Re: Power factor mismatch? Grid very low, SB=1
Posted: Fri Apr 17, 2020 7:31 am
For testing you could try isolating the SkyBox completely and make it look like an off-grid system with only a DC array. A possible logical way to do this and startup sequence from is:
1) Open both 50A breakers in the House PNL
2) Open all breakers in the Barn Main PNL
3) Disconnect phone, CATV, and Ethernet cables
4) Open all breakers in the Barn Aux PNL including the Talesun array
5) Remove the wiring connections (N & G) for the Talesun array from the Barn Aux PNL, observe SkyBox power draw
6) Close 50A breaker in House Main PNL for the SkyBox, observe SkyBox power draw
7) Close 50A breaker in House Main PNL for Barn Main PNL, observe SkyBox power draw
8) In Barn Main PNL, separately close each 20A for Westinghouse array, observe SkyBox power draw
9) In Barn Main PNL, only close breaker powering Envoy
10) In Barn Aux PNL, reconnect N&G wires for Talesun array and observe SkyBox power draw
11) Turn on 20A breaker for Talesun array and observe SkyBox power draw
12) in Barn Aux PNL, close breaker powering Envoy
12) Reconnect phone, CATV, and Ethernet cables one at a time and observe SkyBox power draw
13) Close remaining breakers and observe
Mike, hopefully by step 5 you will have achieved the nominal SkyBox power draw. If you do not see nominal draw, then stop and reconsider what else to disconnect. Starting with step 6 you should observe a higher power draw at some step and we will be able to narrow in on the problem.
1) Open both 50A breakers in the House PNL
2) Open all breakers in the Barn Main PNL
3) Disconnect phone, CATV, and Ethernet cables
4) Open all breakers in the Barn Aux PNL including the Talesun array
5) Remove the wiring connections (N & G) for the Talesun array from the Barn Aux PNL, observe SkyBox power draw
6) Close 50A breaker in House Main PNL for the SkyBox, observe SkyBox power draw
7) Close 50A breaker in House Main PNL for Barn Main PNL, observe SkyBox power draw
8) In Barn Main PNL, separately close each 20A for Westinghouse array, observe SkyBox power draw
9) In Barn Main PNL, only close breaker powering Envoy
10) In Barn Aux PNL, reconnect N&G wires for Talesun array and observe SkyBox power draw
11) Turn on 20A breaker for Talesun array and observe SkyBox power draw
12) in Barn Aux PNL, close breaker powering Envoy
12) Reconnect phone, CATV, and Ethernet cables one at a time and observe SkyBox power draw
13) Close remaining breakers and observe
Mike, hopefully by step 5 you will have achieved the nominal SkyBox power draw. If you do not see nominal draw, then stop and reconsider what else to disconnect. Starting with step 6 you should observe a higher power draw at some step and we will be able to narrow in on the problem.