From the following app note document https://outbackpower.com/downloads/docu ... p_note.pdf we have figure 7 which shows two wires going from the FM100 to the GSLC (labeled "To Inv. On/Off" -- see attached diagram).

Can anyone tell me what I'm supposed to connect these two wires to within the GSLC? It's not clear to me.

Thanks!
Michael
Attachments
Outback + Tigo layout.jpg
MJSullivan56
Forum Guru
Posts: 127
Joined: Fri Aug 13, 2021 4:35 pm
My RE system: BOM
(12) REC alpha-series solar panels
(12) Tigo TS4-A-O optimizers
(1) Tigo CCA outdoor kit
(1) Outback Radian FPR-4048A-300AFCI pre-wired inverter/charger
(2) Fortress eFlex 5.4kWh batteries
(1) Outback RSI
(3) MidNite Solar surge protectors
(1) Midnite MNPV6-250 combiner
(12) Tamarack racking kits
(2) QBox Junction Boxes
Location: Boston MA

Re: Question about FM100 + Tigo + RSI

Post by MJSullivan56 »

Could they possibly mean "Switch INV" as shown in the attached diagram?

M
Switch INV.png
raysun
Forum Emperor
Posts: 7780
Joined: Tue Jul 26, 2016 5:57 am
My RE system: Flexpower Two: (2) FXR3048A-01, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
Honda EU7000is gas fuel generator

Re: Question about FM100 + Tigo + RSI

Post by raysun »

I don't use a Radian/GSLC so can't speak from personal experience. However, the Outback Inverters have an Inverter Off function, that is switchable from a pair of terminals.

On the FX class inverters, the terminal is normally closed for "ON" and open for "OFF". It has a jumper installed on its control board by default.

It appears the GS class inverters bring the function terminals out to the GSLC. I do not know if the terminals are active by default, and switch "OFF" when a signal is applied. Check the GSLC manual for details.

I guess the RSI leads will drive the terminals to the "OFF" state when active.
fcwlp
Forum Czar
Posts: 996
Joined: Wed Jan 22, 2020 9:40 am
My RE system: GS8048A, FM80 w/3,600W PV Fixed, FM80 w/2,700W on Zomeworks tracker, Mate3, 24 Trojan 2V L16 1100AH @ C20, Grid-Tied with Kohler 14RESA LPG Generator and MEP-803 Diesel if needed.

I install and maintain grid-tied and off-grid systems in my area and consult on solar system design/operation.
Location: 80 miles NE of Phoenix at 5500'

Re: Question about FM100 + Tigo + RSI

Post by fcwlp »

raysun wrote: Thu Sep 02, 2021 2:55 pm It appears the GS class inverters bring the function terminals out to the GSLC. I do not know if the terminals are active by default, and switch "OFF" when a signal is applied. Check the GSLC manual for details.
The OP's picture is correct on the terminals to wire to, which are in the Radian inverter itself and not in the GSLC. You need to remove the jumper shown in the picture for the function to work.
raysun
Forum Emperor
Posts: 7780
Joined: Tue Jul 26, 2016 5:57 am
My RE system: Flexpower Two: (2) FXR3048A-01, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
Honda EU7000is gas fuel generator

Re: Question about FM100 + Tigo + RSI

Post by raysun »

fcwlp wrote: Thu Sep 02, 2021 7:24 pm
raysun wrote: Thu Sep 02, 2021 2:55 pm It appears the GS class inverters bring the function terminals out to the GSLC. I do not know if the terminals are active by default, and switch "OFF" when a signal is applied. Check the GSLC manual for details.
The OP's picture is correct on the terminals to wire to, which are in the Radian inverter itself and not in the GSLC. You need to remove the jumper shown in the picture for the function to work.
Thanks for the clarification. I didn't have any context for the location of the 2nd image.
MJSullivan56
Forum Guru
Posts: 127
Joined: Fri Aug 13, 2021 4:35 pm
My RE system: BOM
(12) REC alpha-series solar panels
(12) Tigo TS4-A-O optimizers
(1) Tigo CCA outdoor kit
(1) Outback Radian FPR-4048A-300AFCI pre-wired inverter/charger
(2) Fortress eFlex 5.4kWh batteries
(1) Outback RSI
(3) MidNite Solar surge protectors
(1) Midnite MNPV6-250 combiner
(12) Tamarack racking kits
(2) QBox Junction Boxes
Location: Boston MA

Re: Question about FM100 + Tigo + RSI

Post by MJSullivan56 »

fcwlp wrote: Thu Sep 02, 2021 7:24 pm The OP's picture is correct on the terminals to wire to, which are in the Radian inverter itself and not in the GSLC. You need to remove the jumper shown in the picture for the function to work.
Thank you. Great documentation is hard to achieve, hence the ambiguity.

M
fcwlp
Forum Czar
Posts: 996
Joined: Wed Jan 22, 2020 9:40 am
My RE system: GS8048A, FM80 w/3,600W PV Fixed, FM80 w/2,700W on Zomeworks tracker, Mate3, 24 Trojan 2V L16 1100AH @ C20, Grid-Tied with Kohler 14RESA LPG Generator and MEP-803 Diesel if needed.

I install and maintain grid-tied and off-grid systems in my area and consult on solar system design/operation.
Location: 80 miles NE of Phoenix at 5500'

Re: Question about FM100 + Tigo + RSI

Post by fcwlp »

MJSullivan56 wrote: Fri Sep 03, 2021 7:07 am Thank you. Great documentation is hard to achieve, hence the ambiguity.
In the 1980s I used to design, build and maintain $1+M custom semiconductor production equipment at IBM, including writing detailed manuals. A few USA (for you IBMers EFK and MVA) maintenance techs on the midnight shift got some curt responses when they called me at home. The engineers and techs in France (MOP) actually read the manual, had questions during the install and we only had one emailed question in 5+ years.