What is this LED? VFX3024E

Discussion about OutBack Inverters in Backup Applications

Moderators: OutBack, OutBack Moderator Team

Post Reply
User avatar
occamsrazor
Forum Whiz
Posts: 28
Joined: Sat Mar 19, 2016 3:42 am
My RE system: Outback VFX3024E, MATE, RTS
2 x Ritar 200ah AGM batteries
APC UPSes, Automatic Transfer switch, Metered PDUs
Sollatek AVS surge protectors
Sollatek Automatic Voltage Regulator
Location: Kenya

What is this LED? VFX3024E

Post by occamsrazor »

Hi,

Been having some recent issues with bad mains power (low input voltage) and a VFX3024E used as backup inverter. This orange light is on, I don't remember it being on before. I do not have anything connected to the AUX terminals:

LED.jpg

I checked the manual and it is not indicated what this light is for. Unfortunately I don't have a MATE with me in this country.

Thanks.
raysun
Forum Emperor
Posts: 7777
Joined: Tue Jul 26, 2016 5:57 am
My RE system: Flexpower Two: (2) FXR3048A-01, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
Honda EU7000is gas fuel generator

Re: What is this LED? VFX3024E

Post by raysun »

I don't find any reference to the LED either. If its associated with the AUX terminals, perhaps it signals the ON state. If you have a multimeter, measure for the presence of 12VDC between AUX+ and AUX-
provo
Forum Emperor
Posts: 1103
Joined: Thu Jul 27, 2006 4:34 pm
My RE system: 16 Evergreen EC-120 (4 strings, total 1920W)
2 SimpliPhi 3.8-m-24V (150Ah each)
One FM80
One VFXR3524A
Hub 10
Mate3s
FNDC
Honda EU3000is generator
Location: Sierra foothills

Re: What is this LED? VFX3024E

Post by provo »

Raysun is right -- p.11 of the VFXR manual, (VFX probably the same...)

Aux LED.jpg
JRHill
Forum Emperor
Posts: 2391
Joined: Thu Feb 17, 2011 11:12 am
My RE system: 48v OB inverter and charge controller, hub and mate3s.
Location: PNW
Contact:

Re: What is this LED? VFX3024E

Post by JRHill »

raysun wrote: Tue Jan 11, 2022 9:19 am I don't find any reference to the LED either. If its associated with the AUX terminals, perhaps it signals the ON state. If you have a multimeter, measure for the presence of 12VDC between AUX+ and AUX-
I believe the above is true. As I recall the LED was useful when troubleshooting AGS and it was the relay. I can't recall if the FM has the LED.
User avatar
occamsrazor
Forum Whiz
Posts: 28
Joined: Sat Mar 19, 2016 3:42 am
My RE system: Outback VFX3024E, MATE, RTS
2 x Ritar 200ah AGM batteries
APC UPSes, Automatic Transfer switch, Metered PDUs
Sollatek AVS surge protectors
Sollatek Automatic Voltage Regulator
Location: Kenya

Re: What is this LED? VFX3024E

Post by occamsrazor »

Thanks, that would make sense. I must have an older version of the manual. But I wonder why it would be illuminated when there is nothing at all connected to the Aux+ or Aux- terminals….
JRHill
Forum Emperor
Posts: 2391
Joined: Thu Feb 17, 2011 11:12 am
My RE system: 48v OB inverter and charge controller, hub and mate3s.
Location: PNW
Contact:

Re: What is this LED? VFX3024E

Post by JRHill »

occamsrazor wrote: Tue Jan 11, 2022 11:29 am Thanks, that would make sense. I must have an older version of the manual. But I wonder why it would be illuminated when there is nothing at all connected to the Aux+ or Aux- terminals….
It has nothing to do with anything connected. Its just that the Aux is triggered. You've got something in the VFX enabled related to Aux programming that is turning on the Outputs when conditions are met. No big deal. It shouldn't affect anything.
raysun
Forum Emperor
Posts: 7777
Joined: Tue Jul 26, 2016 5:57 am
My RE system: Flexpower Two: (2) FXR3048A-01, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
Honda EU7000is gas fuel generator

Re: What is this LED? VFX3024E

Post by raysun »

occamsrazor wrote: Tue Jan 11, 2022 11:29 am Thanks, that would make sense. I must have an older version of the manual. But I wonder why it would be illuminated when there is nothing at all connected to the Aux+ or Aux- terminals….
Nothing need be connected to the terminals, rather something in the inverter configuration is enabling the AUX function.

If AUX MODE = ON, the terminals are energized.

If AUX MODE = AUTO, the terminals will be energized in accordance with the selected Aux function's parameter values.

Without a Mate, it won't be possible to interrogate the state of the Aux.