Help needed FP1 startup

A place where users can meetup with other FlexPower One users and can find support for one another. A great place for people who have not purchased the FlexPower One yet to look up information.
Post Reply
Surfpath
Forum Expert
Posts: 59
Joined: Wed Apr 18, 2012 8:46 am
My RE system: Outback Flexpower-1-6 system (VFX3048e, FM80, 48v, 50hz, 240v), 2,750w of PV (4 series of 3 panels/ea, 100v max-combiner to controller), 370amp/hr L16REB battery bank. Honda 2k briefcase generator. 100% offgrid.

Help needed FP1 startup

Post by Surfpath »

Does anybody know where is the controller to battery bank breaker on an FP1?

See this discussion fmi..http://forum.solar-electric.com/discuss ... l-issue/p2
Thanks!
sparksalot
Forum Guru
Posts: 319
Joined: Sun Jul 17, 2016 5:31 am
My RE system: FLEXpower TWO VFXR3648A Grid-Tied and Battery Backup Hybrid, Mate3s
Using Two Midnite 200 Classic Charge Controllers

Traction battery FLA 48 volt 805Ahr.

32 SolarWorld 245w mono, 2x-4S-4P
6 REC 320w on micro-inverters

Re: Help needed FP1 startup

Post by sparksalot »

see below response...
Last edited by sparksalot on Mon Oct 08, 2018 7:47 am, edited 3 times in total.
User avatar
Kurt Lundquist
Alpha Energy Engineering
Posts: 1447
Joined: Tue May 31, 2011 7:23 am
My RE system: VFX3524, Mate3, 200Ah 24V AGM Battery Bank
Location: Arlington, WA

Re: Help needed FP1 startup

Post by Kurt Lundquist »

The breaker with the green handle (GFDI) is the charge controller disconnect. It is on the lower left side of the FP1.

-Kurt
Kurt Lundquist
Renewable Energy Project Engineer
http://alphaenergy.us/
Post Reply