Generator won't stop running, batteries at target V
Posted: Fri Dec 25, 2020 12:54 pm
System includes
Mate3s
3 8048
3 Blue Planet 16 kWh
1 Generac 30 kW genset
1. Each inverter is set to Absorb- 55.2 V for .1 hours
2. AGS on Mate is set to Absorb 55.2 V for .1 hours
55.2 volts is reached by outback and egauge reporting, charging stops (also by charge controllers with same set points) but genset sometimes stops after 30 minutes (too long) or goes for hours, supporting demand and not charging anything with the batteries sitting fully charged at 55.2 V. Using all the propane in an inaccessible location months before a service truck can get in would not make my client happy. Any advice appreciated, please note site is not (easily) accessible and all changes must be made remotely until May.
Mate3s
3 8048
3 Blue Planet 16 kWh
1 Generac 30 kW genset
1. Each inverter is set to Absorb- 55.2 V for .1 hours
2. AGS on Mate is set to Absorb 55.2 V for .1 hours
55.2 volts is reached by outback and egauge reporting, charging stops (also by charge controllers with same set points) but genset sometimes stops after 30 minutes (too long) or goes for hours, supporting demand and not charging anything with the batteries sitting fully charged at 55.2 V. Using all the propane in an inaccessible location months before a service truck can get in would not make my client happy. Any advice appreciated, please note site is not (easily) accessible and all changes must be made remotely until May.