Post by Aore Adventures »

gday guys i have just upgraded my array and outback system
and now have more components than ports available on my hub 10,

at present i have
mate 3s
4 x vfxr 3048e
4 x fm 80
1 x flex max DC

Now i have added another fm80
and i have another hub 10
how do i connect this so all components show up on my optics re site showing the correct data?

thanks for your help

cheers
raysun
Forum Emperor
Posts: 4104
Joined: Tue Jul 26, 2016 5:57 am
My RE system: Flexpower Two: (2) FXR3048A, (2) FM80, MATE3s, FlexNetDC
SimpliPhi 48-3.8 (6 @ 48v)
Outback IBR3 battery enclosure
Suniva 330 watt panels (12 - 6 strings of 2 in series)
Hyundai 355 watt panels (6 - 3 strings of 2 in series)
Honda EU7000is gas fuel generator

Re: hub 10

Post by raysun »

I'd maybe contact OB sales and ask how it's done. I wouldn't think this is the first time its been asked. There should be a diagram somewhere.
Aore Adventures
Forum Whiz
Posts: 46
Joined: Sun May 29, 2016 2:42 am
My RE system: Quad stack VFXR3048E
5 x FM80'S
1 x FlexNet DC
1 x Mate 3s
2 x Hub 10
45 x REC 370 watt Alpha Panels
24 x 2900ah 2v Hoppecke flooded cells in solar air-conditioned Battery room

1 x VFX 3048EM
1 x FM80
1 x FlexNet DC
1 x Hub 10
9 x REC 370 watt Alpha Panels
24 x 2170ah 2v Hoppecke flooded cells

Kubota 18kva backup gen set
Dunlite 12kva inverter back up gen set
Generator start battery solar charger 80watt panel morning star shs-10 controller
Location: Aore Island Vanuatu
Contact:

Re: hub 10

Post by Aore Adventures »

thanks raysun , i have looked in the manual s that i can find online and nothing is mentioned , but yes i beleive that i am not the only one that has come up against this

will send an email

cheers
User avatar
Greg T Fordan
OutBack Technical Service
Posts: 420
Joined: Fri Dec 29, 2017 1:56 pm
My RE system: Radian, FM80, FNDC, 48V batt bank

Re: hub 10

Post by Greg T Fordan »

Aore Adventures wrote: Wed Feb 17, 2021 1:54 pm
at present i have
mate 3s
4 x vfxr 3048e
4 x fm 80
1 x flex max DC

Now i have added another fm80
and i have another hub 10
how do i connect this so all components show up on my optics re site showing the correct data?

thanks for your help

cheers
Please clarify. 4 VFXRs plus 4 FM80s plus 1 FNDC = 9 devices. MATE3s has a separate port. You have room for one more device (FM80)
Greg T Fordan
EngTech
Outback Power Technologies
Mike Curran
Forum Emperor
Posts: 2123
Joined: Sat Aug 28, 2004 6:28 pm
My RE system: Outback - Garage roof:
- 8 (2x4) Evergreen 180's into one FM80 (2007/2020 - replaced MX60)
- 6 (2×3) ALEO S79-300's into one FM80 (2017)
- 2 grid-tied VFXR3524A-01's series stacked, replaced GVFX's (2020)
- 12 Surrette/Rolls 2V x 1766Ah (2007)
- Hub10.3, Mate3s, FNDC, RTS. Tigo ES maximizers on each PV module.

Westinghouse Solar - Barn roof: (2012)
- 30 (2x15) 235W panels with Enphase M215 microinverters, grid-tied

Outback Skybox - Barn roof: (2019)
- 14 Talesun 275W in series (DC array input to SB inverter/charger)
- 3 SimpliPhi 3.8 batteries, 48V, 225Ah total
- AC coupled input from 14 Talesun 275W, Enphase M215 microinverters

All self-designed and self-installed
Location: Chagrin Falls, Ohio

Re: hub 10

Post by Mike Curran »

Based on your original post, Greg Fordan's response looks pretty good.

But based on your profile, looks like you have 2 separate systems with 2 separate batteries. If you're looking to integrate their data onto a single Optics data display, you're probably out of luck.
http://www.tigoenergy.com/site.php?95b2dca2-ca6c
https://enlighten.enphaseenergy.com/public/systems/Hctc107221
Aore Adventures
Forum Whiz
Posts: 46
Joined: Sun May 29, 2016 2:42 am
My RE system: Quad stack VFXR3048E
5 x FM80'S
1 x FlexNet DC
1 x Mate 3s
2 x Hub 10
45 x REC 370 watt Alpha Panels
24 x 2900ah 2v Hoppecke flooded cells in solar air-conditioned Battery room

1 x VFX 3048EM
1 x FM80
1 x FlexNet DC
1 x Hub 10
9 x REC 370 watt Alpha Panels
24 x 2170ah 2v Hoppecke flooded cells

Kubota 18kva backup gen set
Dunlite 12kva inverter back up gen set
Generator start battery solar charger 80watt panel morning star shs-10 controller
Location: Aore Island Vanuatu
Contact:

Re: hub 10

Post by Aore Adventures »

gday Greg thanks for the quick reply

yes you are correct

been a long time since i had the cover off the hub and i was just looking at optics re online on the device page stating i have "10 good devices"

so i have room for the 5th charge controller

but what if down the track i do want to ad more devices is it possible to add another hub 10 and have it all show up on optics re?

cheers
Aore Adventures
Forum Whiz
Posts: 46
Joined: Sun May 29, 2016 2:42 am
My RE system: Quad stack VFXR3048E
5 x FM80'S
1 x FlexNet DC
1 x Mate 3s
2 x Hub 10
45 x REC 370 watt Alpha Panels
24 x 2900ah 2v Hoppecke flooded cells in solar air-conditioned Battery room

1 x VFX 3048EM
1 x FM80
1 x FlexNet DC
1 x Hub 10
9 x REC 370 watt Alpha Panels
24 x 2170ah 2v Hoppecke flooded cells

Kubota 18kva backup gen set
Dunlite 12kva inverter back up gen set
Generator start battery solar charger 80watt panel morning star shs-10 controller
Location: Aore Island Vanuatu
Contact:

Re: hub 10

Post by Aore Adventures »

gday mike , yes two seperat systems , but i am not looking to combine them on optics as its fine to view separate

just in the process of tiding both systems up and energizing the new bank

i believe we have the two largest outback systems in Vanuatu and could not be more happy with them

cheers
User avatar
Greg T Fordan
OutBack Technical Service
Posts: 420
Joined: Fri Dec 29, 2017 1:56 pm
My RE system: Radian, FM80, FNDC, 48V batt bank

Re: hub 10

Post by Greg T Fordan »

Aore Adventures wrote: Wed Feb 17, 2021 2:47 pm so i have room for the 5th charge controller
Good that we got that settled ;-)
Aore Adventures wrote: Wed Feb 17, 2021 2:47 pm but what if down the track i do want to ad more devices is it possible to add another hub 10 and have it all show up on optics re?

cheers
I have to copy Mike C's answer on that one, for now. "You're probably out of luck"
Greg T Fordan
EngTech
Outback Power Technologies
User avatar
Greg T Fordan
OutBack Technical Service
Posts: 420
Joined: Fri Dec 29, 2017 1:56 pm
My RE system: Radian, FM80, FNDC, 48V batt bank

Re: hub 10

Post by Greg T Fordan »

Follow up answer. If you notice, there is a slot for a second MATE3 or MATE3s in hub10. That is non-operational, do not use it. That was probably the planned solution for your question of devices that will exceed 10, add that MATE3/MATE3s then daisy chain another hub 10. I do not know the reason why they did not pursue.
Greg T Fordan
EngTech
Outback Power Technologies
Aore Adventures
Forum Whiz
Posts: 46
Joined: Sun May 29, 2016 2:42 am
My RE system: Quad stack VFXR3048E
5 x FM80'S
1 x FlexNet DC
1 x Mate 3s
2 x Hub 10
45 x REC 370 watt Alpha Panels
24 x 2900ah 2v Hoppecke flooded cells in solar air-conditioned Battery room

1 x VFX 3048EM
1 x FM80
1 x FlexNet DC
1 x Hub 10
9 x REC 370 watt Alpha Panels
24 x 2170ah 2v Hoppecke flooded cells

Kubota 18kva backup gen set
Dunlite 12kva inverter back up gen set
Generator start battery solar charger 80watt panel morning star shs-10 controller
Location: Aore Island Vanuatu
Contact:

Re: hub 10

Post by Aore Adventures »

i thought mike was talking about combining both systems not being possible

not adding more than 10 devices to one system only?

cheers
User avatar
Greg T Fordan
OutBack Technical Service
Posts: 420
Joined: Fri Dec 29, 2017 1:56 pm
My RE system: Radian, FM80, FNDC, 48V batt bank

Re: hub 10

Post by Greg T Fordan »

Aore Adventures wrote: Wed Feb 17, 2021 3:04 pm i thought mike was talking about combining both systems not being possible

not adding more than 10 devices to one system only?

cheers
yes. hub10 and hub10.3 were designed to carry up to 10 devices plus the MATE3/MATE3s/AXs port. One battery bank.
Greg T Fordan
EngTech
Outback Power Technologies
sodamo
Forum Emperor
Posts: 1058
Joined: Mon Apr 03, 2006 1:55 am
My RE system: Totally off grid - Hamakua side, Big Island, Hi

36 Trina 280 & 16 Phono 250 in 48 volt array (fixed) 14080w
Radians GG8048/GS4048 w GSLCs
4 FM 80 charge controllers
Hub 10.3
FNDC w/3 shunts
Mate 3s
OpticsRE - MMKL - Ninole Hi
12 SimpliPhi 3.8
14Kw Kohler 14RESA Propane

Charging Only
2FX3048T
Hub
FNDC. - shared shunt feeds from Radian FNDC
Mate 3s
10Kw MEP 803a Military gen

Honda EU7000i

Davis VantagePro2 Wx Station
On line at: https://www.wunderground.com/dashboard/pws/KHININOL2
Location: Ninole, Hi

Re: hub 10

Post by sodamo »

Take a look at my profile

Basically a single system, but my FX’s are on own HUB, Mate3S and therefore controlled separately. I suspect you might be able to do something similar.

Each Mate3s has it’s own OpticsRE, both a subs to higher level site.
I can view them individually or combined. I don’t know what limitations if any
Below is screenshot of combined. Notice upper right pull down to see how structured
9B3C67A0-BECB-45F2-A6AD-9CC5B28CAB86.png
David
Please visit http://vacation.ninolehawaii.com
Mike Curran
Forum Emperor
Posts: 2123
Joined: Sat Aug 28, 2004 6:28 pm
My RE system: Outback - Garage roof:
- 8 (2x4) Evergreen 180's into one FM80 (2007/2020 - replaced MX60)
- 6 (2×3) ALEO S79-300's into one FM80 (2017)
- 2 grid-tied VFXR3524A-01's series stacked, replaced GVFX's (2020)
- 12 Surrette/Rolls 2V x 1766Ah (2007)
- Hub10.3, Mate3s, FNDC, RTS. Tigo ES maximizers on each PV module.

Westinghouse Solar - Barn roof: (2012)
- 30 (2x15) 235W panels with Enphase M215 microinverters, grid-tied

Outback Skybox - Barn roof: (2019)
- 14 Talesun 275W in series (DC array input to SB inverter/charger)
- 3 SimpliPhi 3.8 batteries, 48V, 225Ah total
- AC coupled input from 14 Talesun 275W, Enphase M215 microinverters

All self-designed and self-installed
Location: Chagrin Falls, Ohio

Re: hub 10

Post by Mike Curran »

David, that's pretty cool. So is that summary page showing both systems, with some data totaled (e.g., the energy numbers) and other (like SOC, looks like) shown individually? The voltage graph looks to be only one battery, unless the two systems track that closely...can you elaborate a bit?
http://www.tigoenergy.com/site.php?95b2dca2-ca6c
https://enlighten.enphaseenergy.com/public/systems/Hctc107221
sodamo
Forum Emperor
Posts: 1058
Joined: Mon Apr 03, 2006 1:55 am
My RE system: Totally off grid - Hamakua side, Big Island, Hi

36 Trina 280 & 16 Phono 250 in 48 volt array (fixed) 14080w
Radians GG8048/GS4048 w GSLCs
4 FM 80 charge controllers
Hub 10.3
FNDC w/3 shunts
Mate 3s
OpticsRE - MMKL - Ninole Hi
12 SimpliPhi 3.8
14Kw Kohler 14RESA Propane

Charging Only
2FX3048T
Hub
FNDC. - shared shunt feeds from Radian FNDC
Mate 3s
10Kw MEP 803a Military gen

Honda EU7000i

Davis VantagePro2 Wx Station
On line at: https://www.wunderground.com/dashboard/pws/KHININOL2
Location: Ninole, Hi

Re: hub 10

Post by sodamo »

Going to try and clarify a bit. Will try post/edit so not to lose anything. Will end up 6 pics of same day.
I picked a day last year when I know both generators ran. The FNDCs were a bit out of sync. I’ve seen that happen from time to time but not reasoned why as they monitor same battery and shunts. As for shunts
A= my Radians, B = my FM80s, and C = my FXs

SS#1 Combined Summary
C31BA987-D2A8-4624-BAB0-5D2FABD05478.png
SS#2 Combined Battery Note Net value for shunts
90CADF95-4419-4F13-9D4D-63A9D8FB1543.png
SS#3 Radian Summary
D8A382DF-895C-463B-9A3B-289E74B41EA0.png
SS#4 Radian Battery Note Shunts
David
Please visit http://vacation.ninolehawaii.com
sodamo
Forum Emperor
Posts: 1058
Joined: Mon Apr 03, 2006 1:55 am
My RE system: Totally off grid - Hamakua side, Big Island, Hi

36 Trina 280 & 16 Phono 250 in 48 volt array (fixed) 14080w
Radians GG8048/GS4048 w GSLCs
4 FM 80 charge controllers
Hub 10.3
FNDC w/3 shunts
Mate 3s
OpticsRE - MMKL - Ninole Hi
12 SimpliPhi 3.8
14Kw Kohler 14RESA Propane

Charging Only
2FX3048T
Hub
FNDC. - shared shunt feeds from Radian FNDC
Mate 3s
10Kw MEP 803a Military gen

Honda EU7000i

Davis VantagePro2 Wx Station
On line at: https://www.wunderground.com/dashboard/pws/KHININOL2
Location: Ninole, Hi

Re: hub 10

Post by sodamo »

Continued from above
SS#4 Radian Battery Note Shunts
C796C8C4-BCCE-473C-8B81-70DDAD7F51C6.png
SS#5 FX Summary
D46C8C21-5A38-446D-A1EC-4497361778C6.png
SS#6 FX Battery Note Shunts
EBBD5996-E653-4C7F-BA50-DB077DF1BB9E.png
So I’m thinking what the OP desired maybe possible, maybe some limitations: 1 Mate3 to 1 Hub 10. Each it’s own system under a common site. Each Mate would only display its HUb connected components, but the OpticsRE site would give a total pic.

Note on FNDC non sync. As said, no clue as to why, but have learned over time that they usually resync next time 100% charge and CPM. I do have same settings on both as they see same battery.
As to how they share shunts (so you don’t have to find that thread), it was too difficult to run w sets of leads to the already installed shunts so I just piggybacked at the Radian FNDC and hoped the additional wires wouldn’t be an issue. Been in service 13 1/2 months now. If you notice the .0x difference in shunt values, I’d didn’t try to determine, just assumed it was internal to each FNDC.

ETA:
There is Temp reading on FX screen as I do have the RTS mounted there. Figured it likely had little to no effect on charging as no PV / CC.
David
Please visit http://vacation.ninolehawaii.com
User avatar
EA6LE-ONE
Forum Guru
Posts: 399
Joined: Tue May 05, 2020 7:51 am
My RE system: System 1:
MATE3s, 3 x Radian GS8048A,
4 x FLEXmax 100, HUB10,
2 x EnergyCell 48V 2700RE,
1 x FLEXnet DC, 4 x FLEXware ICS Plus,
54 x PANASONIC VBHN325SA17 325W

System 2:
MATE3s, Radian GS8048A,
2 x FLEXmax 100, HUB10
1 x EnergyCell 48V 2700RE,
1 x FLEXnet DC, 2 x FLEXware ICS
21 x PANASONIC VBHN325SA17 325W
Location: Providenciales, Turks & Caicos Isl.

Re: hub 10

Post by EA6LE-ONE »

Might want to have 2 separate shunts installed in series, each FNDC with its own shunt.
sodamo
Forum Emperor
Posts: 1058
Joined: Mon Apr 03, 2006 1:55 am
My RE system: Totally off grid - Hamakua side, Big Island, Hi

36 Trina 280 & 16 Phono 250 in 48 volt array (fixed) 14080w
Radians GG8048/GS4048 w GSLCs
4 FM 80 charge controllers
Hub 10.3
FNDC w/3 shunts
Mate 3s
OpticsRE - MMKL - Ninole Hi
12 SimpliPhi 3.8
14Kw Kohler 14RESA Propane

Charging Only
2FX3048T
Hub
FNDC. - shared shunt feeds from Radian FNDC
Mate 3s
10Kw MEP 803a Military gen

Honda EU7000i

Davis VantagePro2 Wx Station
On line at: https://www.wunderground.com/dashboard/pws/KHININOL2
Location: Ninole, Hi

Re: hub 10

Post by sodamo »

EA6LE-ONE wrote: Fri Feb 19, 2021 7:03 pm Might want to have 2 separate shunts installed in series, each FNDC with its own shunt.
Rationale?
David
Please visit http://vacation.ninolehawaii.com
User avatar
EA6LE-ONE
Forum Guru
Posts: 399
Joined: Tue May 05, 2020 7:51 am
My RE system: System 1:
MATE3s, 3 x Radian GS8048A,
4 x FLEXmax 100, HUB10,
2 x EnergyCell 48V 2700RE,
1 x FLEXnet DC, 4 x FLEXware ICS Plus,
54 x PANASONIC VBHN325SA17 325W

System 2:
MATE3s, Radian GS8048A,
2 x FLEXmax 100, HUB10
1 x EnergyCell 48V 2700RE,
1 x FLEXnet DC, 2 x FLEXware ICS
21 x PANASONIC VBHN325SA17 325W
Location: Providenciales, Turks & Caicos Isl.

Re: hub 10

Post by EA6LE-ONE »

having the 2 FNDC on the same shunt might create interference and skew the reading a bit and that why you have different SOC readings. also the Mate3s is uploading the data randomly and I observe that part of the reading from a certain hour might be reflected to the next hour.
sodamo
Forum Emperor
Posts: 1058
Joined: Mon Apr 03, 2006 1:55 am
My RE system: Totally off grid - Hamakua side, Big Island, Hi

36 Trina 280 & 16 Phono 250 in 48 volt array (fixed) 14080w
Radians GG8048/GS4048 w GSLCs
4 FM 80 charge controllers
Hub 10.3
FNDC w/3 shunts
Mate 3s
OpticsRE - MMKL - Ninole Hi
12 SimpliPhi 3.8
14Kw Kohler 14RESA Propane

Charging Only
2FX3048T
Hub
FNDC. - shared shunt feeds from Radian FNDC
Mate 3s
10Kw MEP 803a Military gen

Honda EU7000i

Davis VantagePro2 Wx Station
On line at: https://www.wunderground.com/dashboard/pws/KHININOL2
Location: Ninole, Hi

Re: hub 10

Post by sodamo »

EA6LE-ONE wrote: Sat Feb 20, 2021 3:27 am having the 2 FNDC on the same shunt might create interference and skew the reading a bit and that why you have different SOC readings. also the Mate3s is uploading the data randomly and I observe that part of the reading from a certain hour might be reflected to the next hour.
Possibly true, but I doubt much cause for concern in my case. But if I understand you correctly - each FNDC with its own shunts? That would be a challenge wire unless I’m missing something. Shoot, without a major hassle I couldn’t even get in to run the second sensor wires off the shunts, can’t imagine finding space for 3 more unless the 2nd GSLC and then having to double wire the inverters and CCs, getting more complicated.
Then with two sets which do you believe?

Here is combined SS of today
Graphs running pretty close, close enough not to be concerning.
7C586F85-2AC0-4BEA-9A48-9D814B8442F7.png
David