Battery Bank in Parallel
-
- Forum Member
- Posts: 8
- Joined: Thu Jul 02, 2020 9:03 am
- My RE system: Aquired
Just helping friend with aquired Outback components:
1- Inverter/Charger VFXR3648A
2-SOLAR CHARGER FLEX mAX 80
16-SLA BATTERY 12 VOLYS, 250AH
12-LG365Q1C-A5 365WATT SOLAR MODULES
Battery Bank in Parallel
Have 2 battery banks composed of 8-12 volt 250AH SLA batteries connected series/parallel ( 16-total ). Can I connect the 2 battery banks ( 48-volt 500AH ) in parallel ( 48-volt 1000AH ) total capacity to 1-VFXR3649A Inverter ? Each battery bank is charged thru FlexMax 80 using solar array supplying 110 Volt at 20 Amps each.
-
- Forum Emperor
- Posts: 7740
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: Flexpower Two: (2) FXR3048A-01, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
Honda EU7000is gas fuel generator
Re: Battery Bank in Parallel
Are all the battery monoblocks the same model, and the same age?
-
- Forum Member
- Posts: 8
- Joined: Thu Jul 02, 2020 9:03 am
- My RE system: Aquired
Just helping friend with aquired Outback components:
1- Inverter/Charger VFXR3648A
2-SOLAR CHARGER FLEX mAX 80
16-SLA BATTERY 12 VOLYS, 250AH
12-LG365Q1C-A5 365WATT SOLAR MODULES
Re: Battery Bank in Parallel
Yes, about 1 year old and are fully charged because I tried to charge 4 connected in series using a flexmax 80 CC from a solar array of 110 volt at 9.95 amps and it went directly to Absorb ( .2 Amps ) meaning won't take anymore charge. This I did to see if the batteries are good or not.
- SandyP
- Forum Czar
- Posts: 507
- Joined: Tue Jun 21, 2011 4:44 am
- My RE system: 8 x 190W 24V Suntech panels (4 strings of 2) July 2011
4 x 325W 24V Suntech panels (2 strings of 2) added Sept2018
Mate2
Outback FM60 MPPT (max output lowered to 55amps)
12 x 2V Hoppecke GEL 612 Ah C24 - 24V System (June 2011)
Outback VFX3024 Inverter/Charger
Victron BMV-602s
Honda 5.5kW Genset - Location: Victoria, Australia
Re: Battery Bank in Parallel
Four parallel strings of batteries is not ideal. Make sure all the cabling is good and ALL the interconnectors are of equal length.headsavers wrote: ↑Wed Jul 08, 2020 5:14 pm Have 2 battery banks composed of 8-12 volt 250AH SLA batteries connected series/parallel ( 16-total ). Can I connect the 2 battery banks ( 48-volt 500AH ) in parallel ( 48-volt 1000AH ) total capacity to 1-VFXR3649A Inverter ? Each battery bank is charged thru FlexMax 80 using solar array supplying 110 Volt at 20 Amps each.
The VFXR will operate with the 1000Ah battery bank however the charging using the inverter will not be optimal.
Your solar panel array should give enough current to meet the charging requirements of the battery bank.
-------------------------
http://spwebcam.myddns.me/
http://spwebcam.myddns.me/
-
- Forum Emperor
- Posts: 1093
- Joined: Thu Jul 27, 2006 4:34 pm
- My RE system: 16 Evergreen EC-120 (4 strings, total 1920W)
2 SimpliPhi 3.8-m-24V (150Ah each)
One FM80
One VFXR3524A
Hub 10
Mate3s
FNDC
Honda EU3000is generator - Location: Sierra foothills
Re: Battery Bank in Parallel
I'd say it's marginal. 4380W of panels at full rated power would give 91A at 48V. That's a 9% charge rate for a 1000Ah pack, and that's at a power level you'll rarely see. If you just lost (sold?) one string you'd have a pack that would be somewhat easier to keep balanced, and 91A into a 750Ah pack is a 12% charge rate.SandyP wrote: ↑Wed Jul 08, 2020 7:15 pm
Four parallel strings of batteries is not ideal. Make sure all the cabling is good and ALL the interconnectors are of equal length.
The VFXR will operate with the 1000Ah battery bank however the charging using the inverter will not be optimal.
Your solar panel array should give enough current to meet the charging requirements of the battery bank.
Do you really need that much battery?
-
- Forum Member
- Posts: 8
- Joined: Thu Jul 02, 2020 9:03 am
- My RE system: Aquired
Just helping friend with aquired Outback components:
1- Inverter/Charger VFXR3648A
2-SOLAR CHARGER FLEX mAX 80
16-SLA BATTERY 12 VOLYS, 250AH
12-LG365Q1C-A5 365WATT SOLAR MODULES
Re: Battery Bank in Parallel
This setup is not mine, it was acquired by a friend and I am just helping him check the system so that he can sell the system or the components. I help people install grid tied home solar systems. Thanks for all your suggestions.
Romeo lampa
retired E.E.
Romeo lampa
retired E.E.