Prioritise PV vs Grid
Moderators: OutBack Moderator Team, OutBack
-
- Forum Member
- Posts: 8
- Joined: Wed Apr 07, 2021 3:11 am
Prioritise PV vs Grid
I have an older system, which is sometimes run off-grid and sometimes grid tied:
Mate 3
2 x GVFX3048E
2 x FX80 48V
24 x 12v200aH batteries (Lead Acid)
6kW PV panels
At the moment I try not to Offset PV because we are charged for doing that. That might change in the near future.
When the load is greater than the PV I connect to the grid and the MATE "shares" the load between the PV and grid. Except sometimes it doesn't, it just ignores the PV and uses the grid.
Is there a way to prioritise the PV over the grid?
(Absorb voltage is set at 57.2, Float voltage at 54.4 and Sell voltage at 52.4)
Mate 3
2 x GVFX3048E
2 x FX80 48V
24 x 12v200aH batteries (Lead Acid)
6kW PV panels
At the moment I try not to Offset PV because we are charged for doing that. That might change in the near future.
When the load is greater than the PV I connect to the grid and the MATE "shares" the load between the PV and grid. Except sometimes it doesn't, it just ignores the PV and uses the grid.
Is there a way to prioritise the PV over the grid?
(Absorb voltage is set at 57.2, Float voltage at 54.4 and Sell voltage at 52.4)
-
- Forum Emperor
- Posts: 2237
- Joined: Sat Aug 28, 2004 6:28 pm
- My RE system: Outback - Garage roof:
- 8 (2x4) Evergreen 180's into one FM80 (2007/2020 - replaced MX60)
- 6 (2×3) ALEO S79-300's into one FM80 (2017)
- 2 grid-tied VFXR3524A-01's series stacked, replaced GVFX's (2020)
- 12 Surrette/Rolls 2V x 1766Ah (2007)
- Hub10.3, Mate3s, FNDC, RTS. Tigo ES maximizers on each PV module.
Westinghouse Solar - Barn roof: (2012)
- 30 (2x15) 235W panels with Enphase M215 microinverters, grid-tied
Outback Skybox - Barn roof: (2019)
- 14 Talesun 275W in series (DC array input to SB inverter/charger)
- 3 SimpliPhi 3.8 batteries, 48V, 225Ah total
- AC coupled input from 14 Talesun 275W, Enphase M215 microinverters
All self-designed and self-installed - Location: Chagrin Falls, Ohio
Re: Prioritise PV vs Grid
If your battery voltage is less than your float setting then all your PV will go to the battery, while grid covers the load.
https://smart.tigoenergy.com/p/pZXn7SZQyO45?date=2021-04-19
https://enlighten.enphaseenergy.com/public/systems/Hctc107221
https://enlighten.enphaseenergy.com/public/systems/Hctc107221
-
- Forum Member
- Posts: 8
- Joined: Wed Apr 07, 2021 3:11 am
Re: Prioritise PV vs Grid
Today I had 4kW coming in from the panels while off grid. Battery voltage was 52.6. I changed float voltages on both the inverters and charge controllers to 50.4. I then connected the grid. PV dropped to zero and input from grid was 4kW. The battery voltage was 54.4
So it seems that battery voltage higher than float has the opposite effect to what I want.....
So it seems that battery voltage higher than float has the opposite effect to what I want.....
-
- Forum Emperor
- Posts: 2237
- Joined: Sat Aug 28, 2004 6:28 pm
- My RE system: Outback - Garage roof:
- 8 (2x4) Evergreen 180's into one FM80 (2007/2020 - replaced MX60)
- 6 (2×3) ALEO S79-300's into one FM80 (2017)
- 2 grid-tied VFXR3524A-01's series stacked, replaced GVFX's (2020)
- 12 Surrette/Rolls 2V x 1766Ah (2007)
- Hub10.3, Mate3s, FNDC, RTS. Tigo ES maximizers on each PV module.
Westinghouse Solar - Barn roof: (2012)
- 30 (2x15) 235W panels with Enphase M215 microinverters, grid-tied
Outback Skybox - Barn roof: (2019)
- 14 Talesun 275W in series (DC array input to SB inverter/charger)
- 3 SimpliPhi 3.8 batteries, 48V, 225Ah total
- AC coupled input from 14 Talesun 275W, Enphase M215 microinverters
All self-designed and self-installed - Location: Chagrin Falls, Ohio
Re: Prioritise PV vs Grid
Do your FM80s have grid-tie mode enabled?
https://smart.tigoenergy.com/p/pZXn7SZQyO45?date=2021-04-19
https://enlighten.enphaseenergy.com/public/systems/Hctc107221
https://enlighten.enphaseenergy.com/public/systems/Hctc107221
- EA6LE-ONE
- Forum Guru
- Posts: 475
- Joined: Tue May 05, 2020 7:51 am
- My RE system: System 1:
MATE3s, 3 x Radian GS8048A,
6 x FLEXmax 100, HUB10,
2 x EnergyCell 48V 2700RE,
1 x FLEXnet DC, 6 x FLEXware ICS Plus,
78 x PANASONIC VBHN325SA17 325W
System 2:
MATE3s, Radian GS8048A,
2 x FLEXmax 100, HUB10
1 x EnergyCell 48V 2700RE,
1 x FLEXnet DC, 2 x FLEXware ICS
21 x PANASONIC VBHN325SA17 325W - Location: Providenciales, Turks & Caicos Isl.
Re: Prioritise PV vs Grid
set you inverters battery charger absorb and float 0.4V lower than on the CCs. also try to calibrate the voltage on CCs and inverters when is no sun production and no loads.WyattSmith101 wrote: ↑Sat Apr 10, 2021 4:39 am Today I had 4kW coming in from the panels while off grid. Battery voltage was 52.6. I changed float voltages on both the inverters and charge controllers to 50.4. I then connected the grid. PV dropped to zero and input from grid was 4kW. The battery voltage was 54.4
So it seems that battery voltage higher than float has the opposite effect to what I want.....
-
- Forum Member
- Posts: 8
- Joined: Wed Apr 07, 2021 3:11 am
Re: Prioritise PV vs Grid
Mike, yes they are and I can sell back but I don’t want to because we get charged for it.
-
- Forum Member
- Posts: 8
- Joined: Wed Apr 07, 2021 3:11 am
Re: Prioritise PV vs Grid
Eagle, what do you mean by calibrate?
- EA6LE-ONE
- Forum Guru
- Posts: 475
- Joined: Tue May 05, 2020 7:51 am
- My RE system: System 1:
MATE3s, 3 x Radian GS8048A,
6 x FLEXmax 100, HUB10,
2 x EnergyCell 48V 2700RE,
1 x FLEXnet DC, 6 x FLEXware ICS Plus,
78 x PANASONIC VBHN325SA17 325W
System 2:
MATE3s, Radian GS8048A,
2 x FLEXmax 100, HUB10
1 x EnergyCell 48V 2700RE,
1 x FLEXnet DC, 2 x FLEXware ICS
21 x PANASONIC VBHN325SA17 325W - Location: Providenciales, Turks & Caicos Isl.
Re: Prioritise PV vs Grid
on the inverters and CCs you can calibrate the battery voltage to have all reading the same value.
-
- Forum Emperor
- Posts: 2237
- Joined: Sat Aug 28, 2004 6:28 pm
- My RE system: Outback - Garage roof:
- 8 (2x4) Evergreen 180's into one FM80 (2007/2020 - replaced MX60)
- 6 (2×3) ALEO S79-300's into one FM80 (2017)
- 2 grid-tied VFXR3524A-01's series stacked, replaced GVFX's (2020)
- 12 Surrette/Rolls 2V x 1766Ah (2007)
- Hub10.3, Mate3s, FNDC, RTS. Tigo ES maximizers on each PV module.
Westinghouse Solar - Barn roof: (2012)
- 30 (2x15) 235W panels with Enphase M215 microinverters, grid-tied
Outback Skybox - Barn roof: (2019)
- 14 Talesun 275W in series (DC array input to SB inverter/charger)
- 3 SimpliPhi 3.8 batteries, 48V, 225Ah total
- AC coupled input from 14 Talesun 275W, Enphase M215 microinverters
All self-designed and self-installed - Location: Chagrin Falls, Ohio
Re: Prioritise PV vs Grid
So, with grid-tie mode enabled, are you saying that connecting to grid causes your FM80s' output to drop to zero? Or are you disabling grid tie to avoid selling? Because with grid-tie disabled I suspect that might be causing what you're seeing.WyattSmith101 wrote: ↑Sat Apr 10, 2021 6:11 am Mike, yes they are and I can sell back but I don’t want to because we get charged for it.
If that's the case you might try setting your inverters' AC input mode to generator instead of grid. That setting would prevent selling and possibly allow your FM80s to continue producing.
https://smart.tigoenergy.com/p/pZXn7SZQyO45?date=2021-04-19
https://enlighten.enphaseenergy.com/public/systems/Hctc107221
https://enlighten.enphaseenergy.com/public/systems/Hctc107221
-
- Forum Member
- Posts: 8
- Joined: Wed Apr 07, 2021 3:11 am
Re: Prioritise PV vs Grid
Mike, no I can sell without any problems but in certain circumstances when there is insufficient pv to cover the load if the grid is connected it will share (I think it’s called support), in other cases it will bypass the pv and use almost exclusively grid.
-
- Forum Member
- Posts: 8
- Joined: Wed Apr 07, 2021 3:11 am
Re: Prioritise PV vs Grid
Thanks for your assistance everybody. It seems Mike was right. If the battery had been partly discharged before I connect to the grid then the grid powers the load while the battery recharges with pv. Once the battery is charged it doesn’t switch to using pv for the load.
If the battery isn’t discharged before the grid is connected the load is shared between grid and pv.
This will become academic when I’m able to offset the pv from July, hopefully.
Thanks again.
If the battery isn’t discharged before the grid is connected the load is shared between grid and pv.
This will become academic when I’m able to offset the pv from July, hopefully.
Thanks again.
- EA6LE-ONE
- Forum Guru
- Posts: 475
- Joined: Tue May 05, 2020 7:51 am
- My RE system: System 1:
MATE3s, 3 x Radian GS8048A,
6 x FLEXmax 100, HUB10,
2 x EnergyCell 48V 2700RE,
1 x FLEXnet DC, 6 x FLEXware ICS Plus,
78 x PANASONIC VBHN325SA17 325W
System 2:
MATE3s, Radian GS8048A,
2 x FLEXmax 100, HUB10
1 x EnergyCell 48V 2700RE,
1 x FLEXnet DC, 2 x FLEXware ICS
21 x PANASONIC VBHN325SA17 325W - Location: Providenciales, Turks & Caicos Isl.
Re: Prioritise PV vs Grid
That might happen when you have the float and absorb voltages identical on CCs and inverters, both will try to keep float and if the inverter is trying to push the same voltage which can be marginally higher than CCs then the CCs will dial down the PV production. the fix for that is to have the float and absorb 0.4V lower on the inverter battery charging settings.WyattSmith101 wrote: ↑Sat Apr 10, 2021 6:35 am Mike, no I can sell without any problems but in certain circumstances when there is insufficient pv to cover the load if the grid is connected it will share (I think it’s called support), in other cases it will bypass the pv and use almost exclusively grid.
-
- Forum Emperor
- Posts: 2237
- Joined: Sat Aug 28, 2004 6:28 pm
- My RE system: Outback - Garage roof:
- 8 (2x4) Evergreen 180's into one FM80 (2007/2020 - replaced MX60)
- 6 (2×3) ALEO S79-300's into one FM80 (2017)
- 2 grid-tied VFXR3524A-01's series stacked, replaced GVFX's (2020)
- 12 Surrette/Rolls 2V x 1766Ah (2007)
- Hub10.3, Mate3s, FNDC, RTS. Tigo ES maximizers on each PV module.
Westinghouse Solar - Barn roof: (2012)
- 30 (2x15) 235W panels with Enphase M215 microinverters, grid-tied
Outback Skybox - Barn roof: (2019)
- 14 Talesun 275W in series (DC array input to SB inverter/charger)
- 3 SimpliPhi 3.8 batteries, 48V, 225Ah total
- AC coupled input from 14 Talesun 275W, Enphase M215 microinverters
All self-designed and self-installed - Location: Chagrin Falls, Ohio
Re: Prioritise PV vs Grid
Note Ea6le's post - he has probably identified why your system doesn't continue using PV once the battery is charged. Your inverter float setpoint is too close (or equal) to your FM80 float setpoint, and so the inverter takes over while the FMs back off. To repeat his advice, be sure the float settings on your FM80s are 0.4 volts higher than those on your inverter. That will keep them working.Once the battery is charged it doesn’t switch to using pv for the load.
https://smart.tigoenergy.com/p/pZXn7SZQyO45?date=2021-04-19
https://enlighten.enphaseenergy.com/public/systems/Hctc107221
https://enlighten.enphaseenergy.com/public/systems/Hctc107221
-
- Forum Czar
- Posts: 720
- Joined: Mon Jul 24, 2017 8:40 am
- My RE system: 8330 watts in three strings, Flexmax 60 x 3, Radian 8048A, GSLC load center, Mate 3S, Hub 10.3, FN-DC and 900 Amp, 48V Trojan T105-RE battery bank.
Re: Prioritise PV vs Grid
As part of my graduate work towards my Ph.D in Outback product support via this forum, I have read this thread. This is my 2 cents of observations. Outback has cleverly written into the charging algorithm software a period of time labelled "SILENT". When the charge controller or inverter's charger is in this period, there will be no charging or PV harvest, regardless of available PV or GRID power. This UGLY phase (my label for it, not Outback's) generally occurs after a period of absorption charging (possibly float charging too) and is present until the the RE-BULK voltage or RE-FLOAT voltage is reached for the batteries. So if you actually lowered your float , re-float and re-bulk voltages, and you were in the absorb part of the charge cycle, then after that timer is completed, the SILENT period is in effect until the next voltage setting is reached. And if your load is small, it may take a long time for the voltage to drop and therefore a lot of SILENT mode. Some of this behavior is written and illustrated in the Radian manual under the inverter's charger section.
In my case, I keep my inverter's charger on, but I have a low RE-BULK and RE-FLOAT voltage set for my batteries which they do not reach. Then during PV time, my chargers are in grid tied mode, BULK and the voltage rapidly exceeds the SELL voltage. Selling begins ( I have auto grid tie control disabled) and charging continues and SOC 100% is reached. I go to GRID ZERO in late afternoon and voltage spike of batteries finishes things off above the SELL voltage for the day. When PV is no longer present, my batteries run down to about 80% then I reconnect to the grid when utility prices decrease at 9 PM. But because my battery voltage never got as low as the inverter's RE-BULK or RE-FLOAT setting, no charge cycle begins until the next solar PV day starts.
I am starting my 5th year of Outback studies at present. Learning never stops.
In my case, I keep my inverter's charger on, but I have a low RE-BULK and RE-FLOAT voltage set for my batteries which they do not reach. Then during PV time, my chargers are in grid tied mode, BULK and the voltage rapidly exceeds the SELL voltage. Selling begins ( I have auto grid tie control disabled) and charging continues and SOC 100% is reached. I go to GRID ZERO in late afternoon and voltage spike of batteries finishes things off above the SELL voltage for the day. When PV is no longer present, my batteries run down to about 80% then I reconnect to the grid when utility prices decrease at 9 PM. But because my battery voltage never got as low as the inverter's RE-BULK or RE-FLOAT setting, no charge cycle begins until the next solar PV day starts.
I am starting my 5th year of Outback studies at present. Learning never stops.
- EA6LE-ONE
- Forum Guru
- Posts: 475
- Joined: Tue May 05, 2020 7:51 am
- My RE system: System 1:
MATE3s, 3 x Radian GS8048A,
6 x FLEXmax 100, HUB10,
2 x EnergyCell 48V 2700RE,
1 x FLEXnet DC, 6 x FLEXware ICS Plus,
78 x PANASONIC VBHN325SA17 325W
System 2:
MATE3s, Radian GS8048A,
2 x FLEXmax 100, HUB10
1 x EnergyCell 48V 2700RE,
1 x FLEXnet DC, 2 x FLEXware ICS
21 x PANASONIC VBHN325SA17 325W - Location: Providenciales, Turks & Caicos Isl.
Re: Prioritise PV vs Grid
the only silent period I see is from when absorb is reached and then the battery goes down to float voltage. but I am not selling to grid.pss wrote: ↑Sat Apr 10, 2021 12:40 pm As part of my graduate work towards my Ph.D in Outback product support via this forum, I have read this thread. This is my 2 cents of observations. Outback has cleverly written into the charging algorithm software a period of time labelled "SILENT". When the charge controller or inverter's charger is in this period, there will be no charging or PV harvest, regardless of available PV or GRID power. This UGLY phase (my label for it, not Outback's) generally occurs after a period of absorption charging (possibly float charging too) and is present until the the RE-BULK voltage or RE-FLOAT voltage is reached for the batteries. So if you actually lowered your float , re-float and re-bulk voltages, and you were in the absorb part of the charge cycle, then after that timer is completed, the SILENT period is in effect until the next voltage setting is reached. And if your load is small, it may take a long time for the voltage to drop and therefore a lot of SILENT mode. Some of this behavior is written and illustrated in the Radian manual under the inverter's charger section.
In my case, I keep my inverter's charger on, but I have a low RE-BULK and RE-FLOAT voltage set for my batteries which they do not reach. Then during PV time, my chargers are in grid tied mode, BULK and the voltage rapidly exceeds the SELL voltage. Selling begins ( I have auto grid tie control disabled) and charging continues and SOC 100% is reached. I go to GRID ZERO in late afternoon and voltage spike of batteries finishes things off above the SELL voltage for the day. When PV is no longer present, my batteries run down to about 80% then I reconnect to the grid when utility prices decrease at 9 PM. But because my battery voltage never got as low as the inverter's RE-BULK or RE-FLOAT setting, no charge cycle begins until the next solar PV day starts.
I am starting my 5th year of Outback studies at present. Learning never stops.