Search found 1415 matches
- Wed Sep 23, 2026 10:11 am
- Forum: Simpliphi
- Topic: FNDC SOC irrelevant to LiFePO4 voltage?
- Replies: 17
- Views: 14839
Re: FNDC SOC irrelevant to LiFePO4 voltage?
On a system that I acquired the maintenance of the reported SOC and voltage were significantly different. It is a 24V LFP bank that originally had 33 24V 50AH batteries. Batteries were configured with 2 strings of 6 and 3 strings of 7 connected to a bus bar with multiple different lengths of 4/0 ran...
- Sat Sep 12, 2026 8:42 am
- Forum: Off Grid Applications
- Topic: The breaker box from Hell
- Replies: 6
- Views: 545
Re: The breaker box from Hell
The reason for the large gauge wire is to minimize the voltage drop after the long run. The reason to use Al is cost. I just did an install where the house was 500' away. With a 60A draw, to keep in the ~3.5% voltage drop range required 3/0 Al or 1/0 Cu. Al URD (direct burial) Quadruplex cost $2,350...
- Tue Sep 08, 2026 4:27 pm
- Forum: OutBack
- Topic: Outback installer near Portland, Oregon
- Replies: 13
- Views: 953
Re: Outback installer near Portland, Oregon
There is one guy in my valley of 6 million who has a company of 10-20 employees and an off grid in the city house run by Outback equipment that is my installer. If you ever need help and it is not summer, I am available. We moved out of the Phoenix valley 15 years ago to 5,500 feet, where the deer ...
- Tue Aug 18, 2026 1:32 pm
- Forum: Third-Party Batteries
- Topic: looking for battery recommendations
- Replies: 17
- Views: 1401
- Mon Aug 17, 2026 8:34 pm
- Forum: Third-Party Batteries
- Topic: looking for battery recommendations
- Replies: 17
- Views: 1401
Re: looking for battery recommendations
I have primarily been installing either the Pytes V16 or Fortress eBoost. Both are 16kWh 300lb units with built-in heating, come with required inverter cabling and an outdoor rated housing. If batteries are below 40F in the morning the first solar is used to heat them. . With your current 430AH batt...
- Mon Aug 10, 2026 7:04 am
- Forum: OpticsRE
- Topic: Is OpticsRE working again?
- Replies: 56
- Views: 3192
Re: Is OpticsRE working again?
3-4 updates a day on my most critical system to monitor.
- Mon Aug 03, 2026 11:22 am
- Forum: Off Grid Applications
- Topic: SOC and Voltage disagree wildly
- Replies: 9
- Views: 1346
- Fri Jun 05, 2026 6:45 pm
- Forum: Photos of My OutBack Power System
- Topic: New PV Combiner
- Replies: 2
- Views: 6154
Re: New PV Combiner
or go to 500V and eliminate all those connections. 
- Tue May 12, 2026 11:41 am
- Forum: FLEXmax Charge Controllers
- Topic: 500w panels on an FM80
- Replies: 10
- Views: 7892
Re: 500w panels on an FM80
Ah, the beauty of new systems with up to 500V strings capable of feeding 20+ amps into one CC. Today, I usually end up using 10AWG wire unless it is a 200+ foot run and then use 8 AWG. I just took over a system where they ran 4/0 Cu about 200'.
- Mon May 11, 2026 7:57 pm
- Forum: OpticsRE
- Topic: LiPho battery explosion in Southern California
- Replies: 15
- Views: 10987
Re: LiPho battery explosion in Southern California
Not only did it take off the insulation but it melted the copper in places. Copper melts at 1,984F, it was definitely glowing.SumPowerRays wrote: ↑Mon May 11, 2026 1:25 pmep, the insulation melted off the conductor and turned the conductor into a glow bar
- Mon May 11, 2026 12:03 pm
- Forum: OpticsRE
- Topic: LiPho battery explosion in Southern California
- Replies: 15
- Views: 10987
Re: LiPho battery explosion in Southern California
At 5:58 in the video, look at the battery cables. There is no insulation left and there was no fire that burned the building. I would say there was a major overcurrent event of several thousand amps prior to the explosion. It was a beautiful building and clean looking install, just a little too anal...
- Thu Apr 09, 2026 5:20 am
- Forum: Off Grid Applications
- Topic: OOPS, Obsolete Panels
- Replies: 17
- Views: 10622
Re: OOPS, Obsolete Panels
Re: OOPS, Obsolete Panels by jkirkebo » Tue Apr 07, 2026 7:56 am raysun wrote: ↑Sat Mar 28, 2026 7:16 pm fcwlp wrote: ↑Sat Mar 28, 2026 5:20 pm JRHill wrote: ↑Sat Mar 28, 2026 1:25 pm The part of the roof that is usable for panels is limited. Three ~ 60" panels set lengthwise fits from the pit...
- Sun Apr 05, 2026 6:31 pm
- Forum: OpticsRE
- Topic: FM-100's shut off solar input at random times?
- Replies: 2
- Views: 7421
Re: FM-100's shut off solar input at random times?
It is likely doing an MPPT Sweep which is described in the FM100 manual. Basically trying to find the optimum voltage for maximum power. Could be do the shading or changing sun orientation.
- Sat Mar 28, 2026 5:20 pm
- Forum: Off Grid Applications
- Topic: OOPS, Obsolete Panels
- Replies: 17
- Views: 10622
Re: OOPS, Obsolete Panels
The part of the roof that is usable for panels is limited. Three ~ 60" panels set lengthwise fits from the pitch change to the peak. I have been using 550-watt panels lately that are 44" x 88". Could you put two in landscape mode (44" x 176") or portrait mode (88" x 88...
- Wed Mar 18, 2026 6:22 am
- Forum: Off Grid Applications
- Topic: Outback Radian Receiving 208V vs 240V – Compatibility Question
- Replies: 2
- Views: 7326
Re: Outback Radian Receiving 208V vs 240V – Compatibility Question
Get the manual for the generator. My mil surplus MEP-803 10kW can be configured as 120/208 three phase or 240v split phase. The bigger unit may not have that option.
- Mon Feb 16, 2026 10:23 am
- Forum: OutBack
- Topic: Looking for someone to support existing system
- Replies: 5
- Views: 8071
Re: Looking for someone to support existing system
In your case this is complicated as changing your inverter from off grid (VFX) to grid tied (GVFX) requires a circuit board change. This *might* be possible if you could find a nerd who can source that gear, reconfigure the inverter's wiring and accommodate the utility company permission to accompl...
- Wed Feb 11, 2026 1:27 pm
- Forum: Third-Party Batteries
- Topic: Relion rb24v 100 cold temperature charging
- Replies: 8
- Views: 8969
Re: Relion rb24v 100 cold temperature charging
I just installed two of the new Pytes V16 batteries yesterday and they now have tables for both discharging and charging as a function of temperature and SOC. I am sure Pytes understands LFP chemistry better than any of us and how to prolong the life of the batteries. Their BMS does not allow full c...
- Thu Feb 05, 2026 5:20 pm
- Forum: Off Grid Applications
- Topic: Lithium Upgrade recommendations please
- Replies: 11
- Views: 9698
Re: Lithium Upgrade recommendations please
Were these Helios and eBoost installs with Outback systems? Do you have a preference between the two batteries? Both were on non-Outback systems that supported closed loop communications. Helios is a little easier to setup. I have installed Pytes 48100R open loop on two OB systems (14 and 6 batteri...
- Sun Jan 18, 2026 1:58 pm
- Forum: OpticsRE
- Topic: VFX Inverters not Showing In OpticsRE
- Replies: 22
- Views: 13587
Re: VFX Inverters not Showing In OpticsRE
FYI, the VFX inverters are now showing up in OpticsRE. In "device manager" you have to select the VFX model. Just saved a service call to my customer.
- Tue Jan 06, 2026 7:21 am
- Forum: Grid Tie Applications
- Topic: Radian Settings for Time of Use Utility Billing and Lithium Batteries
- Replies: 6
- Views: 6637
Re: Radian Settings for Time of Use Utility Billing and Lithium Batteries
Grid tied mode is disabled on the MPPT. Rebulk is 51.6 I would read up on the grid-tie mode for the FM100s as it will make your system management easier. . At 51.6V rebulk the batteries are at ~20% SOC. I normally use 52 to 52.4V for rebulk on CCs and possibly higher depending on the system. For my...
- Mon Jan 05, 2026 8:10 pm
- Forum: Grid Tie Applications
- Topic: Radian Settings for Time of Use Utility Billing and Lithium Batteries
- Replies: 6
- Views: 6637
Re: Radian Settings for Time of Use Utility Billing and Lithium Batteries
I am set up very similar. I found by lowering the sell back voltage, I put myself in a situation where the batteries are never at a full SOC and go to a lower SOC each successive day until the BMS trips, so yes that can effect life of the battery. IME, when sell voltage is lowered, batteries never ...
- Tue Dec 30, 2025 2:52 pm
- Forum: Off Grid Applications
- Topic: Lithium Upgrade recommendations please
- Replies: 11
- Views: 9698
Re: Lithium Upgrade recommendations please
I have recently installed both Discover Helios and Fortress eBoost 16kWh batteries and will be picking more up this week. They retail list for mid $3K and do not require racking or multiple cables to bus bars. Nice thing is they are rated for outdoor installs, which saves considerable cost versus ot...
- Thu Dec 25, 2025 8:29 am
- Forum: OpticsRE
- Topic: VFX Inverters not Showing In OpticsRE
- Replies: 22
- Views: 13587
- Thu Dec 25, 2025 8:26 am
- Forum: OutBack
- Topic: I'd rather fight than switch
- Replies: 9
- Views: 9686
Re: I'd rather fight than switch
I have worked on Trace, Xantrex, Outback, Midnite, Victron, SMA, Magnum, Solar Edge, Enphase, Sigineer, Sungold, and MPP Solar systems. Which do you prefer? I would like the ability to be grid tied, have the battery charged going into the night, and once the sun comes up to charge to 100% and then ...
- Wed Dec 24, 2025 6:41 am
- Forum: OutBack
- Topic: I'd rather fight than switch
- Replies: 9
- Views: 9686
Re: I'd rather fight than switch
With 25 Sol-Ark's that I monitor (mostly 15Ks) I have never seen a jump like that. What I see on systems with LFP batteries in closed loop communication is a small jump from 90% to 100% with sometimes an intermediate ~95% step. I attribute this to the battery telling the Sol-Ark it is fully charged....