My RE system: 2007 PS-1
I believe it has
Outback GVFX 3648 Inverter
Outback MPPT Charge Controller - MX60
Outback Mate Remote Display/Control Panel
12 panel solar array
Battery backup (MK Batteries 8G31 Solar Gel, 98AHr/12 V)
8 selected circuits on backup subpanel tied into the PS-1

Help? PS-1 Not defaulting to subpanel with AC dropped

Post by Bethesda »

Very non-expert here!

When power is dropped, our system is set up to default to a subpanel of selected circuits that run off our batteries. This has always worked whenever the power went out or when I tested it by dropping the AC IN on the MATE.

Testing it today, I dropped the AC IN and our entire house was running off the batteries.
Is there a switch or setting that we may have changed?

PS-1 with
Outback GVFX 3648 Inverter
Outback MPPT Charge Controller - MX60
Outback Mate Remote Display/Control Panel
Outback Battery Rack and Enclosure with MK Batteries 8G31 Solar Gel, 98AHr/12 V
12 panels

Thanks!
User avatar
Kurt Lundquist
Alpha Energy Engineering
Posts: 1447
Joined: Tue May 31, 2011 7:23 am
My RE system: VFX3524, Mate3, 200Ah 24V AGM Battery Bank
Location: Arlington, WA

Re: Help? PS-1 Not defaulting to subpanel with AC dropped

Post by Kurt Lundquist »

Press the INV button that is on the right side of the Mate screen. Is the inverter set to ON or OFF?

What lights do you see on the inverter after you drop the AC input?

Thanks,

-Kurt