Adding to the Flex Power One?

A place where users can meetup with other FlexPower One users and can find support for one another. A great place for people who have not purchased the FlexPower One yet to look up information.
Post Reply
wpmaura
Forum Whiz
Posts: 46
Joined: Wed Feb 19, 2020 1:25 pm
My RE system: flex power one 3kw. 16 x 6v 415ah Rolls, 15x 270watt 30V 9amp panels

Adding to the Flex Power One?

Post by wpmaura »

So I will be recieving the flex power one in about 4 weeks. Specificaly its model FP1 FXR3048A. I have the oportunity to buy an outback 2kw inverter/charger. Can this be added to the flex power one? to give me 5kw
Mike Curran
Forum Emperor
Posts: 2284
Joined: Sat Aug 28, 2004 6:28 pm
My RE system: Outback - Garage roof:
- 8 (2x4) Evergreen 180's into one FM80 (2007/2020 - replaced MX60)
- 6 (2×3) ALEO S79-300's into one FM80 (2017)
- 2 grid-tied VFXR3524A-01's series stacked, replaced GVFX's (2020)
- 12 Surrette/Rolls 2V x 1766Ah (2007)
- Hub10.3, Mate3s, FNDC, RTS. Tigo ES maximizers on each PV module.

Westinghouse Solar - Barn roof: (2012)
- 30 (2x15) 235W panels with Enphase M215 microinverters, grid-tied

Outback Skybox - Barn roof: (2019)
- 14 Talesun 275W in series (DC array input to SB inverter/charger)
- 3 SimpliPhi 3.8 batteries, 48V, 225Ah total
- AC coupled input from 14 Talesun 275W, Enphase M215 microinverters

All self-designed and self-installed
Location: Chagrin Falls, Ohio

Re: Adding to the Flex Power One?

Post by Mike Curran »

The installation manual says "All stacked FXR inverters must have the same firmware revision. If inverters are stacked with different firmware revisions, any unit with a revision different from the master will not function. The system display will display the following message: An inverter firmware mismatch has been detected. Inverters X, Y, Z3 are disabled. Visit www.outbackpower.com for current inverter firmware. "

In effect, sounds like the inverter you add must be identical to the one in your FP1. So no, probably can't add a 2000 watt inverter - unless OB uses the same firmware on different model inverters, which I can't speak to..
https://smart.tigoenergy.com/p/pZXn7SZQyO45?date=2021-04-19
https://enlighten.enphaseenergy.com/public/systems/Hctc107221
raysun
Forum Emperor
Posts: 4624
Joined: Tue Jul 26, 2016 5:57 am
My RE system: Flexpower Two: (2) FXR3048A, (2) FM80, MATE3s, FlexNetDC
SimpliPhi 48-3.8 (6 @ 48v)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
Honda EU7000is gas fuel generator

Re: Adding to the Flex Power One?

Post by raysun »

wpmaura wrote: Wed Feb 19, 2020 1:30 pm So I will be recieving the flex power one in about 4 weeks. Specificaly its model FP1 FXR3048A. I have the oportunity to buy an outback 2kw inverter/charger. Can this be added to the flex power one? to give me 5kw
Even if the inverters were identical, getting the additional BOS components and wiring into the very cramped FP1 AC and DC panels would be a major pain.

I added an FM80 to an FP1, am very adept at electrical wiring in cramped spaces, and will not be trying this, or any, upgrades to a similar panel in the future. TBH, if I had an FP1 and realized I needed the 2nd inverter, I'd sell it and buy an FP2.
wpmaura
Forum Whiz
Posts: 46
Joined: Wed Feb 19, 2020 1:25 pm
My RE system: flex power one 3kw. 16 x 6v 415ah Rolls, 15x 270watt 30V 9amp panels

Re: Adding to the Flex Power One?

Post by wpmaura »

Well I dont care about adding into it. I can install it next to it. Right? So as long as I update booths firmware I can stack it then
fcwlp
Forum Czar
Posts: 792
Joined: Wed Jan 22, 2020 9:40 am
My RE system: GS8048A, FM80 w/3,600W PV Fixed, FM80 w/2,700W on Zomeworks tracker, Mate3, 24 Trojan 2V L16 1100AH @ C20, Grid-Tied with Kohler 14RESA LPG Generator and MEP-803 Diesel if needed.

I install and maintain grid-tied and off-grid systems in my area and consult on solar system design/operation.
Location: 80 miles NE of Phoenix at 5500'

Re: Adding to the Flex Power One?

Post by fcwlp »

wpmaura wrote: Wed Feb 19, 2020 1:30 pm I have the oportunity to buy an outback 2kw inverter/charger. Can this be added to the flex power one? to give me 5kw
In addition to the issues highlighted by Mike and raysun. The only 2kW OB inverters that I am aware of are 12V systems. Your FXR3048 is a 48V system. You would therefore need another battery bank at 12v, another CC and another set of solar panels. Do not attempt to tap into a 12V segment of your 48V bank.
wpmaura
Forum Whiz
Posts: 46
Joined: Wed Feb 19, 2020 1:25 pm
My RE system: flex power one 3kw. 16 x 6v 415ah Rolls, 15x 270watt 30V 9amp panels

Re: Adding to the Flex Power One?

Post by wpmaura »

yes a 12v would be a problem
raysun
Forum Emperor
Posts: 4624
Joined: Tue Jul 26, 2016 5:57 am
My RE system: Flexpower Two: (2) FXR3048A, (2) FM80, MATE3s, FlexNetDC
SimpliPhi 48-3.8 (6 @ 48v)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
Honda EU7000is gas fuel generator

Re: Adding to the Flex Power One?

Post by raysun »

wpmaura wrote: Wed Feb 19, 2020 3:16 pm Well I dont care about adding into it. I can install it next to it. Right? So as long as I update booths firmware I can stack it then
You might want to check what's needed for disconnects/breakers, and feed wiring, and make sure all that can be integrated properly.

I've never stacked inverters, but I've never seen mixed models stacked either.
wpmaura
Forum Whiz
Posts: 46
Joined: Wed Feb 19, 2020 1:25 pm
My RE system: flex power one 3kw. 16 x 6v 415ah Rolls, 15x 270watt 30V 9amp panels

Re: Adding to the Flex Power One?

Post by wpmaura »

well I think I need to purchase the identical inverter as the FP1 as I need to convert the house over to 240 from 120 so I can use my split AC units again and more importantly so that the power company will aprove my house so I can get power back into for grid tie.

If I didnt have little ones wouldnt worry about AC but there room is hot and gets no breeze.
wpmaura
Forum Whiz
Posts: 46
Joined: Wed Feb 19, 2020 1:25 pm
My RE system: flex power one 3kw. 16 x 6v 415ah Rolls, 15x 270watt 30V 9amp panels

Re: Adding to the Flex Power One?

Post by wpmaura »

in facat need to turn this into a flex power 2 eventually