Mate3 and Mate3s communications devices for Outback Power
Post Reply
DaimonV
Forum Junior Member
Posts: 3
Joined: Thu Feb 25, 2021 6:26 am
My RE system: Mostly work with FX 24V & 48V systems

Mate3S, Upgrade from Mate

Post by DaimonV »

This should be an easy one. I have a system w/ two stacked VFX3648s for 240VAC output. I was confusing myself w/ the question. 'Max. Inverter kW' on the profile wizard systems settings. On the one hand. I think 3.6kW is right, since each inverter can only do up to 3.6kW. On the other hand, since they are stacked, it could be 30*240. Not sure what this is being used for. Of course, after going through the wizard, I went through the settings menus.....
Q: What is the proper Max. Inverter kW for a stacked ( split ) two inverter system? Thanks for the clarification anyone can provide.
Mike Curran
Forum Emperor
Posts: 2272
Joined: Sat Aug 28, 2004 6:28 pm
My RE system: Outback - Garage roof:
- 8 (2x4) Evergreen 180's into one FM80 (2007/2020 - replaced MX60)
- 6 (2×3) ALEO S79-300's into one FM80 (2017)
- 2 grid-tied VFXR3524A-01's series stacked, replaced GVFX's (2020)
- 12 Surrette/Rolls 2V x 1766Ah (2007)
- Hub10.3, Mate3s, FNDC, RTS. Tigo ES maximizers on each PV module.

Westinghouse Solar - Barn roof: (2012)
- 30 (2x15) 235W panels with Enphase M215 microinverters, grid-tied

Outback Skybox - Barn roof: (2019)
- 14 Talesun 275W in series (DC array input to SB inverter/charger)
- 3 SimpliPhi 3.8 batteries, 48V, 225Ah total
- AC coupled input from 14 Talesun 275W, Enphase M215 microinverters

All self-designed and self-installed
Location: Chagrin Falls, Ohio

Re: Mate3S, Upgrade from Mate

Post by Mike Curran »

It's the total of the two. Uses this number to scale the low meter bar on the Mate3s:
Screenshot_20210225-160757_Adobe Acrobat.jpg
https://smart.tigoenergy.com/p/pZXn7SZQyO45?date=2021-04-19
https://enlighten.enphaseenergy.com/public/systems/Hctc107221
DaimonV
Forum Junior Member
Posts: 3
Joined: Thu Feb 25, 2021 6:26 am
My RE system: Mostly work with FX 24V & 48V systems

Re: Mate3S, Upgrade from Mate

Post by DaimonV »

Thank you! :grin:
JRHill
Forum Emperor
Posts: 1496
Joined: Thu Feb 17, 2011 11:12 am
My RE system: VFXR3648, FM80, 3k panels, Mate3s, FNDC, 4ea 3.8 PHIs. EU7000is AGS.
Location: PNW
Contact:

Re: Mate3S, Upgrade from Mate

Post by JRHill »

This may be an even easier question in upgrading from an old Mate3 to the Mate3s. Of course it will work immediately. What about history and all the stuff on the old Mate3 SD card? Wipe it? Is it useful?
sbrownian
Forum Czar
Posts: 538
Joined: Mon Nov 30, 2020 9:23 am
My RE system: GS8048 FM80 FNDC Mate3
4kw solar
7kw Kubota propane gen
Had 1200 Ahr FLA Locomotive batts
Just replaced with
2 x 300 Ah ReLion Lithium packs
MUCH more efficient!!
Location: Central Washington State

Re: Mate3S, Upgrade from Mate

Post by sbrownian »

If I you use Optics, if I understand correctly, you will have to register the new Mate3s as the MAC address will be different.
Information, you get not; if incorrect question, you ask..
raysun
Forum Emperor
Posts: 4554
Joined: Tue Jul 26, 2016 5:57 am
My RE system: Flexpower Two: (2) FXR3048A, (2) FM80, MATE3s, FlexNetDC
SimpliPhi 48-3.8 (6 @ 48v)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
Honda EU7000is gas fuel generator

Re: Mate3S, Upgrade from Mate

Post by raysun »

sbrownian wrote: Fri Mar 05, 2021 2:48 pm If I you use Optics, if I understand correctly, you will have to register the new Mate3s as the MAC address will be different.
Whatever you do, DON'T register the new Mate3s. You will lose all data from the old Mate3 (from the old MAC address actually). Contact tech support (or one of the red names on this forum) and ask them to update the database manually.
DaimonV
Forum Junior Member
Posts: 3
Joined: Thu Feb 25, 2021 6:26 am
My RE system: Mostly work with FX 24V & 48V systems

Re: Mate3S, Upgrade from Mate

Post by DaimonV »

Thanks for the heads up. It was from a mate, so no problem w/ OpticsRE. But in the future.....
sbrownian
Forum Czar
Posts: 538
Joined: Mon Nov 30, 2020 9:23 am
My RE system: GS8048 FM80 FNDC Mate3
4kw solar
7kw Kubota propane gen
Had 1200 Ahr FLA Locomotive batts
Just replaced with
2 x 300 Ah ReLion Lithium packs
MUCH more efficient!!
Location: Central Washington State

Re: Mate3S, Upgrade from Mate

Post by sbrownian »

raysun wrote: Wed Mar 10, 2021 10:54 pm
sbrownian wrote: Fri Mar 05, 2021 2:48 pm If I you use Optics, if I understand correctly, you will have to register the new Mate3s as the MAC address will be different.
Whatever you do, DON'T register the new Mate3s. You will lose all data from the old Mate3 (from the old MAC address actually). Contact tech support (or one of the red names on this forum) and ask them to update the database manually.
Ouch. You think the system would be smart enough to recognize the swap out of comm equipment (upgrade,) on an existing account, and at least offer you the choice of wiping the data or not. (Perhaps an archive option if swapping out older power gear for newer stuff?)
Information, you get not; if incorrect question, you ask..
raysun
Forum Emperor
Posts: 4554
Joined: Tue Jul 26, 2016 5:57 am
My RE system: Flexpower Two: (2) FXR3048A, (2) FM80, MATE3s, FlexNetDC
SimpliPhi 48-3.8 (6 @ 48v)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
Honda EU7000is gas fuel generator

Re: Mate3S, Upgrade from Mate

Post by raysun »

Ouch. You think the system would be smart enough to recognize the swap out of comm equipment (upgrade,) on an existing account, and at least offer you the choice of wiping the data or not. (Perhaps an archive option if swapping out older power gear for newer stuff?)
Not every system does everything, and last time I checked this system doesn't do that (without help.)

I suspect its the old trap of having intelligence coded into a key - using the MAC address as a primary index. I could be wrong, but the behavior is indicative of it.

On the upside, if thd new Mate is integrated in Optics by the "back end" folks, the integration and data continuity is seamless.
JRHill
Forum Emperor
Posts: 1496
Joined: Thu Feb 17, 2011 11:12 am
My RE system: VFXR3648, FM80, 3k panels, Mate3s, FNDC, 4ea 3.8 PHIs. EU7000is AGS.
Location: PNW
Contact:

Re: Mate3S, Upgrade from Mate

Post by JRHill »

raysun wrote: Wed Mar 10, 2021 10:54 pm
sbrownian wrote: Fri Mar 05, 2021 2:48 pm If I you use Optics, if I understand correctly, you will have to register the new Mate3s as the MAC address will be different.
Whatever you do, DON'T register the new Mate3s. You will lose all data from the old Mate3 (from the old MAC address actually). Contact tech support (or one of the red names on this forum) and ask them to update the database manually.
Wow, thx Raysun. Timely tip as the new 3s will be here by next Monday.
raysun
Forum Emperor
Posts: 4554
Joined: Tue Jul 26, 2016 5:57 am
My RE system: Flexpower Two: (2) FXR3048A, (2) FM80, MATE3s, FlexNetDC
SimpliPhi 48-3.8 (6 @ 48v)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
Honda EU7000is gas fuel generator

Re: Mate3S, Upgrade from Mate

Post by raysun »

JRHill wrote: Thu Mar 11, 2021 9:04 am
raysun wrote: Wed Mar 10, 2021 10:54 pm
sbrownian wrote: Fri Mar 05, 2021 2:48 pm If I you use Optics, if I understand correctly, you will have to register the new Mate3s as the MAC address will be different.
Whatever you do, DON'T register the new Mate3s. You will lose all data from the old Mate3 (from the old MAC address actually). Contact tech support (or one of the red names on this forum) and ask them to update the database manually.
Wow, thx Raysun. Timely tip as the new 3s will be here by next Monday.
YW. Don't ask me how I learned this, but let's just say the "5 years including" view in OpticsRE is not a relevant selection for me yet.
sbrownian
Forum Czar
Posts: 538
Joined: Mon Nov 30, 2020 9:23 am
My RE system: GS8048 FM80 FNDC Mate3
4kw solar
7kw Kubota propane gen
Had 1200 Ahr FLA Locomotive batts
Just replaced with
2 x 300 Ah ReLion Lithium packs
MUCH more efficient!!
Location: Central Washington State

Re: Mate3S, Upgrade from Mate

Post by sbrownian »

Hmmm...
No backup tapes available.

Not a real warm and fuzzy feeling here.

Hope no crypto crooks stumble by...
Information, you get not; if incorrect question, you ask..
raysun
Forum Emperor
Posts: 4554
Joined: Tue Jul 26, 2016 5:57 am
My RE system: Flexpower Two: (2) FXR3048A, (2) FM80, MATE3s, FlexNetDC
SimpliPhi 48-3.8 (6 @ 48v)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
Honda EU7000is gas fuel generator

Re: Mate3S, Upgrade from Mate

Post by raysun »

sbrownian wrote: Sat Mar 13, 2021 3:38 pm Hmmm...
No backup tapes available.

Not a real warm and fuzzy feeling here.

Hope no crypto crooks stumble by...
I don't know that's the case. Rather, registering a new Mate to an existing account disconnects the old data. Had I raised a stink, I imagine some beleaguered IT guy would have been tasked with reconstructing records.

I just didn't care to have my picture on the wall with A-hole scrawled across it.