Search found 28 matches
- Sat Sep 12, 2026 11:02 am
- Forum: FLEXmax 100 AFCI
- Topic: Suggestions for New Array with (2) FM100s
- Replies: 7
- Views: 1065
Re: Suggestions for New Array with (2) FM100s
According to the sizing tool, looks like 5s3p is the sweet spot for 440w panels to safely max out the FM100. I'm going to see if there is a way to squeeze another two modules up there (30 total) so we can just run that to each charge controller. If not, we'll go with 430w and use 4s4p and 4s3p. Than...
- Fri Sep 11, 2026 8:31 pm
- Forum: FLEXmax 100 AFCI
- Topic: Suggestions for New Array with (2) FM100s
- Replies: 7
- Views: 1065
Re: Suggestions for New Array with (2) FM100s
Thanks for the info. I live in North County San Diego, so we get a few frosty mornings, but rarely below 35F, record cold is somewhere around 10F. I see…Splitting 28 panels evenly between the two controllers doesn’t leave many options for how to run them. Could I split it 12/16? Series of 4 on each?...
- Fri Sep 11, 2026 3:01 pm
- Forum: FLEXmax 100 AFCI
- Topic: Suggestions for New Array with (2) FM100s
- Replies: 7
- Views: 1065
Suggestions for New Array with (2) FM100s
I'm looking into replacing my aging and miss-matched solar array. I'd like to max out what our system can safely handle without making any other upgrades other than the modules and rewiring strings as needed. I have an off-grid 48v system with (2) FM100s, (2) GS8048 Radians and 600ah of Relion LiFeP...
- Wed Sep 09, 2026 8:42 pm
- Forum: Off Grid Applications
- Topic: Honda EU7000iS Settings for Backup Charging
- Replies: 18
- Views: 636
Re: Honda EU7000iS Settings for Backup Charging
Ok just tested those settings. 23A for the charge limit was too high, genny revved up to 6kw and quit. Settled on 18A for now, not really sure how that math works out…Mate shows 4.2kw coming from the generator, safe margin for error? Don’t want to push it to hard, but also don’t want to be idling al...
- Wed Sep 09, 2026 5:55 pm
- Forum: Off Grid Applications
- Topic: Honda EU7000iS Settings for Backup Charging
- Replies: 18
- Views: 636
Re: Honda EU7000iS Settings for Backup Charging
The rule of thumb is Generator continuous rating should equal Inverter continuous rating + charging current. That puts dual Radian external AC in the 30kW range. 5.5kW is at the bottom of the curve. 11kW would likely be OK for a "normal" load profile. Just buy a 2nd Honda and run them in ...
- Wed Sep 09, 2026 5:44 pm
- Forum: Off Grid Applications
- Topic: Honda EU7000iS Settings for Backup Charging
- Replies: 18
- Views: 636
Re: Honda EU7000iS Settings for Backup Charging
That makes sense. So I'd just need to Set the "Charger Operating Mode" to OFF on Inverter 2 (Slave) and change the Charger limit to 23A on Inverter 1 (Master).
- Wed Sep 09, 2026 5:16 pm
- Forum: Off Grid Applications
- Topic: Honda EU7000iS Settings for Backup Charging
- Replies: 18
- Views: 636
Re: Honda EU7000iS Settings for Backup Charging
One last thing...
Are the watts displayed on the Mate fairly accurate? If the 12A charger AC limit doesn't seem like it's delivering close to 5kw to the batteries, should I try increasing the limit?
Are the watts displayed on the Mate fairly accurate? If the 12A charger AC limit doesn't seem like it's delivering close to 5kw to the batteries, should I try increasing the limit?
- Wed Sep 09, 2026 5:12 pm
- Forum: Off Grid Applications
- Topic: Honda EU7000iS Settings for Backup Charging
- Replies: 18
- Views: 636
Re: Honda EU7000iS Settings for Backup Charging
Thankfully our system works great and is sufficient 99% of the time. We really just rely on the generator to keep everything alive in the middle of the night during the hottest weeks of summer (blasting AC) and darkest weeks of winter. We used to be AC Coupled, so I'm assuming that's why the Charger...
- Wed Sep 09, 2026 5:01 pm
- Forum: Off Grid Applications
- Topic: Honda EU7000iS Settings for Backup Charging
- Replies: 18
- Views: 636
Re: Honda EU7000iS Settings for Backup Charging
Thanks again. One last time to confirm the details... I'm changing the Gen Input AC Limit on both Radians to 24A. I'm changing the Charger AC Limit to 12A (half of the AC input limit, I think I had tried this before and it did overload at 23A) Support sounds like the ideal setup to keep from overloa...
- Wed Sep 09, 2026 4:40 pm
- Forum: Off Grid Applications
- Topic: Honda EU7000iS Settings for Backup Charging
- Replies: 18
- Views: 636
Re: Honda EU7000iS Settings for Backup Charging
I have (2) GS8048. One is master, one is slave. They both seem to have separate settings for AC/Gen input.
I always assumed those settings needed to match.
I always assumed those settings needed to match.
- Wed Sep 09, 2026 4:18 pm
- Forum: Off Grid Applications
- Topic: Honda EU7000iS Settings for Backup Charging
- Replies: 18
- Views: 636
Re: Honda EU7000iS Settings for Backup Charging
Thanks for the info. Just to confirm...
I'm going to change Gen Input AC Limit to 23A on both master and slave inverters. (previously at 14A)
Also changing Charger AC Limit to 10A on both master and slave inverters. (previously at 30A)
I'm going to change Gen Input AC Limit to 23A on both master and slave inverters. (previously at 14A)
Also changing Charger AC Limit to 10A on both master and slave inverters. (previously at 30A)
- Wed Sep 09, 2026 12:13 pm
- Forum: Off Grid Applications
- Topic: Honda EU7000iS Settings for Backup Charging
- Replies: 18
- Views: 636
Honda EU7000iS Settings for Backup Charging
We have an off-grid system that usually only relies on the generator for intermittent charging of the batteries when they get low at night. Usually not running many appliances when it's on, but lately have been trying to run a portable AC at night since San Diego has decided it is now Phoenix. Recen...
- Tue Dec 10, 2024 4:49 pm
- Forum: Off Grid Applications
- Topic: Batteries failing, off-grid ac coupled system - need advice
- Replies: 39
- Views: 9062
Re: Batteries failing, off-grid ac coupled system - need advice
Ok, did a shutdown this afternoon and got those connections checked and adjusted. Couldn't tell if that battery connection was in fact shorting on the shunt, but I moved my PV input to the other shunt anyway to give it some clearance. Also re-routed all the shunt wires to make sure they were further...
- Sun Dec 08, 2024 5:03 pm
- Forum: Off Grid Applications
- Topic: Batteries failing, off-grid ac coupled system - need advice
- Replies: 39
- Views: 9062
Re: Batteries failing, off-grid ac coupled system - need advice
Shunts are wired that way because installer initially had a shunt for each FM100, but then realized they had to be combined and the shunt needed to be sent to the other inverter. I think the wires were already cut at that point and it was easier to just send B to the master. Also, the perspective is...
- Sun Dec 08, 2024 4:12 pm
- Forum: Off Grid Applications
- Topic: Batteries failing, off-grid ac coupled system - need advice
- Replies: 39
- Views: 9062
Re: Batteries failing, off-grid ac coupled system - need advice
Thanks. That’s how I understood it. I meant that the amount of negative flow on shunt A did t’t seem right. Reason is that nothing additional was turned on in the house, just that the PV started coming in and we were getting more negative flow. .4kw-.6kw is what I’m seeing on the optics dashboard th...
- Sun Dec 08, 2024 1:04 pm
- Forum: Off Grid Applications
- Topic: Batteries failing, off-grid ac coupled system - need advice
- Replies: 39
- Views: 9062
Re: Batteries failing, off-grid ac coupled system - need advice
One last thing I forgot to double-check. I've got my FNDC hooked up and seems to be working decently enough (knowing it will never be completely accurate with my Li Fe batteries). I've got it connected as follows (I have stacked radians and 2 charge controllers) Shunt A White - Slave Radian Solid - ...
- Thu Dec 05, 2024 9:00 pm
- Forum: Off Grid Applications
- Topic: Batteries failing, off-grid ac coupled system - need advice
- Replies: 39
- Views: 9062
Re: Batteries failing, off-grid ac coupled system - need advice
Thanks. One issue we were chasing earlier was an arc fault on one of the FM100’s (turned out to be one of the Hyundai modules) but the installer checked all the connectors in the process. I suppose I could go double check all of them, but again…happy to not be fussing with it anymore. Just wanted to...
- Thu Dec 05, 2024 7:54 pm
- Forum: Off Grid Applications
- Topic: Batteries failing, off-grid ac coupled system - need advice
- Replies: 39
- Views: 9062
Re: Batteries failing, off-grid ac coupled system - need advice
Ok seems like I may be in the ballpark then. Thanks for the info. I actually do have a set of IR binoculars and see some hotspots on a few of my panels. I had my installer check one of them out and their response was that the voltage of the panel was still within acceptable level. Haven’t had them c...
- Thu Dec 05, 2024 10:44 am
- Forum: Off Grid Applications
- Topic: Batteries failing, off-grid ac coupled system - need advice
- Replies: 39
- Views: 9062
Re: Batteries failing, off-grid ac coupled system - need advice
Finally...over a year later and my system has been switched over to DC is running (almost) normally. Replacement batteries are happy with new charge parameters and haven't had to run our generator in months. However, I have a feeling that something isn't quite set right on either my FM100s or the Ma...
- Thu Sep 14, 2023 5:53 am
- Forum: Off Grid Applications
- Topic: Batteries failing, off-grid ac coupled system - need advice
- Replies: 39
- Views: 9062
Re: Batteries failing, off-grid ac coupled system - need advice
Good to know, I’ll adjust the AGS start voltage. Thanks.
- Wed Sep 13, 2023 9:40 pm
- Forum: Off Grid Applications
- Topic: Batteries failing, off-grid ac coupled system - need advice
- Replies: 39
- Views: 9062
Re: Batteries failing, off-grid ac coupled system - need advice
Thanks for all that. I've got the FNDC on order and I'll refer back when I'm able to do the install. I'll order the circuit breaker as well. Also, I notice you have the same generator I'm using. Can you let me know how you have it set up (or would suggest setting up for my inverters)? AGS, Input Mod...
- Wed Sep 13, 2023 4:59 pm
- Forum: Off Grid Applications
- Topic: Batteries failing, off-grid ac coupled system - need advice
- Replies: 39
- Views: 9062
Re: Batteries failing, off-grid ac coupled system - need advice
Here's what I've got going on inside each GSLC:
Inverter 1 Inverter 2
Inverter 1 Inverter 2
- Wed Sep 13, 2023 3:10 pm
- Forum: Off Grid Applications
- Topic: Batteries failing, off-grid ac coupled system - need advice
- Replies: 39
- Views: 9062
Re: Batteries failing, off-grid ac coupled system - need advice
Yes, both of them have a GSLC.
- Wed Sep 13, 2023 3:00 pm
- Forum: Off Grid Applications
- Topic: Batteries failing, off-grid ac coupled system - need advice
- Replies: 39
- Views: 9062
Re: Batteries failing, off-grid ac coupled system - need advice
Understood. The tech from Outback must have thought my 2 inverters were separate and not master/slave. You’re likely spot-on, I’ll confirm the system with the installer and move forward with the single FNDC. Thanks.
- Wed Sep 13, 2023 2:12 pm
- Forum: Off Grid Applications
- Topic: Batteries failing, off-grid ac coupled system - need advice
- Replies: 39
- Views: 9062
Re: Batteries failing, off-grid ac coupled system - need advice
Ok, I was just on the phone with Outback support this morning and they said (2) FNDCs were needed since we had (2) inverters, but he possibly could have been mistaken. To confirm, we have (2) 8048 inverters and (3) RB48V200 batteries. I’m not sure offhand how they specifically connected to each inve...