FXR2024E flashing red

Discussion about OutBack Inverters in Off Grid Applications

Moderators: OutBack, OutBack Moderator Team

Post Reply
pjeffe
Forum Junior Member
Posts: 2
Joined: Sun Jan 23, 2022 2:17 pm
My RE system: FLEXmax 60 charge controllers
FXR2024E inverters

FXR2024E flashing red

Post by pjeffe »

I've got two FXR2024E inverters hooked up to a 24V string (6 x Rolls 4KS21PS), and one of them has a flashing red light. Unfortunately I don't have a MATE in the system. Is there any way I can diagnose what's causing it without one?
raysun
Forum Emperor
Posts: 7795
Joined: Tue Jul 26, 2016 5:57 am
My RE system: Flexpower Two: (2) FXR3048A-01, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
Honda EU7000is gas fuel generator

Re: FXR2024E flashing red

Post by raysun »

The manuals for the inverters will give an indication of possible error conditions. If you don't have them, they can be downloaded from here: https://www.outbackpower.com/resources- ... umentation

Two inverters in the system suggests they are parallel stacked to provide 2X power output. Once configured, the inverters will operate independently of the Mate, but it obviously would be useful to have one for situations like this.
fcwlp
Forum Czar
Posts: 997
Joined: Wed Jan 22, 2020 9:40 am
My RE system: GS8048A, FM80 w/3,600W PV Fixed, FM80 w/2,700W on Zomeworks tracker, Mate3, 24 Trojan 2V L16 1100AH @ C20, Grid-Tied with Kohler 14RESA LPG Generator and MEP-803 Diesel if needed.

I install and maintain grid-tied and off-grid systems in my area and consult on solar system design/operation.
Location: 80 miles NE of Phoenix at 5500'

Re: FXR2024E flashing red

Post by fcwlp »

A flashing red LED is a warning indicator. Likely causes are:
- low/high voltage
- low/high frequency
- input amps > max
- fan failure
- temps over spec

I would turn inverter off/on to reset and then monitor the above.
pjeffe
Forum Junior Member
Posts: 2
Joined: Sun Jan 23, 2022 2:17 pm
My RE system: FLEXmax 60 charge controllers
FXR2024E inverters

Re: FXR2024E flashing red

Post by pjeffe »

Thanks for the response, that's what's odd about it--since both inverters are hooked up in parallel on the DC side they should have the same voltage (which is right in range in any case). And their temperatures should be the same, unless that one is running hotter than the other. And the FXRs are sealed units, so I assume no fan? Unless there's an internal one.
fcwlp
Forum Czar
Posts: 997
Joined: Wed Jan 22, 2020 9:40 am
My RE system: GS8048A, FM80 w/3,600W PV Fixed, FM80 w/2,700W on Zomeworks tracker, Mate3, 24 Trojan 2V L16 1100AH @ C20, Grid-Tied with Kohler 14RESA LPG Generator and MEP-803 Diesel if needed.

I install and maintain grid-tied and off-grid systems in my area and consult on solar system design/operation.
Location: 80 miles NE of Phoenix at 5500'

Re: FXR2024E flashing red

Post by fcwlp »

You are correct on the FXR not having a fan. The low/high voltage and frequency is for the AC output. The "temps over spec" would be the internal components (transformer, FETS and/or capacitors) being too hot and not the ambient.