and an Absorb time of .1 hr, what happens if the BMS isn't done 'balancing' in that .1 time frame? More so, if charging from the inverter to a lower voltage of 56.0 / .1 hr.... This happened last night:
1-22-2022-VFXR.png
I shut the data collection run down at 54.4 but the Wax On, Wax off thing was happening there.
raysun
Forum Emperor
Posts: 7802
Joined: Tue Jul 26, 2016 5:57 am
My RE system: Flexpower Two: (2) FXR3048A-01, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
Honda EU7000is gas fuel generator

Re: SimpliPhi Full Charge and CPM

Post by raysun »

I think the assumed "balancing routine" may hold the key to the fully charged but not CPM mystery.

I was looking through the Victron graph captures I've done, but they are too low resolution. I'll try for some higher resolution graphs under the various charging conditions as the opportunity presents itself.

Here's the best I have at the moment. The 9A CRA will have to be interpolated, as well as the current excursions.
Screenshot_20211214-142223_Microsoft Remote Desktop.jpg
The "top of the Voltage Mesa" is the Absorb stage. Small "jitter" in the charge current around the CRA value can be seen in that time interval.
Last edited by raysun on Sun Jan 23, 2022 11:08 am, edited 1 time in total.
JRHill
Forum Emperor
Posts: 2391
Joined: Thu Feb 17, 2011 11:12 am
My RE system: 48v OB inverter and charge controller, hub and mate3s.
Location: PNW
Contact:

Re: SimpliPhi Full Charge and CPM

Post by JRHill »

raysun wrote: Sun Jan 23, 2022 9:44 am I never found the CC VBAT calibration to be very precise. The trim pot method seems to be more so.
The s/w adjustment seems good enough for my purposes. Esp since the FM works great with the s/w adjustment. The VFXR too, now. Its the divergence of the system voltage (FNDC) that is of interest.

Before I did the calibration it was suggested that because the system voltage was exceeding the absorb set point and therefore then terminated. Now, charging with the VFXR over 54.5, the system voltage is low by .2 to .3 and still terminating early. But now the VFXR is staying pretty close to the FM80 (.2)

I'm holdingoff of any re-flash of the VFXR firmware lest I inject some new oddity. The problems of the day are sufficient.
provo
Forum Emperor
Posts: 1105
Joined: Thu Jul 27, 2006 4:34 pm
My RE system: 16 Evergreen EC-120 (4 strings, total 1920W)
2 SimpliPhi 3.8-m-24V (150Ah each)
One FM80
One VFXR3524A
Hub 10
Mate3s
FNDC
Honda EU3000is generator
Location: Sierra foothills

Re: SimpliPhi Full Charge and CPM

Post by provo »

raysun wrote: Sun Jan 23, 2022 10:35 am
Watch for the "balancing bounce" and see if it may be affecting the time it takes to reach CPM.
Oh definitely! I've always assumed it was just the GCC function on the Mate that couldn't regulate well, but the idea that it's the BMS working behind the scenes is interesting. I don't mind taking 11 or 12m to reach CPM, since Phi Tech Support doesn't seem to. I just need something to mess with, given how boring the charging of the batteries would be otherwise :lol: .

Edit -- actually GCC is out of the picture by absorb....I like your BMS explanation.
Last edited by provo on Sun Jan 23, 2022 11:16 am, edited 1 time in total.
raysun
Forum Emperor
Posts: 7802
Joined: Tue Jul 26, 2016 5:57 am
My RE system: Flexpower Two: (2) FXR3048A-01, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
Honda EU7000is gas fuel generator

Re: SimpliPhi Full Charge and CPM

Post by raysun »

I just need something to mess with, given how boring the charging of the batteries would be otherwise :lol: .
I know right? 😆 Lithium takes a whole lot of fussing over battery charging out of the picture. We have to have SOMETHING to obsess over.

FWIW, when the CCs reach Absorb here, the system consistently reaches CPM (with rare exception).

On generator alone, I don't have enough cycles. Dual inverter chargers reach CPM, IIRC, but the single charger yesterday did not. More gas must be burned before that picture becomes clear.
JRHill
Forum Emperor
Posts: 2391
Joined: Thu Feb 17, 2011 11:12 am
My RE system: 48v OB inverter and charge controller, hub and mate3s.
Location: PNW
Contact:

Re: SimpliPhi Full Charge and CPM

Post by JRHill »

raysun wrote: Sun Jan 23, 2022 11:12 amMore gas must be burned before that picture becomes clear.
That's OK, Raysun. Fuel injection and a catalytic on your generator you are performing a valuable service and saving the planet at the same time.
raysun
Forum Emperor
Posts: 7802
Joined: Tue Jul 26, 2016 5:57 am
My RE system: Flexpower Two: (2) FXR3048A-01, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
Honda EU7000is gas fuel generator

Re: SimpliPhi Full Charge and CPM

Post by raysun »

My Honda sits inside the entrance to my connex, blowing exhaust out the open door. I have a CO detector right near it, and have never heard a peep from it.

I even work in there while the genny is running (but it does make me aware of the potential...)
JRHill
Forum Emperor
Posts: 2391
Joined: Thu Feb 17, 2011 11:12 am
My RE system: 48v OB inverter and charge controller, hub and mate3s.
Location: PNW
Contact:

Re: SimpliPhi Full Charge and CPM

Post by JRHill »

raysun wrote: Sun Jan 23, 2022 11:38 am My Honda sits inside the entrance to my connex, blowing exhaust out the open door. I have a CO detector right near it, and have never heard a peep from it.

I even work in there while the genny is running (but it does make me aware of the potential...)
BTW, the exhaust extension I added a few weeks ago works like a champ. Sorry for the thread drift.
raysun
Forum Emperor
Posts: 7802
Joined: Tue Jul 26, 2016 5:57 am
My RE system: Flexpower Two: (2) FXR3048A-01, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
Honda EU7000is gas fuel generator

Re: SimpliPhi Full Charge and CPM

Post by raysun »

Charge complete and CPM via FM80s.
Screenshot_20220123-130719_Microsoft Remote Desktop.jpg
Absorb stage. Charge current around CRA (9A) note the oscillations around that line.
20220123_131252.jpg
Wider view of charging up to and through the Absorb stage.
20220123_133450.jpg
Charging events for the cycle.
MJSullivan56
Forum Guru
Posts: 127
Joined: Fri Aug 13, 2021 4:35 pm
My RE system: BOM
(12) REC alpha-series solar panels
(12) Tigo TS4-A-O optimizers
(1) Tigo CCA outdoor kit
(1) Outback Radian FPR-4048A-300AFCI pre-wired inverter/charger
(2) Fortress eFlex 5.4kWh batteries
(1) Outback RSI
(3) MidNite Solar surge protectors
(1) Midnite MNPV6-250 combiner
(12) Tamarack racking kits
(2) QBox Junction Boxes
Location: Boston MA

Re: SimpliPhi Full Charge and CPM

Post by MJSullivan56 »

JRHill wrote: Sun Jan 23, 2022 11:46 am BTW, the exhaust extension I added a few weeks ago works like a champ. Sorry for the thread drift.
Thx. Looks like an ideal addition to my outdoor shed.
JRHill
Forum Emperor
Posts: 2391
Joined: Thu Feb 17, 2011 11:12 am
My RE system: 48v OB inverter and charge controller, hub and mate3s.
Location: PNW
Contact:

Re: SimpliPhi Full Charge and CPM

Post by JRHill »

MJSullivan56 wrote: Sun Jan 23, 2022 4:52 pm
JRHill wrote: Sun Jan 23, 2022 11:46 am BTW, the exhaust extension I added a few weeks ago works like a champ. Sorry for the thread drift.
Thx. Looks like an ideal addition to my outdoor shed.
Price has gone up. What else is new:
https://www.amazon.com/gp/product/B07HB ... image&th=1

The SS manifold, adapter and 8' silicon hose are top quality machine work. There is nothing on the end of the hose so its your option. I removed the spark arrestor and the factory flange with the screen from the generator. Exhaust comes out luke warm. I plan to run the hose onto a buried steel 5g pail with the lid perforated and a rain cover. Doubt I'd hear the unit running - I barely can now with the hose pointed away from the house. No fire hazard.
JRHill
Forum Emperor
Posts: 2391
Joined: Thu Feb 17, 2011 11:12 am
My RE system: 48v OB inverter and charge controller, hub and mate3s.
Location: PNW
Contact:

Re: SimpliPhi Full Charge and CPM

Post by JRHill »

raysun wrote: Sun Jan 23, 2022 3:27 pm Charge complete and CPM via FM80s.

Screenshot_20220123-130719_Microsoft Remote Desktop.jpg
Absorb stage. Charge current around CRA (9A) note the oscillations around that line.

20220123_131252.jpg
Wider view of charging up to and through the Absorb stage.

20220123_133450.jpg
Charging events for the cycle.
I am happy for your set up and success. Last night was more of the same for me. From the inverter charging ended early and never came close to Absorb. That's OK, 94% and 54.6 is fine. Those numbers don't align with any charging parameters, on any device. It just ended. I'll let it go another day or so because I can. If lead batteries I'd be pulling my hair out.

I am sure I'll be doing a firmware 'reflash' in the next few days. At this point there isn't much left to try. I hope OB is following this stuff with the FXR series. But from their side if they can't identify a problem there is nothing to fix. It's a curious dilemma. But I bet they have some ideas....
JRHill
Forum Emperor
Posts: 2391
Joined: Thu Feb 17, 2011 11:12 am
My RE system: 48v OB inverter and charge controller, hub and mate3s.
Location: PNW
Contact:

Re: SimpliPhi Full Charge and CPM

Post by JRHill »

Here we go after updating the Mate3s correctly:
1-25-2022-M3-Web.png
1-25-2022-M3-Web.png
Starting the generator. Love the extension hose, BTW.... This test is for malfunctions related to Mate3 firmware programming.
Attachments
1-25-2022-OBRE.png
JRHill
Forum Emperor
Posts: 2391
Joined: Thu Feb 17, 2011 11:12 am
My RE system: 48v OB inverter and charge controller, hub and mate3s.
Location: PNW
Contact:

Re: SimpliPhi Full Charge and CPM

Post by JRHill »

1-25-2022-OPRE.png
Gen mode off, Support on. A full 20aac charge:

Here we go. Two hours or so. Lets see what happens. Will I get an absorb f I can.
Last edited by JRHill on Tue Jan 25, 2022 2:17 pm, edited 1 time in total.
raysun
Forum Emperor
Posts: 7802
Joined: Tue Jul 26, 2016 5:57 am
My RE system: Flexpower Two: (2) FXR3048A-01, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
Honda EU7000is gas fuel generator

Re: SimpliPhi Full Charge and CPM

Post by raysun »

I did some configuration changes today too long to list right now, with inconclusive results, but in the process, ran into to your "spontaneous inverter charge termination" phenomenon.

Hmmm.... this needs more digging.
JRHill
Forum Emperor
Posts: 2391
Joined: Thu Feb 17, 2011 11:12 am
My RE system: 48v OB inverter and charge controller, hub and mate3s.
Location: PNW
Contact:

Re: SimpliPhi Full Charge and CPM

Post by JRHill »

Buddy, this is a problem. Some people have it and some not. There has to be a little tiny bit on its side instead of standing up. It affects some but not others. But believe me, if you're charging is screwed up it is an issue.

Really pisses me off. System voltage is 54.1.
Attachments
1-25-2022-VDC.png
Last edited by JRHill on Tue Jan 25, 2022 3:10 pm, edited 1 time in total.
JRHill
Forum Emperor
Posts: 2391
Joined: Thu Feb 17, 2011 11:12 am
My RE system: 48v OB inverter and charge controller, hub and mate3s.
Location: PNW
Contact:

Re: SimpliPhi Full Charge and CPM

Post by JRHill »

JRHill wrote: Wed Jan 19, 2022 9:53 amIf there is any good news the its sun getting above some of the trees and last two days have gotten me close to half what is needed to recharge the batteries!
Sorry for the poor diction and typos.
raysun
Forum Emperor
Posts: 7802
Joined: Tue Jul 26, 2016 5:57 am
My RE system: Flexpower Two: (2) FXR3048A-01, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
Honda EU7000is gas fuel generator

Re: SimpliPhi Full Charge and CPM

Post by raysun »

JRHill wrote: Tue Jan 25, 2022 2:27 pm Buddy, this is a problem. Some people have it and some not. There has to be a little tiny bit on its side instead of standing up. It affects some but not others. But believe me, if you're charging is screwed up it is an issue.

Really pisses me off. System voltage is 54.1.
System voltage at 54.1 and charger voltages higher than the system voltage is to be expected. The chargers will raise their voltage to a point high enough to allow full charge current to flow.

IME, what is depicted here is normal.
JRHill
Forum Emperor
Posts: 2391
Joined: Thu Feb 17, 2011 11:12 am
My RE system: 48v OB inverter and charge controller, hub and mate3s.
Location: PNW
Contact:

Re: SimpliPhi Full Charge and CPM

Post by JRHill »

No CPM. No difference in behavior.

All is not lost. Mary came home with some beautiful onion bubs. I have to get them out quickly.

Sucks to try to dig holes for bulbs in the frozen zone. Thread drift.
Last edited by JRHill on Wed Jan 26, 2022 1:06 pm, edited 1 time in total.
raysun
Forum Emperor
Posts: 7802
Joined: Tue Jul 26, 2016 5:57 am
My RE system: Flexpower Two: (2) FXR3048A-01, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
Honda EU7000is gas fuel generator

Re: SimpliPhi Full Charge and CPM

Post by raysun »

20220125_150257.jpg
Jim, I don't know if this is good news or bad news. After charging today, I turned off the FM80s and let a little charge bleed off the battery. Then I started the generator and initiated another charge cycle using the FXRs. It was a short cycle that proceeded to Absorb in about 10 minutes. After a couple of Absorb Charging / Not Charging events, the charge current dropped below CRA, and charging terminated. A moment later a CPM record appeared in the event log.

Absorb Voltage = 56.0