Moderators: OutBack Moderator Team, OutBack
-
- Forum Expert
- Posts: 70
- Joined: Tue Jan 07, 2020 7:44 am
- My RE system: OFF GRID
2 3.6 KW Outback VFXR series inverters, stacked
One FM100 charge controller
Mate3 readout system
FlexNet DC S.O.C. Meter
16 Rolls S6 L-16 SC 6v batteries (487 AH) (two parallel series of 8)
Backup Generator : 15KW Generac Ecogen Propane
Backup Backup Generator : 3KW Honda gas powered
12 345W Solar World panels (SW 345 XL MONO SV) (2 strings of 5 panels on the roof, plus 1 string of 2 panels on the hillside.)
Bulk float absorb...repeat
Forgive me, my memory isn't what it used to be, and I have upgraded a couple of components since this time last year (all new battery bank, second inverter stacked). Nevertheless, my recollection was my batteries would get close to 100% SOC, the float charge would then run for two hours and then the absorb would run for two hours (assuming I was at or above 60v.)
Lately I have watched as the batteries get up to full in the morning (bulk charge?) then watched as the two hour float charge begins and completes, with voltage comfortably above 54v. My absorb charge timer stays at 2:00, and never starts, despite the fact that I hover for over two hours at over 60v after the float completes.
Any ideas? Suggestions? Need more info? Thanks in advance.
Lately I have watched as the batteries get up to full in the morning (bulk charge?) then watched as the two hour float charge begins and completes, with voltage comfortably above 54v. My absorb charge timer stays at 2:00, and never starts, despite the fact that I hover for over two hours at over 60v after the float completes.
Any ideas? Suggestions? Need more info? Thanks in advance.
-
- Forum Emperor
- Posts: 4424
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: Flexpower Two: (2) FXR3048A, (2) FM80, MATE3s, FlexNetDC
SimpliPhi 48-3.8 (6 @ 48v)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
Honda EU7000is gas fuel generator
Re: Bulk float absorb...repeat
The normal sequence of charging is Bulk (to about 80% SoC), followed by Absorb (to 100% SoC), and finally Float (to maintain the battery at 100% SoC until there is no further charging current.)
If the charge cycle is different than that, there is likely a misconfiguration in the Absorb Voltage, Absorb Time, and/or Float Voltage.
If all the above parameters are set correctly, check the Re-bulk voltage, it may be set too low.
If the charge cycle is different than that, there is likely a misconfiguration in the Absorb Voltage, Absorb Time, and/or Float Voltage.
If all the above parameters are set correctly, check the Re-bulk voltage, it may be set too low.
-
- Forum Expert
- Posts: 70
- Joined: Tue Jan 07, 2020 7:44 am
- My RE system: OFF GRID
2 3.6 KW Outback VFXR series inverters, stacked
One FM100 charge controller
Mate3 readout system
FlexNet DC S.O.C. Meter
16 Rolls S6 L-16 SC 6v batteries (487 AH) (two parallel series of 8)
Backup Generator : 15KW Generac Ecogen Propane
Backup Backup Generator : 3KW Honda gas powered
12 345W Solar World panels (SW 345 XL MONO SV) (2 strings of 5 panels on the roof, plus 1 string of 2 panels on the hillside.)
Re: Bulk float absorb...repeat
Absorb is set at 60 v (2 hours), float is set at 54 volts (2 hours), rebulk is set at 50 volts.
Is that wrong?
I got the absorb and float parameters from the rolls battery manual, reading the column for a 48v setup with regular charging. I don't see a suggested rebulk voltage anywhere in that manual. The 50v setting for rebulk may have been from my original setup (which I didn't do) on install, four years ago.
Is that wrong?
I got the absorb and float parameters from the rolls battery manual, reading the column for a 48v setup with regular charging. I don't see a suggested rebulk voltage anywhere in that manual. The 50v setting for rebulk may have been from my original setup (which I didn't do) on install, four years ago.
-
- Forum Emperor
- Posts: 2237
- Joined: Sat Aug 28, 2004 6:28 pm
- My RE system: Outback - Garage roof:
- 8 (2x4) Evergreen 180's into one FM80 (2007/2020 - replaced MX60)
- 6 (2×3) ALEO S79-300's into one FM80 (2017)
- 2 grid-tied VFXR3524A-01's series stacked, replaced GVFX's (2020)
- 12 Surrette/Rolls 2V x 1766Ah (2007)
- Hub10.3, Mate3s, FNDC, RTS. Tigo ES maximizers on each PV module.
Westinghouse Solar - Barn roof: (2012)
- 30 (2x15) 235W panels with Enphase M215 microinverters, grid-tied
Outback Skybox - Barn roof: (2019)
- 14 Talesun 275W in series (DC array input to SB inverter/charger)
- 3 SimpliPhi 3.8 batteries, 48V, 225Ah total
- AC coupled input from 14 Talesun 275W, Enphase M215 microinverters
All self-designed and self-installed - Location: Chagrin Falls, Ohio
Re: Bulk float absorb...repeat
Don't forget, the VFXRs also have a refloat setpoint that should be set above your rebulk setting. My VFXR settings are shown below, and my rebulk is 24.4 (48.8 equivalent on 48V system), with refloat at 25.0 (50V equivalent).
It's not clear to me exactly what your system is doing. You say,
There's no float time setting on my FM80s, is there one on your FM100? If not, I thought your FM100 would try to maintain float indefinitely, same as my FM80s.It's not clear to me exactly what your system is doing. You say,
How could your system be hovering at over 60V after float, when float is set for 54? If you can post a screenshot like this for your system (showing battery voltage, not SOC) it would help us understand what's going on.I hover for over two hours at over 60v after the float completes.
https://smart.tigoenergy.com/p/pZXn7SZQyO45?date=2021-04-19
https://enlighten.enphaseenergy.com/public/systems/Hctc107221
https://enlighten.enphaseenergy.com/public/systems/Hctc107221
-
- Forum Expert
- Posts: 70
- Joined: Tue Jan 07, 2020 7:44 am
- My RE system: OFF GRID
2 3.6 KW Outback VFXR series inverters, stacked
One FM100 charge controller
Mate3 readout system
FlexNet DC S.O.C. Meter
16 Rolls S6 L-16 SC 6v batteries (487 AH) (two parallel series of 8)
Backup Generator : 15KW Generac Ecogen Propane
Backup Backup Generator : 3KW Honda gas powered
12 345W Solar World panels (SW 345 XL MONO SV) (2 strings of 5 panels on the roof, plus 1 string of 2 panels on the hillside.)
Re: Bulk float absorb...repeat
I'm not hooked up to the outback web program at present for unrelated reasons, so I cannot post any such screenshot. Hmm...
When I push the charger button in my Mate3 it says the following:
Inverter charger status
Battery 54.5v Charger control ON
Absorb 60.0v 02:00 remaining
Float 54.0v 02:00 remaining
However, when I go to the battery charger settings I don't have an option on float time, either. I can only adjust the voltage.
When I push the charger button in my Mate3 it says the following:
Inverter charger status
Battery 54.5v Charger control ON
Absorb 60.0v 02:00 remaining
Float 54.0v 02:00 remaining
However, when I go to the battery charger settings I don't have an option on float time, either. I can only adjust the voltage.
-
- Forum Emperor
- Posts: 2237
- Joined: Sat Aug 28, 2004 6:28 pm
- My RE system: Outback - Garage roof:
- 8 (2x4) Evergreen 180's into one FM80 (2007/2020 - replaced MX60)
- 6 (2×3) ALEO S79-300's into one FM80 (2017)
- 2 grid-tied VFXR3524A-01's series stacked, replaced GVFX's (2020)
- 12 Surrette/Rolls 2V x 1766Ah (2007)
- Hub10.3, Mate3s, FNDC, RTS. Tigo ES maximizers on each PV module.
Westinghouse Solar - Barn roof: (2012)
- 30 (2x15) 235W panels with Enphase M215 microinverters, grid-tied
Outback Skybox - Barn roof: (2019)
- 14 Talesun 275W in series (DC array input to SB inverter/charger)
- 3 SimpliPhi 3.8 batteries, 48V, 225Ah total
- AC coupled input from 14 Talesun 275W, Enphase M215 microinverters
All self-designed and self-installed - Location: Chagrin Falls, Ohio
Re: Bulk float absorb...repeat
As a reference point, right now (end of day) my float & absorb time remaining both say 0:00. What time did you get these 02:00 remaining readings?
https://smart.tigoenergy.com/p/pZXn7SZQyO45?date=2021-04-19
https://enlighten.enphaseenergy.com/public/systems/Hctc107221
https://enlighten.enphaseenergy.com/public/systems/Hctc107221
-
- Forum Emperor
- Posts: 4424
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: Flexpower Two: (2) FXR3048A, (2) FM80, MATE3s, FlexNetDC
SimpliPhi 48-3.8 (6 @ 48v)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
Honda EU7000is gas fuel generator
Re: Bulk float absorb...repeat
Note this is the Inverter Charger status.Isfry wrote: ↑Wed Apr 07, 2021 4:38 pm I'm not hooked up to the outback web program at present for unrelated reasons, so I cannot post any such screenshot. Hmm...
When I push the charger button in my Mate3 it says the following:
Inverter charger status
Battery 54.5v Charger control ON
Absorb 60.0v 02:00 remaining
Float 54.0v 02:00 remaining
However, when I go to the battery charger settings I don't have an option on float time, either. I can only adjust the voltage.
The inverter charger specifies Float Time. The FlexMax charge controllers maintain float as long as the sun permits, and do not specify Float Time.
The two charging systems work autonomously, but should be adjusted to work in sync.
-
- Forum Expert
- Posts: 70
- Joined: Tue Jan 07, 2020 7:44 am
- My RE system: OFF GRID
2 3.6 KW Outback VFXR series inverters, stacked
One FM100 charge controller
Mate3 readout system
FlexNet DC S.O.C. Meter
16 Rolls S6 L-16 SC 6v batteries (487 AH) (two parallel series of 8)
Backup Generator : 15KW Generac Ecogen Propane
Backup Backup Generator : 3KW Honda gas powered
12 345W Solar World panels (SW 345 XL MONO SV) (2 strings of 5 panels on the roof, plus 1 string of 2 panels on the hillside.)
Re: Bulk float absorb...repeat
When I wake up in the morning both the float and absorb timers say 2:00. The float timer starts ticking down once I get close to 90% SOC or so. The absorb timer (I think) used to start counting down after the float timer finished, which may have been improper to begin with. Nonetheless, the absorb timer never budges now, so I end up with a float timer reading zero and an absorb timer still at 2:00 at the end of the day.
-
- Forum Expert
- Posts: 70
- Joined: Tue Jan 07, 2020 7:44 am
- My RE system: OFF GRID
2 3.6 KW Outback VFXR series inverters, stacked
One FM100 charge controller
Mate3 readout system
FlexNet DC S.O.C. Meter
16 Rolls S6 L-16 SC 6v batteries (487 AH) (two parallel series of 8)
Backup Generator : 15KW Generac Ecogen Propane
Backup Backup Generator : 3KW Honda gas powered
12 345W Solar World panels (SW 345 XL MONO SV) (2 strings of 5 panels on the roof, plus 1 string of 2 panels on the hillside.)
Re: Bulk float absorb...repeat
I have a different battery charger sub menu under the inverter heading that lists the following:
Battery Charger
Absorb Voltage 60.0 VDC Time 2:00
Float Voltage 54.0 VDC Time 2:00
Re-Float Voltage 50.0 VDC
Re-Bulk Voltage 50.0 VDC
No time is listed after either of the latter two, but I can adjust either Re-Float or Re-Bulk Voltage here, if I knew what to reset them to.
Battery Charger
Absorb Voltage 60.0 VDC Time 2:00
Float Voltage 54.0 VDC Time 2:00
Re-Float Voltage 50.0 VDC
Re-Bulk Voltage 50.0 VDC
No time is listed after either of the latter two, but I can adjust either Re-Float or Re-Bulk Voltage here, if I knew what to reset them to.
-
- Forum Expert
- Posts: 73
- Joined: Sat Mar 07, 2015 3:25 pm
Re: Bulk float absorb...repeat
I just checked mine...float voltage 53.6v, 24/7 duration. Once bulk and absorb are done it holds float 24/7 unless charger is turned off. Time is adjustable.
-
- Forum Emperor
- Posts: 4424
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: Flexpower Two: (2) FXR3048A, (2) FM80, MATE3s, FlexNetDC
SimpliPhi 48-3.8 (6 @ 48v)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
Honda EU7000is gas fuel generator
Re: Bulk float absorb...repeat
The sequence described for Absorb and Float is exactly the opposite of normal operation. TBH, I have a hard time envisioning how its even possible.Isfry wrote: ↑Wed Apr 07, 2021 9:27 pm When I wake up in the morning both the float and absorb timers say 2:00. The float timer starts ticking down once I get close to 90% SOC or so. The absorb timer (I think) used to start counting down after the float timer finished, which may have been improper to begin with. Nonetheless, the absorb timer never budges now, so I end up with a float timer reading zero and an absorb timer still at 2:00 at the end of the day.
There are three charging sources in the system: the 2 inverter chargers and the FM100 charge controller.
All three need to be calibrated to the battery voltage.
All three need charging profiles that are compatible with the battery and with the functioning of the other chargers.
Something is very strange here.
Perhaps start by listing the battery charging parameters for all three chargers.
-
- Forum Expert
- Posts: 70
- Joined: Tue Jan 07, 2020 7:44 am
- My RE system: OFF GRID
2 3.6 KW Outback VFXR series inverters, stacked
One FM100 charge controller
Mate3 readout system
FlexNet DC S.O.C. Meter
16 Rolls S6 L-16 SC 6v batteries (487 AH) (two parallel series of 8)
Backup Generator : 15KW Generac Ecogen Propane
Backup Backup Generator : 3KW Honda gas powered
12 345W Solar World panels (SW 345 XL MONO SV) (2 strings of 5 panels on the roof, plus 1 string of 2 panels on the hillside.)
Re: Bulk float absorb...repeat
I had a guy come and stack a second inverter last year, and prior to that the charging all seem to be functioning properly. I'm going to call him and have him come up and see if maybe there's something above my pay grade (which isn't very high) that needs to be tinkered with in the control room itself, outside of the Mate. I'll post whatever solution is achieved.
-
- Forum Expert
- Posts: 70
- Joined: Tue Jan 07, 2020 7:44 am
- My RE system: OFF GRID
2 3.6 KW Outback VFXR series inverters, stacked
One FM100 charge controller
Mate3 readout system
FlexNet DC S.O.C. Meter
16 Rolls S6 L-16 SC 6v batteries (487 AH) (two parallel series of 8)
Backup Generator : 15KW Generac Ecogen Propane
Backup Backup Generator : 3KW Honda gas powered
12 345W Solar World panels (SW 345 XL MONO SV) (2 strings of 5 panels on the roof, plus 1 string of 2 panels on the hillside.)
Re: Bulk float absorb...repeat
UPDATE (for those who have nothing better to do than worry about my problems...)
I had the inverter wiring checked and was told all is correct. The original battery specs I punched in were from the Rolls manual for my S6 L16's. As an attempt to fix the absorb problem, I changed them to the default numbers from the Outback manual. Still no absorb cycle happening. The guy who came up (who seems to know his stuff, better than me, at least) said the Rolls numbers were too high and the default Outback numbers were too low. He tweaked a bunch of them to be somewhere in the middle. Moreover, he identified one error I had made, which was I was adjusting the battery numbers for one inverter (master) in port one without switching to the other inverter (phase master) in port 7. (I know, I know, stupid mistake, but I am new to inverter stacking so give me a break.) I hoped that after he left the next day would reveal an absorb cycle in advance of my float charge, but no such luck. I am at a loss, and am still not hooked back up to Opticsre, so I can't provide any more data than I have, but am more than happy to answer any questions that may help round out the picture. Anyone who thinks they have a simple change that might start my absorb cycle again, I am willing to try. I just bought 16 new batteries last year for the first time and really want to maintain them properly so as to avoid dropping that chunk of change again any time soon. Thanks in advance.
I had the inverter wiring checked and was told all is correct. The original battery specs I punched in were from the Rolls manual for my S6 L16's. As an attempt to fix the absorb problem, I changed them to the default numbers from the Outback manual. Still no absorb cycle happening. The guy who came up (who seems to know his stuff, better than me, at least) said the Rolls numbers were too high and the default Outback numbers were too low. He tweaked a bunch of them to be somewhere in the middle. Moreover, he identified one error I had made, which was I was adjusting the battery numbers for one inverter (master) in port one without switching to the other inverter (phase master) in port 7. (I know, I know, stupid mistake, but I am new to inverter stacking so give me a break.) I hoped that after he left the next day would reveal an absorb cycle in advance of my float charge, but no such luck. I am at a loss, and am still not hooked back up to Opticsre, so I can't provide any more data than I have, but am more than happy to answer any questions that may help round out the picture. Anyone who thinks they have a simple change that might start my absorb cycle again, I am willing to try. I just bought 16 new batteries last year for the first time and really want to maintain them properly so as to avoid dropping that chunk of change again any time soon. Thanks in advance.
-
- Forum Emperor
- Posts: 2237
- Joined: Sat Aug 28, 2004 6:28 pm
- My RE system: Outback - Garage roof:
- 8 (2x4) Evergreen 180's into one FM80 (2007/2020 - replaced MX60)
- 6 (2×3) ALEO S79-300's into one FM80 (2017)
- 2 grid-tied VFXR3524A-01's series stacked, replaced GVFX's (2020)
- 12 Surrette/Rolls 2V x 1766Ah (2007)
- Hub10.3, Mate3s, FNDC, RTS. Tigo ES maximizers on each PV module.
Westinghouse Solar - Barn roof: (2012)
- 30 (2x15) 235W panels with Enphase M215 microinverters, grid-tied
Outback Skybox - Barn roof: (2019)
- 14 Talesun 275W in series (DC array input to SB inverter/charger)
- 3 SimpliPhi 3.8 batteries, 48V, 225Ah total
- AC coupled input from 14 Talesun 275W, Enphase M215 microinverters
All self-designed and self-installed - Location: Chagrin Falls, Ohio
Re: Bulk float absorb...repeat
Is there a reason why no Optics? Because a screenshot of your system dashboard from Optics would help (me, at least) understand what you're describing. No pressure, more info = better solutions.
https://smart.tigoenergy.com/p/pZXn7SZQyO45?date=2021-04-19
https://enlighten.enphaseenergy.com/public/systems/Hctc107221
https://enlighten.enphaseenergy.com/public/systems/Hctc107221
-
- Forum Expert
- Posts: 70
- Joined: Tue Jan 07, 2020 7:44 am
- My RE system: OFF GRID
2 3.6 KW Outback VFXR series inverters, stacked
One FM100 charge controller
Mate3 readout system
FlexNet DC S.O.C. Meter
16 Rolls S6 L-16 SC 6v batteries (487 AH) (two parallel series of 8)
Backup Generator : 15KW Generac Ecogen Propane
Backup Backup Generator : 3KW Honda gas powered
12 345W Solar World panels (SW 345 XL MONO SV) (2 strings of 5 panels on the roof, plus 1 string of 2 panels on the hillside.)
Re: Bulk float absorb...repeat
The optics problem is because the Cat5 went outside along the foundation around the house and then back in for the router connection. I'm building a bedroom and dining room addition, which expanded the foundation beyond the length of the Cat5. I could temporarily run a short Cat5 indoors and just get a snapshot, if that would help, but I can't leave it plugged in as I have two small children and two big dogs and a small space.
Also, if it's relevant, when I push the charger button on my Mate3 and then push the button under charger status it says charger ON and then Bulk and Float Charge Enabled below that. I don't recall if it ever said anything about absorb charge there. Is it possible it's turned off?
Also, if it's relevant, when I push the charger button on my Mate3 and then push the button under charger status it says charger ON and then Bulk and Float Charge Enabled below that. I don't recall if it ever said anything about absorb charge there. Is it possible it's turned off?
-
- Forum Expert
- Posts: 70
- Joined: Tue Jan 07, 2020 7:44 am
- My RE system: OFF GRID
2 3.6 KW Outback VFXR series inverters, stacked
One FM100 charge controller
Mate3 readout system
FlexNet DC S.O.C. Meter
16 Rolls S6 L-16 SC 6v batteries (487 AH) (two parallel series of 8)
Backup Generator : 15KW Generac Ecogen Propane
Backup Backup Generator : 3KW Honda gas powered
12 345W Solar World panels (SW 345 XL MONO SV) (2 strings of 5 panels on the roof, plus 1 string of 2 panels on the hillside.)
Re: Bulk float absorb...repeat
So I tried to hook a thirty foot Cat5 across my house into the modem and the Opticsre site says my system is offline when I log in. I tried a second cable to see if the cable was bad but same result. OpticsRE is "enabled" in the systems menu on my Mate, and I turned on serial data stream, which was disabled, thinking maybe that was the data I needed to be streaming. As usual, my hamhanded attempt to fix one problem has unearthed (or caused) another...
ugh
ugh
-
- Forum Emperor
- Posts: 4424
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: Flexpower Two: (2) FXR3048A, (2) FM80, MATE3s, FlexNetDC
SimpliPhi 48-3.8 (6 @ 48v)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
Honda EU7000is gas fuel generator
Re: Bulk float absorb...repeat
The only way (normally) to disable Absorb is to set Absorb Time to 0H. That actually disables Bulk and Absorb at the same time, skipping directly to Float.don't recall if it ever said anything about absorb charge there. Is it possible it's turned off?
-
- Forum Emperor
- Posts: 4424
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: Flexpower Two: (2) FXR3048A, (2) FM80, MATE3s, FlexNetDC
SimpliPhi 48-3.8 (6 @ 48v)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
Honda EU7000is gas fuel generator
Re: Bulk float absorb...repeat
Is this the same Mate as was originally registered with OpticsRE, or a replacement unit?So I tried to hook a thirty foot Cat5 across my house into the modem and the Opticsre site says my system is offline when I log in.
When the PORT key is pressed while on the main status screen, does the Mate have a valid IP address for your LAN?
-
- Forum Expert
- Posts: 70
- Joined: Tue Jan 07, 2020 7:44 am
- My RE system: OFF GRID
2 3.6 KW Outback VFXR series inverters, stacked
One FM100 charge controller
Mate3 readout system
FlexNet DC S.O.C. Meter
16 Rolls S6 L-16 SC 6v batteries (487 AH) (two parallel series of 8)
Backup Generator : 15KW Generac Ecogen Propane
Backup Backup Generator : 3KW Honda gas powered
12 345W Solar World panels (SW 345 XL MONO SV) (2 strings of 5 panels on the roof, plus 1 string of 2 panels on the hillside.)
Re: Bulk float absorb...repeat
absorb was set at 2 hours ( I think that was the default). Based on my setup the guy who came to tinker with it lowered it to 1.6 hours for some reason. It still doesn't start.
-
- Forum Expert
- Posts: 70
- Joined: Tue Jan 07, 2020 7:44 am
- My RE system: OFF GRID
2 3.6 KW Outback VFXR series inverters, stacked
One FM100 charge controller
Mate3 readout system
FlexNet DC S.O.C. Meter
16 Rolls S6 L-16 SC 6v batteries (487 AH) (two parallel series of 8)
Backup Generator : 15KW Generac Ecogen Propane
Backup Backup Generator : 3KW Honda gas powered
12 345W Solar World panels (SW 345 XL MONO SV) (2 strings of 5 panels on the roof, plus 1 string of 2 panels on the hillside.)
Re: Bulk float absorb...repeat
Same Mate. Never changed it. Which Main status screen? I tried pushing port at the main screen, nothing. I tried pushing it at the main Mate menu, nothing. Not sure which screen you mean. Sorry. I know it's probably like trying to teach a child calculus...raysun wrote: ↑Tue Apr 20, 2021 10:56 amIs this the same Mate as was originally registered with OpticsRE, or a replacement unit?So I tried to hook a thirty foot Cat5 across my house into the modem and the Opticsre site says my system is offline when I log in.
When the PORT key is pressed while on the main status screen, does the Mate have a valid IP address for your LAN?
-
- Forum Expert
- Posts: 70
- Joined: Tue Jan 07, 2020 7:44 am
- My RE system: OFF GRID
2 3.6 KW Outback VFXR series inverters, stacked
One FM100 charge controller
Mate3 readout system
FlexNet DC S.O.C. Meter
16 Rolls S6 L-16 SC 6v batteries (487 AH) (two parallel series of 8)
Backup Generator : 15KW Generac Ecogen Propane
Backup Backup Generator : 3KW Honda gas powered
12 345W Solar World panels (SW 345 XL MONO SV) (2 strings of 5 panels on the roof, plus 1 string of 2 panels on the hillside.)
Re: Bulk float absorb...repeat
In case it's relevant, both of my VFXR3648A inverters are using firmware update 001.006.063. Should I update that? I see that 001.006.067 is newer.raysun wrote: ↑Tue Apr 20, 2021 10:56 amIs this the same Mate as was originally registered with OpticsRE, or a replacement unit?So I tried to hook a thirty foot Cat5 across my house into the modem and the Opticsre site says my system is offline when I log in.
When the PORT key is pressed while on the main status screen, does the Mate have a valid IP address for your LAN?
EDIT: Nevermind. Puerto Rico only.
My Mate appears to have the newest firmware update, as well.
-
- Forum Emperor
- Posts: 2237
- Joined: Sat Aug 28, 2004 6:28 pm
- My RE system: Outback - Garage roof:
- 8 (2x4) Evergreen 180's into one FM80 (2007/2020 - replaced MX60)
- 6 (2×3) ALEO S79-300's into one FM80 (2017)
- 2 grid-tied VFXR3524A-01's series stacked, replaced GVFX's (2020)
- 12 Surrette/Rolls 2V x 1766Ah (2007)
- Hub10.3, Mate3s, FNDC, RTS. Tigo ES maximizers on each PV module.
Westinghouse Solar - Barn roof: (2012)
- 30 (2x15) 235W panels with Enphase M215 microinverters, grid-tied
Outback Skybox - Barn roof: (2019)
- 14 Talesun 275W in series (DC array input to SB inverter/charger)
- 3 SimpliPhi 3.8 batteries, 48V, 225Ah total
- AC coupled input from 14 Talesun 275W, Enphase M215 microinverters
All self-designed and self-installed - Location: Chagrin Falls, Ohio
Re: Bulk float absorb...repeat
Don't worry about it, I just thought if it was something simple we could get it going. Sorry if I've sidetracked your main issue.Isfry wrote: ↑Tue Apr 20, 2021 10:51 am So I tried to hook a thirty foot Cat5 across my house into the modem and the Opticsre site says my system is offline when I log in. I tried a second cable to see if the cable was bad but same result. OpticsRE is "enabled" in the systems menu on my Mate, and I turned on serial data stream, which was disabled, thinking maybe that was the data I needed to be streaming. As usual, my hamhanded attempt to fix one problem has unearthed (or caused) another...
ugh
https://smart.tigoenergy.com/p/pZXn7SZQyO45?date=2021-04-19
https://enlighten.enphaseenergy.com/public/systems/Hctc107221
https://enlighten.enphaseenergy.com/public/systems/Hctc107221
-
- Forum Expert
- Posts: 70
- Joined: Tue Jan 07, 2020 7:44 am
- My RE system: OFF GRID
2 3.6 KW Outback VFXR series inverters, stacked
One FM100 charge controller
Mate3 readout system
FlexNet DC S.O.C. Meter
16 Rolls S6 L-16 SC 6v batteries (487 AH) (two parallel series of 8)
Backup Generator : 15KW Generac Ecogen Propane
Backup Backup Generator : 3KW Honda gas powered
12 345W Solar World panels (SW 345 XL MONO SV) (2 strings of 5 panels on the roof, plus 1 string of 2 panels on the hillside.)
Re: Bulk float absorb...repeat
No. Not at all. I'm trying to get you more info so you might be able to help with the main issue. The optics thing is bugging me, now, too, but I still am mainly concerned with the absorb charge anomaly. I wish I could give you (and others) more data. No sorries, tho. Thanks for the help.Mike Curran wrote: ↑Tue Apr 20, 2021 11:16 amDon't worry about it, I just thought if it was something simple we could get it going. Sorry if I've sidetracked your main issue.Isfry wrote: ↑Tue Apr 20, 2021 10:51 am So I tried to hook a thirty foot Cat5 across my house into the modem and the Opticsre site says my system is offline when I log in. I tried a second cable to see if the cable was bad but same result. OpticsRE is "enabled" in the systems menu on my Mate, and I turned on serial data stream, which was disabled, thinking maybe that was the data I needed to be streaming. As usual, my hamhanded attempt to fix one problem has unearthed (or caused) another...
ugh
If you have any suggestions on what setting might have gotten changed that disabled the optics (despite the fact it's "enabled") I'm all ears.
-
- Forum Expert
- Posts: 70
- Joined: Tue Jan 07, 2020 7:44 am
- My RE system: OFF GRID
2 3.6 KW Outback VFXR series inverters, stacked
One FM100 charge controller
Mate3 readout system
FlexNet DC S.O.C. Meter
16 Rolls S6 L-16 SC 6v batteries (487 AH) (two parallel series of 8)
Backup Generator : 15KW Generac Ecogen Propane
Backup Backup Generator : 3KW Honda gas powered
12 345W Solar World panels (SW 345 XL MONO SV) (2 strings of 5 panels on the roof, plus 1 string of 2 panels on the hillside.)
Re: Bulk float absorb...repeat
UPDATE: I spoke with a guy at Rolls for almost an hour, who advised me to put the absorb back at 60v but to set the time at 5.2 hours, based on the size of my array, which he also recommended (strongly) I increase (double.) RaySun had told me a while back to do the same. Anyway, let's see if the absorb even starts. Today is cloudy so I'll have to wait til tomorrow to see if this helps. I also think I will need to use my generator to help boost the charge a couple hours before the pv really kicks in. We'll see...
-
- Forum Emperor
- Posts: 4424
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: Flexpower Two: (2) FXR3048A, (2) FM80, MATE3s, FlexNetDC
SimpliPhi 48-3.8 (6 @ 48v)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
Honda EU7000is gas fuel generator
Re: Bulk float absorb...repeat
Since you have (two) inverter chargers and a pv charge controller, use all in tandem to get through a full charge cycle.Isfry wrote: ↑Tue Apr 20, 2021 12:46 pm UPDATE: I spoke with a guy at Rolls for almost an hour, who advised me to put the absorb back at 60v but to set the time at 5.2 hours, based on the size of my array, which he also recommended (strongly) I increase (double.) RaySun had told me a while back to do the same. Anyway, let's see if the absorb even starts. Today is cloudy so I'll have to wait til tomorrow to see if this helps. I also think I will need to use my generator to help boost the charge a couple hours before the pv really kicks in. We'll see...
Set the Absorb Voltage on the Flexmax to (the recommended) 60V, and Absorb Voltage on the inverter chargers to 56.6V. Set Absorb Time the same on all chargers.