Array disconnect wiring

Post by raysun »

The 80 panel mounted DC breaker terminals are labeled "Load" and "Line". Does it matter which terminal is connected to the combiner box?
User avatar
Megunticook
Forum Guru
Posts: 266
Joined: Fri Sep 29, 2017 4:08 am
My RE system: 6.4 kW solar array (21 QCell 305 panels in strings of 3)
GS8048A FLEXpower Radian (Radian 8048A, 2 FlexMax 80 cc's, Mate 3s, FlexNet DC, Hub)
8x6v Rolls-Surette 550 FLA batteries, 428AH
Location: Maine
Contact:

Re: Array disconnect wiring

Post by Megunticook »

Some circuit breakers are not designed to be backfed, so I would connect the terminal marked "line" to the combiner box.