Turn off just inverter
Moderators: OutBack Moderator Team, OutBack
Turn off just inverter
We have an VFXR2812A inverter/charger. My question is whether there is an easy way to turn off just the inverter while on shore power so that the float charging would continue. Shore power runs the 120V loads. But if shore power is interrupted, the inverter will come on. The electrical heaters would quickly run down the battery bank. Turning off the inverter would prevent this.
-
- Forum Czar
- Posts: 704
- Joined: Wed Jan 22, 2020 9:40 am
- My RE system: GS8048A, FM80 w/3,600W PV Fixed, FM80 w/2,700W on Zomeworks tracker, Mate3, 24 Trojan 2V L16 1100AH @ C20, Grid-Tied with Kohler 14RESA LPG Generator and MEP-803 Diesel if needed.
I install and maintain grid-tied and off-grid systems in my area and consult on solar system design/operation. - Location: 80 miles NE of Phoenix at 5500'
Re: Turn off just inverter
FWIW I have never worked on a solar system on a boat.
Do you have a charge controller? If you do, hopefully you have an AC bypass switch that would power the AC out directly from shore power. This effectively shuts off the inverter and uses the CC to float the batteries.
Do you have a charge controller? If you do, hopefully you have an AC bypass switch that would power the AC out directly from shore power. This effectively shuts off the inverter and uses the CC to float the batteries.
-
- Forum Emperor
- Posts: 3829
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: Flexpower Two: (2) FXR3048A, (2) FM80, MATE3s, FlexNetDC
SimpliPhi 48-3.8 (6 @ 48v)
Outback IBR3 battery enclosure
Suniva 330 watt panels (12 - 6 strings of 2 in series)
Hyundai 355 watt panels (6 - 3 strings of 2 in series)
Honda EU7000is gas fuel generator
Re: Turn off just inverter
The inverter charger is being used to maintain Float?
Shore power is connected to the inverter's AC IN?
I don't think there is a way to defeat the inverter's AC OUT in its normal configuration. When shore power is being used, the inverter circuit becomes the charger. When the shore power is dropped, the circuit switches back to inverting.
Perhaps some type of manual transfer switch could be used to bypass the output of the inverter such that shore power is fed to the AC IN of the inverter for its charging function, and rather than from AC OUT, shore power directly to the house loads. If shore power fails, the inverter would switch modes, but its output would see an open circuit until the transfer switch was in the inverter position. Check with a competent marine electrician about the feasibility of such an approach.
A related question. Shore power usually provides a bond between neutral and ground. There should only be one N-G bond in the system. When not on shore power how is N-G bonding done? When on shore power, how is the boat's N-G bond lifted? (Outback makes M series inverters that handle this in the inverter. It is recommended that the N-G connection be made at the power source, in this case the inverter.) Is an isolation transformer used?
Shore power is connected to the inverter's AC IN?
I don't think there is a way to defeat the inverter's AC OUT in its normal configuration. When shore power is being used, the inverter circuit becomes the charger. When the shore power is dropped, the circuit switches back to inverting.
Perhaps some type of manual transfer switch could be used to bypass the output of the inverter such that shore power is fed to the AC IN of the inverter for its charging function, and rather than from AC OUT, shore power directly to the house loads. If shore power fails, the inverter would switch modes, but its output would see an open circuit until the transfer switch was in the inverter position. Check with a competent marine electrician about the feasibility of such an approach.
A related question. Shore power usually provides a bond between neutral and ground. There should only be one N-G bond in the system. When not on shore power how is N-G bonding done? When on shore power, how is the boat's N-G bond lifted? (Outback makes M series inverters that handle this in the inverter. It is recommended that the N-G connection be made at the power source, in this case the inverter.) Is an isolation transformer used?
-
- Forum Guru
- Posts: 456
- Joined: Tue Jun 21, 2011 4:44 am
- My RE system: 8 x 190W 24V Suntech panels (4 strings of 2) July 2011
4 x 325W 24V Suntech panels (2 strings of 2) added Sept2018
Mate2
Outback FM60 MPPT (max output lowered to 55amps)
12 x 2V Hoppecke GEL 612 Ah C24 - 24V System
Outback VFX3024 Inverter/Charger
Victron BMV-602s
Honda 5.5kW Genset - Location: Victoria, Australia
Re: Turn off just inverter
I assume the heaters are only used when on shore power?
If so, then the only solution I can see is to power them via the AC IN line that goes to the inverter.
If so, then the only solution I can see is to power them via the AC IN line that goes to the inverter.
-------------------------
http://spwebcam.myddns.me/
http://spwebcam.myddns.me/
-
- Forum Emperor
- Posts: 2022
- Joined: Sat Aug 28, 2004 6:28 pm
- My RE system: Outback - Garage roof:
- 8 (2x4) Evergreen 180's into one FM80 (2007/2020 - replaced MX60)
- 6 (2×3) ALEO S79-300's into one FM80 (2017)
[***2 grid-tied GVFX3524's classic stacked for 120/240VAC (2007-2020)]
- 2 grid-tied VFXR3524A-01's series stacked, ***replaced GVFX's (2020)
- 12 Surrette/Rolls 2V x 1766Ah (2007)
- Hub10.3, Mate3s, FNDC, RTS, OpticsRE. Tigo Energy ES maximizers on each PV module.
Westinghouse Solar - Barn roof: (2012)
- 30 (2x15) 235W panels with Enphase M215 microinverters, grid-tied
Outback Skybox - Barn roof: (2019)
- 14 Talesun 275W in series (DC array input to SB inverter/charger)
- 3 SimpliPhi 3.8 batteries, 48V, 225Ah total
- AC coupled input (manual switch during grid outage only) from 14 Talesun 275W,
Enphase M215 microinverters, normally direct grid tied
All self-designed and self-installed - Location: Chagrin Falls, Ohio
Re: Turn off just inverter
This isn't an easy way but its doable and it'll work.
Put a single throw, double pole relay in the AC out from your inverter, with the coil energized by shore power. When there is shore power, the contacts will be closed and shore power will continue to feed your loads. When shore power is interrupted, the relay will drop out and your loads will be disconnected from your inverter. You could also use the relay for just your heaters if you wanted your inverter to supply other loads during outages and only disconnect the heaters.
Note if you only have a single phase inverter you only need a single pole relay instead of double pole. Just be sure to size the relay contacts for whatever current your desired interruptible loads draw.
Put a single throw, double pole relay in the AC out from your inverter, with the coil energized by shore power. When there is shore power, the contacts will be closed and shore power will continue to feed your loads. When shore power is interrupted, the relay will drop out and your loads will be disconnected from your inverter. You could also use the relay for just your heaters if you wanted your inverter to supply other loads during outages and only disconnect the heaters.
Note if you only have a single phase inverter you only need a single pole relay instead of double pole. Just be sure to size the relay contacts for whatever current your desired interruptible loads draw.
http://www.tigoenergy.com/site.php?95b2dca2-ca6c
https://enlighten.enphaseenergy.com/public/systems/Hctc107221
https://enlighten.enphaseenergy.com/public/systems/Hctc107221
-
- Forum Junior Member
- Posts: 1
- Joined: Sun Nov 29, 2020 9:09 am
- My RE system: 2 X VFX2812M with hub and MATE2
ReLion LiFePO batteries
Re: Turn off just inverter
Do you have a MATE controller/display? My system has two VFX2812 inverter/chargers and a MATE2. Using the MATE, I can turn the inverter off with a press of a button and leave the charger on to float the batteries. I do this often when away from shore power to save the idle current when the inverter is not needed.
(press INV twice, then press the soft key for OFF or SRCH or ON, as needed)
(press INV twice, then press the soft key for OFF or SRCH or ON, as needed)
-
- Forum Emperor
- Posts: 2022
- Joined: Sat Aug 28, 2004 6:28 pm
- My RE system: Outback - Garage roof:
- 8 (2x4) Evergreen 180's into one FM80 (2007/2020 - replaced MX60)
- 6 (2×3) ALEO S79-300's into one FM80 (2017)
[***2 grid-tied GVFX3524's classic stacked for 120/240VAC (2007-2020)]
- 2 grid-tied VFXR3524A-01's series stacked, ***replaced GVFX's (2020)
- 12 Surrette/Rolls 2V x 1766Ah (2007)
- Hub10.3, Mate3s, FNDC, RTS, OpticsRE. Tigo Energy ES maximizers on each PV module.
Westinghouse Solar - Barn roof: (2012)
- 30 (2x15) 235W panels with Enphase M215 microinverters, grid-tied
Outback Skybox - Barn roof: (2019)
- 14 Talesun 275W in series (DC array input to SB inverter/charger)
- 3 SimpliPhi 3.8 batteries, 48V, 225Ah total
- AC coupled input (manual switch during grid outage only) from 14 Talesun 275W,
Enphase M215 microinverters, normally direct grid tied
All self-designed and self-installed - Location: Chagrin Falls, Ohio
Re: Turn off just inverter
Great first post, JeffJeffTaylor wrote: ↑Sun Nov 29, 2020 9:17 am Do you have a MATE controller/display? My system has two VFX2812 inverter/chargers and a MATE2. Using the MATE, I can turn the inverter off with a press of a button and leave the charger on to float the batteries. I do this often when away from shore power to save the idle current when the inverter is not needed.
(press INV twice, then press the soft key for OFF or SRCH or ON, as needed)

http://www.tigoenergy.com/site.php?95b2dca2-ca6c
https://enlighten.enphaseenergy.com/public/systems/Hctc107221
https://enlighten.enphaseenergy.com/public/systems/Hctc107221
-
- Forum Emperor
- Posts: 3829
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: Flexpower Two: (2) FXR3048A, (2) FM80, MATE3s, FlexNetDC
SimpliPhi 48-3.8 (6 @ 48v)
Outback IBR3 battery enclosure
Suniva 330 watt panels (12 - 6 strings of 2 in series)
Hyundai 355 watt panels (6 - 3 strings of 2 in series)
Honda EU7000is gas fuel generator
Re: Turn off just inverter
In all the time I've employed an FX class inverter, I've never set it OFF, and thought to test whether the charger mode continues to function.JeffTaylor wrote: ↑Sun Nov 29, 2020 9:17 am Do you have a MATE controller/display? My system has two VFX2812 inverter/chargers and a MATE2. Using the MATE, I can turn the inverter off with a press of a button and leave the charger on to float the batteries. I do this often when away from shore power to save the idle current when the inverter is not needed.
(press INV twice, then press the soft key for OFF or SRCH or ON, as needed)
Does it?
-
- Forum Guru
- Posts: 456
- Joined: Tue Jun 21, 2011 4:44 am
- My RE system: 8 x 190W 24V Suntech panels (4 strings of 2) July 2011
4 x 325W 24V Suntech panels (2 strings of 2) added Sept2018
Mate2
Outback FM60 MPPT (max output lowered to 55amps)
12 x 2V Hoppecke GEL 612 Ah C24 - 24V System
Outback VFX3024 Inverter/Charger
Victron BMV-602s
Honda 5.5kW Genset - Location: Victoria, Australia
Re: Turn off just inverter
Interested to know this as well.
For the heaters to still work the pass through function would also need to operate with the inverter in OFF mode.
Edit: The only reference I can see to the Inverter On/Off function and its impact on other functions is in the FX/VFX Mobile manual, page 10 :
On/Off Switch
If a system display is not in use, the inverter can be equipped with a switch to turn it on and off.
This switch is not sold as an inverter accessory; a common toggle switch can be used. The switch
is wired to the INVERTER ON/OFF auxiliary terminals. (See the FX and VFX Mobile Series
Inverter/Charger Installation Manual for more information on wiring the switch.)
This switch turns only the inverter on and off. It does not turn the charger or any other function on
or off. All inverter functions will operate according to their programmed settings. Functions
included with a system display will not be available.
-------------------------
http://spwebcam.myddns.me/
http://spwebcam.myddns.me/
-
- Forum Emperor
- Posts: 3829
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: Flexpower Two: (2) FXR3048A, (2) FM80, MATE3s, FlexNetDC
SimpliPhi 48-3.8 (6 @ 48v)
Outback IBR3 battery enclosure
Suniva 330 watt panels (12 - 6 strings of 2 in series)
Hyundai 355 watt panels (6 - 3 strings of 2 in series)
Honda EU7000is gas fuel generator
Re: Turn off just inverter
If the On/Off switch works as the manual implies, then the solution is very simple! A single pole - single throw switch and some small gauge wire does the trick.SandyP wrote: ↑Mon Nov 30, 2020 1:38 amInterested to know this as well.
For the heaters to still work the pass through function would also need to operate with the inverter in OFF mode.
Edit: The only reference I can see to the Inverter On/Off function and its impact on other functions is in the FX/VFX Mobile manual, page 10 :
On/Off Switch
If a system display is not in use, the inverter can be equipped with a switch to turn it on and off.
This switch is not sold as an inverter accessory; a common toggle switch can be used. The switch
is wired to the INVERTER ON/OFF auxiliary terminals. (See the FX and VFX Mobile Series
Inverter/Charger Installation Manual for more information on wiring the switch.)
This switch turns only the inverter on and off. It does not turn the charger or any other function on
or off. All inverter functions will operate according to their programmed settings. Functions
included with a system display will not be available.
-
- Forum Emperor
- Posts: 2022
- Joined: Sat Aug 28, 2004 6:28 pm
- My RE system: Outback - Garage roof:
- 8 (2x4) Evergreen 180's into one FM80 (2007/2020 - replaced MX60)
- 6 (2×3) ALEO S79-300's into one FM80 (2017)
[***2 grid-tied GVFX3524's classic stacked for 120/240VAC (2007-2020)]
- 2 grid-tied VFXR3524A-01's series stacked, ***replaced GVFX's (2020)
- 12 Surrette/Rolls 2V x 1766Ah (2007)
- Hub10.3, Mate3s, FNDC, RTS, OpticsRE. Tigo Energy ES maximizers on each PV module.
Westinghouse Solar - Barn roof: (2012)
- 30 (2x15) 235W panels with Enphase M215 microinverters, grid-tied
Outback Skybox - Barn roof: (2019)
- 14 Talesun 275W in series (DC array input to SB inverter/charger)
- 3 SimpliPhi 3.8 batteries, 48V, 225Ah total
- AC coupled input (manual switch during grid outage only) from 14 Talesun 275W,
Enphase M215 microinverters, normally direct grid tied
All self-designed and self-installed - Location: Chagrin Falls, Ohio
Re: Turn off just inverter
Or if there's a Mate in the system, control via Optics.
http://www.tigoenergy.com/site.php?95b2dca2-ca6c
https://enlighten.enphaseenergy.com/public/systems/Hctc107221
https://enlighten.enphaseenergy.com/public/systems/Hctc107221
-
- Forum Member
- Posts: 16
- Joined: Thu Nov 21, 2002 11:01 pm
- My RE system: 12 Shell SQ 165 and 175 (2kW)
MX60
2 FX3048T
X240 Autotransformer
Mate (original)
FNDC
Hub-4
Hawker PowerSafe AGM Battery, 1800 Ah
Northern Lights 8 kW Diesel Generator - Location: Big Island, HI
Re: Turn off just inverter
That should work as my generator will charge batteries and power loads when the FX3048T is turned off by the original Mate at status/fx/modes/inv control.Mike Curran wrote: ↑Mon Nov 30, 2020 5:36 pm Or if there's a Mate in the system, control via Optics.
Screenshot_20201130-203507_Samsung Internet.jpg