Post Reply
jimatlowergulch
Forum Junior Member
Posts: 1
Joined: Wed Jun 09, 2021 5:52 pm
My RE system: gs8084 , gslc. flex max 60

SOC Not Correct

Post by jimatlowergulch »

My SOC reading 12% battery is reading 52 volts
constant events relating to this I am sure i have missed a step at start up
sbrownian
Forum Czar
Posts: 551
Joined: Mon Nov 30, 2020 9:23 am
My RE system: GS8048 FM80 FNDC Mate3
4kw solar
7kw Kubota propane gen
Had 1200 Ahr FLA Locomotive batts
Just replaced with
2 x 300 Ah ReLion Lithium packs
MUCH more efficient!!
Location: Central Washington State

Re: SOC Not Correct

Post by sbrownian »

Yes you have.

Including posting enough information...
Information, you get not; if incorrect question, you ask..
Mike Curran
Forum Emperor
Posts: 2304
Joined: Sat Aug 28, 2004 6:28 pm
My RE system: Outback - Garage roof:
- 8 (2x4) Evergreen 180's into one FM80 (2007/2020 - replaced MX60)
- 6 (2×3) ALEO S79-300's into one FM80 (2017)
- 2 grid-tied VFXR3524A-01's series stacked, replaced GVFX's (2020)
- 12 Surrette/Rolls 2V x 1766Ah (2007)
- Hub10.3, Mate3s, FNDC, RTS. Tigo ES maximizers on each PV module.

Westinghouse Solar - Barn roof: (2012)
- 30 (2x15) 235W panels with Enphase M215 microinverters, grid-tied

Outback Skybox - Barn roof: (2019)
- 14 Talesun 275W in series (DC array input to SB inverter/charger)
- 3 SimpliPhi 3.8 batteries, 48V, 225Ah total
- AC coupled input from 14 Talesun 275W, Enphase M215 microinverters

All self-designed and self-installed
Location: Chagrin Falls, Ohio

Re: SOC Not Correct

Post by Mike Curran »

Assuming there's a flexnet DC (FNDC) in your system, to get an accurate SOC measurement you must first fully charge your battery (specific gravity is a good indicator if your batteries are FLA's; follow your battery manufacturer's guidelines to get a full charge), then unplug your FNDC LAN cable from your hub, wait a few seconds, then plug it back in, and it will then show 100% SOC. These steps are described in the FNDC manual and related app note, and remember, when all else fails...

https://outbackpower.com/downloads/docu ... _guide.pdf
https://outbackpower.com/downloads/docu ... p_note.pdf
https://smart.tigoenergy.com/p/pZXn7SZQyO45?date=2021-04-19
https://enlighten.enphaseenergy.com/public/systems/Hctc107221
SandyP
Forum Guru
Posts: 470
Joined: Tue Jun 21, 2011 4:44 am
My RE system: 8 x 190W 24V Suntech panels (4 strings of 2) July 2011
4 x 325W 24V Suntech panels (2 strings of 2) added Sept2018
Mate2
Outback FM60 MPPT (max output lowered to 55amps)
12 x 2V Hoppecke GEL 612 Ah C24 - 24V System (June 2011)
Outback VFX3024 Inverter/Charger
Victron BMV-602s
Honda 5.5kW Genset
Location: Victoria, Australia

Re: SOC Not Correct

Post by SandyP »

jimatlowergulch wrote: Wed Jun 09, 2021 5:58 pm My SOC reading 12% battery is reading 52 volts
constant events relating to this I am sure i have missed a step at start up
Interesting, normally the issue is the SoC being higher than that indicated by the battery voltage.
When you mention "start up" does this mean this has only recently been installed?
-------------------------