Grid Zero question
Moderators: OutBack, OutBack Moderator Team
-
- Forum Whiz
- Posts: 48
- Joined: Sun Mar 22, 2015 7:18 am
- My RE system: gvfx 3648, fm80, 12 trojan J185-re, hub 10-4, mate3, fndc monitor, 12 CSX-310P canadian solar panels
20 450 panels, Fpr 8048a (8kw radian, 2 fm80 cc, fndc, 15kw lifepo4 batteries
Grid Zero question
I have 6-7 year old GVFX 3648 and I've never had any problems with it. I usually just sell excess to grid but I was wondering if the GVFX supports grid zero. It is not an option on this mate3 but I haven't updated any of the firmware in 6 years so I don't know if that's the problem. I hate to fix something that's been working so I haven't messed with any of the updates.
It has occurred to me the GVFX doesn't support grid zero. I asked Outback a couple of weeks ago but they haven't responded yet. So I thought I'd ask the forum.
It has occurred to me the GVFX doesn't support grid zero. I asked Outback a couple of weeks ago but they haven't responded yet. So I thought I'd ask the forum.
-
- Forum Emperor
- Posts: 7779
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: Flexpower Two: (2) FXR3048A-01, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
Honda EU7000is gas fuel generator
Re: Grid Zero question
The GVFX is OB's original grid interactive inverter. It has limited modes, and Grid Zero is a much later introduction.
If its been in operation for 6-7 years, that's great, and par for the course of OB kit. The model was discontinued a lot of years ago. Thats a vintage inverter. The firmware cannot be field-upgraded.
The basic guts of the inverter architecture are essentially the same. Hats off to the original designers. The brains evolve however, also as designed. The latest VFXR-A models have a lot of smarts, like 7 Inverter Modes and Lithium battery support.
If its been in operation for 6-7 years, that's great, and par for the course of OB kit. The model was discontinued a lot of years ago. Thats a vintage inverter. The firmware cannot be field-upgraded.
The basic guts of the inverter architecture are essentially the same. Hats off to the original designers. The brains evolve however, also as designed. The latest VFXR-A models have a lot of smarts, like 7 Inverter Modes and Lithium battery support.
-
- Forum Whiz
- Posts: 48
- Joined: Sun Mar 22, 2015 7:18 am
- My RE system: gvfx 3648, fm80, 12 trojan J185-re, hub 10-4, mate3, fndc monitor, 12 CSX-310P canadian solar panels
20 450 panels, Fpr 8048a (8kw radian, 2 fm80 cc, fndc, 15kw lifepo4 batteries
Re: Grid Zero question
That’s sort of what I guessed. Just wanted to make sure. I’m in the process of upgrading to FPR 8048 radian and I was going to try grid zero with it.
Will the radian and gvfx play nice together with one grid tie and the other grid zero or will they fight? I’m probably going to end up with two separate essential load panels.
Thanks for your reply
Will the radian and gvfx play nice together with one grid tie and the other grid zero or will they fight? I’m probably going to end up with two separate essential load panels.
Thanks for your reply
-
- Forum Emperor
- Posts: 7779
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: Flexpower Two: (2) FXR3048A-01, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
Honda EU7000is gas fuel generator
Re: Grid Zero question
I'd imagine the system will throw a lot of errors if both are active on the same Hub.
Is that much output really needed? Will the battery / charging systems handle that much load?
Is that much output really needed? Will the battery / charging systems handle that much load?
-
- Forum Whiz
- Posts: 48
- Joined: Sun Mar 22, 2015 7:18 am
- My RE system: gvfx 3648, fm80, 12 trojan J185-re, hub 10-4, mate3, fndc monitor, 12 CSX-310P canadian solar panels
20 450 panels, Fpr 8048a (8kw radian, 2 fm80 cc, fndc, 15kw lifepo4 batteries
Re: Grid Zero question
Well….I’ve use the gvfx all this time for backup for all my 110 loads. My plan is to use the radian for as much as is reasonably possible for 220 loads. It will operate totally separately from gvfx. Only thing they will share is grid input. I will have separate load centers, panels, charge controller, inverter, mate, batteries. . . . . .
As I understand it, fpr8048A-300 comes with all that factory wired.
I was hoping to be able to continue using the gvfx somehow.
Here in Texas, little has been built for energy efficiency - but that’s a whole different discussion.
As I understand it, fpr8048A-300 comes with all that factory wired.
I was hoping to be able to continue using the gvfx somehow.
Here in Texas, little has been built for energy efficiency - but that’s a whole different discussion.
-
- Forum Emperor
- Posts: 7779
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: Flexpower Two: (2) FXR3048A-01, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
Honda EU7000is gas fuel generator
Re: Grid Zero question
Separate systems is perfectly fine, of course.
Also, I'm sure you know the Radian (two 4kW modules in the chassis = 8kW) is standard North American 240V split phase, so they output L1<-120V->NEUTRAL<-120V->L2.
240V is L1<->L2. 120V on each L1<->NEUTRAL and NEUTRAL<->L2. In case both 240V and 120V are required from the Radian.
Also, I'm sure you know the Radian (two 4kW modules in the chassis = 8kW) is standard North American 240V split phase, so they output L1<-120V->NEUTRAL<-120V->L2.
240V is L1<->L2. 120V on each L1<->NEUTRAL and NEUTRAL<->L2. In case both 240V and 120V are required from the Radian.
-
- Forum Whiz
- Posts: 48
- Joined: Sun Mar 22, 2015 7:18 am
- My RE system: gvfx 3648, fm80, 12 trojan J185-re, hub 10-4, mate3, fndc monitor, 12 CSX-310P canadian solar panels
20 450 panels, Fpr 8048a (8kw radian, 2 fm80 cc, fndc, 15kw lifepo4 batteries
Re: Grid Zero question
Ah yes I may have had typo there.
I assumed as separate systems they would work but you what assume means. Still I’m going to be interested in how/if the gvfx sees radian as grid when I lose the real grid(happens more often than you might think).
I assumed as separate systems they would work but you what assume means. Still I’m going to be interested in how/if the gvfx sees radian as grid when I lose the real grid(happens more often than you might think).
-
- Forum Emperor
- Posts: 7779
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: Flexpower Two: (2) FXR3048A-01, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
Honda EU7000is gas fuel generator
Re: Grid Zero question
Way above my pay grade. (I'm strictly off-grid.)Still I’m going to be interested in how/if the gvfx sees radian as grid when I lose the real grid(
- Mike Curran
- Forum Emperor
- Posts: 2771
- Joined: Sat Aug 28, 2004 6:28 pm
- My RE system: Outback - Garage roof:
- 8 (2x4) Evergreen 180's into one FM80 (2007/2020 - replaced MX60)
- 6 (2×3) ALEO S79-300's into one FM80 (2017)
- 2 grid-tied VFXR3524A-01's series stacked, replaced GVFX's (2020)
- 12 Surrette/Rolls 2V x 1766Ah (2007)
- Hub10.3, Mate3s, FNDC, RTS. Tigo ES maximizers on each PV module.
Westinghouse Solar - Barn roof: (2012)
- 30 (2x15) 235W panels with Enphase M215 microinverters, grid-tied
Outback Skybox - Barn roof: (2019)
- 14 Talesun 275W in series (DC array input to SB inverter/charger)
- 3 SimpliPhi 3.8 batteries, 48V, 225Ah total
- AC coupled input from 14 Talesun 275W, Enphase M215 microinverters
Battery systems operate in grid-tied, net metering w/backup mode
All self-designed and self-installed - Location: Chagrin Falls, Ohio
Re: Grid Zero question
It sounds like you're connecting the GVFX grid input terminals to the Radian's output, so that during a grid outage your GVFX will think it's still connected to "grid". If that's what you're doing, it's called AC coupling. Your Radian is perfectly capable of handling this connection. Note that your GVFX will be charging your Radian's battery in this setup, as well as its own, but the GVFX battery will have priority as long as its own charge parameters have not been met. (Normally in a grid-tied system with an FNDC you cannot "sell" to [your Radian's] grid until charge parameters are met.) If your Radian's battery gets fully charged in this setup, the Radian will try to get your GVFX to disconnect by raising its output frequency, which the GVFX will see as a bad AC input and disconnect itself.Still I’m going to be interested in how/if the gvfx sees radian as grid when I lose the real grid
Unusual setup, overly complex IMO. Good luck.
Edit: If it were me and I needed two battery-based systems I would keep them totally separate.
https://ei.tigoenergy.com/p/pZXn7SZQyO45
https://enlighten.enphaseenergy.com/public/systems/Hctc107221
https://enlighten.enphaseenergy.com/public/systems/Hctc107221
-
- Forum Whiz
- Posts: 48
- Joined: Sun Mar 22, 2015 7:18 am
- My RE system: gvfx 3648, fm80, 12 trojan J185-re, hub 10-4, mate3, fndc monitor, 12 CSX-310P canadian solar panels
20 450 panels, Fpr 8048a (8kw radian, 2 fm80 cc, fndc, 15kw lifepo4 batteries
Re: Grid Zero question
I haven’t set anything up yet so I could do it like that. I just need to wrap my head around the wiring.
Thanks for your help
Thanks for your help
-
- Forum Guru
- Posts: 109
- Joined: Sat Mar 07, 2015 3:25 pm
Re: Grid Zero question
I couldn't wrap my head around Grid zero and mini grid. I've been running HBX since commissioning my system (Mate3, VFXR3648). I tried GZ and MG and low battery grid transfer and couldn't get the GZ and MG to work, the LBX would still have grid through to the loads (as I think it's supposed to). Does LBX just synch to grid (voltages same on grid outlet and "inverted" outlets) or does it actually use grid to power the loads.
Went back to HBX since it's tried and proven for me.
Went back to HBX since it's tried and proven for me.