Post by afuege »

Checking my email this morning, I had 50 messages from Outback for subscribed event notifications. When I checked the event logs, I found that numerous settings had been changed on the inverter and Comms. This started at 06:00 today, and the settings continue to change even as I write this post. Since I didn't make these changes/am not making changes, I find this somewhat alarming. The table below lists all of the changes from the first batch in the event logs. OpticsRe also just sent an e-mail saying that due to the large number of events on the system, that it was moving to hourly updates. Anyone have any clue as to why this might be happening? The mate3s is at FW 1.4.3. Thanks.


Type Device Port Description Initial State New State Unit User Timestamp
Config COMM M System Inverter AC1 Input Limit 55 220 AAC On-Site 12/21/2020 07:52
Config COMM M Sell Current Limit 30 120 AAC On-Site 12/21/2020 07:52
Config COMM M System Inverter AC2 Input Limit 55 220 AAC On-Site 12/21/2020 07:52
Config COMM M System Charger Input Limit 30 120 AAC On-Site 12/21/2020 07:52
Config COMM M OB AC Current SF -2 -1 -- On-Site 12/21/2020 07:52
Config COMM M Sell Current Limit 0 30 AAC On-Site 12/21/2020 07:49
Config COMM M Sell Current Limit 30 0 AAC On-Site 12/21/2020 07:46
Config COMM M Sell Current Limit 0 30 AAC On-Site 12/21/2020 07:31
Config INV 1 GSconfig EE Write Enable 1 0 -- On-Site 12/21/2020 07:31
Config INV 1 High Battery Cut-Out Voltage 64 0 VDC On-Site 12/21/2020 07:31
Config INV 1 Re-Bulk Voltage 48 0 VDC On-Site 12/21/2020 07:31
Config INV 1 Mini Grid Delay 10 0 Minutes On-Site 12/21/2020 07:31
Config INV 1 Grid Zero DOD Volts 50 0 VDC On-Site 12/21/2020 07:31
Config INV 1 Low Battery Cut-Out Delay 00:00:06 00:00:00 hh:mm:ss On-Site 12/21/2020 07:31
Config INV 1 High Battery Cut-In Voltage 60 0 VDC On-Site 12/21/2020 07:31
Config INV 1 High Battery Cut-Out Delay 00:00:01 00:00:00 hh:mm:ss On-Site 12/21/2020 07:31
Config INV 1 Mini Grid Connect to Grid 48 0 VDC On-Site 12/21/2020 07:31
Config INV 1 Grid Zero DOD Amps 5 0 AAC On-Site 12/21/2020 07:31
Config COMM M Sell Current Limit 30 0 AAC On-Site 12/21/2020 07:28
Config INV 1 Re-Bulk Voltage 0 48 VDC On-Site 12/21/2020 07:25
Config INV 1 High Battery Cut-In Voltage 0 60 VDC On-Site 12/21/2020 07:25
Config INV 1 High Battery Cut-Out Voltage 0 64 VDC On-Site 12/21/2020 07:25
Config INV 1 GSconfig EE Write Enable 0 1 -- On-Site 12/21/2020 07:25
Config INV 1 Low Battery Cut-Out Delay 00:00:00 00:00:06 hh:mm:ss On-Site 12/21/2020 07:25
Config INV 1 Grid Zero DOD Volts 50 0 VDC On-Site 12/21/2020 07:25
Config INV 1 Mini Grid Connect to Grid 0 48 VDC On-Site 12/21/2020 07:25
Config INV 1 Grid Zero DOD Amps 0 5 AAC On-Site 12/21/2020 07:25
Config INV 1 High Battery Cut-Out Delay 00:00:00 00:00:01 hh:mm:ss On-Site 12/21/2020 07:25
Config INV 1 Mini Grid Delay 0 10 Minutes On-Site 12/21/2020 07:25
Config INV 1 Mini Grid Delay 10 0 Minutes On-Site 12/21/2020 07:22
Config INV 1 Low Battery Cut-Out Delay 00:00:06 00:00:00 hh:mm:ss On-Site 12/21/2020 07:22
Config INV 1 High Battery Cut-Out Voltage 64 0 VDC On-Site 12/21/2020 07:22
Config INV 1 Re-Bulk Voltage 48 0 VDC On-Site 12/21/2020 07:22
Config INV 1 Grid Zero DOD Volts 50 0 VDC On-Site 12/21/2020 07:22
Config INV 1 High Battery Cut-In Voltage 60 0 VDC On-Site 12/21/2020 07:22
Config INV 1 GSconfig EE Write Enable 1 0 -- On-Site 12/21/2020 07:22
Config INV 1 Mini Grid Connect to Grid 48 0 VDC On-Site 12/21/2020 07:22
Config INV 1 High Battery Cut-Out Delay 00:00:01 00:00:00 hh:mm:ss On-Site 12/21/2020 07:22
Config INV 1 Grid Zero DOD Amps 5 0 AAC On-Site 12/21/2020 07:22
Config COMM M Sell Current Limit 0 30 AAC On-Site 12/21/2020 07:22
Config COMM M Sell Current Limit 30 0 AAC On-Site 12/21/2020 07:19
Config COMM M Sell Current Limit 120 30 AAC On-Site 12/21/2020 07:16
Config COMM M System Inverter AC1 Input Limit 220 55 AAC On-Site 12/21/2020 07:16
Config COMM M System Inverter AC2 Input Limit 220 55 AAC On-Site 12/21/2020 07:16
Config COMM M System Charger Input Limit 120 30 AAC On-Site 12/21/2020 07:16
Config COMM M OB AC Current SF -1 -2 -- On-Site 12/21/2020 07:16
Config COMM M System Inverter AC2 Input Limit 55 220 AAC On-Site 12/21/2020 07:13
Config COMM M System Inverter AC1 Input Limit 55 220 AAC On-Site 12/21/2020 07:13
Config COMM M Sell Current Limit 30 120 AAC On-Site 12/21/2020 07:13
Config COMM M System Charger Input Limit 30 120 AAC On-Site 12/21/2020 07:13
User avatar
EA6LE-ONE
Forum Guru
Posts: 362
Joined: Tue May 05, 2020 7:51 am
My RE system: System 1:
MATE3s, 3 x Radian GS8048A,
4 x FLEXmax 100, HUB10,
2 x EnergyCell 48V 2700RE,
1 x FLEXnet DC, 4 x FLEXware ICS Plus,
54 x PANASONIC VBHN325SA17 325W

System 2:
MATE3s, Radian GS8048A,
2 x FLEXmax 100, HUB10
1 x EnergyCell 48V 2700RE,
1 x FLEXnet DC, 2 x FLEXware ICS
21 x PANASONIC VBHN325SA17 325W
Location: Providenciales, Turks & Caicos Isl.

Re: Mate making configuration changes to the system

Post by EA6LE-ONE »

Don't worry about that. is just a gremlin in there that is playing with the settings.

We all get this messages more or less. they are like ghost messages that don't really reflect on the mate settings.
User avatar
afuege
Forum Member
Posts: 14
Joined: Mon Oct 19, 2020 9:28 am
My RE system: System 1: GS8048A, GSLC, 2 FM100, FlexnetDC, Mate3s, 15.9 KW Array
System 2: 3 GVFX3648, 3 FM80, FlexnetDC 9 KW Array
System 3: 16 310W panels with APS Microinverters tied directly to utility
eGauge 4x00 metering
Contact:

Re: Mate making configuration changes to the system

Post by afuege »

ah... OK... I guess. Are you just turning off notifications?
User avatar
EA6LE-ONE
Forum Guru
Posts: 362
Joined: Tue May 05, 2020 7:51 am
My RE system: System 1:
MATE3s, 3 x Radian GS8048A,
4 x FLEXmax 100, HUB10,
2 x EnergyCell 48V 2700RE,
1 x FLEXnet DC, 4 x FLEXware ICS Plus,
54 x PANASONIC VBHN325SA17 325W

System 2:
MATE3s, Radian GS8048A,
2 x FLEXmax 100, HUB10
1 x EnergyCell 48V 2700RE,
1 x FLEXnet DC, 2 x FLEXware ICS
21 x PANASONIC VBHN325SA17 325W
Location: Providenciales, Turks & Caicos Isl.

Re: Mate making configuration changes to the system

Post by EA6LE-ONE »

I had a lot before, then they stopped, occasionally I get some.
User avatar
EA6LE-ONE
Forum Guru
Posts: 362
Joined: Tue May 05, 2020 7:51 am
My RE system: System 1:
MATE3s, 3 x Radian GS8048A,
4 x FLEXmax 100, HUB10,
2 x EnergyCell 48V 2700RE,
1 x FLEXnet DC, 4 x FLEXware ICS Plus,
54 x PANASONIC VBHN325SA17 325W

System 2:
MATE3s, Radian GS8048A,
2 x FLEXmax 100, HUB10
1 x EnergyCell 48V 2700RE,
1 x FLEXnet DC, 2 x FLEXware ICS
21 x PANASONIC VBHN325SA17 325W
Location: Providenciales, Turks & Caicos Isl.

Re: Mate making configuration changes to the system

Post by EA6LE-ONE »

I just checked my logs and I see a lot of them again.

Also I tried to initiate a connection to grid to charge the batteries and is not executing it.

I will try the other system to see if is working.
raysun
Forum Emperor
Posts: 3841
Joined: Tue Jul 26, 2016 5:57 am
My RE system: Flexpower Two: (2) FXR3048A, (2) FM80, MATE3s, FlexNetDC
SimpliPhi 48-3.8 (6 @ 48v)
Outback IBR3 battery enclosure
Suniva 330 watt panels (12 - 6 strings of 2 in series)
Hyundai 355 watt panels (6 - 3 strings of 2 in series)
Honda EU7000is gas fuel generator

Re: Mate making configuration changes to the system

Post by raysun »

It looks like a scan of the configuration settings. Did you notice if any settings had changed?
User avatar
afuege
Forum Member
Posts: 14
Joined: Mon Oct 19, 2020 9:28 am
My RE system: System 1: GS8048A, GSLC, 2 FM100, FlexnetDC, Mate3s, 15.9 KW Array
System 2: 3 GVFX3648, 3 FM80, FlexnetDC 9 KW Array
System 3: 16 310W panels with APS Microinverters tied directly to utility
eGauge 4x00 metering
Contact:

Re: Mate making configuration changes to the system

Post by afuege »

I usually get one message in the morning when the system wakes up. So far today I have over 950. If I look at the configuration settings, some (but not all) have changed to default setting and subsequently changed to other values.

I've just filtered out the events for Enable Voltage below. This seems to be bouncing between 0, 24, and 57.6 volts.

Config Town Forest CC 8 Enable Voltage > 57.6 0 VDC On-Site 12/21/2020 06:13
Config Town Forest CC 8 Enable Voltage > 24 0 VDC On-Site 12/21/2020 06:13
Config Town Forest CC 8 Enable Voltage > 0 24 VDC On-Site 12/21/2020 06:16
Config Town Forest CC 8 Enable Voltage > 0 57.6 VDC On-Site 12/21/2020 06:16
Config Town Forest CC 9 Enable Voltage > 57.6 0 VDC On-Site 12/21/2020 06:34
Config Town Forest CC 9 Enable Voltage > 24 0 VDC On-Site 12/21/2020 06:34
Config Town Forest CC 9 Enable Voltage > 57.6 0 VDC On-Site 12/21/2020 06:34
Config Town Forest CC 9 Enable Voltage > 24 0 VDC On-Site 12/21/2020 06:34
Config Town Forest CC 9 Enable Voltage > 0 57.6 VDC On-Site 12/21/2020 06:37
Config Town Forest CC 9 Enable Voltage > 0 24 VDC On-Site 12/21/2020 06:37
Config Town Forest CC 8 Enable Voltage > 24 0 VDC On-Site 12/21/2020 07:04
Config Town Forest CC 8 Enable Voltage > 57.6 0 VDC On-Site 12/21/2020 07:04
Config Town Forest CC 8 Enable Voltage > 0 57.6 VDC On-Site 12/21/2020 07:10
Config Town Forest CC 8 Enable Voltage > 0 57.6 VDC On-Site 12/21/2020 07:10
Config Town Forest CC 8 Enable Voltage > 0 24 VDC On-Site 12/21/2020 07:10
Config Town Forest CC 8 Enable Voltage > 0 24 VDC On-Site 12/21/2020 07:10
Config Town Forest CC 8 Enable Voltage > 24 0 VDC On-Site 12/21/2020 09:01
Config Town Forest CC 8 Enable Voltage > 57.6 0 VDC On-Site 12/21/2020 09:01
Config Town Forest CC 8 Enable Voltage > 24 0 VDC On-Site 12/21/2020 09:01
Config Town Forest CC 8 Enable Voltage > 57.6 0 VDC On-Site 12/21/2020 09:01
Config Town Forest CC 8 Enable Voltage > 0 57.6 VDC On-Site 12/21/2020 09:07
Config Town Forest CC 8 Enable Voltage > 0 24 VDC On-Site 12/21/2020 09:07
Config Town Forest CC 8 Enable Voltage > 57.6 0 VDC On-Site 12/21/2020 09:10
Config Town Forest CC 8 Enable Voltage > 24 0 VDC On-Site 12/21/2020 09:10
Config Town Forest CC 8 Enable Voltage > 0 57.6 VDC On-Site 12/21/2020 09:13
Config Town Forest CC 8 Enable Voltage > 0 24 VDC On-Site 12/21/2020 09:13
Config Town Forest CC 8 Enable Voltage > 57.6 0 VDC On-Site 12/21/2020 09:34
Config Town Forest CC 8 Enable Voltage > 24 0 VDC On-Site 12/21/2020 09:34
Config Town Forest CC 8 Enable Voltage > 0 24 VDC On-Site 12/21/2020 09:37
Config Town Forest CC 8 Enable Voltage > 0 57.6 VDC On-Site 12/21/2020 09:37
Config Town Forest CC 8 Enable Voltage > 0 24 VDC On-Site 12/21/2020 09:37
Config Town Forest CC 8 Enable Voltage > 0 57.6 VDC On-Site 12/21/2020 09:37
Config Town Forest CC 8 Enable Voltage > 57.6 0 VDC On-Site 12/21/2020 10:52
Config Town Forest CC 8 Enable Voltage > 24 0 VDC On-Site 12/21/2020 10:52
Config Town Forest CC 8 Enable Voltage > 24 0 VDC On-Site 12/21/2020 10:52
Config Town Forest CC 8 Enable Voltage > 57.6 0 VDC On-Site 12/21/2020 10:52
Config Town Forest CC 8 Enable Voltage > 0 57.6 VDC On-Site 12/21/2020 10:55
Config Town Forest CC 8 Enable Voltage > 0 24 VDC On-Site 12/21/2020 10:55
Config Town Forest CC 8 Enable Voltage > 57.6 0 VDC On-Site 12/21/2020 11:01
Config Town Forest CC 8 Enable Voltage > 24 0 VDC On-Site 12/21/2020 11:01
Config Town Forest CC 8 Enable Voltage > 0 24 VDC On-Site 12/21/2020 11:04
Config Town Forest CC 8 Enable Voltage > 0 57.6 VDC On-Site 12/21/2020 11:04
Config Town Forest CC 8 Enable Voltage > 0 57.6 VDC On-Site 12/21/2020 11:04
Config Town Forest CC 8 Enable Voltage > 0 24 VDC On-Site 12/21/2020 11:04
Config Town Forest CC 8 Enable Voltage > 57.6 0 VDC On-Site 12/21/2020 11:07
Config Town Forest CC 8 Enable Voltage > 24 0 VDC On-Site 12/21/2020 11:07
Config Town Forest CC 8 Enable Voltage > 0 24 VDC On-Site 12/21/2020 11:10
Config Town Forest CC 8 Enable Voltage > 0 57.6 VDC On-Site 12/21/2020 11:10
Config Town Forest CC 9 Enable Voltage > 57.6 0 VDC On-Site 12/21/2020 11:55
Config Town Forest CC 9 Enable Voltage > 24 0 VDC On-Site 12/21/2020 11:55
Config Town Forest CC 9 Enable Voltage > 0 24 VDC On-Site 12/21/2020 11:58
Config Town Forest CC 9 Enable Voltage > 0 57.6 VDC On-Site 12/21/2020 11:58
Config Town Forest CC 8 Enable Voltage > 57.6 0 VDC On-Site 12/21/2020 12:01
Config Town Forest CC 8 Enable Voltage > 24 0 VDC On-Site 12/21/2020 12:01
Config Town Forest CC 8 Enable Voltage > 0 24 VDC On-Site 12/21/2020 12:04
Config Town Forest CC 8 Enable Voltage > 0 24 VDC On-Site 12/21/2020 12:04
Config Town Forest CC 8 Enable Voltage > 0 57.6 VDC On-Site 12/21/2020 12:04
Config Town Forest CC 8 Enable Voltage > 0 57.6 VDC On-Site 12/21/2020 12:04
User avatar
afuege
Forum Member
Posts: 14
Joined: Mon Oct 19, 2020 9:28 am
My RE system: System 1: GS8048A, GSLC, 2 FM100, FlexnetDC, Mate3s, 15.9 KW Array
System 2: 3 GVFX3648, 3 FM80, FlexnetDC 9 KW Array
System 3: 16 310W panels with APS Microinverters tied directly to utility
eGauge 4x00 metering
Contact:

Re: Mate making configuration changes to the system

Post by afuege »

I just noticed that the System Inverter ACx Input Limit is flipping from the configured setting of 55AAC to 220AAC and then back. This is interesting in that the allowable values range from 5 to 55AAC. A value outside this range cannot even be manually entered.

Config Town Forest COMM M System Inverter AC1 Input Limit 55 220 AAC On-Site 12/21/2020 06:25
Config Town Forest COMM M System Inverter AC1 Input Limit 220 55 AAC On-Site 12/21/2020 06:28
Config Town Forest COMM M System Inverter AC1 Input Limit 55 220 AAC On-Site 12/21/2020 07:13
Config Town Forest COMM M System Inverter AC1 Input Limit 220 55 AAC On-Site 12/21/2020 07:16
Config Town Forest COMM M System Inverter AC1 Input Limit 55 220 AAC On-Site 12/21/2020 07:52
Config Town Forest COMM M System Inverter AC1 Input Limit 220 55 AAC On-Site 12/21/2020 07:55
Config Town Forest COMM M System Inverter AC1 Input Limit 55 220 AAC On-Site 12/21/2020 08:19
Config Town Forest COMM M System Inverter AC1 Input Limit 220 55 AAC On-Site 12/21/2020 08:22
Config Town Forest COMM M System Inverter AC1 Input Limit 55 220 AAC On-Site 12/21/2020 11:40
Config Town Forest COMM M System Inverter AC1 Input Limit 220 55 AAC On-Site 12/21/2020 11:43
Config Town Forest COMM M System Inverter AC2 Input Limit 55 220 AAC On-Site 12/21/2020 06:25
Config Town Forest COMM M System Inverter AC2 Input Limit 220 55 AAC On-Site 12/21/2020 06:28
Config Town Forest COMM M System Inverter AC2 Input Limit 55 220 AAC On-Site 12/21/2020 07:13
Config Town Forest COMM M System Inverter AC2 Input Limit 220 55 AAC On-Site 12/21/2020 07:16
Config Town Forest COMM M System Inverter AC2 Input Limit 55 220 AAC On-Site 12/21/2020 07:52
Config Town Forest COMM M System Inverter AC2 Input Limit 220 55 AAC On-Site 12/21/2020 07:55
Config Town Forest COMM M System Inverter AC2 Input Limit 55 220 AAC On-Site 12/21/2020 08:19
Config Town Forest COMM M System Inverter AC2 Input Limit 220 55 AAC On-Site 12/21/2020 08:22
Config Town Forest COMM M System Inverter AC2 Input Limit 55 220 AAC On-Site 12/21/2020 11:40
Config Town Forest COMM M System Inverter AC2 Input Limit 220 55 AAC On-Site 12/21/2020 11:43
User avatar
EA6LE-ONE
Forum Guru
Posts: 362
Joined: Tue May 05, 2020 7:51 am
My RE system: System 1:
MATE3s, 3 x Radian GS8048A,
4 x FLEXmax 100, HUB10,
2 x EnergyCell 48V 2700RE,
1 x FLEXnet DC, 4 x FLEXware ICS Plus,
54 x PANASONIC VBHN325SA17 325W

System 2:
MATE3s, Radian GS8048A,
2 x FLEXmax 100, HUB10
1 x EnergyCell 48V 2700RE,
1 x FLEXnet DC, 2 x FLEXware ICS
21 x PANASONIC VBHN325SA17 325W
Location: Providenciales, Turks & Caicos Isl.

Re: Mate making configuration changes to the system

Post by EA6LE-ONE »

that is way too many. I guess outback will have to check this again. supposed to be fixed with the latest firmware.
raysun
Forum Emperor
Posts: 3841
Joined: Tue Jul 26, 2016 5:57 am
My RE system: Flexpower Two: (2) FXR3048A, (2) FM80, MATE3s, FlexNetDC
SimpliPhi 48-3.8 (6 @ 48v)
Outback IBR3 battery enclosure
Suniva 330 watt panels (12 - 6 strings of 2 in series)
Hyundai 355 watt panels (6 - 3 strings of 2 in series)
Honda EU7000is gas fuel generator

Re: Mate making configuration changes to the system

Post by raysun »

EA6LE-ONE wrote: Mon Dec 21, 2020 10:11 am that is way too many. I guess outback will have to check this again. supposed to be fixed with the latest firmware.
OP might want to update firmware to 1.4.5
User avatar
afuege
Forum Member
Posts: 14
Joined: Mon Oct 19, 2020 9:28 am
My RE system: System 1: GS8048A, GSLC, 2 FM100, FlexnetDC, Mate3s, 15.9 KW Array
System 2: 3 GVFX3648, 3 FM80, FlexnetDC 9 KW Array
System 3: 16 310W panels with APS Microinverters tied directly to utility
eGauge 4x00 metering
Contact:

Re: Mate making configuration changes to the system

Post by afuege »

raysun wrote: Mon Dec 21, 2020 10:29 am
EA6LE-ONE wrote: Mon Dec 21, 2020 10:11 am that is way too many. I guess outback will have to check this again. supposed to be fixed with the latest firmware.
OP might want to update firmware to 1.4.5
Yeah. I already downloaded the file. I'll try a bit later today.
User avatar
afuege
Forum Member
Posts: 14
Joined: Mon Oct 19, 2020 9:28 am
My RE system: System 1: GS8048A, GSLC, 2 FM100, FlexnetDC, Mate3s, 15.9 KW Array
System 2: 3 GVFX3648, 3 FM80, FlexnetDC 9 KW Array
System 3: 16 310W panels with APS Microinverters tied directly to utility
eGauge 4x00 metering
Contact:

Re: Mate making configuration changes to the system

Post by afuege »

I updated the firmware this afternoon and that seems to have stopped the issue. I now have to go back through the config and fix any changes made during this event. Anybody want to hazard a guess as to why this started happening today? The system has been quiet (from an event perspective) since it was installed in October. I haven't made any recent changes and everything has been functioning fine. It seems that it just woke up this morning and decided to start randomly changing settings on it's own.
raysun
Forum Emperor
Posts: 3841
Joined: Tue Jul 26, 2016 5:57 am
My RE system: Flexpower Two: (2) FXR3048A, (2) FM80, MATE3s, FlexNetDC
SimpliPhi 48-3.8 (6 @ 48v)
Outback IBR3 battery enclosure
Suniva 330 watt panels (12 - 6 strings of 2 in series)
Hyundai 355 watt panels (6 - 3 strings of 2 in series)
Honda EU7000is gas fuel generator

Re: Mate making configuration changes to the system

Post by raysun »

afuege wrote: Mon Dec 21, 2020 1:34 pm I updated the firmware this afternoon and that seems to have stopped the issue. I now have to go back through the config and fix any changes made during this event. Anybody want to hazard a guess as to why this started happening today? The system has been quiet (from an event perspective) since it was installed in October. I haven't made any recent changes and everything has been functioning fine. It seems that it just woke up this morning and decided to start randomly changing settings on it's own.
I notice 2 outback systems listed. No Mate listed for either. Which system is affected?

Also, can you list the parameters that were changed (as opposed to just read)?
User avatar
afuege
Forum Member
Posts: 14
Joined: Mon Oct 19, 2020 9:28 am
My RE system: System 1: GS8048A, GSLC, 2 FM100, FlexnetDC, Mate3s, 15.9 KW Array
System 2: 3 GVFX3648, 3 FM80, FlexnetDC 9 KW Array
System 3: 16 310W panels with APS Microinverters tied directly to utility
eGauge 4x00 metering
Contact:

Re: Mate making configuration changes to the system

Post by afuege »

raysun wrote: Mon Dec 21, 2020 1:41 pm
afuege wrote: Mon Dec 21, 2020 1:34 pm I updated the firmware this afternoon and that seems to have stopped the issue. I now have to go back through the config and fix any changes made during this event. Anybody want to hazard a guess as to why this started happening today? The system has been quiet (from an event perspective) since it was installed in October. I haven't made any recent changes and everything has been functioning fine. It seems that it just woke up this morning and decided to start randomly changing settings on it's own.
I notice 2 outback systems listed. No Mate listed for either. Which system is affected?

Also, can you list the parameters that were changed (as opposed to just read)?
It's the Mate3s with the Radian. I'm going through all the settings in my config spreadsheet now and will list anything that remained changed after the FW update. Not sure I understand the "as opposed to just read" part of the question. While the event was unfolding, I was checking parameters to see if they were actually being changed. As an example, I verified that the Enable Voltage setting was being changed to three different values. It would go from 57.6 to 0, then from 0 to 24, and finally from 0 to 57.6. Are you thinking the system was just reading the values and then logging it to the event log? Thanks.
raysun
Forum Emperor
Posts: 3841
Joined: Tue Jul 26, 2016 5:57 am
My RE system: Flexpower Two: (2) FXR3048A, (2) FM80, MATE3s, FlexNetDC
SimpliPhi 48-3.8 (6 @ 48v)
Outback IBR3 battery enclosure
Suniva 330 watt panels (12 - 6 strings of 2 in series)
Hyundai 355 watt panels (6 - 3 strings of 2 in series)
Honda EU7000is gas fuel generator

Re: Mate making configuration changes to the system

Post by raysun »

Most of the events that list "Config" are parameters being read, but not necessarily updated.
User avatar
afuege
Forum Member
Posts: 14
Joined: Mon Oct 19, 2020 9:28 am
My RE system: System 1: GS8048A, GSLC, 2 FM100, FlexnetDC, Mate3s, 15.9 KW Array
System 2: 3 GVFX3648, 3 FM80, FlexnetDC 9 KW Array
System 3: 16 310W panels with APS Microinverters tied directly to utility
eGauge 4x00 metering
Contact:

Re: Mate making configuration changes to the system

Post by afuege »

raysun wrote: Mon Dec 21, 2020 2:01 pm Most of the events that list "Config" are parameters being read, but not necessarily updated.
I went back in the log to initial setup and I see what you mean by some events that are more of an on/off state are listed as "config" in the event log. For those it would show initial state as enable and new state as disable. However, everywhere that there is a set value as in a specified voltage, the initial state is the old value, and the new state is the current value. Unfortunately they are all listed as "config" events. Is there any more detailed logging available for the Mate3s? Thanks.
raysun
Forum Emperor
Posts: 3841
Joined: Tue Jul 26, 2016 5:57 am
My RE system: Flexpower Two: (2) FXR3048A, (2) FM80, MATE3s, FlexNetDC
SimpliPhi 48-3.8 (6 @ 48v)
Outback IBR3 battery enclosure
Suniva 330 watt panels (12 - 6 strings of 2 in series)
Hyundai 355 watt panels (6 - 3 strings of 2 in series)
Honda EU7000is gas fuel generator

Re: Mate making configuration changes to the system

Post by raysun »

I'm not aware of any more detailed logging.

You are on the right track in checking the parameters.

You might want to report the event to the Optics team. On the OpticsRE status screen, the ? in the lower left opens up a dialog for reporting.
User avatar
afuege
Forum Member
Posts: 14
Joined: Mon Oct 19, 2020 9:28 am
My RE system: System 1: GS8048A, GSLC, 2 FM100, FlexnetDC, Mate3s, 15.9 KW Array
System 2: 3 GVFX3648, 3 FM80, FlexnetDC 9 KW Array
System 3: 16 310W panels with APS Microinverters tied directly to utility
eGauge 4x00 metering
Contact:

Re: Mate making configuration changes to the system

Post by afuege »

I thought that I had corrected this issue with the firmware upgrade. Unfortunately, this seems not to be the case. Starting at about 1:00 AM today, I started getting event overflow notifications from OpticsRe. So far today I've received 1342 messages indicating configuration changes. The system event log shows the same number of configuration updates. I was able to verify that the changes are actually being made. Here's a partial view of what's happening sorted by the configuration item and then timestamp:

Type System Device Port Description Initial State New State Unit User Timestamp
Config Town Forest CC 9 Absorb Time 2 0 Hours On-Site 01/13/2021 06:00
Config Town Forest CC 9 Absorb Time 0 2 Hours On-Site 01/13/2021 06:03
Config Town Forest CC 9 Absorb Time 2 0 Hours On-Site 01/13/2021 07:54
Config Town Forest CC 9 Absorb Time 0 2 Hours On-Site 01/13/2021 07:57
Config Town Forest CC 8 Absorb Voltage 57.6 0 VDC On-Site 01/13/2021 01:57
Config Town Forest CC 8 Absorb Voltage 0 57.6 VDC On-Site 01/13/2021 02:00
Config Town Forest CC 8 Absorb Voltage 0 57.6 VDC On-Site 01/13/2021 02:00
Config Town Forest CC 8 Absorb Voltage 57.6 0 VDC On-Site 01/13/2021 02:09
Config Town Forest CC 8 Absorb Voltage 0 57.6 VDC On-Site 01/13/2021 02:12
Config Town Forest CC 8 Absorb Voltage 57.6 0 VDC On-Site 01/13/2021 02:15
Config Town Forest CC 8 Absorb Voltage 0 57.6 VDC On-Site 01/13/2021 02:18
Config Town Forest CC 8 Absorb Voltage 57.6 0 VDC On-Site 01/13/2021 02:45
Config Town Forest CC 8 Absorb Voltage 57.6 0 VDC On-Site 01/13/2021 02:45
Config Town Forest CC 8 Absorb Voltage 0 57.6 VDC On-Site 01/13/2021 02:48
Config Town Forest CC 8 Absorb Voltage 0 57.6 VDC On-Site 01/13/2021 02:48
Config Town Forest CC 8 Absorb Voltage 57.6 0 VDC On-Site 01/13/2021 03:21
Config Town Forest CC 8 Absorb Voltage 0 57.6 VDC On-Site 01/13/2021 03:24
Config Town Forest CC 8 Absorb Voltage 57.6 0 VDC On-Site 01/13/2021 03:27
Config Town Forest CC 8 Absorb Voltage 0 57.6 VDC On-Site 01/13/2021 03:30
Config Town Forest CC 8 Absorb Voltage 57.6 0 VDC On-Site 01/13/2021 03:57
Config Town Forest CC 8 Absorb Voltage 0 57.6 VDC On-Site 01/13/2021 04:00
Config Town Forest CC 8 Absorb Voltage 0 57.6 VDC On-Site 01/13/2021 04:00
Config Town Forest CC 8 Absorb Voltage 57.6 0 VDC On-Site 01/13/2021 04:33
Config Town Forest CC 8 Absorb Voltage 0 57.6 VDC On-Site 01/13/2021 04:39
Config Town Forest CC 8 Absorb Voltage 57.6 0 VDC On-Site 01/13/2021 04:45
Config Town Forest CC 8 Absorb Voltage 57.6 0 VDC On-Site 01/13/2021 04:45
Config Town Forest CC 8 Absorb Voltage 0 57.6 VDC On-Site 01/13/2021 04:48
Config Town Forest CC 8 Absorb Voltage 0 57.6 VDC On-Site 01/13/2021 04:48
Config Town Forest CC 8 Absorb Voltage 57.6 0 VDC On-Site 01/13/2021 05:15
Config Town Forest CC 8 Absorb Voltage 0 57.6 VDC On-Site 01/13/2021 05:18
Config Town Forest CC 8 Absorb Voltage 0 57.6 VDC On-Site 01/13/2021 05:18
Config Town Forest CC 8 Absorb Voltage 57.6 0 VDC On-Site 01/13/2021 05:39
Config Town Forest CC 8 Absorb Voltage 0 57.6 VDC On-Site 01/13/2021 05:42
Config Town Forest CC 8 Absorb Voltage 0 57.6 VDC On-Site 01/13/2021 05:42
Config Town Forest CC 9 Absorb Voltage 57.6 0 VDC On-Site 01/13/2021 06:00
Config Town Forest CC 9 Absorb Voltage 0 57.6 VDC On-Site 01/13/2021 06:03
Config Town Forest CC 8 Absorb Voltage 57.6 0 VDC On-Site 01/13/2021 06:12
Config Town Forest CC 8 Absorb Voltage 0 57.6 VDC On-Site 01/13/2021 06:15
Config Town Forest CC 8 Absorb Voltage 0 57.6 VDC On-Site 01/13/2021 06:15
Config Town Forest CC 9 Absorb Voltage 57.6 0 VDC On-Site 01/13/2021 06:18
Config Town Forest CC 9 Absorb Voltage 0 57.6 VDC On-Site 01/13/2021 06:21
Config Town Forest CC 9 Absorb Voltage 0 57.6 VDC On-Site 01/13/2021 06:21
Config Town Forest CC 9 Absorb Voltage 57.6 0 VDC On-Site 01/13/2021 07:18
Config Town Forest CC 9 Absorb Voltage 0 57.6 VDC On-Site 01/13/2021 07:21
Config Town Forest CC 9 Absorb Voltage 0 57.6 VDC On-Site 01/13/2021 07:21
Config Town Forest CC 8 Absorb Voltage 57.6 0 VDC On-Site 01/13/2021 08:09
Config Town Forest CC 8 Absorb Voltage 0 57.6 VDC On-Site 01/13/2021 08:12
Config Town Forest CC 8 Aux Mode Vent Fan Float -- On-Site 01/13/2021 01:57
Config Town Forest CC 8 Aux Mode Float Vent Fan -- On-Site 01/13/2021 02:00
Config Town Forest CC 8 Aux Mode Float Vent Fan -- On-Site 01/13/2021 02:00
Config Town Forest CC 8 Aux Mode Vent Fan Float -- On-Site 01/13/2021 02:15
Config Town Forest CC 8 Aux Mode Float Vent Fan -- On-Site 01/13/2021 02:18
Config Town Forest CC 8 Aux Mode Vent Fan Float -- On-Site 01/13/2021 02:45
Config Town Forest CC 8 Aux Mode Vent Fan Float -- On-Site 01/13/2021 02:45
Config Town Forest CC 8 Aux Mode Float Vent Fan -- On-Site 01/13/2021 02:48
Config Town Forest CC 8 Aux Mode Float Vent Fan -- On-Site 01/13/2021 02:48
Config Town Forest CC 8 Aux Mode Vent Fan Float -- On-Site 01/13/2021 03:27
Config Town Forest CC 8 Aux Mode Float Vent Fan -- On-Site 01/13/2021 03:30
Config Town Forest CC 8 Aux Mode Vent Fan Float -- On-Site 01/13/2021 04:33
Config Town Forest CC 8 Aux Mode Float Vent Fan -- On-Site 01/13/2021 04:39
Config Town Forest CC 8 Aux Mode Vent Fan Float -- On-Site 01/13/2021 04:45
Config Town Forest CC 8 Aux Mode Vent Fan Float -- On-Site 01/13/2021 04:45
Config Town Forest CC 8 Aux Mode Float Vent Fan -- On-Site 01/13/2021 04:48
Config Town Forest CC 8 Aux Mode Float Vent Fan -- On-Site 01/13/2021 04:48
Config Town Forest CC 8 Aux Mode Vent Fan Float -- On-Site 01/13/2021 05:15
Config Town Forest CC 8 Aux Mode Float Vent Fan -- On-Site 01/13/2021 05:18
Config Town Forest CC 8 Aux Mode Float Vent Fan -- On-Site 01/13/2021 05:18
Config Town Forest CC 8 Aux Mode Vent Fan Float -- On-Site 01/13/2021 05:39
Config Town Forest CC 8 Aux Mode Float Vent Fan -- On-Site 01/13/2021 05:42
Config Town Forest CC 8 Aux Mode Float Vent Fan -- On-Site 01/13/2021 05:42
Config Town Forest CC 9 Aux Mode Vent Fan Float -- On-Site 01/13/2021 06:00
Config Town Forest CC 9 Aux Mode Float Vent Fan -- On-Site 01/13/2021 06:03
Config Town Forest CC 8 Aux Mode Vent Fan Float -- On-Site 01/13/2021 06:12
Config Town Forest CC 8 Aux Mode Float Vent Fan -- On-Site 01/13/2021 06:15
Config Town Forest CC 8 Aux Mode Float Vent Fan -- On-Site 01/13/2021 06:15
Config Town Forest CC 9 Aux Mode Vent Fan Float -- On-Site 01/13/2021 06:18
Config Town Forest CC 9 Aux Mode Float Vent Fan -- On-Site 01/13/2021 06:21
Config Town Forest CC 9 Aux Mode Float Vent Fan -- On-Site 01/13/2021 06:21
Config Town Forest CC 9 Aux Mode Vent Fan Float -- On-Site 01/13/2021 07:18
Config Town Forest CC 9 Aux Mode Float Vent Fan -- On-Site 01/13/2021 07:21
Config Town Forest CC 9 Aux Mode Float Vent Fan -- On-Site 01/13/2021 07:21
Config Town Forest CC 8 Current Limit 100 0 ADC On-Site 01/13/2021 01:57
Config Town Forest CC 8 Current Limit 0 100 ADC On-Site 01/13/2021 02:00
Config Town Forest CC 8 Current Limit 0 100 ADC On-Site 01/13/2021 02:00
Config Town Forest CC 8 Current Limit 100 0 ADC On-Site 01/13/2021 02:09
Config Town Forest CC 8 Current Limit 0 100 ADC On-Site 01/13/2021 02:12
Config Town Forest CC 8 Current Limit 100 0 ADC On-Site 01/13/2021 02:15
Config Town Forest CC 8 Current Limit 0 100 ADC On-Site 01/13/2021 02:18
Config Town Forest CC 8 Current Limit 100 0 ADC On-Site 01/13/2021 02:45
Config Town Forest CC 8 Current Limit 100 0 ADC On-Site 01/13/2021 02:45
Config Town Forest CC 8 Current Limit 0 100 ADC On-Site 01/13/2021 02:48
Config Town Forest CC 8 Current Limit 0 100 ADC On-Site 01/13/2021 02:48
Config Town Forest CC 8 Current Limit 100 0 ADC On-Site 01/13/2021 03:21
Config Town Forest CC 8 Current Limit 0 100 ADC On-Site 01/13/2021 03:24
Config Town Forest CC 8 Current Limit 100 0 ADC On-Site 01/13/2021 03:27
Config Town Forest CC 8 Current Limit 0 100 ADC On-Site 01/13/2021 03:30
Config Town Forest CC 8 Current Limit 100 0 ADC On-Site 01/13/2021 03:57
Config Town Forest CC 8 Current Limit 0 100 ADC On-Site 01/13/2021 04:00
Config Town Forest CC 8 Current Limit 0 100 ADC On-Site 01/13/2021 04:00
Config Town Forest CC 8 Current Limit 100 0 ADC On-Site 01/13/2021 04:33
Config Town Forest CC 8 Current Limit 0 100 ADC On-Site 01/13/2021 04:39
Config Town Forest CC 8 Current Limit 100 0 ADC On-Site 01/13/2021 04:45
Config Town Forest CC 8 Current Limit 100 0 ADC On-Site 01/13/2021 04:45
Config Town Forest CC 8 Current Limit 0 100 ADC On-Site 01/13/2021 04:48
Config Town Forest CC 8 Current Limit 0 100 ADC On-Site 01/13/2021 04:48
Config Town Forest CC 8 Current Limit 100 0 ADC On-Site 01/13/2021 05:15
Config Town Forest CC 8 Current Limit 0 100 ADC On-Site 01/13/2021 05:18
Config Town Forest CC 8 Current Limit 0 100 ADC On-Site 01/13/2021 05:18
Config Town Forest CC 8 Current Limit 100 0 ADC On-Site 01/13/2021 05:39
Config Town Forest CC 8 Current Limit 0 100 ADC On-Site 01/13/2021 05:42
Config Town Forest CC 8 Current Limit 0 100 ADC On-Site 01/13/2021 05:42
Config Town Forest CC 9 Current Limit 100 0 ADC On-Site 01/13/2021 06:00
Config Town Forest CC 9 Current Limit 0 100 ADC On-Site 01/13/2021 06:03
Config Town Forest CC 8 Current Limit 100 0 ADC On-Site 01/13/2021 06:12
Config Town Forest CC 8 Current Limit 0 100 ADC On-Site 01/13/2021 06:15
Config Town Forest CC 8 Current Limit 0 100 ADC On-Site 01/13/2021 06:15
Config Town Forest CC 9 Current Limit 100 0 ADC On-Site 01/13/2021 06:18
Config Town Forest CC 9 Current Limit 0 100 ADC On-Site 01/13/2021 06:21
Config Town Forest CC 9 Current Limit 0 100 ADC On-Site 01/13/2021 06:21
Config Town Forest CC 9 Current Limit 100 0 ADC On-Site 01/13/2021 07:18
Config Town Forest CC 9 Current Limit 0 100 ADC On-Site 01/13/2021 07:21
Config Town Forest CC 9 Current Limit 0 100 ADC On-Site 01/13/2021 07:21
Config Town Forest CC 8 Current Limit 100 0 ADC On-Site 01/13/2021 08:09
Config Town Forest CC 8 Current Limit 0 100 ADC On-Site 01/13/2021 08:12
raysun
Forum Emperor
Posts: 3841
Joined: Tue Jul 26, 2016 5:57 am
My RE system: Flexpower Two: (2) FXR3048A, (2) FM80, MATE3s, FlexNetDC
SimpliPhi 48-3.8 (6 @ 48v)
Outback IBR3 battery enclosure
Suniva 330 watt panels (12 - 6 strings of 2 in series)
Hyundai 355 watt panels (6 - 3 strings of 2 in series)
Honda EU7000is gas fuel generator

Re: Mate making configuration changes to the system

Post by raysun »

The "On Site" configuration changes suggest the issue is originating with the Mate (as opposed to coming from OpticsRE, for example).

I wonder if this is corrupt NVRAM, or possibly a defective unit. Perhaps try reloading the latest firmware.

Also, consider opening a ticket with Tech support. A replacement may be in order.
User avatar
afuege
Forum Member
Posts: 14
Joined: Mon Oct 19, 2020 9:28 am
My RE system: System 1: GS8048A, GSLC, 2 FM100, FlexnetDC, Mate3s, 15.9 KW Array
System 2: 3 GVFX3648, 3 FM80, FlexnetDC 9 KW Array
System 3: 16 310W panels with APS Microinverters tied directly to utility
eGauge 4x00 metering
Contact:

Re: Mate making configuration changes to the system

Post by afuege »

I did open a ticket this morning. I might try to reload FW later today.

Thanks.
Post Reply