FXR3048 and FM60 updates and compatibility questions

General Talk

Moderators: OutBack, OutBack Moderator Team

rewired
Forum Member
Posts: 11
Joined: Fri Oct 23, 2020 7:53 pm
My RE system: 2x FlexMax60
OutBack GVFX3648 inverter
2x GSL 10kw LiFePO4 powerwalls (16S4P)
12x Suntech STP190S-24 panels (2280 watts @STC)
Honda EU7000is generator (gas)
Mate3s with hub4
2x 445 watt Canadian Solar panels
Location: St Croix US Virgin Islands

Re: FXR3048 and FM60 updates and compatibility questions

Post by rewired »

Thanks, everyone for the feedback and advice.
I've had the new panels and CC in place for about 2 weeks now and spent a fair amount of that time off grid to see how they would fare (and do some setting tweaking).

Here are the specs for my battery packs (I have 2 in parallel)
20220123_153840.jpg
20220123_153911.jpg
I've set my Absorb to 56.4v for 0.1 hours and both my float and sell at 55.2v.
This gives me charge voltage of 3.525v and float at 3.45v (16S4P configuration), both will within the safe voltage range for the cells.

I have the GVFX charger disabled and global charge control is set to 70A, but even on a very sunny day, in seeing max combined charge currents of about 58A (or about 0.29C based on the combined max charge rate of 200A). At this point, the batteries seen to be happy staying between 53.1v and 55.8v (except for their brief so at 56.4v).

According to USPS tracking, my FNDC should be delivered tomorrow and my electrician is scheduled to be here Wednesday to install it.

Once it's in place, I'll be able to provide an update on how things are going.
User avatar
Mike Curran
Forum Emperor
Posts: 2770
Joined: Sat Aug 28, 2004 6:28 pm
My RE system: Outback - Garage roof:
- 8 (2x4) Evergreen 180's into one FM80 (2007/2020 - replaced MX60)
- 6 (2×3) ALEO S79-300's into one FM80 (2017)
- 2 grid-tied VFXR3524A-01's series stacked, replaced GVFX's (2020)
- 12 Surrette/Rolls 2V x 1766Ah (2007)
- Hub10.3, Mate3s, FNDC, RTS. Tigo ES maximizers on each PV module.

Westinghouse Solar - Barn roof: (2012)
- 30 (2x15) 235W panels with Enphase M215 microinverters, grid-tied

Outback Skybox - Barn roof: (2019)
- 14 Talesun 275W in series (DC array input to SB inverter/charger)
- 3 SimpliPhi 3.8 batteries, 48V, 225Ah total
- AC coupled input from 14 Talesun 275W, Enphase M215 microinverters

Battery systems operate in grid-tied, net metering w/backup mode
All self-designed and self-installed
Location: Chagrin Falls, Ohio

Re: FXR3048 and FM60 updates and compatibility questions

Post by Mike Curran »

I've set my Absorb to 56.4v for 0.1 hours and both my float and sell at 55.2v.
Make sure your charge controllers are set to grid-tie mode. Setting them to grid-tied will automatically (and "artificially") raise your float setting to the Absorb setpoint, forcing your system to push up against the sell voltage and insuring you'll sell. Described here:
Screenshot_20220124-091049_Adobe Acrobat.jpg
While you're selling in this mode your FM60s will show they are in "Bulk", meaning they're trying to reach Absorb voltage but are being constrained by the sell setpoint.
https://ei.tigoenergy.com/p/pZXn7SZQyO45
https://enlighten.enphaseenergy.com/public/systems/Hctc107221
rewired
Forum Member
Posts: 11
Joined: Fri Oct 23, 2020 7:53 pm
My RE system: 2x FlexMax60
OutBack GVFX3648 inverter
2x GSL 10kw LiFePO4 powerwalls (16S4P)
12x Suntech STP190S-24 panels (2280 watts @STC)
Honda EU7000is generator (gas)
Mate3s with hub4
2x 445 watt Canadian Solar panels
Location: St Croix US Virgin Islands

Re: FXR3048 and FM60 updates and compatibility questions

Post by rewired »

Thanks, Mike!

I also figured out that I needed to turn off Automatic Charge Termination in the Global Charge Control settings on the Mate3s. Once the batteries were fully charged and I plugged in the FNDC, I was a bit freaked out when the CCs are showing almost no charging in full sun. Once I realized the CCs were showing a status of Charged, I remembered a post I'd read (that I think you'd posted a while back) about turning off ACT. Once I did that, the CCs started charging again.

Now if I can just figure out calibration on the FNDC..
rewired
Forum Member
Posts: 11
Joined: Fri Oct 23, 2020 7:53 pm
My RE system: 2x FlexMax60
OutBack GVFX3648 inverter
2x GSL 10kw LiFePO4 powerwalls (16S4P)
12x Suntech STP190S-24 panels (2280 watts @STC)
Honda EU7000is generator (gas)
Mate3s with hub4
2x 445 watt Canadian Solar panels
Location: St Croix US Virgin Islands

Re: FXR3048 and FM60 updates and compatibility questions

Post by rewired »

Reposting link I found to another thread with document regarding calibration of FNDC
viewtopic.php?f=28&t=12697&p=56958&hili ... ate#p56958

I'll see how the FNDC does over the next few days against other measurements, but wanted to go ahead and relink it here for future reference.