Yup, its disconnected. Just getting to the end of the charge cycle now. This is the excitement in my life during rainy season....
LI battery tuning
-
- Forum Emperor
- Posts: 1199
- Joined: Thu Feb 17, 2011 11:12 am
- My RE system: VFX 3648, FM80, 3k panels, Mate3, FNDC, 3ea 3.8 PHIs. And still, a wonderful wife.
- Location: Not
- Contact:
Re: LI battery tuning
-
- Forum Emperor
- Posts: 3843
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: Flexpower Two: (2) FXR3048A, (2) FM80, MATE3s, FlexNetDC
SimpliPhi 48-3.8 (6 @ 48v)
Outback IBR3 battery enclosure
Suniva 330 watt panels (12 - 6 strings of 2 in series)
Hyundai 355 watt panels (6 - 3 strings of 2 in series)
Honda EU7000is gas fuel generator
Re: LI battery tuning
LOL!
Hang in there Jim! Rainy season will be over in 6 months, tops!
BTW. Today was a very strange day. It was the 1st time in nearly 5 years that I forgot to look at OpticsRE to check on my system. Then somebody texted me with a question, and I was like: Oh yeah, let's see. Oh look at that! 100% SoC. OK, cool, whatever.
-
- Forum Emperor
- Posts: 1199
- Joined: Thu Feb 17, 2011 11:12 am
- My RE system: VFX 3648, FM80, 3k panels, Mate3, FNDC, 3ea 3.8 PHIs. And still, a wonderful wife.
- Location: Not
- Contact:
Re: LI battery tuning
I'm just taking notes. Sure enough the charge kicked out before 54.7. The key to this is in the Battery Status screen. I forced a Bulk and its climbing again at full amps incoming. I have .2 to go to hit the Days Since voltage reset (I lowered it to 54.9 temporally).raysun wrote: ↑Mon Jan 11, 2021 9:55 pmLOL!
Hang in there Jim! Rainy season will be over in 6 months, tops!
BTW. Today was a very strange day. It was the 1st time in nearly 5 years that I forgot to look at OpticsRE to check on my system. Then somebody texted me with a question, and I was like: Oh yeah, let's see. Oh look at that! 100% SoC. OK, cool, whatever.
![]()
Son of a gun, the charge kicked out again at 54.7. Forced another Bulk and its charging again at full amps in. What the heck? Why can't I get to the Absorb set point of 55.2? Why does this have to be so hard?
BTW, one thing is obvious and that's a lot of generator run time happens above 54.4 for the few amp hours going into the batteries above that voltage at full charge load. I will be rethinking generator charging above 54.5 or 54.6. If it was sunlight, cool. But this is like generator run time on a lead acid battery for absorb finishing - or at least thats the way it feels.
More to come....
-
- Forum Emperor
- Posts: 1199
- Joined: Thu Feb 17, 2011 11:12 am
- My RE system: VFX 3648, FM80, 3k panels, Mate3, FNDC, 3ea 3.8 PHIs. And still, a wonderful wife.
- Location: Not
- Contact:
Re: LI battery tuning
OK, I'm done. Fully met all the parameters and couldn't get the FNDC to self reset. My eyes are getting blurry staring at the Mate3. Good 'ol Honda needs a break.
-
- Forum Emperor
- Posts: 3843
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: Flexpower Two: (2) FXR3048A, (2) FM80, MATE3s, FlexNetDC
SimpliPhi 48-3.8 (6 @ 48v)
Outback IBR3 battery enclosure
Suniva 330 watt panels (12 - 6 strings of 2 in series)
Hyundai 355 watt panels (6 - 3 strings of 2 in series)
Honda EU7000is gas fuel generator
Re: LI battery tuning
Interpreting the graph today, between 54.4V and 100% SoC, the system added 60AH of charge to my battery.JRHill wrote: ↑Mon Jan 11, 2021 10:32 pmI'm just taking notes. Sure enough the charge kicked out before 54.7. The key to this is in the Battery Status screen. I forced a Bulk and its climbing again at full amps incoming. I have .2 to go to hit the Days Since voltage reset (I lowered it to 54.9 temporally).raysun wrote: ↑Mon Jan 11, 2021 9:55 pmLOL!
Hang in there Jim! Rainy season will be over in 6 months, tops!
BTW. Today was a very strange day. It was the 1st time in nearly 5 years that I forgot to look at OpticsRE to check on my system. Then somebody texted me with a question, and I was like: Oh yeah, let's see. Oh look at that! 100% SoC. OK, cool, whatever.
![]()
Son of a gun, the charge kicked out again at 54.7. Forced another Bulk and its charging again at full amps in. What the heck? Why can't I get to the Absorb set point of 55.2? Why does this have to be so hard?
BTW, one thing is obvious and that's a lot of generator run time happens above 54.4 for the few amp hours going into the batteries above that voltage at full charge load. I will be rethinking generator charging above 54.5 or 54.6. If it was sunlight, cool. But this is like generator run time on a lead acid battery for absorb finishing - or at least thats the way it feels.
More to come....
At 450AH capacity that's pretty well in line with the old lead acid Absorb phase in terms of state of charge (mid to high 80's) and added charge, though the correlation is basically meaningless. The time to was 1 hour to full charge @ 60A charge current. Again an essentially meaningless correlation with lead acid charging.
I guess the takeaway here is 54.4V is well away from full charge, and it takes a lot of additional charge to "move the needle" on battery voltage.
What you describe isn't much different than one of our fellow users in Haiti described when trying to charge from grid or gen and using the lower Absorb voltage @ 1 hour spec that Phi used to publish. After much experiment, I suggested he switch to the higher voltage Absorb @ 0.1 hour spec, and he's not reported any issues in months.
I tried the 54.x @ 2H absorb profile, and it worked OK for me. Absorb terminated at 1:29 on the dot for a week. I switched back to the higher termination voltage, and haven't had problems with it either. However, I don't rely on generator/inverter charging for reaching much more than 80% SoC. On a couple of occasions when letting it run toward its 56.0V termination, it did stop charging early, however, I didn't pursue the reason for it.
When I commissioned the battery, I charged it using a single inverter charger, and the generator ran for 12 straight hours to 56.4V termination.
I wonder is there's a calibration issue at play? When I set up the battery, I was very careful to "tweak" both charge controllers, the FNDC, and both inverters. The FM80s are the most precise, the FNDC is "off" by 0.05V (it would seem), and the 0.4V precision of the inverters has them wandering +/- 0.2V relative to the FM80s.
Solar charging is faultless. Inverter charging rarely gets to where it would show calibration fault. The FNDC is pretty dutiful in tracking charge termination. It may be my imagination, but calibrating voltage seems to have improved its SoC tracking as well. Maybe something to do with Peukerts, even though the constant is fixed at lead acid curve rather than lithium.
-
- Forum Emperor
- Posts: 3843
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: Flexpower Two: (2) FXR3048A, (2) FM80, MATE3s, FlexNetDC
SimpliPhi 48-3.8 (6 @ 48v)
Outback IBR3 battery enclosure
Suniva 330 watt panels (12 - 6 strings of 2 in series)
Hyundai 355 watt panels (6 - 3 strings of 2 in series)
Honda EU7000is gas fuel generator
Re: LI battery tuning
Note: The screen capture was slightly prior to charge termination, which occurred approximately 3 minutes later.
-
- Forum Emperor
- Posts: 3843
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: Flexpower Two: (2) FXR3048A, (2) FM80, MATE3s, FlexNetDC
SimpliPhi 48-3.8 (6 @ 48v)
Outback IBR3 battery enclosure
Suniva 330 watt panels (12 - 6 strings of 2 in series)
Hyundai 355 watt panels (6 - 3 strings of 2 in series)
Honda EU7000is gas fuel generator
Re: LI battery tuning
This is 2.5 hours after full charge.
-
- Forum Guru
- Posts: 395
- Joined: Thu Dec 21, 2017 10:39 am
- My RE system: Outback: off-grid
- 1 GS8048A, Mate3, FlexNetDC, Hub10.3
- 2 FLEXmax 80
- 1 FLEXmax 60
- 30 (10x3) 300w panels (9000w total)
- 6 SimpliPhi 3.4 kWh LI batteries (400ah , 20kWh)
- 1 Honda EM5000 generator + one EU3000 - Location: Wainiha, Kauai, HI
Re: LI battery tuning
I have read multiple times that LI batteries don't like being at 100% SOC all the time, e.g. for a backup supply. However, for off-grid, where we discharge them every day, does it still hurt to keep them at float (e.g. 54v) for 3-6 hours before the sun goes down?
-
- Forum Emperor
- Posts: 3843
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: Flexpower Two: (2) FXR3048A, (2) FM80, MATE3s, FlexNetDC
SimpliPhi 48-3.8 (6 @ 48v)
Outback IBR3 battery enclosure
Suniva 330 watt panels (12 - 6 strings of 2 in series)
Hyundai 355 watt panels (6 - 3 strings of 2 in series)
Honda EU7000is gas fuel generator
Re: LI battery tuning
I don't know. In my case I don't need to, so I don'tgtarolli wrote: ↑Tue Jan 12, 2021 5:52 pm I have read multiple times that LI batteries don't like being at 100% SOC all the time, e.g. for a backup supply. However, for off-grid, where we discharge them every day, does it still hurt to keep them at float (e.g. 54v) for 3-6 hours before the sun goes down?
-
- Forum Emperor
- Posts: 1016
- Joined: Mon Apr 03, 2006 1:55 am
- My RE system: Totally off grid - Hamakua side, Big Island, Hi
36 Trina 280 & 16 Phono 250 in 48 volt array (fixed) 14080w
Radians GG8048/GS4048 w GSLCs
4 FM 80 charge controllers
Hub 10.3
FNDC w/3 shunts
Mate 3s
OpticsRE - MMKL - Ninole Hi
12 SimpliPhi 3.8
14Kw Kohler 14RESA Propane
Charging Only
2FX3048T
Hub
FNDC. - shared shunt feeds from Radian FNDC
Mate 3s
10Kw MEP 803a Military gen
Honda EU7000i
Davis VantagePro2 Wx Station
On line at: https://www.wunderground.com/dashboard/pws/KHININOL2 - Location: Ninole, Hi
Re: LI battery tuning
I hit 56.4 briefly then seems to hover 98-99. Probably related to load as well.
David
Please visit http://vacation.ninolehawaii.com
Please visit http://vacation.ninolehawaii.com
-
- Forum Emperor
- Posts: 1199
- Joined: Thu Feb 17, 2011 11:12 am
- My RE system: VFX 3648, FM80, 3k panels, Mate3, FNDC, 3ea 3.8 PHIs. And still, a wonderful wife.
- Location: Not
- Contact:
Re: LI battery tuning
I take it back. Return amps weren't satisfied as I kept forcing a Bulk but killed the genset manually at 55v. So the charge didn't fall back normally. Tonight's charge run will be yet another test. The one thing that I am curious about is y'all are charging via your FM. I'm doing this with the FX. To the FNDC it should not matter?
Edit: I originally wrote 50v above - it was 55)
-
- Forum Emperor
- Posts: 1199
- Joined: Thu Feb 17, 2011 11:12 am
- My RE system: VFX 3648, FM80, 3k panels, Mate3, FNDC, 3ea 3.8 PHIs. And still, a wonderful wife.
- Location: Not
- Contact:
Re: LI battery tuning
BTW, it occurred to me on the trip to town yesterday that this VFX charging behavior may coincide with the failure of the AGS which is most likely the AC board. I've NEVER had this problem (or any other problem) with the VFX before. So there may be a problem with the control board as well.
Anyway, I have the new VFXR ready to swap with the my problematic VFX. So before I do any more whining I should get myself in gear and do what I've been putting off. Zonna has the VFX control board at $345. It has to be worth it since I hate throwing a circuit board at something that may have multiple problems that could take the replacement AC board out.
Anyway, I have the new VFXR ready to swap with the my problematic VFX. So before I do any more whining I should get myself in gear and do what I've been putting off. Zonna has the VFX control board at $345. It has to be worth it since I hate throwing a circuit board at something that may have multiple problems that could take the replacement AC board out.